      fL4sH 0 @hardwarefreak last edited by

      @foxriver76 am idTag lag es nicht! Anscheind liegt das Problem beim Chargelimit in der RemoteStartTransaction. Wenn das Limit auf 0 gesetzt wird, beginnt er die RemoteStartTransaction mit folgendem Befehl Sending RemoteStartTransaction for /TACW1142021G1020: {"connectorId":1,"idTag":"1"} (ohne das ChargingProfil) und anschließend kann das Ladelimit wieder variabel eingestellt werden. Wird das LadeLimit vor dem Start gesetzt passiert nichts und dieser Befehl wird abgeschickt:
      Sending RemoteStartTransaction for /TACW1142021G1020: {"connectorId":1,"idTag":"1","chargingProfile":{"chargingProfileId":1,"stackLevel":0,"chargingProfilePurpose":"TxDefaultProfile","chargingProfileKind":"Recurring","recurrencyKind":"Daily","chargingSchedule":{"duration":86400,"startSchedule":"2013-01-01T00:00Z","chargingRateUnit":"A","chargingSchedulePeriod":[{"startPeriod":0,"limit":6}]}}}

      @hardwarefreak
      Ich habe auch Probleme mit der Firmware 1.5.2.
      Versuch mal dein Chargelimit auf 0 zu setzen und anschließend mit transactionActive=true.
      Bei mir sieht das dann so aus und der Ladevorgang kann über umwegen gestartet werden.

      ocpp.0 2022-02-14 21:37:41.814	debug	Sending RemoteStopTransaction for /TACW1142021G1020
      ocpp.0 2022-02-14 21:37:28.354	info	Received Status Notification from "/TACW1142021G1020": Charging
      ocpp.0 2022-02-14 21:37:28.353	debug	{"connectorId":1,"errorCode":"NoError","info":"null","status":"Charging","vendorErrorCode":"0x00","commandOcpp":"StatusNotification"}
      ocpp.0 2022-02-14 21:37:27.854	info	Received Status Notification from "/TACW1142021G1020": SuspendedEV
      ocpp.0 2022-02-14 21:37:27.854	debug	{"connectorId":1,"errorCode":"NoError","info":"null","status":"SuspendedEV","vendorErrorCode":"0x00","commandOcpp":"StatusNotification"}
      ocpp.0 2022-02-14 21:37:18.513	debug	Sending SetChargingProfile for /TACW1142021G1020
      ocpp.0 2022-02-14 21:37:17.917	info	Received MeterValues from "/TACW1142021G1020"
      ocpp.0 2022-02-14 21:37:17.916	debug	{"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-02-14T20:37:17.000Z","sampledValue":[{"value":"233.90","context":"Transaction.Begin","format":"Raw","measurand":"Voltage","phase":"L1-N","unit":"V"},{"value":"0.0","context":"Transaction.Begin","format":"Raw","measurand":"Current.Import","phase":"L1","unit":"A"},{"value":"0","context":"Transaction.Begin","format":"Raw","measurand":"Power.Active.Import","phase":"L1","unit":"W"},{"value":"234.20","context":"Transaction.Begin","format":"Raw","measurand":"Voltage","phase":"L2-N","unit":"V"},{"value":"0.0","context":"Transaction.Begin","format":"Raw","measurand":"Current.Import","phase":"L2","unit":"A"},{"value":"0","context":"Transaction.Begin","format":"Raw","measurand":"Power.Active.Import","phase":"L2","unit":"W"},{"value":"234.00","context":"Transaction.Begin","format":"Raw","measurand":"Voltage","phase":"L3-N","unit":"V"},{"value":"0.0","context":"Transaction.Begin","format":"Raw","measurand":"Current.Import","phase":"L3","unit":"A"},{"value":"0","context":"Transaction.Begin","format":"Raw","measurand":"Power.Active.Import","phase":"L3","unit":"W"},{"value":"0","context":"Transaction.Begin","format":"Raw","measurand":"Energy.Active.Import.Register","unit":"Wh"},{"value":"10","context":"Transaction.Begin","format":"Raw","measurand":"Current.Offered","unit":"A"}]}],"commandOcpp":"MeterValues"}
      ocpp.0 2022-02-14 21:37:09.510	info	Received Status Notification from "/TACW1142021G1020": SuspendedEVSE
      ocpp.0 2022-02-14 21:37:09.509	debug	{"connectorId":1,"errorCode":"NoError","info":"null","status":"SuspendedEVSE","vendorErrorCode":"0x00","commandOcpp":"StatusNotification"}
      ocpp.0 2022-02-14 21:37:09.011	info	Received Start transaction from "/TACW1142021G1020"
      ocpp.0 2022-02-14 21:37:09.010	debug	{"connectorId":1,"idTag":"1","meterStart":0,"timestamp":"2022-02-14T20:37:07.000Z","commandOcpp":"StartTransaction"}
      ocpp.0 2022-02-14 21:37:08.510	info	Received Status Notification from "/TACW1142021G1020": Charging
      ocpp.0 2022-02-14 21:37:08.510	debug	{"connectorId":1,"errorCode":"NoError","info":"null","status":"Charging","vendorErrorCode":"0x00","commandOcpp":"StatusNotification"}
      ocpp.0 2022-02-14 21:37:08.010	info	Received Status Notification from "/TACW1142021G1020": SuspendedEV
      ocpp.0 2022-02-14 21:37:08.010	debug	{"connectorId":1,"errorCode":"NoError","info":"null","status":"SuspendedEV","vendorErrorCode":"0x00","commandOcpp":"StatusNotification"}
      ocpp.0 2022-02-14 21:37:07.500	debug	Sending RemoteStartTransaction for /TACW1142021G1020: {"connectorId":1,"idTag":"1"}
      
      1 Reply Last reply Reply Quote 0
      • F
        fL4sH 0 @hardwarefreak last edited by

        @hardwarefreak said in Alpha Testing: OCPP Wallbox Adapter:

        @fl4sh-0
        Worüber bringe ich dein Script für die PV-Überschussladung zur Ausführung im iobroker?

        Das kannst du über Javascript im iobroker ausführen. Du musst dann nur deine Variablen hinterlegen.
        Ich kann dir das sonst auch als Blockly-Script zur Verfügung stellen.

        1 Reply Last reply Reply Quote 0
        • Y
          yymsc last edited by yymsc

          Hallo,
          bin gerade auch am testen der OCPP Funktionen meiner Wallbox. Es handelt sich um eine M3W von Wallbox24.de welche OCPP 1.6 unterstützt.
          Leider funktioniert das setzen des Ladestroms mittels chargeLimit bei mir nicht. Weder zu Begin der Transaktion noch während des Ladens.
          Hab dazu mal ein Debug-Log angehängt, wäre echt prima wenn das funktionieren würde dann könnte ich nämlich das PV-Überschussladen angehen.
          Das Log zeigt den Start des Ladevorgangs durch Setzen von transactionActive=true mit chargeLimit=6. Wie man in den folgenden Zeilen sieht steigt der Ladestrom dennoch auf über 16A an.
          Wenn ich danach das chargeLimit ändere steht im Log nur 'Sending SetChargingProfile for /61689674063277'

          2022-03-21 16:42:57.217  - debug: ocpp.0 (12131) Sending RemoteStartTransaction for /61689674063277: {"connectorId":1,"idTag":"1","chargingProfile":{"chargingProfileId":1,"stackLevel":0,"chargingProfilePurpose":"TxDefaultProfile","chargingProfileKind":"Recurring","recurrencyKind":"Daily","chargingSchedule":{"duration":86400,"startSchedule":"2013-01-01T00:00Z","chargingRateUnit":"A","chargingSchedulePeriod":[{"startPeriod":0,"limit":7}]}}}
          2022-03-21 16:42:57.945  - debug: ocpp.0 (12131) {"connectorId":1,"idTag":"1","meterStart":2103200,"timestamp":"2022-03-21T15:42:56.333Z","reservationId":0,"commandOcpp":"StartTransaction"}
          2022-03-21 16:42:57.946  - info: ocpp.0 (12131) Received Start transaction from "/61689674063277"
          2022-03-21 16:42:58.393  - debug: ocpp.0 (12131) {"connectorId":1,"errorCode":"NoError","status":"Preparing","commandOcpp":"StatusNotification"}
          2022-03-21 16:42:58.394  - info: ocpp.0 (12131) Received Status Notification from "/61689674063277": Preparing
          2022-03-21 16:42:59.088  - debug: ocpp.0 (12131) {"connectorId":1,"errorCode":"NoError","status":"Charging","commandOcpp":"StatusNotification"}
          2022-03-21 16:42:59.089  - info: ocpp.0 (12131) Received Status Notification from "/61689674063277": Charging
          2022-03-21 16:43:08.729  - debug: ocpp.0 (12131) {"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-03-21T15:43:07.333Z","sampledValue":[{"measurand":"Energy.Active.Import.Register","unit":"Wh","value":"2103200"},{"measurand":"Power.Active.Import","unit":"kW","value":"0.1"},{"measurand":"Temperature","unit":"Celsius","value":"35"},{"measurand":"Voltage","phase":"L1-N","unit":"V","value":"238.2"},{"measurand":"Voltage","phase":"L2-N","unit":"V","value":"238.0"},{"measurand":"Voltage","phase":"L3-N","unit":"V","value":"238.4"},{"measurand":"Current.Import","phase":"L1","unit":"A","value":"0.8"},{"measurand":"Current.Import","phase":"L2","unit":"A","value":"0.2"},{"measurand":"Current.Import","phase":"L3","unit":"A","value":"0.2"}]}],"commandOcpp":"MeterValues"}
          2022-03-21 16:43:08.730  - info: ocpp.0 (12131) Received MeterValues from "/61689674063277"
          2022-03-21 16:43:18.513  - debug: ocpp.0 (12131) {"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-03-21T15:43:18.333Z","sampledValue":[{"measurand":"Energy.Active.Import.Register","unit":"Wh","value":"2103200"},{"measurand":"Power.Active.Import","unit":"kW","value":"2.4"},{"measurand":"Temperature","unit":"Celsius","value":"35"},{"measurand":"Voltage","phase":"L1-N","unit":"V","value":"236.8"},{"measurand":"Voltage","phase":"L2-N","unit":"V","value":"236.6"},{"measurand":"Voltage","phase":"L3-N","unit":"V","value":"238.7"},{"measurand":"Current.Import","phase":"L1","unit":"A","value":"5.3"},{"measurand":"Current.Import","phase":"L2","unit":"A","value":"5.3"},{"measurand":"Current.Import","phase":"L3","unit":"A","value":"0.2"}]}],"commandOcpp":"MeterValues"}
          2022-03-21 16:43:18.514  - info: ocpp.0 (12131) Received MeterValues from "/61689674063277"
          2022-03-21 16:43:25.355  - debug: ocpp.0 (12131) {"commandOcpp":"Heartbeat"}
          2022-03-21 16:43:25.356  - debug: ocpp.0 (12131) Received heartbeat from "/61689674063277"
          2022-03-21 16:43:28.575  - debug: ocpp.0 (12131) {"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-03-21T15:43:27.333Z","sampledValue":[{"measurand":"Energy.Active.Import.Register","unit":"Wh","value":"2103200"},{"measurand":"Power.Active.Import","unit":"kW","value":"9.1"},{"measurand":"Temperature","unit":"Celsius","value":"35"},{"measurand":"Voltage","phase":"L1-N","unit":"V","value":"236.2"},{"measurand":"Voltage","phase":"L2-N","unit":"V","value":"235.8"},{"measurand":"Voltage","phase":"L3-N","unit":"V","value":"236.0"},{"measurand":"Current.Import","phase":"L1","unit":"A","value":"12.8"},{"measurand":"Current.Import","phase":"L2","unit":"A","value":"12.9"},{"measurand":"Current.Import","phase":"L3","unit":"A","value":"12.9"}]}],"commandOcpp":"MeterValues"}
          2022-03-21 16:43:28.577  - info: ocpp.0 (12131) Received MeterValues from "/61689674063277"
          2022-03-21 16:43:38.564  - debug: ocpp.0 (12131) {"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-03-21T15:43:38.333Z","sampledValue":[{"measurand":"Energy.Active.Import.Register","unit":"Wh","value":"2103300"},{"measurand":"Power.Active.Import","unit":"kW","value":"11.4"},{"measurand":"Temperature","unit":"Celsius","value":"35"},{"measurand":"Voltage","phase":"L1-N","unit":"V","value":"235.6"},{"measurand":"Voltage","phase":"L2-N","unit":"V","value":"235.1"},{"measurand":"Voltage","phase":"L3-N","unit":"V","value":"235.8"},{"measurand":"Current.Import","phase":"L1","unit":"A","value":"16.1"},{"measurand":"Current.Import","phase":"L2","unit":"A","value":"16.2"},{"measurand":"Current.Import","phase":"L3","unit":"A","value":"16.2"}]}],"commandOcpp":"MeterValues"}
          2022-03-21 16:43:38.565  - info: ocpp.0 (12131) Received MeterValues from "/61689674063277"
          2022-03-21 16:43:44.563  - debug: ocpp.0 (12131) Sending SetChargingProfile for /61689674063277
          2022-03-21 16:43:48.532  - debug: ocpp.0 (12131) {"connectorId":1,"transactionId":1,"meterValue":[{"timestamp":"2022-03-21T15:43:48.333Z","sampledValue":[{"measurand":"Energy.Active.Import.Register","unit":"Wh","value":"2103300"},{"measurand":"Power.Active.Import","unit":"kW","value":"11.4"},{"measurand":"Temperature","unit":"Celsius","value":"35"},{"measurand":"Voltage","phase":"L1-N","unit":"V","value":"234.7"},{"measurand":"Voltage","phase":"L2-N","unit":"V","value":"235.4"},{"measurand":"Voltage","phase":"L3-N","unit":"V","value":"235.8"},{"measurand":"Current.Import","phase":"L1","unit":"A","value":"16.2"},{"measurand":"Current.Import","phase":"L2","unit":"A","value":"16.3"},{"measurand":"Current.Import","phase":"L3","unit":"A","value":"16.2"}]}],"commandOcpp":"MeterValues"}
          
          
          foxriver76 1 Reply Last reply Reply Quote 0
          • foxriver76
            foxriver76 Developer @yymsc last edited by

            @yymsc finde für die leider kein Dokument welches den Umfang der ocpp Implementierung beschreibt.

            Y 1 Reply Last reply Reply Quote 0
            • Y
              yymsc @foxriver76 last edited by

              @foxriver76 said in Alpha Testing: OCPP Wallbox Adapter:

              @yymsc finde für die leider kein Dokument welches den Umfang der ocpp Implementierung beschreibt.

              alles klar, sowas hatte ich fast befürchtet... Trotzdem vielen Dank für die schnelle Antwort !!!

              1 Reply Last reply Reply Quote 0
              • foxriver76
                foxriver76 Developer last edited by

                Ich habe eben eine 0.4.0 veröffentlicht, diese unterstützt nun Authentifizierung. Sprich wenn in den Adapteroptionen Auth aktiviert wird und ein Passwort/Username vergeben wird und ein Client abweichende Credentials bereitstellt, wird die Verbindung abgelehnt.

                1 Reply Last reply Reply Quote 0
                • M
                  Matti1993 @schwimbi last edited by

                  @schwimbi Hey ich hab auch eine Terra AC, wie hast du alles genau gemacht ?
                  komme kein Schritt weiter.

                  T 1 Reply Last reply Reply Quote 0
                  • T
                    thoko @Matti1993 last edited by

                    @foxriver76 Zunächst einmal Hochachtung für dein Engagement und diesen Adapter!

                    Ich verwende zwei Wallboxen Pulsar Plus mit konfiguriertem Power Sharing (Verbindung per CAN).

                    Testweise habe ich für eine Wallbox eine Instanz OCPP eingerichtet. Nun ist die Wallbox gesperrt (LEDs und auch in der App gelb -> gesperrt). Im Objektbaum wird availability=true, status=Available und transactionActive=true angezeigt.

                    Ändere ich im Objektbaum transactionActive zunächst auf false und dann wieder auf true, so ändert sich status auf Preparing und die Sperre ist aufgehoben (LEDs und auch in der App grün-> bereit).

                    Allerdings wird nach 2 Minuten status wieder auf Available gesetzt und die Station ist wieder gesperrt:

                    2022-05-11 09:32:05.215  - debug: ocpp.0 (23470) Sending RemoteStopTransaction for /Admin
                    2022-05-11 09:32:16.891  - debug: ocpp.0 (23470) Sending RemoteStartTransaction for /Admin: {"connectorId":1,"idTag":"1","chargingProfile":{"chargingProfileId":1,"stackLevel":0,"chargingProfilePurpose":"TxDefaultProfile","chargingProfileKind":"Recurring","recurrencyKind":"Daily","chargingSchedule":{"duration":86400,"startSchedule":"2013-01-01T00:00Z","chargingRateUnit":"A","chargingSchedulePeriod":[{"startPeriod":0,"limit":32}]}}}
                    2022-05-11 09:32:18.160  - debug: ocpp.0 (23470) {"info":"","vendorId":"com.wallbox","vendorErrorCode":"","connectorId":1,"errorCode":"NoError","status":"Preparing","timestamp":"2022-05-11T07:32:17Z","commandOcpp":"StatusNotification"}
                    2022-05-11 09:32:18.161  - info: ocpp.0 (23470) Received Status Notification from "/Admin": Preparing
                    2022-05-11 09:32:48.419  - debug: ocpp.0 (23470) {"commandOcpp":"Heartbeat"}
                    2022-05-11 09:32:48.421  - debug: ocpp.0 (23470) Received heartbeat from "/Admin"
                    2022-05-11 09:33:43.581  - debug: ocpp.0 (23470) {"commandOcpp":"Heartbeat"}
                    2022-05-11 09:33:43.584  - debug: ocpp.0 (23470) Received heartbeat from "/Admin"
                    2022-05-11 09:34:20.221  - debug: ocpp.0 (23470) {"info":"","vendorId":"com.wallbox","vendorErrorCode":"","connectorId":1,"errorCode":"NoError","status":"Available","timestamp":"2022-05-11T07:34:19Z","commandOcpp":"StatusNotification"}
                    2022-05-11 09:34:20.224  - info: ocpp.0 (23470) Received Status Notification from "/Admin": Available
                    

                    Siehst du eine Möglichkeit, das zu verhindern?

                    foxriver76 1 Reply Last reply Reply Quote 0
                    • foxriver76
                      foxriver76 Developer @thoko last edited by

                      @thoko sagte in Alpha Testing: OCPP Wallbox Adapter:

                      Allerdings wird nach 2 Minuten status wieder auf Available gesetzt und die Station ist wieder gesperrt:

                      Bei mir ist dieses Verhalten nur wenn aktuell kein Auto angestöpselt ist, passiert das bei dir bei einem aktiven Ladevorgang?

                      T 2 Replies Last reply Reply Quote 0
                      • T
                        thoko @foxriver76 last edited by

                        @foxriver76 Das werde ich gleich mal ausprobieren. Stay tuned 🙂

                        T 1 Reply Last reply Reply Quote 0
                        • T
                          thoko @thoko last edited by

                          @foxriver76 Wenn ich den Ladestecker einstecke, ändert sich status auf Preparing, aber die Wallbox bleibt blockiert. Erst wenn ich transactionActive erst auf von true auf false und dann wieder auf true setze, ändert sich status über SuspendedEV auf Charging (LEDs und auch in der App grün-> laden).

                          Ohne OCPP musste ich eben nur den Ladestecker einstecken und konnte direkt laden.

                          Sehr cool ist aber, dass ich alle 5 Minuten die aktuell geladenen (oder bezogenen?) Wh geliefert bekomme. In der App wird mir das ja erst nach dem Tageswechsel dargestellt.

                          T 1 Reply Last reply Reply Quote 0
                          • T
                            thoko @foxriver76 last edited by

                            @foxriver76 Hier noch der Log-Auszug:

                            2022-05-11 10:36:21.451  - debug: ocpp.0 (23470) {"info":"","vendorId":"com.wallbox","vendorErrorCode":"","connectorId":1,"errorCode":"NoError","status":"Preparing","timestamp":"2022-05-11T08:36:21Z","commandOcpp":"StatusNotification"}
                            2022-05-11 10:36:21.452  - info: ocpp.0 (23470) Received Status Notification from "/Admin": Preparing
                            [heartbeat]
                            2022-05-11 10:38:37.317  - debug: ocpp.0 (23470) Sending RemoteStopTransaction for /Admin
                            2022-05-11 10:38:55.321  - debug: ocpp.0 (23470) Sending RemoteStartTransaction for /Admin: {"connectorId":1,"idTag":"1","chargingProfile":{"chargingProfileId":1,"stackLevel":0,"chargingProfilePurpose":"TxDefaultProfile","chargingProfileKind":"Recurring","recurrencyKind":"Daily","chargingSchedule":{"duration":86400,"startSchedule":"2013-01-01T00:00Z","chargingRateUnit":"A","chargingSchedulePeriod":[{"startPeriod":0,"limit":32}]}}}
                            [heartbeat]
                            2022-05-11 10:38:56.680  - debug: ocpp.0 (23470) {"meterStop":0,"timestamp":"2022-05-11T08:38:56Z","idTag":"1","transactionData":[],"reason":"Other","transactionId":0,"commandOcpp":"StopTransaction"}
                            2022-05-11 10:38:56.684  - info: ocpp.0 (23470) Received stop transaction from "/Admin"
                            2022-05-11 10:38:56.837  - debug: ocpp.0 (23470) {"connectorId":1,"meterStart":0,"idTag":"1","timestamp":"2022-05-11T08:38:56Z","commandOcpp":"StartTransaction"}
                            2022-05-11 10:38:56.838  - info: ocpp.0 (23470) Received Start transaction from "/Admin"
                            2022-05-11 10:38:57.216  - debug: ocpp.0 (23470) {"info":"","vendorId":"com.wallbox","vendorErrorCode":"","connectorId":1,"errorCode":"NoError","status":"SuspendedEV","timestamp":"2022-05-11T08:38:56Z","commandOcpp":"StatusNotification"}
                            2022-05-11 10:38:57.217  - info: ocpp.0 (23470) Received Status Notification from "/Admin": SuspendedEV
                            2022-05-11 10:39:00.061  - debug: ocpp.0 (23470) {"info":"","vendorId":"com.wallbox","vendorErrorCode":"","connectorId":1,"errorCode":"NoError","status":"Charging","timestamp":"2022-05-11T08:38:59Z","commandOcpp":"StatusNotification"}
                            2022-05-11 10:39:00.064  - info: ocpp.0 (23470) Received Status Notification from "/Admin": Charging
                            [heartbeat]
                            2022-05-11 10:42:14.940  - debug: ocpp.0 (23470) {"meterValue":[{"timestamp":"2022-05-11T08:42:13Z","sampledValue":[{"format":"Raw","location":"Outlet","context":"Sample.Periodic","measurand":"Energy.Active.Import.Register","unit":"Wh","value":"393"}]}],"connectorId":1,"transactionId":1,"commandOcpp":"MeterValues"}
                            2022-05-11 10:42:14.942  - info: ocpp.0 (23470) Received MeterValues from "/Admin"
                            [heartbeat]
                            2022-05-11 10:47:14.693  - debug: ocpp.0 (23470) {"meterValue":[{"timestamp":"2022-05-11T08:47:13Z","sampledValue":[{"format":"Raw","location":"Outlet","context":"Sample.Periodic","measurand":"Energy.Active.Import.Register","unit":"Wh","value":"1020"}]}],"connectorId":1,"transactionId":1,"commandOcpp":"MeterValues"}
                            2022-05-11 10:47:14.695  - info: ocpp.0 (23470) Received MeterValues from "/Admin"
                            
                            1 Reply Last reply Reply Quote 0
                            • T
                              thoko @thoko last edited by

                              @thoko said in Alpha Testing: OCPP Wallbox Adapter:

                              (LEDs und auch in der App grün-> laden)

                              Natürlich blau, nicht grün.

                              1 Reply Last reply Reply Quote 0
                              • foxriver76
                                foxriver76 Developer last edited by

                                Ja, mit availability kannst du die Box quasi in den richtigen Lock Zustand setzen, das mache ich z. B. nicht. Wenn die grundsätzlich true ist, kannst du alleine über transactionActive steuern.

                                N 1 Reply Last reply Reply Quote 0
                                • N
                                  NimrodMatze @foxriver76 last edited by

                                  @foxriver76

                                  Hallo Foxriver, vielen Dank vorab für den tollen Adapter. Bin schon oft auf der Suche gewesen meine beiden ABB Terra (mit RFID) Wallboxen irgendwie zu regeln. Dachte eigentlich das ABB mal hier was auf TCP/IP realisiert und ich die OpenWB Software verwende. Es sieht aber danach aus das hier keine Anstregungen unternommen werden.

                                  Allgemein bin ich echt begeistert was sich alles so mit IO Broker realisieren lässt. Fuchse mich da auch immer mehr und mehr rein. Es macht sehr viel Spaß. Ich bin da aber ehrlich gesagt noch nicht so weit und aktuell nur Anfänger. Ein paar Programmierungen nach Anleitung sind da schon möglich aber dann hört es schon auf.

                                  Der OCPP Adapter läuft schon bei mir. Die Wallbox(en) reagieren auch schon entsprechend. Nur der Befehl über transactionAction läuft noch nicht so ganz rund so das ich die Wallbox einfach an und wieder ausschalte. Wenn ich den transactionAction Befehl setzte, wird die Ladung als finish deglariert und gut ist. Ein neuer Start geht nur über den RFID Startbefehl an der Wallbox selbst (Oder ich stelle es einfach auf ohne Authentifizierung in der APP) und es wird wieder geladen und aufsummiert nachdem ich den Stecker vom Auto wieder angeschlossen habe .
                                  Die variable Amperevorgabe geht immer. Hier ist mir aufgefallen das ich einfach die Ampervorgabe <6A stellen kann und der Ladevorgang pausiert wird. Nach Vorgabe >6A geht es wieder weiter und es wird auch fleißig wieder weitergezählt. Also hier könnte man bestimmt einfach ein Skript schreiben um die PV Überschussladung hinzukriegen. Ich denke dies bekomme ich irgendwann auch wohl mal hin nachdem ich die restlichen 111 Tutorials mir angesehen habe 😉

                                  In meinem Fall wäre es nun denke ich auch einfacher, wenn mann die ABB Wallboxen via MQTT und der OpenWB Software kombiniert. In der OpenWB sind die Funktionen schon echt gut ausgereift. Also IOBroker mit dem OCPP Server und Anbindung an die OpenWB via MQTT. Hat dies schon einer gemacht? Wenn ja wie?

                                  Beste Grüße

                                  1 Reply Last reply Reply Quote 0
                                  • H
                                    HEINDUSA last edited by

                                    Hier findet man eine gute OCPP Dokumentation, vielleicht hilft es ja jemandem...
                                    Ist in diesem Fall der Bender controller.

                                    https://office.elinc.de/dokumentation#occp_parameter_zuordnung

                                    1 Reply Last reply Reply Quote 0
                                    • B
                                      baeckerman83 last edited by baeckerman83

                                      Hi!

                                      Ich habe auch eine Terra Box von ABB und wollte diese jetzt mit iobroker verbinden. Leider benötige ich aber in Terra Config ein Zertifikat:
                                      "1.Format supported:'.pfx','.cer','.pem'
                                      2.Encoding format supported:Basic64"

                                      Was habt ihr da hoch geladen? Ich habe mit openssl verschiedene Zertifikate generiert, leider klappte aber nichts. 😞 Danach kann ich ja erst den tollen Adapter ausprobieren.

                                      Edit: Hat sich erledigt, falls noch mal jemand sucht. Das Protokoll muss auf ws stehen und nicht auf wss.

                                      1 Reply Last reply Reply Quote 1
                                      • B
                                        baeckerman83 last edited by

                                        Nun habe ich die Wallbox verbunden und es sieht alles gut aus.
                                        Eine Frage habe ich, kann ich denn mehrer Autos unterscheiden?
                                        Ich habe verstanden, dass du alle Werte die es gibt weg schreibst. Oder gibt es noch Werte die noch nicht weg geschrieben werden?

                                        Dann müsste ich mir die mal anzeigen lassen....

                                        foxriver76 1 Reply Last reply Reply Quote 0
                                        • foxriver76
                                          foxriver76 Developer @baeckerman83 last edited by

                                          @baeckerman83 sagte in Alpha Testing: OCPP Wallbox Adapter:

                                          Eine Frage habe ich, kann ich denn mehrer Autos unterscheiden?

                                          Nein, der Charger bekommt im Normalfall keine Daten von deinem Auto. Für viele neuere Autos gibt es allerdings auch Adapter, villt. hilft das weiter.

                                          B 1 Reply Last reply Reply Quote 0
                                          • B
                                            baeckerman83 @foxriver76 last edited by baeckerman83

                                            @foxriver76 Danke für deine schnelle Antwort. Das ist schade. Hatte gehofft, das wird ne ID ausgetauscht. Dann hätte man auch was bauen können statt RFID Chip über diese ID freischalten. Aber gut, dann weiß ich nur wieviel meine Autos geladen haben.

                                            Ich habe noch eine Fragen.
                                            Ich wolle jetzt den Energie Stand auslesen, und zwar per NodeRed. Damit ich ihn immer Speichern kann wenn der Status wieder auf "Available" springt. Leider bekomm ich aber statt den Value aber: ""Object for state ocpp.1..Wally.meterValues.Energy_Active_Import_Register do not exist""

                                            Kann Energy_Active_Import_Register denn nicht einfach ausgelesen werden? In der Objekt Liste ist der Wert gesetzt und ich kann ihn auch sehen.

                                            Edit: Ich glaube mein Problem ist das /, aber wie bekomme ich das Weg aus der ID: "ocpp.1./Wally.meterValues.Energy_Active_Import_Register"

                                            foxriver76 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            601
                                            Online

                                            31.6k
                                            Users

                                            79.5k
                                            Topics

                                            1.3m
                                            Posts

                                            adapter ocpp wallbox
                                            48
                                            439
                                            70433
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo