Skip to content
  • Home
  • Aktuell
  • Tags
  • 0 Ungelesen 0
  • Kategorien
  • Unreplied
  • Beliebt
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Standard: (Kein Skin)
  • Kein Skin
Einklappen
ioBroker Logo

Community Forum

donate donate
  1. ioBroker Community Home
  2. Deutsch
  3. ioBroker Allgemein
  4. Adapter "smartmeter"

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.6k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.1k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    2.8k

Adapter "smartmeter"

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
3.6k Beiträge 280 Kommentatoren 2.4m Aufrufe 161 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • E Offline
    E Offline
    easymeter
    schrieb am zuletzt editiert von
    #470

    so, smartmeter angehalten und PI (mit deaktivierten Adapter) rebootet, leider ohne erfolg.
    2624_log5.txt

    1 Antwort Letzte Antwort
    0
    • apollon77A Offline
      apollon77A Offline
      apollon77
      schrieb am zuletzt editiert von
      #471

      Dann alle overwrites raus, Request Response (bidirektional) als Transport und dann nochmal log. Fangen wir nochmal bei 0 an

      Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

      • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
      • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
      1 Antwort Letzte Antwort
      0
      • E Offline
        E Offline
        easymeter
        schrieb am zuletzt editiert von
        #472

        ich habe die Änderungen eingetragen anbei einmal die Screenshots.

        Der LOG liegt auch bei
        2624_einstellungen1.jpg
        2624_einstellungen2.jpg
        2624_log6.txt

        1 Antwort Letzte Antwort
        0
        • apollon77A Offline
          apollon77A Offline
          apollon77
          schrieb am zuletzt editiert von
          #473

          Versuch bitte jetzt mal Mode-Override wieder auf B zu setzen, aber nur das ändern!

          Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

          • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
          • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
          1 Antwort Letzte Antwort
          0
          • J Offline
            J Offline
            joergg
            schrieb am zuletzt editiert von
            #474

            Guten Morgen,

            habe eben folgendes getestet:

            D0: Mode Overwrite = Use Mode defined by device

            Debug-Log hierzu:

            ! D0: Mode Overwrite = Use Mode defined by device
            ! host.HomeServer 2017-05-08 08:34:57.519 info Restart adapter system.adapter.smartmeter.0 because enabled
            ! host.HomeServer 2017-05-08 08:34:57.519 error instance system.adapter.smartmeter.0 terminated with code 0 (OK)
            ! smartmeter.0 2017-05-08 08:34:56.987 debug SERIALPORT CLOSE
            ! smartmeter.0 2017-05-08 08:34:56.987 warn Exception: Error: SerialResponseTransport do not support sending of Data!
            ! smartmeter.0 2017-05-08 08:34:56.987 error Error: SerialResponseTransport do not support sending of Data! at Error (native) at SerialPort. (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\transports\SerialResponseTransport.js:77:27) at emitOne (events.js:96:13) at SerialPort.emit (events.js:188:7) at SerialPort.raw (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\serialport\lib\parsers.js:7:13)
            ! smartmeter.0 2017-05-08 08:34:56.987 error uncaught exception: SerialResponseTransport do not support sending of Data!
            ! smartmeter.0 2017-05-08 08:34:56.987 debug CURRENT PROCESS STEP 3 IN ISPROCESSCOMPLETE: false
            ! smartmeter.0 2017-05-08 08:34:56.987 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
            ! smartmeter.0 2017-05-08 08:34:56.987 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
            ! smartmeter.0 2017-05-08 08:34:56.987 debug MATCH-RESULT SIGNON: '/EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032941.' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
            ! smartmeter.0 2017-05-08 08:34:56.987 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
            ! smartmeter.0 2017-05-08 08:34:54.955 debug SET MESSAGE TIMEOUT TIMER: 120000
            ! smartmeter.0 2017-05-08 08:34:54.955 debug SERIALPORT OPEN
            ! smartmeter.0 2017-05-08 08:34:54.877 debug CREATE SERIALPORT: 9600 7 1 even
            ! smartmeter.0 2017-05-08 08:34:54.877 debug SmartmeterObis options: {'debug':2,'protocol':'D0Protocol','transport':'SerialResponseTransport','requestInterval':'60','transportSerialPort':'COM3','transportSerialBaudrate':9600,'transportSerialDataBits':7,'transportSerialStopBits':1,'transportSerialParity':'even','transportSerialMessageTimeout':null,'protocolD0WakeupCharacters':0,'obisFallbackMedium':1}
            ! smartmeter.0 2017-05-08 08:34:54.877 info starting. Version 0.5.8 in C:/ioBroker/node_modules/iobroker.smartmeter, node: v6.10.2
            ! host.HomeServer 2017-05-08 08:34:53.361 info instance system.adapter.smartmeter.0 started with pid 4964

            Gruß joergg

            1 Antwort Letzte Antwort
            0
            • apollon77A Offline
              apollon77A Offline
              apollon77
              schrieb am zuletzt editiert von
              #475

              Bitte alle beide Update vom Github installieren

              @easymeter: ggf ohne den protocol-Overwrite

              Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

              • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
              • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
              1 Antwort Letzte Antwort
              0
              • J Offline
                J Offline
                joergg
                schrieb am zuletzt editiert von
                #476

                Kann es sein, dass Du nicht alle Dateien eingequellt hast.

                Wenn ich wie folgt mit npm abrufe, habe ich immer noch die 0.5.8 mit den Fehlern.

                Abruf aus GitHub:

                npm install iobroker.smartmeter –production --prefix "C:/ioBroker"

                Gruß joergg

                1 Antwort Letzte Antwort
                0
                • apollon77A Offline
                  apollon77A Offline
                  apollon77
                  schrieb am zuletzt editiert von
                  #477

                  Version vom Github installieren ist was anderes als com npm!

                  Admin, das dritte Icon von Links, dann dort smartmeter auswählen

                  Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

                  • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
                  • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
                  1 Antwort Letzte Antwort
                  0
                  • J Offline
                    J Offline
                    joergg
                    schrieb am zuletzt editiert von
                    #478

                    Ich habe die Webseite auf (localhost:8081).

                    Aktiviere die Karte "Adapters".

                    Klicke auf das dritte Icon von Links mit dem GitHub-Logo.

                    In der Dropdownbox finde ich kein "smartmeter"-Adapter.

                    Sorry, aber was mache ich falsch?

                    Gruß joergg

                    1 Antwort Letzte Antwort
                    0
                    • J Offline
                      J Offline
                      joergg
                      schrieb am zuletzt editiert von
                      #479

                      Habe den Adapter jetzt manuell von GitHub aktualisiert.

                      Der Adapter hat jetzt die Versionsnummer 0.5.9.

                      Der Fehler kommt aber immer noch vor, seltener, aber es gibt ihn noch.

                      Debug-Log:

                      ! Press Ctrl+A and Ctrl+C to copy log to clipboard and click with mouse anywhere to close.
                      ! host.HomeServer 2017-05-08 10:37:54.873 info Restart adapter system.adapter.smartmeter.0 because enabled
                      ! host.HomeServer 2017-05-08 10:37:54.873 error instance system.adapter.smartmeter.0 terminated with code 0 (OK)
                      ! smartmeter.0 2017-05-08 10:37:54.859 info terminating
                      ! smartmeter.0 2017-05-08 10:37:54.308 debug SERIALPORT CLOSE
                      ! smartmeter.0 2017-05-08 10:37:54.293 warn 1-0:0.0.0255
                      ! smartmeter.0 2017-05-08 10:37:54.293 warn
                      ! smartmeter.0 2017-05-08 10:37:54.293 warn Exception: Error: Invalid Obis String EMH5–--eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at SerialPort.raw (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\serialport\lib\parsers.js:7:13)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at SerialPort.emit (events.js:188:7)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at emitOne (events.js:96:13)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at SerialPort. (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\transports\SerialResponseTransport.js:63:41)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at D0Protocol.handleMessage (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\protocols\D0Protocol.js:157:27)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at D0Protocol.prepareResult (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\protocols\D0Protocol.js:198:31)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error at new ObisMeasurement (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\ObisMeasurement.js:46:23)
                      ! smartmeter.0 2017-05-08 10:37:54.293 error 1-0:0.0.0
                      255
                      ! smartmeter.0 2017-05-08 10:37:54.293 error
                      ! smartmeter.0 2017-05-08 10:37:54.293 error Error: Invalid Obis String EMH5----eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:37:54.293 error 1-0:0.0.0255
                      ! smartmeter.0 2017-05-08 10:37:54.293 error
                      ! smartmeter.0 2017-05-08 10:37:54.293 error uncaught exception: Invalid Obis String EMH5----eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:37:54.277 debug CURRENT PROCESS STEP 4 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:37:54.277 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:37:54.277 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0
                      255(331200-5009810)\r\n1-0:1.8.1255(032942.0358)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n/EMH5----eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0361)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0361)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n','EMH5----eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0361)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n']
                      ! smartmeter.0 2017-05-08 10:37:54.277 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug !
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug 0-0:96.1.255
                      255(0000680476)
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug 1-0:96.5.5255(80)
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug 1-0:1.8.1
                      255(032942.0358)
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug 1-0:0.0.0255(331200-5009810)
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug OVERWRITE D0-MODE C WITH A
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug MATCH-RESULT SIGNON: '/EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0
                      255(331200-5009810)\r\n1-0:1.8.1255(032942.0358)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
                      ! smartmeter.0 2017-05-08 10:37:51.998 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:37:50.818 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:37:50.818 debug SERIALPORT OPEN
                      ! smartmeter.0 2017-05-08 10:36:50.724 debug SERIALPORT CLOSE
                      ! smartmeter.0 2017-05-08 10:36:50.718 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:36:50.717 debug SCHEDULE NEXT RUN IN 60s
                      ! smartmeter.0 2017-05-08 10:36:50.717 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:36:50.716 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:36:50.716 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:36:50.716 info Received 4 values, 4 updated
                      ! smartmeter.0 2017-05-08 10:36:50.716 debug Set State 0-0:96_1_255
                      255.value = 0000680476
                      ! smartmeter.0 2017-05-08 10:36:50.715 debug Set State 0-0:96_1_255255.rawvalue = 0000680476
                      ! smartmeter.0 2017-05-08 10:36:50.715 debug Create State 0-0:96_1_255
                      255.value
                      ! smartmeter.0 2017-05-08 10:36:50.715 debug Create State 0-0:96_1_255255.rawvalue
                      ! smartmeter.0 2017-05-08 10:36:50.714 debug Create Channel 0-0:96_1_255
                      255 with name Factory number
                      ! smartmeter.0 2017-05-08 10:36:50.713 debug 0-0:96.1.255255: Factory number = 0000680476
                      ! smartmeter.0 2017-05-08 10:36:50.711 debug Set State 1-0:96_5_5
                      255.value = 80
                      ! smartmeter.0 2017-05-08 10:36:50.710 debug Set State 1-0:96_5_5255.rawvalue = 80
                      ! smartmeter.0 2017-05-08 10:36:50.709 debug Create State 1-0:96_5_5
                      255.value
                      ! smartmeter.0 2017-05-08 10:36:50.708 debug Create State 1-0:96_5_5255.rawvalue
                      ! smartmeter.0 2017-05-08 10:36:50.708 debug Create Channel 1-0:96_5_5
                      255 with name Status
                      ! smartmeter.0 2017-05-08 10:36:50.708 debug 1-0:96.5.5255: Status = 80
                      ! smartmeter.0 2017-05-08 10:36:50.707 debug Set State 1-0:1_8_1
                      255.value = 032942.0282
                      ! smartmeter.0 2017-05-08 10:36:50.707 debug Set State 1-0:1_8_1255.rawvalue = 032942.0282
                      ! smartmeter.0 2017-05-08 10:36:50.706 debug Create State 1-0:1_8_1
                      255.value
                      ! smartmeter.0 2017-05-08 10:36:50.706 debug Create State 1-0:1_8_1255.rawvalue
                      ! smartmeter.0 2017-05-08 10:36:50.706 debug Create Channel 1-0:1_8_1
                      255 with name Zählerstand 1 Summe Wirkarbeit Bezug + (T1)
                      ! smartmeter.0 2017-05-08 10:36:50.705 debug 1-0:1.8.1255: Zählerstand 1 Summe Wirkarbeit Bezug + (T1) = 032942.0282
                      ! smartmeter.0 2017-05-08 10:36:50.704 debug Set State 1-0:0_0_0
                      255.value = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:36:50.702 debug Set State 1-0:0_0_0255.rawvalue = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:36:50.701 debug Create State 1-0:0_0_0
                      255.value
                      ! smartmeter.0 2017-05-08 10:36:50.701 debug Create State 1-0:0_0_0255.rawvalue
                      ! smartmeter.0 2017-05-08 10:36:50.699 debug Create Channel 1-0:0_0_0
                      255 with name Meter owner number
                      ! smartmeter.0 2017-05-08 10:36:50.699 debug 1-0:0.0.0255: Meter owner number = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:36:50.696 debug STORE DATA
                      ! smartmeter.0 2017-05-08 10:36:50.691 debug CURRENT PROCESS STEP 4 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:50.691 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:36:50.691 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0
                      255(331200-5009810)\r\n1-0:1.8.1255(032942.0282)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0282)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n','1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0282)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n']
                      ! smartmeter.0 2017-05-08 10:36:50.690 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:50.577 debug
                      ! smartmeter.0 2017-05-08 10:36:50.577 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:36:50.577 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:36:50.576 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:36:50.576 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:36:50.575 debug OVERWRITE D0-MODE C WITH A
                      ! smartmeter.0 2017-05-08 10:36:50.574 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:50.573 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:36:50.572 debug MATCH-RESULT SIGNON: '/EMH5–--eHZ-E0018E\r\n\r\n' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
                      ! smartmeter.0 2017-05-08 10:36:50.571 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:49.623 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:36:49.620 debug SERIALPORT OPEN
                      ! smartmeter.0 2017-05-08 10:36:49.541 debug CREATE SERIALPORT: 9600 7 1 even
                      ! smartmeter.0 2017-05-08 10:36:49.536 debug SmartmeterObis options: {'debug':2,'protocol':'D0Protocol','transport':'SerialResponseTransport','requestInterval':'60','transportSerialPort':'com3','transportSerialBaudrate':9600,'transportSerialDataBits':7,'transportSerialStopBits':1,'transportSerialParity':'even','transportSerialMessageTimeout':null,'protocolD0WakeupCharacters':0,'protocolD0ModeOverwrite':'A','obisFallbackMedium':1}
                      ! smartmeter.0 2017-05-08 10:36:49.532 info starting. Version 0.5.9 in C:/ioBroker/node_modules/iobroker.smartmeter, node: v6.10.3
                      ! smartmeter.0 2017-05-08 10:36:49.492 debug statesDB connected
                      ! smartmeter.0 2017-05-08 10:36:49.450 debug objectDB connected
                      ! host.HomeServer 2017-05-08 10:36:41.372 info instance system.adapter.smartmeter.0 started with pid 5312
                      ! host.HomeServer 2017-05-08 10:36:11.144 info Restart adapter system.adapter.smartmeter.0 because enabled
                      ! host.HomeServer 2017-05-08 10:36:11.144 error instance system.adapter.smartmeter.0 terminated with code 0 (OK)
                      ! smartmeter.0 2017-05-08 10:36:11.108 info terminating
                      ! smartmeter.0 2017-05-08 10:36:10.606 debug SERIALPORT CLOSE
                      ! smartmeter.0 2017-05-08 10:36:10.590 warn 1-0:0.0.0
                      255
                      ! smartmeter.0 2017-05-08 10:36:10.590 warn
                      ! smartmeter.0 2017-05-08 10:36:10.590 warn Exception: Error: Invalid Obis String EMH5–--eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at SerialPort.raw (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\serialport\lib\parsers.js:7:13)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at SerialPort.emit (events.js:188:7)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at emitOne (events.js:96:13)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at SerialPort. (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\transports\SerialResponseTransport.js:63:41)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at D0Protocol.handleMessage (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\protocols\D0Protocol.js:157:27)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at D0Protocol.prepareResult (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\protocols\D0Protocol.js:198:31)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error at new ObisMeasurement (C:\ioBroker\node_modules\iobroker.smartmeter\node_modules\smartmeter-obis\lib\ObisMeasurement.js:46:23)
                      ! smartmeter.0 2017-05-08 10:36:10.590 error 1-0:0.0.0255
                      ! smartmeter.0 2017-05-08 10:36:10.590 error
                      ! smartmeter.0 2017-05-08 10:36:10.590 error Error: Invalid Obis String EMH5----eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:36:10.590 error 1-0:0.0.0
                      255
                      ! smartmeter.0 2017-05-08 10:36:10.590 error
                      ! smartmeter.0 2017-05-08 10:36:10.590 error uncaught exception: Invalid Obis String EMH5----eHZ-E0018E
                      ! smartmeter.0 2017-05-08 10:36:10.575 debug CURRENT PROCESS STEP 4 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:10.575 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:36:10.575 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0231)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n/EMH5----eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0234)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0234)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n','EMH5----eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0234)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n']
                      ! smartmeter.0 2017-05-08 10:36:10.575 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug !
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug 0-0:96.1.255255(0000680476)
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug 1-0:96.5.5
                      255(80)
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug 1-0:1.8.1255(032942.0231)
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug 1-0:0.0.0
                      255(331200-5009810)
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug OVERWRITE D0-MODE C WITH A
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug MATCH-RESULT SIGNON: '/EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0231)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
                      ! smartmeter.0 2017-05-08 10:36:08.078 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:36:07.216 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:36:07.216 debug SERIALPORT OPEN
                      ! smartmeter.0 2017-05-08 10:35:07.121 debug SERIALPORT CLOSE
                      ! smartmeter.0 2017-05-08 10:35:07.120 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:35:07.119 debug SCHEDULE NEXT RUN IN 60s
                      ! smartmeter.0 2017-05-08 10:35:07.119 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:35:07.119 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:35:07.119 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:35:07.118 info Received 4 values, 1 updated
                      ! smartmeter.0 2017-05-08 10:35:07.118 debug Data for 0-0:96_1_255255 unchanged
                      ! smartmeter.0 2017-05-08 10:35:07.118 debug 0-0:96.1.255
                      255: Factory number = 0000680476
                      ! smartmeter.0 2017-05-08 10:35:07.117 debug Data for 1-0:96_5_5255 unchanged
                      ! smartmeter.0 2017-05-08 10:35:07.117 debug 1-0:96.5.5
                      255: Status = 80
                      ! smartmeter.0 2017-05-08 10:35:07.116 debug Set State 1-0:1_8_1255.value = 032942.0159
                      ! smartmeter.0 2017-05-08 10:35:07.115 debug Set State 1-0:1_8_1
                      255.rawvalue = 032942.0159
                      ! smartmeter.0 2017-05-08 10:35:07.115 debug 1-0:1.8.1255: Zählerstand 1 Summe Wirkarbeit Bezug + (T1) = 032942.0159
                      ! smartmeter.0 2017-05-08 10:35:07.115 debug Data for 1-0:0_0_0
                      255 unchanged
                      ! smartmeter.0 2017-05-08 10:35:07.114 debug 1-0:0.0.0255: Meter owner number = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:35:07.114 debug STORE DATA
                      ! smartmeter.0 2017-05-08 10:35:07.113 debug CURRENT PROCESS STEP 4 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.113 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.112 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0
                      255(331200-5009810)\r\n1-0:1.8.1255(032942.0159)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0159)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n','1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0159)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n']
                      ! smartmeter.0 2017-05-08 10:35:07.112 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.077 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0
                      255(331200-5009810)\r\n1-0:1.8.1255(032942.0159)\r\n1-0:96.5.5255(80)\r\n' -> null
                      ! smartmeter.0 2017-05-08 10:35:07.076 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug 1-0:96.5.
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug 1-0:1.8.1255(032942.0159)
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug 1-0:0.0.0
                      255(331200-5009810)
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug OVERWRITE D0-MODE C WITH A
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug MATCH-RESULT SIGNON: '/EMH5–--eHZ-E0018E\r\n\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0159)\r\n1-0:96.5.' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
                      ! smartmeter.0 2017-05-08 10:35:07.062 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:35:06.049 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:35:06.047 debug SERIALPORT OPEN
                      ! smartmeter.0 2017-05-08 10:34:05.985 debug SERIALPORT CLOSE
                      ! smartmeter.0 2017-05-08 10:34:05.967 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:34:05.966 debug SCHEDULE NEXT RUN IN 60s
                      ! smartmeter.0 2017-05-08 10:34:05.966 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:34:05.966 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:34:05.965 debug CURRENT PROCESS STEP 10 IN ISPROCESSCOMPLETE: true
                      ! smartmeter.0 2017-05-08 10:34:05.965 info Received 4 values, 4 updated
                      ! smartmeter.0 2017-05-08 10:34:05.964 debug Set State 0-0:96_1_255255.value = 0000680476
                      ! smartmeter.0 2017-05-08 10:34:05.964 debug Set State 0-0:96_1_255
                      255.rawvalue = 0000680476
                      ! smartmeter.0 2017-05-08 10:34:05.964 debug Create State 0-0:96_1_255255.value
                      ! smartmeter.0 2017-05-08 10:34:05.964 debug Create State 0-0:96_1_255
                      255.rawvalue
                      ! smartmeter.0 2017-05-08 10:34:05.963 debug Create Channel 0-0:96_1_255255 with name Factory number
                      ! smartmeter.0 2017-05-08 10:34:05.963 debug 0-0:96.1.255
                      255: Factory number = 0000680476
                      ! smartmeter.0 2017-05-08 10:34:05.963 debug Set State 1-0:96_5_5255.value = 80
                      ! smartmeter.0 2017-05-08 10:34:05.962 debug Set State 1-0:96_5_5
                      255.rawvalue = 80
                      ! smartmeter.0 2017-05-08 10:34:05.962 debug Create State 1-0:96_5_5255.value
                      ! smartmeter.0 2017-05-08 10:34:05.962 debug Create State 1-0:96_5_5
                      255.rawvalue
                      ! smartmeter.0 2017-05-08 10:34:05.961 debug Create Channel 1-0:96_5_5255 with name Status
                      ! smartmeter.0 2017-05-08 10:34:05.960 debug 1-0:96.5.5
                      255: Status = 80
                      ! smartmeter.0 2017-05-08 10:34:05.960 debug Set State 1-0:1_8_1255.value = 032942.0081
                      ! smartmeter.0 2017-05-08 10:34:05.959 debug Set State 1-0:1_8_1
                      255.rawvalue = 032942.0081
                      ! smartmeter.0 2017-05-08 10:34:05.959 debug Create State 1-0:1_8_1255.value
                      ! smartmeter.0 2017-05-08 10:34:05.958 debug Create State 1-0:1_8_1
                      255.rawvalue
                      ! smartmeter.0 2017-05-08 10:34:05.956 debug Create Channel 1-0:1_8_1255 with name Zählerstand 1 Summe Wirkarbeit Bezug + (T1)
                      ! smartmeter.0 2017-05-08 10:34:05.955 debug 1-0:1.8.1
                      255: Zählerstand 1 Summe Wirkarbeit Bezug + (T1) = 032942.0081
                      ! smartmeter.0 2017-05-08 10:34:05.954 debug Set State 1-0:0_0_0255.value = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:34:05.952 debug Set State 1-0:0_0_0
                      255.rawvalue = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:34:05.951 debug Create State 1-0:0_0_0255.value
                      ! smartmeter.0 2017-05-08 10:34:05.950 debug Create State 1-0:0_0_0
                      255.rawvalue
                      ! smartmeter.0 2017-05-08 10:34:05.948 debug Create Channel 1-0:0_0_0255 with name Meter owner number
                      ! smartmeter.0 2017-05-08 10:34:05.947 debug 1-0:0.0.0
                      255: Meter owner number = 331200-5009810
                      ! smartmeter.0 2017-05-08 10:34:05.944 debug STORE DATA
                      ! smartmeter.0 2017-05-08 10:34:05.939 debug CURRENT PROCESS STEP 4 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.938 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.938 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0081)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n' -> ['1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0081)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n','1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0081)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n']
                      ! smartmeter.0 2017-05-08 10:34:05.937 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.900 debug MATCH-RESULT DATA: '\r\n1-0:0.0.0255(331200-5009810)\r\n1-0:1.8.1255(032942.0081)\r\n1-0:96.5.5255(80)\r\n' -> null
                      ! smartmeter.0 2017-05-08 10:34:05.900 debug CURRENT PROCESS STEP 4 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.822 debug
                      ! smartmeter.0 2017-05-08 10:34:05.822 debug REMAINING DATA AFTER MESSAGE HANDLING:
                      ! smartmeter.0 2017-05-08 10:34:05.822 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:34:05.822 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:34:05.821 debug CURRENT PROCESS STEP 4 IN ISPROCESSCOMPLETE: false
                      ! smartmeter.0 2017-05-08 10:34:05.820 debug OVERWRITE D0-MODE C WITH A
                      ! smartmeter.0 2017-05-08 10:34:05.819 debug CURRENT PROCESS STEP 2 IN HANDLEMESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.818 debug PAUSE READING SERIALPORT TO HANDLE MESSAGE
                      ! smartmeter.0 2017-05-08 10:34:05.818 debug MATCH-RESULT SIGNON: '200-5009810)\r\n1-0:1.8.1
                      255(032942.0078)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255255(0000680476)\r\n!\r\n/EMH5–--eHZ-E0018E\r\n\r\n' -> ['/EMH5–--eHZ-E0018E\r\n','/EMH5----eHZ-E0018E']
                      ! smartmeter.0 2017-05-08 10:34:05.816 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! host.HomeServer 2017-05-08 10:34:04.157 warn instance system.adapter.smartmeter.0 already running with pid 7784
                      ! smartmeter.0 2017-05-08 10:34:03.666 debug MATCH-RESULT SIGNON: '200-5009810)\r\n1-0:1.8.1255(032942.0078)\r\n1-0:96.5.5255(80)\r\n0-0:96.1.255*255(0000680476)\r\n!\r\n' -> null
                      ! smartmeter.0 2017-05-08 10:34:03.666 debug CURRENT PROCESS STEP 0 IN CHECKMESSAGE
                      ! smartmeter.0 2017-05-08 10:34:03.561 debug SET MESSAGE TIMEOUT TIMER: 120000
                      ! smartmeter.0 2017-05-08 10:34:03.559 debug SERIALPORT OPEN
                      ! smartmeter.0 2017-05-08 10:34:03.474 debug CREATE SERIALPORT: 9600 7 1 even
                      ! smartmeter.0 2017-05-08 10:34:03.474 debug SmartmeterObis options: {'debug':2,'protocol':'D0Protocol','transport':'SerialResponseTransport','requestInterval':'60','transportSerialPort':'com3','transportSerialBaudrate':9600,'transportSerialDataBits':7,'transportSerialStopBits':1,'transportSerialParity':'even','transportSerialMessageTimeout':null,'protocolD0WakeupCharacters':0,'protocolD0ModeOverwrite':'A','obisFallbackMedium':1}
                      ! smartmeter.0 2017-05-08 10:34:03.474 info starting. Version 0.5.9 in C:/ioBroker/node_modules/iobroker.smartmeter, node: v6.10.3
                      ! smartmeter.0 2017-05-08 10:34:03.442 debug statesDB connected
                      ! smartmeter.0 2017-05-08 10:34:03.396 debug objectDB connected
                      ! host.HomeServer 2017-05-08 10:34:01.938 info instance system.adapter.smartmeter.0 started with pid 7784
                      ! host.HomeServer 2017-05-08 10:34:01.663 info instance system.adapter.smartmeter.0 terminated with code null ()
                      ! host.HomeServer 2017-05-08 10:34:01.662 warn instance system.adapter.smartmeter.0 terminated due to SIGTERM
                      ! host.HomeServer 2017-05-08 10:34:01.647 info stopInstance system.adapter.smartmeter.0 killing pid 7772
                      ! host.HomeServer 2017-05-08 10:34:01.646 info stopInstance system.adapter.smartmeter.0

                      Gruß joergg

                      1 Antwort Letzte Antwort
                      0
                      • J Offline
                        J Offline
                        joergg
                        schrieb am zuletzt editiert von
                        #480

                        Anpassung der Datei "ObisMeasurement.js" lässt die Werteermittelung funktionieren:

                        Zeile 23 & 37: "^" aus der RegEx entfernt.

                        Offensichtlich wird hier ein reiner OBIS-String erwartet, was aber nicht ankommt.

                        Gruß joergg

                        1 Antwort Letzte Antwort
                        0
                        • apollon77A Offline
                          apollon77A Offline
                          apollon77
                          schrieb am zuletzt editiert von
                          #481

                          Diese Änderung ist etwas zu kurz gedacht :-)

                          Ich hab nochmal was geändert: Please Update from GitHub

                          Es lag daran das dein Zähler zu schnell sendet …

                          Ingo F

                          Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

                          • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
                          • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
                          1 Antwort Letzte Antwort
                          0
                          • E Offline
                            E Offline
                            easymeter
                            schrieb am zuletzt editiert von
                            #482

                            Hallo, jetzt kommen Daten, aber lediglich die Zählernummer.

                            Diese habe ich mittlerweile jetzt 10 mal unter den Objekten, immer in einem anderen Ordner.

                            Gruß

                            Markus
                            2624_objekte.jpg
                            2624_log.txt

                            1 Antwort Letzte Antwort
                            0
                            • J Offline
                              J Offline
                              joergg
                              schrieb am zuletzt editiert von
                              #483

                              :D War eben ein Workaround… Quick und Dirty, wie es sich gehört!

                              Habe den "smartmeter"-Adapter wieder aktualisiert und jetzt rennt es richtig bei mir. Kannst also meinen Strommesser mit in die Kompatibilitätsliste aufnehmen.

                              Danke für Deine Unterstützung!

                              Gruß joergg

                              1 Antwort Letzte Antwort
                              0
                              • E Offline
                                E Offline
                                easymeter
                                schrieb am zuletzt editiert von
                                #484

                                Eben erst gesehen, dass es ein update gibt. Habe es eingespielt.

                                Folgender Log kam dabei heraus. (ohne den protocol-Overwrite)
                                2624_log.txt

                                1 Antwort Letzte Antwort
                                0
                                • E Offline
                                  E Offline
                                  easymeter
                                  schrieb am zuletzt editiert von
                                  #485

                                  Irgendwie hat das aus dem GIT nicht geklappt, es läuft noch die 0.5.8. Welche URL verwendet Ihr?

                                  1 Antwort Letzte Antwort
                                  0
                                  • J Offline
                                    J Offline
                                    joergg
                                    schrieb am zuletzt editiert von
                                    #486

                                    Aktualisierung

                                    • Localhost:8081 als Webseite öffnen.

                                    • Karte "Adapter" auswählen.

                                    • Drittes Icon von Links mit GitHub-Logo anklicken.

                                    • Im neuen Dialog "smartmeter" auswählen.

                                    • Falls "smartmeter" nicht zur Verfügung steht: Karte "Custom" aktivieren und folgende URL angeben: https://github.com/Apollon77/ioBroker.smartmeter

                                    Gruß joergg

                                    1 Antwort Letzte Antwort
                                    0
                                    • E Offline
                                      E Offline
                                      easymeter
                                      schrieb am zuletzt editiert von
                                      #487

                                      mmmm klappt irgendwie nicht
                                      2624_fehler.jpg

                                      1 Antwort Letzte Antwort
                                      0
                                      • apollon77A Offline
                                        apollon77A Offline
                                        apollon77
                                        schrieb am zuletzt editiert von
                                        #488

                                        @easymeter: nach update mal bitte auch mit "Seriell jur lesen" … also nicht bidirektional versuchen

                                        Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

                                        • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
                                        • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
                                        1 Antwort Letzte Antwort
                                        0
                                        • apollon77A Offline
                                          apollon77A Offline
                                          apollon77
                                          schrieb am zuletzt editiert von
                                          #489

                                          @easymeter:

                                          mmmm klappt irgendwie nicht `

                                          Was sagt das es nicht läuft? Dieser Fehler ist normal, er sagt ja "Falling back to compile selbst" … INSTALL LÄUFT NOCH!!! Abwarten

                                          Beitrag hat geholfen? Votet rechts unten im Beitrag :-) https://paypal.me/Apollon77 / https://github.com/sponsors/Apollon77

                                          • Debug-Log für Instanz einschalten? Admin -> Instanzen -> Expertenmodus -> Instanz aufklappen - Loglevel ändern
                                          • Logfiles auf Platte /opt/iobroker/log/… nutzen, Admin schneidet Zeilen ab
                                          1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          837

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe