NEWS
Test Adapter luxtronik2-controller V1.0.x
-
0.22.0 (2026-10-24)
🐛 Performance & Tweaks
- Modbus Queue & Socket Protection: Added a sequential operation queue (mutex) with a 50ms socket release delay in
ModbusManagerto prevent TCP port 502 connection collisions when polling and event-driven writes occur simultaneously. - COP Database Optimization: Added an in-memory object cache (
ensuredObjects) tocopManager, eliminating redundantsetObjectNotExistsAsyncdatabase calls during every polling cycle. - DTA Backup & Firmware Check Improvements: Added a 30-second request timeout (
AbortSignal.timeout) and properdta_historyfile naming on fallback tobackupManager, and expanded the version regex inupdateManagerto supportF1.,WWB, andsmofirmware strings.
- Modbus Queue & Socket Protection: Added a sequential operation queue (mutex) with a 50ms socket release delay in
-
Hallo zusammen,
nach den umfangreichen Updates der letzten Zeit (PV-Steuerung, Hybrid-Modus, Takt-Optimierung) ist erst einmal ein Feature-Freeze: Es sind aktuell keine neuen Features geplant.
Mein Fokus liegt jetzt zu 100 % auf Fehlerbereinigung und Stabilität, um den Adapter zeitnah ins offizielle Stable-Repository von ioBroker zu bringen.
Testet den aktuellen Stand gerne ausgiebig! Anmerkungen, Anregungen oder auch einfach kurze "Läuft fehlerfrei"-Rückmeldungen sind jederzeit herzlich willkommen.
Jedes Feedback hilft uns enorm auf dem Weg zum Stable-Release.
Danke für euren fantastischen Support und das fleißige Testen!
-
0.22.6 (2026-11-06)
🐛 Bugfixes
- Cycle Optimization & Hardware Sync (
main.ts):- Pre-Heating & Heating Limit Type Fix: Fixed strict type comparison bugs (
booleanvs.number) when evaluatingheatingLimitandVD1out(vd1). Previously, boolean state values causedisHeatingAllowedByLimitandvd1to evaluate tofalse, which blocked pre-heating before hot water generation (raisingheating_curve_parallel_offsetto 35 °C), prevented the 10-minute base point reset, and skipped HUP voltage optimization. - Raw Data Fallbacks (
rawValues/rawParams): Added direct fallbacks to raw heat pump telemetry and parameter arrays inrunOptimizationScheduleso cycle optimization, HUP control, and heating limit checks remain fully functional even if individual datapoints (thresholdHeatingLimit,Mitteltemperatur,heatingLimit,VD1out, etc.) are disabled in the ioBroker object tree. - Hardware Out-of-Sync Verification: Enhanced
syncConfigValueto verify target values against the live hardware parameter cache (currentRawParams), ensuring parameters are reliably written to the controller even if the local ioBroker state is disabled or out of sync with the heat pump.
- Pre-Heating & Heating Limit Type Fix: Fixed strict type comparison bugs (
0.22.5 (2026-11-06)
🔧 Maintenance & Compatibility
- Repository Compliance: Added missing multi-language translations (i18n) for all configuration dropdown menus (e.g. COP sources, PV modes) to meet strict ioBroker stable repository requirements.
0.22.4 (2026-11-06)
🐛 Bugfixes & Tweaks
- PV Surplus Management (
pvManager.ts):- Cycle Completion & Reset Deadlock: Fixed a critical bug in
initiateDeactivationwhenpv_finish_cyclewas enabled: the inactive operating mode (e.g., hot water while heating is running) is now immediately reset to baseline[cite: 26, 28, 29]. This prevents infinite cycle loops where cycle optimization erroneously triggered forced 60 °C hot water runs at the end of a heating cycle[cite: 25, 28]. - Target Reset vs. PV Max: Corrected cycle completion behavior so active compressor runs finish at normal baseline setpoints instead of continuing to heat to elevated PV boost targets with grid/battery power[cite: 26, 28, 29]. Added a dynamic timer to enforce the 10-minute minimum compressor run time before final reset[cite: 26].
- Hysteresis Deadband & Timer Protection: Prevented the deactivation timer (
pvStopTimer) from being aborted by minor meter/battery balancing fluctuations in the deadband between the stop threshold and start threshold[cite: 26, 27, 29]. - Startup Recovery: Added baseline recovery during
initPvManagementto clear orphaned boost targets left behind after an adapter update or reboot. - Input Parsing: Added
parseConfigFloatto safely parse decimal values formatted with commas (e.g.,"1,5") in the admin configuration[cite: 26, 29]. - Direct Hardware Sync: Switched state updates to
syncConfigValuefor immediate, queue-safe synchronization via native TCP and Modbus[cite: 25, 26].
- Cycle Completion & Reset Deadlock: Fixed a critical bug in
0.22.3 (2026-11-06)
- Notifications & Alarming:
- Fixed an initialization bug where
lastKnownErrorTimestampandlastKnownOutageTimestampwere not set on adapter startup if the history remained unchanged, which previously caused the first genuine error or outage after a restart to be silently ignored. - Decoupled the 60-minute flow warning cooldown (
lastFlowNotificationTime) from critical heat pump malfunctions so genuine fault alarms are never suppressed by preceding flow warnings. - Added language-independent outage code detection (codes 0, 1, 11, 18) alongside text-based fallbacks.
- Fixed an initialization bug where
- ZIP Circulation Control:
- Added a raw parameter fallback (
currentRawParams) when backing uporiginalZipConfigto prevent timer schedules from being overwritten withnullif the corresponding timer states are disabled in the object tree. - Fixed an issue in
stopZipAndDeaerationwhere manually disablingActivate_Zipdid not stop the hardware deaeration program (runDeaerate) by checkingVirtual_ZIP_Statusin addition to the trigger state.
- Added a raw parameter fallback (
- Stability & Helpers:
- Wrapped the automated DTA backup cron job initialization (
initAutoBackup) in atry/catchblock to prevent startup crashes on malformed cron expressions. - Hardened
safeCloseinModbusManagerto cleanly terminate sockets even if a connection timeout occurs before the socket is marked as open. - Improved input validation in
formatTimerSecondsToTime(guarding against negative values andNaN) andgetNumber(supporting numeric strings).
- Wrapped the automated DTA backup cron job initialization (
0.22.2 (2026-11-06)
🐛 Bugfixes & Tweaks
-
Cycle Optimization & PV Integration: Fixed an issue where the cycle optimization was blocked during an active PV boost. The adapter now correctly forces seamless transitions between heating and hot water (without compressor shutdown and anti-cycle delays) even when solar surplus is available. A new handshake mechanism ensures that PV target temperatures are immediately and safely restored after the cycle optimization resets the baseline idle defaults.
-
PV Surplus Management & Compressor Optimization:
- Fixed read-only datapoint errors in
activateBoostanddeactivateBoost(now correctly targetingtemperature_hot_water_target). - Resolved baseline configuration mix-ups between
fusspunktand the heating parallel offset (heating_temperature). - Fixed the heating saturation check (
isHzFull) to prevent premature boost revocation. - Implemented a seamless "PV-Boost Handshake" allowing cycle optimization to force hot water transitions even during active solar surplus without triggering anti-cycle compressor delays.
- Fixed read-only datapoint errors in
-
ZIP Circulation & Timer Logic:
- Fixed a bug where hot water timer slots (
WW_MoSo_...) were mistakenly backed up and overwritten instead of circulation pump slots (Zirkulation_MoSo_...). - Improved time string conversions and state restoration robustness.
- Fixed a bug where hot water timer slots (
-
COP Calculation & Virtual States:
- Fixed a UTC timezone offset in daily rollovers so COP snapshots trigger precisely at local midnight.
- Included defrosting cycles (
WP_BZ_akt = 4) into the heating COP calculations and added clamping protection against negative energy deltas. - Added an in-memory object cache (
ensuredObjects) to drastically reduce redundant database write calls. - Added a raw value fallback for total energy and thermal energy calculations if individual states are disabled in the object tree.
-
Modbus & Raw Communication Stability:
- Implemented a strict serial operation queue (mutex) with a 50ms release delay in
ModbusManagerto prevent TCP port 502 connection collisions. - Added a 30-second request timeout (
AbortSignal.timeout) to DTA backups and corrected file naming for fallback paths (dta_history). - Expanded firmware version regex in
updateManagerto supportF1.,WWB, andsmofirmware formats. - Added socket
closeevent listeners and safe number roundings for raw write operations.
- Implemented a strict serial operation queue (mutex) with a 50ms release delay in
-
Repository Compliance & Maintenance:
-
Added complete multi-language translations (i18n) for all configuration dropdown menus to meet strict ioBroker stable repository requirements.
-
Cleaned up unpublished ghost versions from the
io-package.jsonnews section. -
Standardized the README changelog header format (
## Changelog). -
Repository Compliance: Added missing multi-language translations (i18n) for all configuration dropdown menus (e.g. COP sources, PV modes) to meet strict ioBroker stable repository requirements.
-
0.22.1 (2026-11-06)
🐛 Bugfixes & Tweaks
- PV Manager Target & Offset Fixes: Fixed remaining references to the read-only
Wamwassertemperatur_Solldatapoint inactivateBoostanddeactivateBoost(now consistently targetingtemperature_hot_water_target). Resolved a baseline mix-up wherefusspunktwas mistakenly applied to the parallel offset (heating_temperature), and fixed the heating saturation check (isHzFull) to compare actual return temperature against target return + hysteresis without prematurely revoking active boosts. - Cycle Optimization & Heating Limit: Replaced the language-dependent
'Heating limit'string check during idle with a reliable numerical evaluation of the heating limit parameters. Added a!pvIsBoostActiveguard to prevent forced hot water triggers from overwriting active solar boosts, and included a baseline reset (0 K) forheating_temperatureinsetIdleDefaults. - ZIP Controller Timer Fix: Fixed a bug in
zipManager(internal controller mode) where hot water timer slots (WW_MoSo_...) were backed up and overwritten instead of the circulation pump timer slots (Zirkulation_MoSo_...), and improved time string restoration. - COP Calculation Accuracy: Fixed a UTC timezone offset in the daily rollover check so COP snapshots occur accurately at local midnight (00:00). Included defrosting cycles (
WP_BZ_akt = 4) in the heating COP bucket and added clamping against negative deltas if external energy meters are reset. - Object Management & Virtual States: Removed a redundant loop in
onReadythat recreated disabled virtual datapoints on startup, and fixedPREFIX_MAPPINGfor weekend timer tables (SaSo) to properly reference the52SatSunconfiguration flags.
0.22.0 (2026-11-06)
🐛 Performance & Tweaks
- Modbus Queue & Socket Protection: Added a sequential operation queue (mutex) with a 50ms socket release delay in
ModbusManagerto prevent TCP port 502 connection collisions when polling and event-driven writes occur simultaneously. - COP Database Optimization: Added an in-memory object cache (
ensuredObjects) tocopManager, eliminating redundantsetObjectNotExistsAsyncdatabase calls during every polling cycle. - DTA Backup & Firmware Check Improvements: Added a 30-second request timeout (
AbortSignal.timeout) and properdta_historyfile naming on fallback tobackupManager, and expanded the version regex inupdateManagerto supportF1.,WWB, andsmofirmware strings.
- Cycle Optimization & Hardware Sync (
-
-
Hallo @tbsjah ich habe Deinen Adapter getestet (ohne modbus), da ich den nur lesend Use Case für Monitoring habe.
Sehr schön finde ich die konfigurierbaren Felder zum auslesen, da ältere Modelle oder Typen von WP bestimmte Werte nicht haben.
Bei mir muss der Modus zwingend read only sein, weil ich den Adapter nutze um WP Daten zu visualisieren, um Anlagenprobleme aus den Charts, welche ich aus den Daten erstelle, zu erkennen. (z. B. zu viele Takte, undichtes 3-Wege Ventil, Temperaturkurven...)
Teilweise stehen die WPs in Mietobjekten, da möchte man an der Konfiguration nichts ändern. Da wäre ein Schalter im Verbindungstab read-only nicht schlecht, aber das gleiche kann ja erreicht werden, wenn die Steuerungen in den anderen Tabs nicht aktiviert werden?
VG,
René -
-
0.24.0 (2026-11-09)
🐛 Bugfixes & Tweaks
- Operating Mode & Write Protection (
jsonConfig.json,main.ts):- Explicit Operating Mode Selection: Added a central "Operating Mode" selector in the Connection tab with color-coded status banners to clearly distinguish between Read-Only (Monitoring), Read & Write without Modbus (Native via Port 8889), and Read & Write with Modbus TCP (Hybrid RAM access).
- Dynamic UI Locking: When "Read-Only" is selected, all write-related configuration tabs (Modbus, Idle Defaults, Cycle Optimization, HUP, ZIP, and PV Surplus) and their inputs are automatically grayed out and disabled. Selecting native write mode unlocks the optimization tabs while keeping the Modbus tab disabled.
- Strict Backend Write Lock: Enforced a global hardware write lock in Read-Only mode across
onReady,syncConfigValue,runOptimizationSchedule, andonStateChange(while keeping diagnostic functions like debug logging, raw dumps, and firmware checks active). - Automatic Config Migration: Existing installations are seamlessly migrated on startup to the matching operating mode based on their previously active Modbus and optimization settings.
0.23.2 (2026-11-07)
- COP & Efficiency Calculation (
copManager.ts):- Isolated Counter Tracking: Introduced dedicated reference states for Total, Heating, and Hot Water counters (
last_raw_power_*andlast_raw_thermal_*). Each counter is now compared strictly against its own previous value, completely preventing cross-mode "ghost deltas" and astronomical COP spikes during cycle transitions. - Automatic Total-Delta Fallback: Added seamless fallback detection for controllers with firmware bugs (e.g., Novelan LAV) where mode-specific counters like
energy_warmwaterremain permanently at0. If a specific counter reports a delta of0during an active cycle, the adapter automatically uses the live delta of the corresponding total counter (energy_total/thermalenergy_total) without requiring manual configuration workarounds.
- Isolated Counter Tracking: Introduced dedicated reference states for Total, Heating, and Hot Water counters (
0.23.1 (2026-11-07)
- COP & Efficiency Calculation Fix (
copManager.ts):- Fixed Astronomical COP Values: Resolved a critical bug where the internal calculation logic switched between specific and total energy counters, causing massive "ghost deltas" and resulting in astronomical COP values (e.g., > 1000).
- Restored Robust Routing: The adapter now strictly and safely relies on the continuous total counters (
energy_totalandthermalenergy_total). It calculates the delta over the polling interval and dynamically routes it into the Heating or Hot Water buckets based on the active operating state. - Note: Users facing the hardware bug where the heat pump does not track DHW power internally should select "External Object ID" in the adapter settings and link their
energy_totaldatapoint as a workaround.
0.23.0 (2026-11-07)
🐛 Bugfixes & Tweaks
- Configuration & Baseline Logic:
- Custom Heating Offset Baseline: Added a new configuration field in the "Idle Defaults" tab for the default heating target temperature offset (Parallelverschiebung)[cite: 10].
- Preserved Baselines: The idle reset mechanism (
main.ts) and the PV surplus manager (pvManager.ts) now respect this custom baseline (e.g., +1 K) instead of hard-resetting the offset to0 K[cite: 7, 13]. This ensures that your manual baseline heating curve is perfectly preserved when returning from a PV boost or entering standby.
- Operating Mode & Write Protection (
-
1.0.0 (2026-11-16)
STABLE
0.25.2 (2026-11-16)
- Fix i18n
0.25.1 (2026-11-16)
- Removed Dependencies:
- WS
0.25.0 (2026-11-16)
- Operating Mode & UI Protection (
jsonConfig.json,main.ts):- Explicit Operating Mode Selection: Added a central selector in the Connection tab with color-coded status banners to clearly distinguish between Read-Only (Monitoring), Read & Write without Modbus (Native via Port 8889), and Read & Write with Modbus TCP (Hybrid RAM access).
- Dynamic UI & Backend Write Locking: In Read-Only mode, all write-related configuration tabs (Modbus, Idle Defaults, Cycle Optimization, HUP, ZIP, PV Surplus) are automatically grayed out and all hardware write commands are strictly blocked in the backend.
- Automatic Config Migration: Existing installations are seamlessly migrated on startup to the matching operating mode based on previously active settings.
- Modbus V3.9x Smart Home Interface (SHI) & Diagnostics (
modbusManager.ts,settings.ts,info.ts):- Dual-Protocol Auto-Detection: The Modbus manager now automatically detects and supports both the classic Modbus register mapping (
0..23) and the modern V3.90+ / V3.92.x Smart Home Interface (SHI) register architecture (10000+). - Automated SHI Mode-Gating: Writing to SHI setpoints and offsets (
10001,10002,10006) automatically activates the required SHI control mode registers (10000,10005,10065) and releases heating curve control (mode = 0) when the offset returns to0 K. - Granular Register Polling & Diagnostic Scanner: Replaced rigid block reads with individual register polling to prevent
Exception 2 (Illegal data address)crashes on unsupported registers, and integrated a full Modbus register scanner intoDump_Raw_To_Log.
- Dual-Protocol Auto-Detection: The Modbus manager now automatically detects and supports both the classic Modbus register mapping (
- Core Stability, COP & Pure TCP Communication (
main.ts,rawFunctions.ts,copManager.ts):- Pure Native TCP Architecture: Removed deprecated WebSocket (port 8214) code in favor of stable, password-free native TCP communication over port
8889. - Isolated COP & Energy Tracking: Enforced strict separation of reference states for heating, hot water, and total consumption with fallback logic for controllers affected by zero-value firmware bugs.
- Bug Fixes: Fixed Modbus RAM vs. EEPROM sync loops (
hardwareOutOfSync), unified°Ctemperature scaling across all data sources, and fixed offline detection (info.connection&errorCount) when telemetry reads fail. - Repository Checker & i18n: Completed missing 11-language translations in
jsonConfig.jsonand updated@iobroker/testingto6.3.2.
- Pure Native TCP Architecture: Removed deprecated WebSocket (port 8214) code in favor of stable, password-free native TCP communication over port
-
Hallo TbsJah,
vielen Dank für den super Adapter und das Update auf v1.0.3 – der Modbus-Hybrid-Modus läuft damit bei mir absolut stabil und verschleißfrei für die PV-Überschuss-Steuerung!
Mir ist bei der Überwachung von write_cycles_today noch ein kleines Detail aufgefallen:
Wenn die Intelligente Takt-Optimierung („Takt-Kopplung startet“ / „Heizen nach WW“) aktiv wird, um den Rücklauf-Sollwert temporär auf 35 °C anzuheben, schreibt der Adapter diesen Wert offenbar über das native Luxtronik-Protokoll (Port 8889) in Settings.02_Heating.heating_curve_parallel_offset (Wert: 35), was jedes Mal einen EEPROM-Schreibzyklus (write_cycles_today +1) auslöst.
Mein System-Setup:
• Adapter-Version: luxtronik2-controller v1.0.3
• Luxtronik Firmware: V3.92.3 (Modernes SHI-Interface mit Register 10000+ wurde beim Start sauber erkannt)
• Modbus Hybrid: Aktiviert (Port 502), u. a. mit Haken bei Heizen Parallelverschiebung (Holding 23) und Feste Rücklaufsolltemperatur (Holding 2)
Wäre es in einem künftigen Update möglich, die Sollwert-Anhebung der Takt-Optimierung bei aktiviertem Hybrid-Modus ebenfalls über Modbus TCP (RAM) statt über Port 8889 auszuführen, um diese Schreibzyklen auch noch einzusparen?
Vielen Dank vorab und beste Grüße! -
Hallo TbsJah,
Beim Überwachen der EEPROM-Schreibzyklen im Hybrid-Modus mit aktiviertem SHI (V3.92.3) sind mir noch drei Stellen im Code aufgefallen, die trotz aktivem SHI weiterhin über WebSocket/Legacy ins EEPROM schreiben:- Takt-Optimierung / Vorheizen vor Warmwasser & Zwangsheizen (main.ts & actionHandlers.ts):
• In runOptimizationSchedule() (istWarmwasser && nachWasser, istLeerlauf, istHeizen), setIdleDefaults() sowie in handleZwangsheizen() wird heating_curve_parallel_offset temporär auf 35 °C bzw. wieder zurück auf den Fußpunkt (config.fusspunkt) gesetzt.
• Da der Fußpunkt im V3.9x-SHI-Protokoll kein flüchtiges Register hat, erzeugt jeder Takt- und Vorheizvorgang zwei EEPROM-Schreibzyklen.
• Vorschlag: Wenn modbusManager.isAvailable && modbusManager.protocolVersion === 'shi' aktiv ist, stattdessen flüchtig einen Offset von +10.0 K (modbusManager.writeRegister(23, 100) → SHI-Register 10002 / Modus 10000 = 2) setzen und beim Beenden bzw. im Leerlauf wieder auf 0 (modbusManager.writeRegister(23, 0)) zurückstellen. - PV-Überschuss-Heizungsboost (pvManager.ts):
• In evaluatePvBoost(), deactivateBoost() und initiateDeactivation() wird für die Heizungsanhebung aktuell heating_temperature (klassisches Holding-Register 15) beschrieben. Laut ModbusManager hat Register 15 im V3.9x-SHI-Protokoll jedoch kein direktes Gegenstück und erzeugt eine Log-Warnung bzw. schreibt über WebSocket ins EEPROM.
• Vorschlag: Im SHI-Modus die Heizungs-Offset-Anhebung (boostHzAmount * 10) ebenfalls flüchtig über modbusManager.writeRegister(23, ...) (SHI 10002) abwickeln. - Start-Reihenfolge in onReady() (main.ts & pvManager.ts):
• Beim Adapterstart wird initPvManagement(this) aktuell vor this.modbusManager.checkAvailability() aufgerufen und schreibt bei aktivem idle_defaults_aktiv sofort heating_temperature = 0 über WebSocket ins EEPROM (da modbusManager.isAvailable zu dem Zeitpunkt noch false ist).
• Vorschlag: this.modbusManager.checkAvailability() vor initPvManagement(this) ausführen und den Reset beim Start nur dann senden, wenn pv_boost_active tatsächlich noch auf true stand.
Ich teste gerade diese drei Anpassungen lokal bei mir und bisher läuft der Adapter inklusive Neustarts, PV-Boost und Vorheiz-Optimierung mit 0 EEPROM-Schreibzyklen.
Viele Grüße!
- Takt-Optimierung / Vorheizen vor Warmwasser & Zwangsheizen (main.ts & actionHandlers.ts):
-
-
Hallo JuergenH,
vielen Dank für die super Analyse und das direkte Mitdenken – solche detaillierten Rückmeldungen aus dem Echtbetrieb mit V3.92.3 SHI sind Gold wert!
Ich habe mir alle drei Punkte im Code angeschaut und direkt für das nächste Update umgesetzt:
-
Takt-Optimierung, Vorheizen & Zwangsheizen (
main.ts/actionHandlers.ts):
Volltreffer – der Heizkurven-Fußpunkt (heating_curve_parallel_offset, Parameter 12) lief im SHI-Modus bisher ins EEPROM, weil es dafür kein flüchtiges SHI-Register gibt. Wenn SHI-Modbus aktiv und Holding 23 angehakt ist, nutzt der Adapter jetzt für Takt-Kopplung, Vorheizen und Zwangsheizen flüchtig den Offset+10.0 Küber Holding 23 (SHI10002, Modus10000 = 2) und setzt ihn anschließend sauber zurück (inkl. Wiederherstellung eines ggf. laufenden PV-Boosts). Auch insetIdleDefaults()werden Endpunkt/Fußpunkt im SHI-Modus nicht mehr unnötig angefasst. -
PV-Überschuss-Heizungsboost (
pvManager.ts):
Hier kurz zur Einordnung: InpvManager.tswird bereitsheating_temperaturebeschrieben – und der liegt im Mapping schon auf Holding 23 (SHI10002), nicht auf Holding 15 (das wäre der Heizkurven-Endpunkt). Dass beim Start trotzdem ein EEPROM-Write kam, war tatsächlich die Folge von deinem Punkt 3. Ich habe den PV-Manager aber zusätzlich gegen die neue SHI-Takt-Kopplung abgesichert, damit sich beide Offsets auf Register10002nicht gegenseitig überschreiben. -
Start-Reihenfolge & PV-Recovery (
main.ts/pvManager.ts):
Ebenfalls ein echter Bug!modbusManager.checkAvailability()läuft jetzt direkt vorinitPvManagement(), und das Recovery beim Start setzt die Sollwerte nur noch zurück, wennpv_boost_activevor dem Neustart tatsächlichtruewar.
Als kleinen Bonus habe ich gleich noch drei verwandte Stellen mitgezogen:
disableHardwareZipTimer()läuft erst nach dem erstenupdateData(), damit der Read-Before-Write-Cache (currentRawParams) beim Start schon gefüllt ist.- HUP-Spannungen werden in
setIdleDefaults()nur noch geschrieben, wenn die HUP-Optimierung auch aktiviert ist. - Beim Zurücksetzen von Warmwasser-Soll auf den Basiswert im SHI-Modus wird
10005jetzt wieder auf0gesetzt, damit manuelle Änderungen am WP-Display nicht dauerhaft übersteuert bleiben.
Das Ganze kommt mit dem nächsten Release – gib danach gerne kurz Bescheid, ob der Zähler bei dir damit dauerhaft auf 0 bleibt!
Viele Grüße
-
-
1.0.4 (2026-11-21)
**Thanks to @juergenh **
- Optimized V3.9x SHI Modbus Hybrid mode to achieve zero EEPROM write cycles during cycle optimization, pre-heating, and forced heating (uses volatile SHI offset
+10.0 Kvia Holding 23 /10002instead of base point parameter12) - Fixed startup order in
onReady()so Modbus TCP availability is checked before PV initialization and hardware ZIP timer disable runs after initial raw parameter fetch - Improved PV startup recovery to only reset setpoints if a PV boost was actually active before restart, and decoupled PV heating boost from active SHI cycle optimization
- Released SHI DHW mode (
10005 = 0) when reverting hot water target to baseline and avoided unnecessary HUP voltage writes insetIdleDefaults()when HUP optimization is disabled
- Optimized V3.9x SHI Modbus Hybrid mode to achieve zero EEPROM write cycles during cycle optimization, pre-heating, and forced heating (uses volatile SHI offset
-
Hallo JuergenH,
vielen Dank für die super Analyse und das direkte Mitdenken – solche detaillierten Rückmeldungen aus dem Echtbetrieb mit V3.92.3 SHI sind Gold wert!
Ich habe mir alle drei Punkte im Code angeschaut und direkt für das nächste Update umgesetzt:
-
Takt-Optimierung, Vorheizen & Zwangsheizen (
main.ts/actionHandlers.ts):
Volltreffer – der Heizkurven-Fußpunkt (heating_curve_parallel_offset, Parameter 12) lief im SHI-Modus bisher ins EEPROM, weil es dafür kein flüchtiges SHI-Register gibt. Wenn SHI-Modbus aktiv und Holding 23 angehakt ist, nutzt der Adapter jetzt für Takt-Kopplung, Vorheizen und Zwangsheizen flüchtig den Offset+10.0 Küber Holding 23 (SHI10002, Modus10000 = 2) und setzt ihn anschließend sauber zurück (inkl. Wiederherstellung eines ggf. laufenden PV-Boosts). Auch insetIdleDefaults()werden Endpunkt/Fußpunkt im SHI-Modus nicht mehr unnötig angefasst. -
PV-Überschuss-Heizungsboost (
pvManager.ts):
Hier kurz zur Einordnung: InpvManager.tswird bereitsheating_temperaturebeschrieben – und der liegt im Mapping schon auf Holding 23 (SHI10002), nicht auf Holding 15 (das wäre der Heizkurven-Endpunkt). Dass beim Start trotzdem ein EEPROM-Write kam, war tatsächlich die Folge von deinem Punkt 3. Ich habe den PV-Manager aber zusätzlich gegen die neue SHI-Takt-Kopplung abgesichert, damit sich beide Offsets auf Register10002nicht gegenseitig überschreiben. -
Start-Reihenfolge & PV-Recovery (
main.ts/pvManager.ts):
Ebenfalls ein echter Bug!modbusManager.checkAvailability()läuft jetzt direkt vorinitPvManagement(), und das Recovery beim Start setzt die Sollwerte nur noch zurück, wennpv_boost_activevor dem Neustart tatsächlichtruewar.
Als kleinen Bonus habe ich gleich noch drei verwandte Stellen mitgezogen:
disableHardwareZipTimer()läuft erst nach dem erstenupdateData(), damit der Read-Before-Write-Cache (currentRawParams) beim Start schon gefüllt ist.- HUP-Spannungen werden in
setIdleDefaults()nur noch geschrieben, wenn die HUP-Optimierung auch aktiviert ist. - Beim Zurücksetzen von Warmwasser-Soll auf den Basiswert im SHI-Modus wird
10005jetzt wieder auf0gesetzt, damit manuelle Änderungen am WP-Display nicht dauerhaft übersteuert bleiben.
Das Ganze kommt mit dem nächsten Release – gib danach gerne kurz Bescheid, ob der Zähler bei dir damit dauerhaft auf 0 bleibt!
Viele Grüße
Hallo TbsJah,
nochmals vielen Dank für die schnelle Umsetzung der EEPROM-Fixes! Diesen werde ich morgen einsetzen und testen. Aus meinen DTA-Auswertungen im Echtbetrieb hat sich noch ein wichtiger Verbesserungsvorschlag für die „Intelligente Takt-Optimierung“ ergeben, der besonders für gut gedämmte Gebäude und Passivhäuser mit Fußbodenheizung einen riesigen Unterschied machen würde:
Das aktuelle Problem bei milden Außentemperaturen in der Übergangszeit:
In meinem Passivhaus mit Fußbodenheizung entsteht das Problem speziell bei milden Außentemperaturen in der Übergangszeit (ca. +5 °C bis +12 °C). Während die Funktion im tiefen Winter (bei Dauerfrost und ohnehin höherem Rücklauf) gut funktionieren wird, liegt der reguläre Rücklauf-Sollwert ((TRL_{soll})) in der Übergangszeit sehr niedrig bei etwa 25,0 bis 26,5 °C. Wenn die Takt-Optimierung den Rücklauf-Sollwert (bzw. nun das flüchtige SHI-Register 10002) pauschal hart auf 35 °C (bzw. +10,0 K) anhebt, entsteht bei geringer Heizlast ein schlagartiger Temperatursprung von +8,5 bis +10 K.
Unser Estrich kann diese enorme Wärmemenge in der Übergangszeit nicht schnell genug abnehmen. Die konkreten Auswirkungen in meinem aktuellen DTA-Log:
• Regulärer Heizbetrieb (ohne Eingriff): Sehr ruhige, lange Verdichterläufe von 1 Std. 40 Min. bis knapp 5 Stunden bei ca. 30,4 °C Vorlauf und einer Arbeitszahl (AZ1/AZ2) von 3,88 bis 4,03.
• Mit aktiver Takt-Optimierung (+10 K / 35 °C): Die Vorlauftemperatur schoss sofort auf ca. 33,8 °C hoch (Spreizung bis zu 6,2 K). Da die Wärme bei den milden Außentemperaturen nicht abgenommen werden konnte, lief die Wärmepumpe vorzeitig in die Taktsperre (SSP), bevor die Warmwasserbereitung überhaupt startete.
• Ergebnis: Statt eines durchgehenden Taktes entstanden 7 kurze Fehlstarts in gut 2 Stunden (Laufzeiten von nur 5 bis 19 Minuten, unterbrochen durch Zwangspausen von 7 bis 16 Minuten), und die Arbeitszahl brach von ~4,0 auf 2,70 ein.
Konkreter Verbesserungsvorschlag für den Adapter:
Könnte man im Reiter „Takt-Optimierung“ anstelle des fest einprogrammierten Sprungs (+10 K / 35 °C) eine konfigurierbare, relative Anhebung (z. B. ein Eingabefeld „Rücklauf-Anhebung in K“ mit einem Einstellbereich von +2,0 K bis +10,0 K) einbauen?
Im SHI-Modus ließe sich dieser konfigurierte Wert direkt als flüchtiger Offset auf Register 10002 schreiben (z. B. +3,0 K statt pauschal +10,0 K). Damit würde der Verdichter sanft auf Betriebstemperatur gehalten, ohne den Heizkreis in der Übergangszeit thermisch zu überfahren – und die Takt-Kopplung wäre auch in Passiv- und Niedrigenergiehäusern ganzjährig nutzbar, ohne sie im Frühjahr/Herbst manuell deaktivieren zu müssen.
Viele Grüße
Jürgen -
-
@juergenh
Hallo Jürgen,vielen Dank für die geniale DTA-Auswertung – die Messwerte sprechen wirklich für sich! Mein Haus liegt mit 15,9 kWh/(m²·a) ebenfalls sehr nah am Passivhaus-Standard, daher ist dein Feedback für mich ein super Parallelvergleich :)
Deine Idee mit einer dynamischen bzw. konfigurierbaren Anhebung statt der starren 35 °C / +10 K ist richtig gut – da mache ich mir definitiv ein paar Gedanken zu einer sauberen Umsetzung. Eine dynamische Kopplung direkt an das aktuelle RL-Soll (also relativ in K statt fix 35 °C) schlägt sogar zwei Fliegen mit einer Klappe: In gut gedämmten Häusern überfährt man in der Übergangszeit den Estrich nicht mehr, und umgekehrt löst es das Problem bei weniger gut gedämmten Gebäuden oder Heizkörper-Anlagen, bei denen ein RL-Soll von 35 °C im Normalbetrieb eventuell ohnehin schon anliegt.
Mal eine Frage rein aus Interesse (für die meisten hier vermutlich leicht Offtopic 🙈):
Wie sieht deine Heizkurve aktuell aus? Meine liegt bei 21,7 °C Fußpunkt zu 23,0 °C Endpunkt – also extrem flach. Damit komme ich bei einer Mitteltemperatur unter 5 °C auf knapp 22–23 °C Raumtemperatur. In den Übergangsmonaten gebe ich dann einfach eine Parallelverschiebung von +1 K drauf.
Hast du bei dir noch Einzelraumthermostate verbaut oder sind alle Heizkreise komplett offen (so läuft es bei mir)?Kleiner Tipp am Rande (ich glaube, das Feature habe ich hier im Thread noch gar nicht richtig erwähnt): Im Adapter kannst du unter dem Reiter Vorgaben direkt prüfen, wie deine Heizkurve verläuft – das Diagramm dort wird gemäß deinen Vorgaben live und dynamisch dargestellt.

Viele Grüße
Tobi -
@juergenh
Hallo Jürgen,vielen Dank für die geniale DTA-Auswertung – die Messwerte sprechen wirklich für sich! Mein Haus liegt mit 15,9 kWh/(m²·a) ebenfalls sehr nah am Passivhaus-Standard, daher ist dein Feedback für mich ein super Parallelvergleich :)
Deine Idee mit einer dynamischen bzw. konfigurierbaren Anhebung statt der starren 35 °C / +10 K ist richtig gut – da mache ich mir definitiv ein paar Gedanken zu einer sauberen Umsetzung. Eine dynamische Kopplung direkt an das aktuelle RL-Soll (also relativ in K statt fix 35 °C) schlägt sogar zwei Fliegen mit einer Klappe: In gut gedämmten Häusern überfährt man in der Übergangszeit den Estrich nicht mehr, und umgekehrt löst es das Problem bei weniger gut gedämmten Gebäuden oder Heizkörper-Anlagen, bei denen ein RL-Soll von 35 °C im Normalbetrieb eventuell ohnehin schon anliegt.
Mal eine Frage rein aus Interesse (für die meisten hier vermutlich leicht Offtopic 🙈):
Wie sieht deine Heizkurve aktuell aus? Meine liegt bei 21,7 °C Fußpunkt zu 23,0 °C Endpunkt – also extrem flach. Damit komme ich bei einer Mitteltemperatur unter 5 °C auf knapp 22–23 °C Raumtemperatur. In den Übergangsmonaten gebe ich dann einfach eine Parallelverschiebung von +1 K drauf.
Hast du bei dir noch Einzelraumthermostate verbaut oder sind alle Heizkreise komplett offen (so läuft es bei mir)?Kleiner Tipp am Rande (ich glaube, das Feature habe ich hier im Thread noch gar nicht richtig erwähnt): Im Adapter kannst du unter dem Reiter Vorgaben direkt prüfen, wie deine Heizkurve verläuft – das Diagramm dort wird gemäß deinen Vorgaben live und dynamisch dargestellt.

Viele Grüße
TobiHallo Tobi,
anbei meine Heizkurve. Sieht ziemlich gleich aus.
Meine Heizkurve ist nicht optimal , da unsere Zimmertemperatur aktuell noch zu hoch ist (24° bei 7°). Ich habe Einzelraumthermostate verbaut, welche aber bis aufs Schlafzimmer komplett offen sind. Dein neues Release ist installiert und bisher sind keine EEPROM Schreibzyklen erkennbar. Sieht sauber aus.
P.S. Habe gerade die Einstellung geändert. Jetzt muss ich mal 2 Tage warten.
Viele Grüße
Jürgen -
-
Hey! Du scheinst an dieser Unterhaltung interessiert zu sein, hast aber noch kein Konto.
Hast du es satt, bei jedem Besuch durch die gleichen Beiträge zu scrollen? Wenn du dich für ein Konto anmeldest, kommst du immer genau dorthin zurück, wo du zuvor warst, und kannst dich über neue Antworten benachrichtigen lassen (entweder per E-Mail oder Push-Benachrichtigung). Du kannst auch Lesezeichen speichern und Beiträge positiv bewerten, um anderen Community-Mitgliedern deine Wertschätzung zu zeigen.
Mit deinem Input könnte dieser Beitrag noch besser werden 💗
Registrieren Anmelden
