(erledigt)Problem mit Modbusadapter
-
@mcm1957 sagte in Problem mit Modbusadapter:
Lt. log ist sentry schon disabled:
ja sentry ist disable
Hier noch ein Log alle Scrips abgeschaltet die auf die Modbusdaten zugreifen.
modbus.0 2026-02-12 21:34:12.080 debug Initialize Objects for inputRegs: [] modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1005_Boost_Mode: {"_id":"holdingRegisters.1005_Boost_Mode","type":"state","common":{"name":"(R/W) 0=off , 1=on (for Mode 1)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1005,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1003_Status: {"_id":"holdingRegisters.1003_Status","type":"state","common":{"name":"(R) see Status codes","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1003,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1001_Temp_1: {"_id":"holdingRegisters.1001_Temp_1","type":"state","common":{"name":"(R) internal Sensor in AC ELWA 2","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1001,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}} modbus.0 2026-02-12 21:34:12.081 debug Initialize Objects for holdingRegs: [{"_address":1000,"name":"Power","description":"(R/W ) 0-3.500 for Mode 1 ","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1000,"id":"holdingRegisters.1000_Power"},{"_address":1001,"name":"Temp 1","description":"(R) internal Sensor in AC ELWA 2","unit":"°C","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1001,"id":"holdingRegisters.1001_Temp_1"},{"_address":1002,"name":"Tmax ","description":"(R) target temperature solar powered","unit":"°C","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1002,"id":"holdingRegisters.1002_Tmax_"},{"_address":1003,"name":"Status","description":"(R) see Status codes","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1003,"id":"holdingRegisters.1003_Status"},{"_address":1004,"name":"Power timout","description":"(R/W) 10 - 600sec","unit":"sec","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1004,"id":"holdingRegisters.1004_Power_timout"},{"_address":1005,"name":"Boost Mode","description":"(R/W) 0=off , 1=on (for Mode 1)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1005,"id":"holdingRegisters.1005_Boost_Mode"},{"_address":1006,"name":"Tmin","description":"(R/W) Boost backup target temperature","unit":"°C","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1006,"id":"holdingRegisters.1006_Tmin"},{"_address":1007,"name":"Boost time 1 start","description":"(R/W)","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1007,"id":"holdingRegisters.1007_Boost_time_1_start"},{"_address":1008,"name":"Boost time 1 stop","description":"(R/W)","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1008,"id":"holdingRegisters.1008_Boost_time_1_stop"},{"_address":1009,"name":"Actual Time (Hour)","description":"(R/W ) ","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1009,"id":"holdingRegisters.1009_Actual_Time_(Hour)"},{"_address":1010,"name":"Actual Time (Minute)","description":"(R/W ) ","unit":"min","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1010,"id":"holdingRegisters.1010_Actual_Time_(Minute)"},{"_address":1011,"name":"Actual Time (Second)","description":"(R/W) ","unit":"sec","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1011,"id":"holdingRegisters.1011_Actual_Time_(Second)"},{"_address":1012,"name":"Boost activate","description":"(R/W) see documentation","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1012,"id":"holdingRegisters.1012_Boost_activate"},{"_address":1013,"name":"ELWA 2 Number","description":"(R/W)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1013,"id":"holdingRegisters.1013_ELWA_2_Number"},{"_address":1014,"name":"max Power","description":"(R/W) 500-3500 W","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1014,"id":"holdingRegisters.1014_max_Power"},{"_address":1015,"name":"tempchip","description":"(R) Controller temperature","unit":"°C","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1015,"id":"holdingRegisters.1015_tempchip"},{"_address":1016,"name":"Controller firmware main version","description":"(R) (exxxxxyy)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1016,"id":"holdingRegisters.1016_Controller_firmware_main_version"},{"_address":1017,"name":"Powerstage firmware version","description":"(R) (epxxx)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1017,"id":"holdingRegisters.1017_Powerstage_firmware_version"},{"_address":1026,"name":"Boost time 2 start","description":"(R/W)","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1026,"id":"holdingRegisters.1026_Boost_time_2_start"},{"_address":1027,"name":"Boost time 2 stop","description":"(R/W)","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1027,"id":"holdingRegisters.1027_Boost_time_2_stop"},{"_address":1028,"name":"Controller firmware sub version","description":"(R) (exxxxxyy)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1028,"id":"holdingRegisters.1028_Controller_firmware_sub_version"},{"_address":1030,"name":"Temp 2","description":"(R) external Sensor of AC ELWA 2","unit":"°C","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1030,"id":"holdingRegisters.1030_Temp_2"},{"_address":1053,"name":"Legionella interval","description":"(R/W) 1-14 days","unit":"day","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1053,"id":"holdingRegisters.1053_Legionella_interval"},{"_address":1054,"name":"Legionella start","description":"(R/W) 0-23 hrs","unit":"h","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1054,"id":"holdingRegisters.1054_Legionella_start"},{"_address":1055,"name":"Legionella temp","description":"(R/W)","unit":"°C","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1055,"id":"holdingRegisters.1055_Legionella_temp"},{"_address":1056,"name":"Legionella mode","description":"(R/W) 0 or 1","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1056,"id":"holdingRegisters.1056_Legionella_mode"},{"_address":1058,"name":"Relay status","description":"(R) bit 0 AUX (0 off; 1 on) bit 1 SELV (0 off; 1 on)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1058,"id":"holdingRegisters.1058_Relay_status"},{"_address":1061,"name":"U L1","description":"(R) power stage input voltage","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1061,"id":"holdingRegisters.1061_U_L1"},{"_address":1064,"name":"Freq","description":"(R) ","unit":"mHz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1064,"id":"holdingRegisters.1064_Freq"},{"_address":1065,"name":"Operation mode","description":"(R/W) 1 or 3","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1065,"id":"holdingRegisters.1065_Operation_mode"},{"_address":1067,"name":"U L2","description":"(R) AUX relay voltage","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1067,"id":"holdingRegisters.1067_U_L2"},{"_address":1068,"name":"I L2","description":"(R) AUX relay current 100mA","unit":"mA","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1068,"id":"holdingRegisters.1068_I_L2"},{"_address":1071,"name":"Pmax_abs","description":"(R) Max. power currently possible","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1071,"id":"holdingRegisters.1071_Pmax_abs"},{"_address":1074,"name":"P out1","description":"(R) Power at ELWA immersion heater","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1074,"id":"holdingRegisters.1074_P_out1"},{"_address":1075,"name":"P out2","description":"(R) Power at AUX relay","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1075,"id":"holdingRegisters.1075_P_out2"},{"_address":1077,"name":"operation state","description":"(R) see manual","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1077,"id":"holdingRegisters.1077_operation_state"},{"_address":1081,"name":"Device state","description":"(R/W) 0 or 1","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1081,"id":"holdingRegisters.1081_Device_state"}] modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1000_Power: {"_id":"holdingRegisters.1000_Power","type":"state","common":{"name":"(R/W ) 0-3.500 for Mode 1 ","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":1000,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1002_Tmax_: {"_id":"holdingRegisters.1002_Tmax_","type":"state","common":{"name":"(R) target temperature solar powered","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1002,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}} modbus.0 2026-02-12 21:34:12.081 debug Add holdingRegisters.1004_Power_timout: {"_id":"holdingRegisters.1004_Power_timout","type":"state","common":{"name":"(R/W) 10 - 600sec","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"sec"},"native":{"regType":"holdingRegs","address":1004,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1016_Controller_firmware_main_version: {"_id":"holdingRegisters.1016_Controller_firmware_main_version","type":"state","common":{"name":"(R) (exxxxxyy)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1016,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1014_max_Power: {"_id":"holdingRegisters.1014_max_Power","type":"state","common":{"name":"(R/W) 500-3500 W","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":1014,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1012_Boost_activate: {"_id":"holdingRegisters.1012_Boost_activate","type":"state","common":{"name":"(R/W) see documentation","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1012,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1010_Actual_Time_(Minute): {"_id":"holdingRegisters.1010_Actual_Time_(Minute)","type":"state","common":{"name":"(R/W ) ","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"min"},"native":{"regType":"holdingRegs","address":1010,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1008_Boost_time_1_stop: {"_id":"holdingRegisters.1008_Boost_time_1_stop","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1008,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1006_Tmin: {"_id":"holdingRegisters.1006_Tmin","type":"state","common":{"name":"(R/W) Boost backup target temperature","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1006,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1007_Boost_time_1_start: {"_id":"holdingRegisters.1007_Boost_time_1_start","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1007,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1009_Actual_Time_(Hour): {"_id":"holdingRegisters.1009_Actual_Time_(Hour)","type":"state","common":{"name":"(R/W ) ","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1009,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1011_Actual_Time_(Second): {"_id":"holdingRegisters.1011_Actual_Time_(Second)","type":"state","common":{"name":"(R/W) ","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"sec"},"native":{"regType":"holdingRegs","address":1011,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1013_ELWA_2_Number: {"_id":"holdingRegisters.1013_ELWA_2_Number","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1013,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.082 debug Add holdingRegisters.1015_tempchip: {"_id":"holdingRegisters.1015_tempchip","type":"state","common":{"name":"(R) Controller temperature","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1015,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1065_Operation_mode: {"_id":"holdingRegisters.1065_Operation_mode","type":"state","common":{"name":"(R/W) 1 or 3","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1065,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1061_U_L1: {"_id":"holdingRegisters.1061_U_L1","type":"state","common":{"name":"(R) power stage input voltage","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":1061,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1056_Legionella_mode: {"_id":"holdingRegisters.1056_Legionella_mode","type":"state","common":{"name":"(R/W) 0 or 1","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1056,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1054_Legionella_start: {"_id":"holdingRegisters.1054_Legionella_start","type":"state","common":{"name":"(R/W) 0-23 hrs","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1054,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1030_Temp_2: {"_id":"holdingRegisters.1030_Temp_2","type":"state","common":{"name":"(R) external Sensor of AC ELWA 2","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1030,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1027_Boost_time_2_stop: {"_id":"holdingRegisters.1027_Boost_time_2_stop","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1027,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1017_Powerstage_firmware_version: {"_id":"holdingRegisters.1017_Powerstage_firmware_version","type":"state","common":{"name":"(R) (epxxx)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1017,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1026_Boost_time_2_start: {"_id":"holdingRegisters.1026_Boost_time_2_start","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"h"},"native":{"regType":"holdingRegs","address":1026,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1028_Controller_firmware_sub_version: {"_id":"holdingRegisters.1028_Controller_firmware_sub_version","type":"state","common":{"name":"(R) (exxxxxyy)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1028,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1053_Legionella_interval: {"_id":"holdingRegisters.1053_Legionella_interval","type":"state","common":{"name":"(R/W) 1-14 days","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"day"},"native":{"regType":"holdingRegs","address":1053,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1055_Legionella_temp: {"_id":"holdingRegisters.1055_Legionella_temp","type":"state","common":{"name":"(R/W)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":1055,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1058_Relay_status: {"_id":"holdingRegisters.1058_Relay_status","type":"state","common":{"name":"(R) bit 0 AUX (0 off; 1 on) bit 1 SELV (0 off; 1 on)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1058,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.083 debug Add holdingRegisters.1064_Freq: {"_id":"holdingRegisters.1064_Freq","type":"state","common":{"name":"(R) ","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mHz"},"native":{"regType":"holdingRegs","address":1064,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1081_Device_state: {"_id":"holdingRegisters.1081_Device_state","type":"state","common":{"name":"(R/W) 0 or 1","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1081,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1075_P_out2: {"_id":"holdingRegisters.1075_P_out2","type":"state","common":{"name":"(R) Power at AUX relay","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":1075,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1071_Pmax_abs: {"_id":"holdingRegisters.1071_Pmax_abs","type":"state","common":{"name":"(R) Max. power currently possible","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":1071,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1067_U_L2: {"_id":"holdingRegisters.1067_U_L2","type":"state","common":{"name":"(R) AUX relay voltage","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":1067,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1068_I_L2: {"_id":"holdingRegisters.1068_I_L2","type":"state","common":{"name":"(R) AUX relay current 100mA","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mA"},"native":{"regType":"holdingRegs","address":1068,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1074_P_out1: {"_id":"holdingRegisters.1074_P_out1","type":"state","common":{"name":"(R) Power at ELWA immersion heater","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":1074,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} modbus.0 2026-02-12 21:34:12.084 debug Add holdingRegisters.1077_operation_state: {"_id":"holdingRegisters.1077_operation_state","type":"state","common":{"name":"(R) see manual","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1077,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}} host.borkum-pi5 2026-02-12 21:34:12.142 info stopInstance system.adapter.modbus.0 (force=false, process=true) modbus.0 2026-02-12 21:34:12.145 info Got terminate signal TERMINATE_YOURSELF modbus.0 2026-02-12 21:34:12.155 info terminating modbus.0 2026-02-12 21:34:12.155 debug Plugin sentry destroyed modbus.0 2026-02-12 21:34:12.156 info Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason host.borkum-pi5 2026-02-12 21:34:12.186 info stopInstance system.adapter.modbus.0 send kill signal modbus.0 2026-02-12 21:34:12.380 info Connected to slave 192.168.178.5 modbus.0 2026-02-12 21:34:12.381 debug [DevID_1] Poll start --------------------- modbus.0 2026-02-12 21:34:12.381 warn setTimeout called, but adapter is shutting down modbus.0 2026-02-12 21:34:12.381 debug Initialization of scale factors done! modbus.0 2026-02-12 21:34:12.381 debug [DevID_1/holdingRegs] Poll address 1000 - 1 registers modbus.0 2026-02-12 21:34:12.382 warn setTimeout called, but adapter is shutting down modbus.0 2026-02-12 21:34:12.387 debug [DevID_1/holdingRegs] Poll address 1000 DONE modbus.0 2026-02-12 21:34:12.387 warn setTimeout called, but adapter is shutting down modbus.0 2026-02-12 21:34:12.647 info terminating host.borkum-pi5 2026-02-12 21:34:12.676 info instance system.adapter.modbus.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION) host.borkum-pi5 2026-02-12 21:34:12.849 info instance system.adapter.modbus.0 in version "6.3.2" started with pid 2157 modbus.0 2026-02-12 21:34:13.401 debug Redis Objects: Use Redis connection: 127.0.0.1:9001 modbus.0 2026-02-12 21:34:13.416 debug Objects client ready ... initialize now modbus.0 2026-02-12 21:34:13.417 debug Objects create System PubSub Client modbus.0 2026-02-12 21:34:13.417 debug Objects create User PubSub Client modbus.0 2026-02-12 21:34:13.436 debug Objects client initialize lua scripts modbus.0 2026-02-12 21:34:13.438 debug Objects connected to redis: 127.0.0.1:9001 modbus.0 2026-02-12 21:34:13.458 debug Redis States: Use Redis connection: 127.0.0.1:9000 modbus.0 2026-02-12 21:34:13.463 debug States create System PubSub Client modbus.0 2026-02-12 21:34:13.464 debug States create User PubSub Client modbus.0 2026-02-12 21:34:13.514 debug States connected to redis: 127.0.0.1:9000 modbus.0 2026-02-12 21:34:13.528 debug Plugin sentry Do not initialize Plugin (enabled=false) host.borkum-pi5 2026-02-12 21:34:13.573 info "system.adapter.modbus.0" disabled host.borkum-pi5 2026-02-12 21:34:13.573 info stopInstance system.adapter.modbus.0 (force=false, process=true) modbus.0 2026-02-12 21:34:13.578 info Got terminate signal TERMINATE_YOURSELF modbus.0 2026-02-12 21:34:13.582 info starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v22.22.0, js-controller: 7.0.7 host.borkum-pi5 2026-02-12 21:34:13.624 info stopInstance system.adapter.modbus.0 send kill signal modbus.0 2026-02-12 21:34:14.079 info terminating modbus.0 2026-02-12 21:34:14.080 debug Plugin sentry destroyed modbus.0 2026-02-12 21:34:14.080 info Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason host.borkum-pi5 2026-02-12 21:34:14.600 info instance system.adapter.modbus.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION) javascript.0 2026-02-12 21:34:14.602 warn script.js.Statusinfos.Modbusfehler: Cannot restart instance "modbus.0", because not running -
-
@Homoran sagte in Problem mit Modbusadapter:
da läuft noch was
klar läuft da noch was in Javascript. Heizungssteuerung rund Rest vom Haus
@ubecker sagte in Problem mit Modbusadapter:
Heizungssteuerung
heisst
@ubecker sagte in Problem mit Modbusadapter:
script.js.Statusinfos.Modbusfehler:
???
und
er: Cannot restart instance "modbus.0"
-
@ubecker sagte in Problem mit Modbusadapter:
Heizungssteuerung
heisst
@ubecker sagte in Problem mit Modbusadapter:
script.js.Statusinfos.Modbusfehler:
???
und
er: Cannot restart instance "modbus.0"
-
@Homoran sagte in Problem mit Modbusadapter:
???
Das sind scripte die direkt auf die Heeizung zugreifen, Messungen aber alles über MQTT.
Modbus ist hier nur für einen Steuerbaren Heizstab für Warmwasser@ubecker und was versucht das Skript da
er: Cannot restart instance "modbus.0"
-
@Homoran sagte in Problem mit Modbusadapter:
er: Cannot restart instance "modbus.0"
sind etliche. Es wird PV ertrag gemessen, Viele Verbräuche von Strom, Darauf wird der PV Überschuss berechnet und an den Heizstag gegeben. Ist ein sehr alter Wechselrichter auf den kein Zugriff vorhanden ist, so muss ich alle Werte anders messen und daraus den Überschuss der PV
kann aber mal komplett alles abschalten, kurz, MQTT, Javascript -
Kannst du mal ALLE Scripte kurzzeitig stoppen?
Es wäre zu klären ob es irgendein Skript gibt, dass den Adapter beendet. Irgendwas scheint den Adapter vis system states zu stoppen.
Im Prinzip wäre natürlich das allerbste ALLE Adapter (aßer admin) zu stoppen und zu checken ob dann modbus startet. Damit sollte man checken können ob was im Adapter faul ist oder von außen reingreift.Zusätzlich kannst du auch die neueste Version testen. War seit November im LATEST verfügbar und wurde heute ins STABLE released, sollte also morgen dort verfügbar sein. Lt. Releasenotes wurde nichts was offensichtloich mit deinem Problem zusammenhängt gefixed. Aber wenn man im Adapter zu suchen anfängt, macht das nur Sinn mit der neuesten Version.
EDIT:
Grad gesehn, dass du das eh schon angeboten hast. DANKE -
@Homoran sagte in Problem mit Modbusadapter:
er: Cannot restart instance "modbus.0"
sind etliche. Es wird PV ertrag gemessen, Viele Verbräuche von Strom, Darauf wird der PV Überschuss berechnet und an den Heizstag gegeben. Ist ein sehr alter Wechselrichter auf den kein Zugriff vorhanden ist, so muss ich alle Werte anders messen und daraus den Überschuss der PV
kann aber mal komplett alles abschalten, kurz, MQTT, Javascriptsagte in Problem mit Modbusadapter:
aber mal komplett alles abschalten, kurz, MQTT, Javascript
so, alles abgeschaltet, dann Modbus eingeschaltet - und ok. Alle wieder eingeschaltet - und ok. jetzt kann ich auch das eine oder andere abschalten, ist immer ok.
Keine Ahnung was da los ist. Neustart alle Instanzen an ausser Modbus. Dann modbus eingeschaltet geht nicht (Problem wie vorher)
Wieder MQTT und Javascript abgeschaltet - Modbus eingeschaltet danach wieder alles ein. So läuft alles.
Warum auch immer.
Da das hier ein life system ist kann ich da nicht viele Möglichkeiten teste.Aber danke an alle.
-
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht - siehe log Eintrag.
Als Arbeitshypothese würde ich mal annehmen, dass das Script sich komisch verhält wenn der Modbus Adapter nicht läuft. Das neue OS kann das Timing beim Starten verändert haben.Da der Modbus bei ansonsten laufendem System nicht startbar ist, kannst du folgendes Versuchen:
- modbus stoppen
- modbus starten - wird schief gehen
- Script für Script beenden und modbus zversuchen zu starten
- spätestens wenn alle scripte gestopp sind sollte der modbus starten. Realistischer Weise aber früher. Und damit sollte das zuletzt gestoppte Scritp hoch verdächtig sein.
-
ich wollte doch hier nur auf Trixie updaten. Jetzt bin ich hier schon den ganzen Tag zugange. Mach jetzt schluss. (ist auf Borkum)
-
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht - siehe log Eintrag.
Als Arbeitshypothese würde ich mal annehmen, dass das Script sich komisch verhält wenn der Modbus Adapter nicht läuft. Das neue OS kann das Timing beim Starten verändert haben.Da der Modbus bei ansonsten laufendem System nicht startbar ist, kannst du folgendes Versuchen:
- modbus stoppen
- modbus starten - wird schief gehen
- Script für Script beenden und modbus zversuchen zu starten
- spätestens wenn alle scripte gestopp sind sollte der modbus starten. Realistischer Weise aber früher. Und damit sollte das zuletzt gestoppte Scritp hoch verdächtig sein.
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Hatte ich vergessen das das hier auch drin ist. -
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Hatte ich vergessen das das hier auch drin ist. -
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Hatte ich vergessen das das hier auch drin ist.@ubecker sagte in (erledigt)Problem mit Modbusadapter:
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Dann schau dir mal die neue (Major) Release an. Da wurde ein Memory Leak behoben:
https://github.com/ioBroker/iobroker.modbus#700-2025-10-06
Sowas könnte ev. dein Symptom erklären. -
@ubecker sagte in (erledigt)Problem mit Modbusadapter:
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Dann schau dir mal die neue (Major) Release an. Da wurde ein Memory Leak behoben:
https://github.com/ioBroker/iobroker.modbus#700-2025-10-06
Sowas könnte ev. dein Symptom erklären. -
@mcm1957 sagte in Problem mit Modbusadapter:
Also such mal gezielt nach dem Script wo das restarten des modbus Adapters drinnen steht
jaaaa, da der Modbusadapter das Problem hat nach ca 2 - 3 Wochen dann täglich einen Timeoutfehler zu produzieren gibt es ein Script das den Adapter neu startet wenn der Fehler auftritt. Diesen Fehler hatte ich schon vor langem mal gemeldet. ( habe ich an allen systemen mit Modbus, andere auch)
Hatte ich vergessen das das hier auch drin ist.@ubecker das hatte ich dir doch gezeigt
sagte in (erledigt)Problem mit Modbusadapter:
@ubecker sagte in Problem mit Modbusadapter:
Heizungssteuerung
heisst
@ubecker sagte in Problem mit Modbusadapter:
script.js.Statusinfos.Modbusfehler:
???
und
er: Cannot restart instance "modbus.0"
bei diesem Block
@ubecker sagte in (erledigt)Problem mit Modbusadapter:
sagte in Problem mit Modbusadapter:
Hatte ich vergessen das das hier auch drin ist.

bin ich überfragt, aber genau so etwas hab ich befürchtet
ein restart ist kein start.
der Restart stoppt vorher einen laufenden Adapter
(zumindest auf der Konsole)