  4. Einbinden von Modbus - R4DCB08 sensoren
29 Beiträge 2 Kommentatoren 1.5k Aufrufe 1 Beobachtet
  • M Marc 3
    inputRegs: [{"_address":"1","deviceId":3,"name":"Temp","description":"Temp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value.temperature","room":"","cw":"","isScale":"","address":1,"id":"inputRegisters.1_Temp"}]
    hattest du was geändert?
    ja, das hatte ich mal auf "nichts" gestellt
    und was bei den Holdingregistern eingetragen?
    auch hier hab ich mal was ausprobiert, aber leider ohne Erfolg
    modbus.4
    	2024-10-20 20:30:06.239	warn	Poll error count: 4 code: "ReadInputRegisters: Invalid FC 3"
    modbus.4
    	2024-10-20 20:30:05.928	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
    modbus.4
    	2024-10-20 20:30:05.926	debug	[DevID_3] Poll start ---------------------
    modbus.4
    	2024-10-20 20:29:55.874	warn	Poll error count: 3 code: "ReadInputRegisters: Invalid FC 3"
    modbus.4
    	2024-10-20 20:29:55.563	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
    modbus.4
    	2024-10-20 20:29:55.562	debug	[DevID_3] Poll start ---------------------
    modbus.4
    	2024-10-20 20:29:45.510	warn	Poll error count: 2 code: "ReadInputRegisters: Invalid FC 3"
    modbus.4
    	2024-10-20 20:29:45.199	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
    modbus.4
    	2024-10-20 20:29:45.197	debug	[DevID_3] Poll start ---------------------
    modbus.4
    	2024-10-20 20:29:35.144	warn	Poll error count: 1 code: "ReadInputRegisters: Invalid FC 3"
    modbus.4
    	2024-10-20 20:29:34.102	error	unknown function code: 0x0, 0xc1
    modbus.4
    	2024-10-20 20:29:34.091	error	Error response: Value is not accepted by slave
    modbus.4
    	2024-10-20 20:29:34.089	error	Error response for FCx17: Illegal Data Value
    modbus.4
    	2024-10-20 20:29:33.339	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
    modbus.4
    	2024-10-20 20:29:33.338	debug	Initialization of scale factors done!
    modbus.4
    	2024-10-20 20:29:33.334	debug	[DevID_3] Poll start ---------------------
    modbus.4
    	2024-10-20 20:29:33.332	info	Connected to slave
    modbus.4
    	2024-10-20 20:29:33.304	debug	connect to serial /dev/ttyUSB0 with 9600
    modbus.4
    	2024-10-20 20:29:32.138	debug	Initialize Objects for holdingRegs: []
    modbus.4
    	2024-10-20 20:29:32.137	debug	Add inputRegisters.1_Temp: {"_id":"inputRegisters.1_Temp","type":"state","common":{"name":"Temp","role":"value.temperature","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":1,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.4
    	2024-10-20 20:29:32.135	debug	Initialize Objects for inputRegs: [{"_address":"1","deviceId":3,"name":"Temp","description":"Temp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value.temperature","room":"","cw":"","isScale":"","address":1,"id":"inputRegisters.1_Temp"}]
    modbus.4
    	2024-10-20 20:29:32.134	debug	Initialize Objects for coils: []
    modbus.4
    	2024-10-20 20:29:32.127	debug	Initialize Objects for disInputs: []
    modbus.4
    	2024-10-20 20:29:31.305	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 4.0.24
    modbus.4
    	2024-10-20 20:29:29.864	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.4
    	2024-10-20 20:29:18.548	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.4
    	2024-10-20 20:29:18.547	debug	Plugin sentry destroyed
    modbus.4
    	2024-10-20 20:29:18.545	info	terminating
    modbus.4
    	2024-10-20 20:29:18.542	info	Got terminate signal TERMINATE_YOURSELF
    modbus.4
    	2024-10-20 20:28:50.621	debug	Cleaning up request fifo.
    modbus.4
    	2024-10-20 20:28:50.616	debug	Clearing timeout of the current request.
    modbus.4
    	2024-10-20 20:28:50.601	info	Disconnected from slave
    @marc-3 sagte in Einbinden von Modbus - R4DCB08 sensoren:
    ich kenne den Temperaturbereich nicht, abe u(nsigned) bedeutet ohne Vorzeichen.
    Das ist bei Temperaturen eigentlich unüblich
    nimm mal Int16be
    mach das weg!
    @homoran sagte in Einbinden von Modbus - R4DCB08 sensoren:
    immer nur mit einem probieren bis es läuft
    sobald auch nur ein Fehler drin ist, kommt kein einziger Wert
      Marc 3
      Hab alles andere raus.
      Int16be hat aber nur eine Länge von 1, ich brauche aber eine Länge von 2. Der Temperaturwert sieht dann wie folgt aus: erste Ziffer 0 = +, 1=-. Rest ist Hex, muss in's Dec und *0,1. Gibt es dafür einen geeigneten Typ?
      modbus.4
      	2024-10-20 20:40:00.478	warn	Poll error count: 4 code: "ReadInputRegisters: Invalid FC 3"
      modbus.4
      	2024-10-20 20:40:00.141	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
      modbus.4
      	2024-10-20 20:40:00.139	debug	[DevID_3] Poll start ---------------------
      modbus.4
      	2024-10-20 20:39:50.087	warn	Poll error count: 3 code: "ReadInputRegisters: Invalid FC 3"
      modbus.4
      	2024-10-20 20:39:49.775	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
      modbus.4
      	2024-10-20 20:39:49.773	debug	[DevID_3] Poll start ---------------------
      modbus.4
      	2024-10-20 20:39:39.721	warn	Poll error count: 2 code: "ReadInputRegisters: Invalid FC 3"
      modbus.4
      	2024-10-20 20:39:39.418	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
      modbus.4
      	2024-10-20 20:39:39.416	debug	[DevID_3] Poll start ---------------------
      modbus.4
      	2024-10-20 20:39:29.362	warn	Poll error count: 1 code: "ReadInputRegisters: Invalid FC 3"
      modbus.4
      	2024-10-20 20:39:28.315	error	unknown function code: 0x0, 0xc3
      modbus.4
      	2024-10-20 20:39:28.303	error	Error response: Value is not accepted by slave
      modbus.4
      	2024-10-20 20:39:28.301	error	Error response for FCx17: Illegal Data Value
      modbus.4
      	2024-10-20 20:39:27.651	debug	[DevID_3/inputRegs] Poll address 1 - 1 registers
      modbus.4
      	2024-10-20 20:39:27.649	debug	Initialization of scale factors done!
      modbus.4
      	2024-10-20 20:39:27.645	debug	[DevID_3] Poll start ---------------------
      modbus.4
      	2024-10-20 20:39:27.641	info	Connected to slave
      modbus.4
      	2024-10-20 20:39:27.614	debug	connect to serial /dev/ttyUSB0 with 9600
      modbus.4
      	2024-10-20 20:39:26.378	debug	Initialize Objects for holdingRegs: []
      modbus.4
      	2024-10-20 20:39:26.377	debug	Add inputRegisters.1_Temp: {"_id":"inputRegisters.1_Temp","type":"state","common":{"name":"Temp","role":"value.temperature","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":1,"deviceId":3,"type":"int16be","len":1,"offset":0,"factor":1}}
      modbus.4
      	2024-10-20 20:39:26.376	debug	Initialize Objects for inputRegs: [{"_address":"1","deviceId":3,"name":"Temp","description":"Temp","unit":"","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value.temperature","room":"","cw":"","isScale":"","address":1,"id":"inputRegisters.1_Temp"}]
      modbus.4
      	2024-10-20 20:39:26.375	debug	Initialize Objects for coils: []
      modbus.4
      	2024-10-20 20:39:26.374	debug	Initialize Objects for disInputs: []
      modbus.4
      	2024-10-20 20:39:25.311	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 4.0.24
      modbus.4
      	2024-10-20 20:39:23.754	debug	Plugin sentry Initialize Plugin (enabled=true)
      modbus.4
      	2024-10-20 20:39:22.063	debug	States connected to redis: 127.0.0.1:9000
      modbus.4
      	2024-10-20 20:39:21.413	debug	States create User PubSub Client
      modbus.4
      	2024-10-20 20:39:21.408	debug	States create System PubSub Client
      modbus.4
      	2024-10-20 20:39:21.181	debug	Redis States: Use Redis connection: 127.0.0.1:9000
      modbus.4
      	2024-10-20 20:39:21.000	debug	Objects connected to redis: 127.0.0.1:9001
      modbus.4
      	2024-10-20 20:39:20.900	debug	Objects client initialize lua scripts
      modbus.4
      	2024-10-20 20:39:20.303	debug	Objects create User PubSub Client
      modbus.4
      	2024-10-20 20:39:20.300	debug	Objects create System PubSub Client
      modbus.4
      	2024-10-20 20:39:20.184	debug	Objects client ready ... initialize now
      modbus.4
      	2024-10-20 20:39:19.773	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
      modbus.4
      	2024-10-20 20:39:12.156	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
      modbus.4
      	2024-10-20 20:39:12.155	debug	Plugin sentry destroyed
      modbus.4
      	2024-10-20 20:39:12.153	info	terminating
      modbus.4
      	2024-10-20 20:39:12.150	info	Got terminate signal TERMINATE_YOURSELF
      modbus.4
      	2024-10-20 20:38:47.233	info	List of port: [{"path":"/dev/ttyS0"},{"path":"/dev/ttyS1"},{"path":"/dev/ttyS2"},{"path":"/dev/ttyS3"},{"path":"/dev/ttyUSB0"}]
      modbus.4
      	2024-10-20 20:38:47.231	info	Check /dev/ttyUSB0 : true
      modbus.4
      	2024-10-20 20:38:47.230	info	Check /dev/ttyS3 : true
      modbus.4
      	2024-10-20 20:38:47.230	info	Check /dev/ttyS2 : true
      modbus.4
      	2024-10-20 20:38:47.229	info	Check /dev/ttyS1 : true
      modbus.4
      	2024-10-20 20:38:47.226	info	Check /dev/ttyS0 : true
      modbus.4
      	2024-10-20 20:38:47.221	info	Verify [{"path":"/dev/ttyUSB0","manufacturer":"FTDI","serialNumber":"A10OG1BO","pnpId":"usb-FTDI_FT232R_USB_UART_A10OG1BO-if00-port0","vendorId":"0403","productId":"6001"},{"path":"/dev/ttyS1"},{"path":"/dev/ttyS2"},{"path":"/dev/ttyS3"},{"path":"/dev/ttyS0"}]
      modbus.4
      	2024-10-20 20:38:29.263	debug	Cleaning up request fifo.
      modbus.4
      	2024-10-20 20:38:29.262	debug	Clearing timeout of the current request.
      modbus.4
      	2024-10-20 20:38:29.252	info	Disconnected from slave
      • M Marc 3
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        modbus.4
        dann doch int32be 🤔 ich hab schief gedacht: 16bit sind 2 byte 😊
        hab gerade nachgesehen, stimmt!
        Bei länge von 2 hab ich auch (u)Int32be
        Da bin ich überfragt.
        Die fuunction codes erzeugt der Adapter
        fc3 ist
        Read Multiple Holding Registers fc3
        Quelle: https://en.m.wikipedia.org/wiki/Modbus
        wieso das noch auftritt wenn da nichts drin steht ???
        edit:
        trag die gleichen Werte mal statt bei inputRegisters bei Holdingregister ein
        manche Geräte wollen das so
          Marc 3
          Eingangs und Holding nun das gleiche:
          Interessant is der "unkown function code: 0x0, 0xc0" das ergibt rund 19,2°C, was für meinen Keller realistisch ist und was auch der Wert des ersten Temp Sensors ist:
          modbus.4
          	2024-10-20 21:10:13.258	warn	Poll error count: 2 code: "ReadInputRegisters: Invalid FC 3"
          modbus.4
          	2024-10-20 21:10:12.965	debug	[DevID_3/inputRegs] Poll address 0 - 2 registers
          modbus.4
          	2024-10-20 21:10:12.963	debug	[DevID_3] Poll start ---------------------
          modbus.4
          	2024-10-20 21:10:02.902	warn	Poll error count: 1 code: "ReadInputRegisters: Invalid FC 3"
          modbus.4
          	2024-10-20 21:10:01.850	error	unknown function code: 0x0, 0xc0
          modbus.4
          	2024-10-20 21:10:01.836	error	Error response: Value is not accepted by slave
          modbus.4
          	2024-10-20 21:10:01.836	error	Error response for FCx17: Illegal Data Value
          modbus.4
          	2024-10-20 21:10:01.368	debug	[DevID_3/inputRegs] Poll address 0 - 2 registers
          modbus.4
          	2024-10-20 21:10:01.367	debug	Initialization of scale factors done!
          modbus.4
          	2024-10-20 21:10:01.360	debug	[DevID_3] Poll start ---------------------
          modbus.4
          	2024-10-20 21:10:01.355	info	Connected to slave
          modbus.4
          	2024-10-20 21:10:01.331	debug	connect to serial /dev/ttyUSB0 with 9600
          modbus.4
          	2024-10-20 21:09:59.175	debug	Add holdingRegisters.1_TempH: {"_id":"holdingRegisters.1_TempH","type":"state","common":{"name":"TempH","role":"level","type":"number","read":false,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1,"deviceId":3,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":""}}
          modbus.4
          	2024-10-20 21:09:59.173	debug	Initialize Objects for holdingRegs: [{"_address":"1","name":"TempH","description":"TempH","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":"","wp":"","cw":"","isScale":"","address":1,"deviceId":3,"id":"holdingRegisters.1_TempH"}]
          modbus.4
          	2024-10-20 21:09:59.172	debug	Add inputRegisters.0_Temp: {"_id":"inputRegisters.0_Temp","type":"state","common":{"name":"Temp","role":"level","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":0,"deviceId":3,"type":"uint32be","len":2,"offset":0,"factor":1}}
          modbus.4
          	2024-10-20 21:09:59.170	debug	Initialize Objects for inputRegs: [{"_address":0,"name":"Temp","description":"Temp","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":0,"deviceId":3,"id":"inputRegisters.0_Temp"}]
          modbus.4
          	2024-10-20 21:09:59.168	debug	Initialize Objects for coils: []
          modbus.4
          	2024-10-20 21:09:59.166	debug	Initialize Objects for disInputs: []
          modbus.4
          	2024-10-20 21:09:58.517	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 4.0.24
          modbus.4
          	2024-10-20 21:09:57.170	debug	Plugin sentry Initialize Plugin (enabled=true)
          modbus.4
          	2024-10-20 21:09:46.117	debug	Cleaning up request fifo.
          modbus.4
          	2024-10-20 21:09:46.102	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
          modbus.4
          	2024-10-20 21:09:46.101	debug	Plugin sentry destroyed
          modbus.4
          	2024-10-20 21:09:46.099	info	terminating
          Falls ich dich falsch verstanden hab und das Eingangsregister löschen soll und nur Holding:
          modbus.4
          	2024-10-20 21:18:59.090	debug	No current request.
          modbus.4
          	2024-10-20 21:18:58.045	debug	No current request.
          modbus.4
          	2024-10-20 21:18:57.007	debug	No current request.
          modbus.4
          	2024-10-20 21:18:55.964	debug	No current request.
          modbus.4
          	2024-10-20 21:18:54.940	debug	No current request.
          modbus.4
          	2024-10-20 21:18:53.901	debug	No current request.
          modbus.4
          	2024-10-20 21:18:53.367	debug	[DevID_3] Poll start ---------------------
          modbus.4
          	2024-10-20 21:18:52.861	debug	No current request.
          modbus.4
          	2024-10-20 21:18:51.821	debug	No current request.
          modbus.4
          	2024-10-20 21:18:50.782	debug	No current request.
          modbus.4
          	2024-10-20 21:18:49.742	debug	No current request.
          modbus.4
          	2024-10-20 21:18:48.717	debug	No current request.
          modbus.4
          	2024-10-20 21:18:47.664	debug	No current request.
          modbus.4
          	2024-10-20 21:18:46.638	debug	No current request.
          modbus.4
          	2024-10-20 21:18:45.599	debug	No current request.
          modbus.4
          	2024-10-20 21:18:44.559	debug	No current request.
          modbus.4
          	2024-10-20 21:18:43.520	debug	No current request.
          modbus.4
          	2024-10-20 21:18:43.313	debug	[DevID_3] Poll start ---------------------
          modbus.4
          	2024-10-20 21:18:42.482	debug	No current request.
          modbus.4
          	2024-10-20 21:18:41.439	debug	No current request.
          modbus.4
          	2024-10-20 21:18:40.415	debug	No current request.
          modbus.4
          	2024-10-20 21:18:39.375	debug	No current request.
          modbus.4
          	2024-10-20 21:18:38.335	debug	No current request.
          modbus.4
          	2024-10-20 21:18:37.295	debug	No current request.
          modbus.4
          	2024-10-20 21:18:36.258	debug	No current request.
          modbus.4
          	2024-10-20 21:18:35.224	debug	No current request.
          modbus.4
          	2024-10-20 21:18:34.179	error	unknown function code: 0x0, 0xc3
          modbus.4
          	2024-10-20 21:18:34.162	error	Error response: Value is not accepted by slave
          modbus.4
          	2024-10-20 21:18:34.161	error	Error response for FCx17: Illegal Data Value
          modbus.4
          	2024-10-20 21:18:33.258	debug	[DevID_3] Poll start ---------------------
          modbus.4
          	2024-10-20 21:18:33.255	info	Connected to slave
          modbus.4
          	2024-10-20 21:18:33.225	debug	connect to serial /dev/ttyUSB0 with 9600
          modbus.4
          	2024-10-20 21:18:32.240	debug	Remove old object modbus.4.inputRegisters.0_Temp
          modbus.4
          	2024-10-20 21:18:32.006	debug	Add holdingRegisters.1_TempH: {"_id":"holdingRegisters.1_TempH","type":"state","common":{"name":"TempH","role":"level","type":"number","read":false,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1,"deviceId":3,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":""}}
          modbus.4
          	2024-10-20 21:18:32.005	debug	Initialize Objects for holdingRegs: [{"_address":"1","name":"TempH","description":"TempH","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":"","wp":"","cw":"","isScale":"","address":1,"deviceId":3,"id":"holdingRegisters.1_TempH"}]
          modbus.4
          	2024-10-20 21:18:32.004	debug	Initialize Objects for inputRegs: []
          modbus.4
          	2024-10-20 21:18:32.002	debug	Initialize Objects for coils: []
          modbus.4
          	2024-10-20 21:18:32.001	debug	Initialize Objects for disInputs: []
          modbus.4
          	2024-10-20 21:18:31.502	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 4.0.24
          modbus.4
          	2024-10-20 21:18:29.259	debug	Plugin sentry Initialize Plugin (enabled=true)
          modbus.4
          	2024-10-20 21:18:18.042	debug	Cleaning up request fifo.
          modbus.4
          	2024-10-20 21:18:18.042	debug	Clearing timeout of the current request.
          modbus.4
          	2024-10-20 21:18:18.030	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
          modbus.4
          	2024-10-20 21:18:18.029	debug	Plugin sentry destroyed
          modbus.4
          	2024-10-20 21:18:18.027	info	terminating
          modbus.4
          	2024-10-20 21:18:18.022	info	Got terminate signal TERMINATE_YOURSELF
          • M Marc 3
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            modbus.4
            ja, aber Haken bei Abfrage setzen
              Marc 3
              schrieb am zuletzt editiert von Marc 3
              wir kommen voran! die 12714179°C aktualisieren sich alle ~1 sekunde (alle 1 Sekunde wird der Wert tatsächlich gesendet, daher ist die Polltime quatsch, ABER!!!! es kommt was an)
              Jetzt muss man das nur noch in 8 verschiedene Temperaturwerte aufdröseln, entsprechend umwandeln, dann hätten wir es schon.
              12714179 in Hex sind C2 00 C3 und scheint die Antwort auf die Anfrage davor zu sein.
              modbus.4
              	2024-10-20 21:28:12.583	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:28:12.512	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:28:12.511	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:28:02.457	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:28:02.392	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:28:02.390	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:27:52.331	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:27:52.262	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:27:52.261	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:27:42.205	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:27:42.133	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:27:42.132	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:27:32.078	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:27:32.007	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:27:32.006	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:27:21.936	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:27:21.864	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:27:21.863	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:27:11.809	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:27:10.770	error	Error response: 0
              modbus.4
              	2024-10-20 21:27:10.755	error	Wrong CRC for frame: 3,3,16,0,193,0,194,0,195,0,193,0,192,0,191,0,195,3,3,16,0
              modbus.4
              	2024-10-20 21:27:09.720	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:27:09.719	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:59.668	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:59.596	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:59.595	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:49.542	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:49.471	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:49.470	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:39.416	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:39.346	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:39.345	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:29.289	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:28.249	error	Error response: 0
              modbus.4
              	2024-10-20 21:26:28.233	error	Wrong CRC for frame: 3,3,16,0,254,56,64,240,128,195,0,193,4,145,3,3,16,0,192,0,194
              modbus.4
              	2024-10-20 21:26:27.177	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:27.176	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:17.122	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:17.065	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:17.064	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:26:07.012	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:26:06.943	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:26:06.941	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:56.885	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:56.814	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:56.812	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:46.759	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:45.719	error	unknown function code: 0x0, 0xc0
              modbus.4
              	2024-10-20 21:25:45.703	error	Wrong CRC for frame: 3,3,16,0,192,0,194,0,195,0,193,17,91,3,3,16,0,192,0,194,0
              modbus.4
              	2024-10-20 21:25:44.658	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:44.657	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:34.602	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:34.533	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:34.532	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:24.476	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:24.408	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:24.407	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:14.350	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:14.277	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:14.276	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:25:04.223	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:25:03.202	error	Wrong CRC for frame: 3,3,16,0,192,0,194,0,195,0,193,0,192,0,192,0,195,0,193,4,209
              modbus.4
              	2024-10-20 21:25:03.179	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:25:03.178	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:53.123	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:53.048	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:53.047	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:42.995	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:42.925	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:42.924	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:32.869	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:32.796	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:32.795	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:22.742	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:22.722	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:22.719	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:12.664	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:12.597	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:12.594	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:24:02.539	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:24:02.471	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:24:02.470	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:23:52.413	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:23:52.349	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:23:52.347	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:23:42.290	debug	[DevID_3/holdingRegs] Poll address 1 DONE
              modbus.4
              	2024-10-20 21:23:41.245	error	Error response: 0
              modbus.4
              	2024-10-20 21:23:41.229	error	unknown function code: 0x5e, 0x3
              modbus.4
              	2024-10-20 21:23:40.529	error	Error response: Value is not accepted by slave
              modbus.4
              	2024-10-20 21:23:40.528	error	Error response for FCx17: Illegal Data Value
              modbus.4
              	2024-10-20 21:23:40.456	debug	[DevID_3/holdingRegs] Poll address 1 - 2 registers
              modbus.4
              	2024-10-20 21:23:40.454	debug	Initialization of scale factors done!
              modbus.4
              	2024-10-20 21:23:40.448	debug	[DevID_3] Poll start ---------------------
              modbus.4
              	2024-10-20 21:23:40.432	info	Connected to slave
              modbus.4
              	2024-10-20 21:23:40.383	debug	connect to serial /dev/ttyUSB0 with 9600
              modbus.4
              	2024-10-20 21:23:39.163	debug	Add holdingRegisters.1_TempH: {"_id":"holdingRegisters.1_TempH","type":"state","common":{"name":"TempH","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1,"deviceId":3,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
              modbus.4
              	2024-10-20 21:23:39.159	debug	Initialize Objects for holdingRegs: [{"_address":"1","name":"TempH","description":"TempH","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":1,"deviceId":3,"id":"holdingRegisters.1_TempH"}]
              modbus.4
              	2024-10-20 21:23:39.156	debug	Initialize Objects for inputRegs: []
              modbus.4
              	2024-10-20 21:23:39.144	debug	Initialize Objects for coils: []
              modbus.4
              	2024-10-20 21:23:39.133	debug	Initialize Objects for disInputs: []
              modbus.4
              	2024-10-20 21:23:38.554	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 4.0.24
              modbus.4
              	2024-10-20 21:23:36.715	debug	Plugin sentry Initialize Plugin (enabled=true)
              modbus.4
              	2024-10-20 21:23:34.615	debug	States connected to redis: 127.0.0.1:9000
              modbus.4
              	2024-10-20 21:23:34.016	debug	States create User PubSub Client
              modbus.4
              	2024-10-20 21:23:34.014	debug	States create System PubSub Client
              modbus.4
              	2024-10-20 21:23:33.771	debug	Redis States: Use Redis connection: 127.0.0.1:9000
              modbus.4
              	2024-10-20 21:23:33.401	debug	Objects connected to redis: 127.0.0.1:9001
              modbus.4
              	2024-10-20 21:23:33.082	debug	Objects client initialize lua scripts
              modbus.4
              	2024-10-20 21:23:32.281	debug	Objects create User PubSub Client
              modbus.4
              	2024-10-20 21:23:32.278	debug	Objects create System PubSub Client
              modbus.4
              	2024-10-20 21:23:32.160	debug	Objects client ready ... initialize now
              modbus.4
              	2024-10-20 21:23:31.770	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
              modbus.4
              	2024-10-20 21:23:25.797	warn	get state error: Connection is closed.
              modbus.4
              	2024-10-20 21:23:25.284	debug	Cleaning up request fifo.
              modbus.4
              	2024-10-20 21:23:25.269	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
              • M Marc 3
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                modbus.4
                was ist denn das Intervall?
                hier
                https://forum.iobroker.net/post/1211358
                waren es 10 Sekunden.
                nee, das sind verschiedene Register pro Sensor
                Möglicherweise ist auch nur das Zahlenformat falsch.
                wenn du uint32 hast mal int32 nehmen oder umgekehrt
                • M Marc 3
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  modbus.4
                  das ist die Dauer des polls von request bis zur Antwort
                    Marc 3
                    Es tut :
                    jetzt nur noch die Werte mit 0,1 multiplizieren und es ist erledigt :)
                    • M Marc 3
                      Es tut :
                      Expertenmodus (Kopf) aktivieren.
                      Spalte Faktor erscheint :-)
                      also doch Int16!???
                        fc3 ist
                        edit:
                        edit:
                        steht doch auch hier 🤦
                        fc3 ist Read Holdingregister
                          edit:
                          Marc 3
                          Naja, wenn man das lesen kann... Aber vielen Dank dir, für deine Unterstützung :) nun läuft es.
                          nächster Schritt, schauen, was passiert, wenn's über 25,5°C wird (Länge 1 = FF = 25,5°C)
                          übernächster Schritt, alles über ModBus to ETH Adapter.
                          Das alles aber erst, wenn ich wieder Zeit dafür hab.
                          Vielen Dank nochmal und einen schönen Abend noch!
                          • M Marc 3
                            das sollte dann zumindest mit den Modbusadapter Einstellungen klappen.
                            Dann muss nur noch ™ der Konverter korrekt konfiguriert werden.
                            dann doch Int32be??
                            was kam denn jetzt dahei raus?
                            gerne und dito!
                              Marc 3
                              @Homoran Um das ganze nochmal abzuschließen.
                              ja es ist Signed16BE, trotz dessen, dass es 4 Stellig ist. Bei 32 hatte ich das Problem, dass 2 Werte zusammen genommen wurden.
                              Modbus Adapter per Ethernet hat heut auch geklappt.
                              Als nächstes kommen noch meine weiteren Boards dran, dann kann ich endlich sehen, was meine Fußbodenheizung so macht. Wenn ich es von meinem Brettaufbau verteilt fest eingebaut habe :-)
                              (In jeden Verteiler kommt ein Board mich bis zu 8 Sensoren, und im Keller direkt an der Heizung auch an den Vor/Rücklauf.)
                              Insgesamt hat mich das nun keine 100€ gekostet. Alternative und sicher einfacher wäre alles in KNX gewesen, aber preislich ist as über Modbus und den günstigen Sensoren kein Vergleich.