Skip to content
  • Aktuell
  • Tags
  • 0 Ungelesen 0
  • Kategorien
  • Unreplied
  • Beliebt
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Standard: (Kein Skin)
  • Kein Skin
Einklappen
ioBroker Logo
  1. ioBroker Community Home
  2. Deutsch
  3. Einsteigerfragen
  4. Einbindung von Geräten
  5. Deye Wechselrichter Modbus Register beschreiben

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.2k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    1.9k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.2k

Deye Wechselrichter Modbus Register beschreiben

Geplant Angeheftet Gesperrt Verschoben Einbindung von Geräten
230 Beiträge 27 Kommentatoren 57.9k Aufrufe 26 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • miaelM Offline
    miaelM Offline
    miael
    schrieb am zuletzt editiert von
    #130

    Inzwischen habe ich meinen Anschluss noch aufgeräumt.
    Vom BMS Port mit einem Adapter auf Schraubpins. Daran sind dann nur die Leitungen zum BMS und zum Modbus Adapter angeschlossen. 12Volt kommt direkt vom Inverter:
    IMG_20230809_091040.jpg

    Die Stromversorgung werde ich noch auf extern ändern, damit ich den WR auch per Modbus an und ausschalten kann.

    Hier meine Iobroker Einstellunge:
    Unbenannt1.JPG

    Unbenannt2.JPG

    Hier die vom Elfin:
    Unbenannt3.JPG

    Und hier noch Bsp für die Register:
    60713d9f-52be-4c2c-a246-3fbfbaac1456-grafik.png

    wendy2702W 1 Antwort Letzte Antwort
    0
    • miaelM Offline
      miaelM Offline
      miael
      schrieb am zuletzt editiert von
      #131

      Deye:

      IMG_20231203_130935.jpg

      1 Antwort Letzte Antwort
      0
      • W Waly_de

        @thebam Ich hab mal ein wenig weiter gemacht und getestet. Klappt ganz gut, auch ohne Formeln.
        Ich hab auch die Register zum Schreiben eingefügt. Was mir großen Spaß macht: Mit "Fernsperre" und "SchalterModus" kann man den WR ein und aus schalten. (Nur vorher den Beeper abstellen denn er geht dann in Störung, so lange er abgeschaltet ist. 😉

        Auch die Netzspeisung lässt sich nun schön fernsteuern. Das könnte vor allem für Leute mit dynamischen Stromtarifen (Timber & Co) eine Freude sein.

        Ich hab angefangen in Vis eine Oberfläche zum steuern zu bauen... klappt schon mal prima 😉 Bildschirmfoto 2023-07-28 um 14.22.12.jpg

        hier meine überarbeiteten Definitionen:

        _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
        40001	1	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
        40004	1	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
        40061	1	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
        40081	1	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
        40105	1	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
        40109	1	Max A Charge	Maximaler Ladestrom der Batterie	A	int16be	1	0	0		level		true	false	false	false
        40110	1	Max A discharge	Max A Entladung	A	int16be	1	0	0		level		true	false	false	false
        40122	1	Max-Gen-Time	Max-Gen-Time	h	int16be	1	0,1	0		level		true	false	false	false
        40123	1	Gen-Cool-Time	Gen-Cool-Time	h	int16be	1	0,1	0		level		true	false	false	false
        40124	1	Gen-Start-Volt	Gen-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
        40125	1	Gen-Start-Proz	Gen-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
        40126	1	Gen-Charge-Current	Gen-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
        40127	1	Grid-Start-Volt	Grid-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
        40128	1	Grid-Start-Proz	Grid-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
        40129	1	Grid-Charge-Current	Grid-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
        40130	1	Gen-Charge-Enable	Gen-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
        40131	1	Grid-Charge-Enable	Grid-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
        40144	1	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	int16be	1	0	0		level		true	false	false	false
        40145	1	External current sensor clamp phase	Klemmphase des externen Stromsensors	W	int16be	1	0	0		level		true	false	false	false
        40146	1	Solar sell	Verkauf von Solar		uint8be	1	0	0		value		true	false	false	false
        40147	1	TOUBits	TOUBits	Bits	uint8be	1	0	0		value		true	false	false	false
        40149	1	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
        40150	1	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
        40151	1	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
        40152	1	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
        40153	1	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
        40154	1	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
        40155	1	BatMaxPower1	BatMaxPower1	W	int16be	1	0	0		level		true	false	false	false
        40156	1	BatMaxPower2	BatMaxPower2	W	int16be	1	0	0		level		true	false	false	false
        40157	1	BatMaxPower3	BatMaxPower3	W	int16be	1	0	0		level		true	false	false	false
        40158	1	BatMaxPower4	BatMaxPower4	W	int16be	1	0	0		level		true	false	false	false
        40159	1	BatMaxPower5	BatMaxPower5	W	int16be	1	0	0		level		true	false	false	false
        40160	1	BatMaxPower6	BatMaxPower6	W	int16be	1	0	0		level		true	false	false	false
        40167	1	BatProz1	BatProz1	%	int16be	1	0	0		level		true	false	false	false
        40168	1	BatProz2	BatProz2	%	int16be	1	0	0		level		true	false	false	false
        40169	1	BatProz3	BatProz3	%	int16be	1	0	0		level		true	false	false	false
        40170	1	BatProz4	BatProz4	%	int16be	1	0	0		level		true	false	false	false
        40171	1	BatProz5	BatProz5	%	int16be	1	0	0		level		true	false	false	false
        40172	1	BatProz6	BatProz6	%	int16be	1	0	0		level		true	false	false	false
        40173	1	GridGenEn1	GridGenEn1	Bits	int16be	1	0	0		level		true	false	false	false
        40174	1	GridGenEn2	GridGenEn2	Bits	int16be	1	0	0		level		true	false	false	false
        40175	1	GridGenEn3	GridGenEn3	Bits	int16be	1	0	0		level		true	false	false	false
        40176	1	GridGenEn4	GridGenEn4	Bits	int16be	1	0	0		level		true	false	false	false
        40177	1	GridGenEn5	GridGenEn5	Bits	int16be	1	0	0		level		true	false	false	false
        40178	1	GridGenEn6	GridGenEn6	Bits	int16be	1	0	0		level		true	false	false	false
        40341	1	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	int16be	1	0	0		level		true	false	false	false
        40341	1	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	int16be	1	0	0		level		true	false	false	false
        40501	1	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
        40502	1	active power generation of today	active power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
        40503	1	reactive power generation of today	reactive power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
        40504	1	Grid connection time of today	Grid connection time of today	s	uint16be	1	1	0		level		true	false	false	false
        40515	1	Today charge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40516	1	Today discharge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40517	1	Total charge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40518	1	Total charge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40519	1	Total discharge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40520	1	Total discharge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40521	1	Day Grid Buy Power kWh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40522	1	Day_GridSell_Power kWh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40523	1	Total_GridBuy_Power kWh_low word	Total_GridBuy_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40524	1	Total_GridBuy_Power kWh_high word	Total_GridBuy_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40525	1	Total_GridSell_Power kWh_low word	Total_GridSell_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40526	1	Total_GridSell_Power kWh_high word	Total_GridSell_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40527	1	Day_Load_Power kWH	Day_Load_Power kWH	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40528	1	Total_Load_Power kWh_low word	Total_Load_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40529	1	Total_Load_Power kWh_high word	Total_Load_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40530	1	Day_PV_Power kWh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40531	1	Day_PV-1_Power kWh	Day_PV-1_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40532	1	Day_PV-2_Power kWh	Day_PV-2_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40533	1	Day_PV-3_Power kWh	Day_PV-3_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40534	1	Day_PV-4_Power kWh	Day_PV-4_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40535	1	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40536	1	Total PV power Wh high word	Gesamt-PV-Leistung Wh hohes Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
        40587	1	battery temperature	Batterietemperatur	°C	int16be	1	0,01	10		level		true	false	false	false
        40588	1	battery voltage	Batteriespannung	V	int16be	1	0,01	0		level		true	false	false	false
        40589	1	battery capacity	Batteriekapazität	%	int16be	1	1	0		level		true	false	false	false
        40591	1	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
        40592	1	Battery output current	Ausgangsstrom der Batterie	A	int16be	1	0,01	0		level		true	false	false	false
        40593	1	Corrected AH	AH korrigiert	AH	int16be	1	1	0		level		true	false	false	false
        40599	1	Grid phase voltage A	Netzphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
        40600	1	Grid phase voltage B	Netzphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
        40601	1	Grid phase voltage C	Netzphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
        40602	1	Grid line voltage AB	Netzphasenspannung L1-L2	V	int16be	1	0,1	0		level		true	false	false	false
        40603	1	Grid line voltage BC	Netzphasenspannung L2-L3	V	int16be	1	0,1	0		level		true	false	false	false
        40604	1	Grid line voltage CA	Netzphasenspannung L3-L1	V	int16be	1	0,1	0		level		true	false	false	false
        40605	1	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
        40606	1	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
        40607	1	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
        40608	1	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
        40609	1	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	int16be	1	1	0		level		true	false	false	false
        40610	1	Grid-side frequency	Grid Seite Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
        40611	1	grid side inner current L1	netzseitiger Innenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
        40612	1	grid side inner current L2	netzseitiger Innenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
        40613	1	grid side inner current L3	netzseitiger Innenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
        40614	1	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	int16be	1	0,01	0		level		true	false	false	false
        40615	1	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	int16be	1	0,01	0		level		true	false	false	false
        40616	1	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	int16be	1	0,01	0		level		true	false	false	false
        40617	1	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	int16be	1	1	0		level		true	false	false	false
        40618	1	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	int16be	1	1	0		level		true	false	false	false
        40619	1	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	int16be	1	1	0		level		true	false	false	false
        40620	1	Out-of-grid-total-power	Außerhalb des Netzes - Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
        40621	1	Out-of-grid-total-apparent-power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16le	1	1	0		level		true	false	false	false
        40622	1	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		int16be	1	1	0		level		true	false	false	false
        40623	1	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
        40624	1	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
        40625	1	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
        40626	1	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
        40628	1	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
        40629	1	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
        40630	1	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
        40631	1	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	int16be	1	0,01	0		level		true	false	false	false
        40632	1	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	int16be	1	0,01	0		level		true	false	false	false
        40633	1	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	int16be	1	0,01	0		level		true	false	false	false
        40634	1	Inverter output phase power A	Ausgangsphase des Wechselrichters Macht L1	W	int16be	1	1	0		level		true	false	false	false
        40635	1	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	int16be	1	1	0		level		true	false	false	false
        40636	1	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	int16be	1	1	0		level		true	false	false	false
        40637	1	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	int16be	1	1	0		level		true	false	false	false
        40638	1	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	int16be	1	1	0		level		true	false	false	false
        40639	1	Inverter frequency	Wechselrichter frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
        40641	1	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	int16be	1	1	0		level		true	false	false	false
        40642	1	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	int16be	1	1	0		level		true	false	false	false
        40643	1	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	int16be	1	1	0		level		true	false	false	false
        40644	1	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	int16be	1	1	0		level		true	false	false	false
        40645	1	Load phase voltage A	Load phasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
        40646	1	Load phase voltage B	Load phasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
        40647	1	Load phase voltage C	Load phasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
        40648	1	Load phase current A	Load phasenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
        40649	1	Load phase current B	Load phasenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
        40650	1	Load phase current C	Load phasenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
        40651	1	Load phase power A	Load phase Leistung L1	W	int16be	1	1	0		level		true	false	false	false
        40652	1	Load phase power B	Load phase Leistung L2	W	int16be	1	1	0		level		true	false	false	false
        40653	1	Load phase power C	Load phase Leistung L3	W	int16be	1	1	0		level		true	false	false	false
        40654	1	Load totalpower	Load Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
        40655	1	Load phase apparent power	Scheinleistung der Lastphase	VA	int16be	1	1	0		level		true	false	false	false
        40656	1	Load frequency	Load Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
        40662	1	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	int16be	1	0,1	0		level		true	false	false	false
        40663	1	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	int16be	1	0,1	0		level		true	false	false	false
        40664	1	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	int16be	1	0,1	0		level		true	false	false	false
        40665	1	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	int16be	1	1	0		level		true	false	false	false
        40666	1	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	int16be	1	1	0		level		true	false	false	false
        40667	1	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	int16be	1	1	0		level		true	false	false	false
        40668	1	total power of Gen port	Gesamtleistung des Gen-Ports	W	int16be	1	1	0		level		true	false	false	false
        40673	1	PV1 input power	PV1 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
        40674	1	PV2 input power	PV2 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
        40675	1	PV3 input power	PV3 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
        40676	1	PV4 input power	PV4 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
        40677	1	Dc voltage 1	Gleichspannung 1	V	int16be	1	0,1	0		level		true	false	false	false
        40678	1	Dc current 1	Gleichstrom 1	A	int16be	1	0,1	0		level		true	false	false	false
        40679	1	Dc voltage 2	Gleichspannung 2	V	int16be	1	0,1	0		level		true	false	false	false
        40680	1	Dc current 2	Gleichstrom 2	A	int16be	1	0,1	0		level		false	false	false	false
        40681	1	Dc voltage 3	Gleichspannung 3	V	int16be	1	0,1	0		level		true	false	false	false
        40682	1	Dc current 3	Gleichstrom 3	A	int16be	1	0,1	0		level		false	false	false	false
        40683	1	Dc voltage 4	Gleichspannung 4	V	int16be	1	0,1	0		level		true	false	false	false
        40684	1	Dc current 4	Gleichstrom 4	A	int16be	1	0,1	0		level		false	false	false	false
        

        Viel spaß Damit 😉
        VG Markus

        TheBamT Offline
        TheBamT Offline
        TheBam
        schrieb am zuletzt editiert von
        #132

        @waly_de

        ich habe da mal noch 2 Fragen weil ich mit die Tou auch nachgebastelt habe.

        Welche register sind für den haken beim generator?

        und wie Fragst du den Status Normal ab???

        W 1 Antwort Letzte Antwort
        0
        • TheBamT TheBam

          @waly_de

          ich habe da mal noch 2 Fragen weil ich mit die Tou auch nachgebastelt habe.

          Welche register sind für den haken beim generator?

          und wie Fragst du den Status Normal ab???

          W Offline
          W Offline
          Waly_de
          schrieb am zuletzt editiert von Waly_de
          #133

          @thebam

          @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

          und wie Fragst du den Status Normal ab???

          Der Status seht im Register "modbus.0.holdingRegisters.1.40501_Status"
          In Vis dann eine "Standard Werteliste Text" und in die Werteliste eintragen:
          "Standby; Selbsttest;Normal;Alarm;Fault"

          @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

          Welche register sind für den haken beim generator?

          Das ist etwas komplizierter.
          Grundsätzlich seht das in diesem Registern:
          modbus.0.holdingRegisters.1.40173_GridGenEn1 -
          modbus.0.holdingRegisters.1.40178_GridGenEn6

          Das sind aber Bit-Register.
          Bit0 ist Grid charge Ein/Aus
          Bit1 ist Gen charge Ein/Aus

          Um die zu setzten bzw. zu lesen, habe ich mir 2 JavaScript-Funktionen geschrieben und bei Skripten im Vis hinterlegt:

          function setBit(currentValue, bitPosition) {
            // Berechne die neue Bit-Maske basierend auf der Bit-Position
            const bitmask = 1 << bitPosition;
            // Setze das entsprechende Bit auf 1 oder 0, abhängig vom Wert
            if (!(currentValue & bitmask)) {
              return (currentValue | bitmask) ;  // Bit auf 1 setzen
            } else {
              return (currentValue & ~bitmask); // Bit auf 0 setzen
            }
          }
          
          function getBit(currentValue, bitPosition) {
            // Hole den aktuellen Wert des States
            // onst currentValue = getState(stateName).val;
            // Überprüfe, ob das Bit an der gegebenen Position gesetzt ist
            const bitmask = 1 << bitPosition;
            return ((currentValue & bitmask) !== 0) ? "1":"0" ;
          }
          
          //{n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
          

          Das Vis-Element ist ein ButtonState.
          Bei Objectid habe ich das Register angegeben:
          modbus.0.holdingRegisters.1.40173_GridGenEn1

          für den GridButton dann:

          Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,0)}
          Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,0)}
          

          für den GenButton:

          Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
          Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,1)}
          

          Das ganze dann 6 mal für alle Register bis GridGenEn6...

          Ich hoffe das hilft Dir weiter 🙂

          C TheBamT 2 Antworten Letzte Antwort
          0
          • W Waly_de

            @thebam

            @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

            und wie Fragst du den Status Normal ab???

            Der Status seht im Register "modbus.0.holdingRegisters.1.40501_Status"
            In Vis dann eine "Standard Werteliste Text" und in die Werteliste eintragen:
            "Standby; Selbsttest;Normal;Alarm;Fault"

            @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

            Welche register sind für den haken beim generator?

            Das ist etwas komplizierter.
            Grundsätzlich seht das in diesem Registern:
            modbus.0.holdingRegisters.1.40173_GridGenEn1 -
            modbus.0.holdingRegisters.1.40178_GridGenEn6

            Das sind aber Bit-Register.
            Bit0 ist Grid charge Ein/Aus
            Bit1 ist Gen charge Ein/Aus

            Um die zu setzten bzw. zu lesen, habe ich mir 2 JavaScript-Funktionen geschrieben und bei Skripten im Vis hinterlegt:

            function setBit(currentValue, bitPosition) {
              // Berechne die neue Bit-Maske basierend auf der Bit-Position
              const bitmask = 1 << bitPosition;
              // Setze das entsprechende Bit auf 1 oder 0, abhängig vom Wert
              if (!(currentValue & bitmask)) {
                return (currentValue | bitmask) ;  // Bit auf 1 setzen
              } else {
                return (currentValue & ~bitmask); // Bit auf 0 setzen
              }
            }
            
            function getBit(currentValue, bitPosition) {
              // Hole den aktuellen Wert des States
              // onst currentValue = getState(stateName).val;
              // Überprüfe, ob das Bit an der gegebenen Position gesetzt ist
              const bitmask = 1 << bitPosition;
              return ((currentValue & bitmask) !== 0) ? "1":"0" ;
            }
            
            //{n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
            

            Das Vis-Element ist ein ButtonState.
            Bei Objectid habe ich das Register angegeben:
            modbus.0.holdingRegisters.1.40173_GridGenEn1

            für den GridButton dann:

            Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,0)}
            Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,0)}
            

            für den GenButton:

            Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
            Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,1)}
            

            Das ganze dann 6 mal für alle Register bis GridGenEn6...

            Ich hoffe das hilft Dir weiter 🙂

            C Offline
            C Offline
            ChrisBGL
            schrieb am zuletzt editiert von
            #134

            Wäre das nicht eine Alternative bei der man kein zusätzliches Kabel benötigt und bequem den MQTT Adapter nutzen kann?

            https://github.com/kbialek/deye-inverter-mqtt

            TheBamT 1 Antwort Letzte Antwort
            0
            • C ChrisBGL

              Wäre das nicht eine Alternative bei der man kein zusätzliches Kabel benötigt und bequem den MQTT Adapter nutzen kann?

              https://github.com/kbialek/deye-inverter-mqtt

              TheBamT Offline
              TheBamT Offline
              TheBam
              schrieb am zuletzt editiert von
              #135

              @chrisbgl
              also wenn ich das richtig verstehe läuft das dann über den webstick. Da kannst du dann doch sogar den Iobroker adapter nutzen der geht soweit ich weiß auch schon direkt mit den großen hybriden.

              S 1 Antwort Letzte Antwort
              0
              • TheBamT TheBam

                @chrisbgl
                also wenn ich das richtig verstehe läuft das dann über den webstick. Da kannst du dann doch sogar den Iobroker adapter nutzen der geht soweit ich weiß auch schon direkt mit den großen hybriden.

                S Offline
                S Offline
                shipper
                schrieb am zuletzt editiert von
                #136

                @thebam
                also am 28.12. der letze Post? Kann doch nicht sein.
                Ich lese die Holdingregister mit dem Modus.iobroker , stabil seit Wochen. Und nun will ich eine TOU-Steuerung aufbauen ähnlich wie batterylife von victron, nur dass ich dazu pvforecast-Werte verwenden möchte. Dazu muss ich aber schreiben können. Kann ich auch, aber nur mit modpoll und nicht mit iobroker. Modpoll ist aber auch nicht so prickelnd, weil bei Schreiben eines einzelnen Wertes 06 genommen wird (ist standard), und nicht 10. 06 kann aber der Deye nicht. Also müsste man immer 2 Werte schreiben, mit mbpoll, beim Adapter gibt es ja den F16-Haken.
                Wie ihr dem Adapter das Schreiben beigebracht habt, ist mir echt schleierhaft. Das Aktualisieren der Objekte per script funktioniert, kommen aber nicht beim Deye an.
                Wenn ich mit mbpoll schreibe, sind die Werte sofort auf dem Deye und auch in den Objekten.
                Was hier so gesehen habe, ist ja echt phantastisch. Ich habe auch gesehen, dass oft wp auf false steht. Hat denn WP nichts mit dem Schreiben zu tun, bzw darf der nicht angekreuzt sein? Und was bewirkt multiples Schreiben, also CW. Bei wird das Register auf 0 gesetzt.
                Vielleicht ist der thread hier doch noch nicht zu Ende

                1 Antwort Letzte Antwort
                0
                • W Waly_de

                  @thebam

                  @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

                  und wie Fragst du den Status Normal ab???

                  Der Status seht im Register "modbus.0.holdingRegisters.1.40501_Status"
                  In Vis dann eine "Standard Werteliste Text" und in die Werteliste eintragen:
                  "Standby; Selbsttest;Normal;Alarm;Fault"

                  @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

                  Welche register sind für den haken beim generator?

                  Das ist etwas komplizierter.
                  Grundsätzlich seht das in diesem Registern:
                  modbus.0.holdingRegisters.1.40173_GridGenEn1 -
                  modbus.0.holdingRegisters.1.40178_GridGenEn6

                  Das sind aber Bit-Register.
                  Bit0 ist Grid charge Ein/Aus
                  Bit1 ist Gen charge Ein/Aus

                  Um die zu setzten bzw. zu lesen, habe ich mir 2 JavaScript-Funktionen geschrieben und bei Skripten im Vis hinterlegt:

                  function setBit(currentValue, bitPosition) {
                    // Berechne die neue Bit-Maske basierend auf der Bit-Position
                    const bitmask = 1 << bitPosition;
                    // Setze das entsprechende Bit auf 1 oder 0, abhängig vom Wert
                    if (!(currentValue & bitmask)) {
                      return (currentValue | bitmask) ;  // Bit auf 1 setzen
                    } else {
                      return (currentValue & ~bitmask); // Bit auf 0 setzen
                    }
                  }
                  
                  function getBit(currentValue, bitPosition) {
                    // Hole den aktuellen Wert des States
                    // onst currentValue = getState(stateName).val;
                    // Überprüfe, ob das Bit an der gegebenen Position gesetzt ist
                    const bitmask = 1 << bitPosition;
                    return ((currentValue & bitmask) !== 0) ? "1":"0" ;
                  }
                  
                  //{n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
                  

                  Das Vis-Element ist ein ButtonState.
                  Bei Objectid habe ich das Register angegeben:
                  modbus.0.holdingRegisters.1.40173_GridGenEn1

                  für den GridButton dann:

                  Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,0)}
                  Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,0)}
                  

                  für den GenButton:

                  Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
                  Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,1)}
                  

                  Das ganze dann 6 mal für alle Register bis GridGenEn6...

                  Ich hoffe das hilft Dir weiter 🙂

                  TheBamT Offline
                  TheBamT Offline
                  TheBam
                  schrieb am zuletzt editiert von
                  #137

                  @shipper was möchtest du denn ist doch hier alles gut beschrieben. bzw. auch in den posts oben. Ich kann alles steuern bzw. setzen wie ich das möchte

                  waly_de sagte in Deye Wechselrichter Modbus Register beschreiben:

                  @thebam

                  @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

                  und wie Fragst du den Status Normal ab???

                  Der Status seht im Register "modbus.0.holdingRegisters.1.40501_Status"
                  In Vis dann eine "Standard Werteliste Text" und in die Werteliste eintragen:
                  "Standby; Selbsttest;Normal;Alarm;Fault"

                  @thebam sagte in Deye Wechselrichter Modbus Register beschreiben:

                  Welche register sind für den haken beim generator?

                  Das ist etwas komplizierter.
                  Grundsätzlich seht das in diesem Registern:
                  modbus.0.holdingRegisters.1.40173_GridGenEn1 -
                  modbus.0.holdingRegisters.1.40178_GridGenEn6

                  Das sind aber Bit-Register.
                  Bit0 ist Grid charge Ein/Aus
                  Bit1 ist Gen charge Ein/Aus

                  Um die zu setzten bzw. zu lesen, habe ich mir 2 JavaScript-Funktionen geschrieben und bei Skripten im Vis hinterlegt:

                  function setBit(currentValue, bitPosition) {
                    // Berechne die neue Bit-Maske basierend auf der Bit-Position
                    const bitmask = 1 << bitPosition;
                    // Setze das entsprechende Bit auf 1 oder 0, abhängig vom Wert
                    if (!(currentValue & bitmask)) {
                      return (currentValue | bitmask) ;  // Bit auf 1 setzen
                    } else {
                      return (currentValue & ~bitmask); // Bit auf 0 setzen
                    }
                  }
                  
                  function getBit(currentValue, bitPosition) {
                    // Hole den aktuellen Wert des States
                    // onst currentValue = getState(stateName).val;
                    // Überprüfe, ob das Bit an der gegebenen Position gesetzt ist
                    const bitmask = 1 << bitPosition;
                    return ((currentValue & bitmask) !== 0) ? "1":"0" ;
                  }
                  
                  //{n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
                  

                  Das Vis-Element ist ein ButtonState.
                  Bei Objectid habe ich das Register angegeben:
                  modbus.0.holdingRegisters.1.40173_GridGenEn1

                  für den GridButton dann:

                  Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,0)}
                  Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,0)}
                  

                  für den GenButton:

                  Knopftext: {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;getBit(n,1)}
                  Wert:      {n:modbus.0.holdingRegisters.1.40173_GridGenEn1;setBit(n,1)}
                  

                  Das ganze dann 6 mal für alle Register bis GridGenEn6...

                  Ich hoffe das hilft Dir weiter 🙂

                  1 Antwort Letzte Antwort
                  0
                  • E Offline
                    E Offline
                    etzeste13
                    schrieb am zuletzt editiert von
                    #138

                    @shipper Hallo,
                    also bei mir funktioniert es auch über den ioBroker per anpassung der States die Register im Wechselrichter zu beschreiben....
                    ich mache es zwar nicht per skript, sonder tlw nur per hand, aber wie gesagt es funktioniert ohne probleme.

                    CW ist nicht gesetzt -> einfach den Wert im Objekt im Rahmen der erlaubten werte verändern und bei der nächste Poll-Abfrage werden die Daten bestätigt.

                    Verwende Waveshare TCP to RS485 converter.

                    S 2 Antworten Letzte Antwort
                    0
                    • E etzeste13

                      @shipper Hallo,
                      also bei mir funktioniert es auch über den ioBroker per anpassung der States die Register im Wechselrichter zu beschreiben....
                      ich mache es zwar nicht per skript, sonder tlw nur per hand, aber wie gesagt es funktioniert ohne probleme.

                      CW ist nicht gesetzt -> einfach den Wert im Objekt im Rahmen der erlaubten werte verändern und bei der nächste Poll-Abfrage werden die Daten bestätigt.

                      Verwende Waveshare TCP to RS485 converter.

                      S Offline
                      S Offline
                      shipper
                      schrieb am zuletzt editiert von
                      #139

                      @etzeste13
                      Danke, auch thebam, das der thread noch lebt. Ich verwende auch waveshare rs485toEth. Funktioniert tadellos.
                      Frage: muss WP gesetzt sein?
                      Welche pollrate fährst du?

                      @TheBam
                      scripte in vis habe ich noch nicht gemacht, vorzugsweise nehme ich blockly nur wenns nicht anders geht z.B. zum lesen der Sensoren von mobil-alerts.
                      Erstmal muss das Schreiben mit dem Adapter funktionieren. Mit modpoll geht es ja.
                      Die Protokollaufzeichnung im debugmode bringt mir poll-einträge von allen Registern, die ich eingetragen habe , von schreiben habe ich da nichts gefunden, egal ob WP gesetzt ist oder nicht.
                      Frage: Ist da was von schreiben zu sehen?
                      danke, dass ihr mir helfen wollt.

                      1 Antwort Letzte Antwort
                      0
                      • E etzeste13

                        @shipper Hallo,
                        also bei mir funktioniert es auch über den ioBroker per anpassung der States die Register im Wechselrichter zu beschreiben....
                        ich mache es zwar nicht per skript, sonder tlw nur per hand, aber wie gesagt es funktioniert ohne probleme.

                        CW ist nicht gesetzt -> einfach den Wert im Objekt im Rahmen der erlaubten werte verändern und bei der nächste Poll-Abfrage werden die Daten bestätigt.

                        Verwende Waveshare TCP to RS485 converter.

                        S Offline
                        S Offline
                        shipper
                        schrieb am zuletzt editiert von
                        #140

                        @etzeste13

                        ok, wert setzen in den Objekten funktioniert, nachdem ich WP rausgenommen habe, dann wird's auch mit Skript gehen

                        danke

                        S 1 Antwort Letzte Antwort
                        0
                        • S shipper

                          @etzeste13

                          ok, wert setzen in den Objekten funktioniert, nachdem ich WP rausgenommen habe, dann wird's auch mit Skript gehen

                          danke

                          S Offline
                          S Offline
                          shipper
                          schrieb am zuletzt editiert von
                          #141

                          @etzeste13
                          du hast mich gerettet. Wenn ich die Werte in den Objekten setze, werden die register erfolgreich beschrieben. Wenn ich in blockly die Funktion "aktualisiere Object " nehme dann nicht. Mit "steuere object" geht es dann.
                          Da konnte ich lange suchen, nichts gefunden, weil sonst nichts zu finden war.

                          E 1 Antwort Letzte Antwort
                          1
                          • S shipper

                            @etzeste13
                            du hast mich gerettet. Wenn ich die Werte in den Objekten setze, werden die register erfolgreich beschrieben. Wenn ich in blockly die Funktion "aktualisiere Object " nehme dann nicht. Mit "steuere object" geht es dann.
                            Da konnte ich lange suchen, nichts gefunden, weil sonst nichts zu finden war.

                            E Offline
                            E Offline
                            etzeste13
                            schrieb am zuletzt editiert von
                            #142

                            @shipper freut mich das es funktioniert und ich mal wem helfen konnte....:-)
                            vG

                            1 Antwort Letzte Antwort
                            0
                            • miaelM Offline
                              miaelM Offline
                              miael
                              schrieb am zuletzt editiert von
                              #143

                              Hallo,
                              kann mir einer sagen was ich da im Register eintragen muss um eine vernünftige Temperatur zu bekommmen?
                              Unbenannt.JPG

                              Danke
                              michael

                              W 1 Antwort Letzte Antwort
                              0
                              • miaelM miael

                                Hallo,
                                kann mir einer sagen was ich da im Register eintragen muss um eine vernünftige Temperatur zu bekommmen?
                                Unbenannt.JPG

                                Danke
                                michael

                                W Offline
                                W Offline
                                warp735
                                schrieb am zuletzt editiert von
                                #144

                                @miael
                                AC ist Faktor 0,1 und bei Offset -100. Dann hast den richtigen Wert. Beim DC Wert genau so, bekommst aber nur Daten wenn nen DC Batt Tempfühler angeschlossen hast. Sonst steht der immer auf 25°

                                Schreiben geht bei mir übrigens problemlos.

                                miaelM 1 Antwort Letzte Antwort
                                0
                                • W warp735

                                  @miael
                                  AC ist Faktor 0,1 und bei Offset -100. Dann hast den richtigen Wert. Beim DC Wert genau so, bekommst aber nur Daten wenn nen DC Batt Tempfühler angeschlossen hast. Sonst steht der immer auf 25°

                                  Schreiben geht bei mir übrigens problemlos.

                                  miaelM Offline
                                  miaelM Offline
                                  miael
                                  schrieb am zuletzt editiert von
                                  #145

                                  @warp735
                                  Besten dank!
                                  Der Hinweis mit den 25°C war es. Bin jetzt auf "Heat sink temperatur" gewechselt und funktioniert.

                                  W 1 Antwort Letzte Antwort
                                  0
                                  • miaelM miael

                                    @warp735
                                    Besten dank!
                                    Der Hinweis mit den 25°C war es. Bin jetzt auf "Heat sink temperatur" gewechselt und funktioniert.

                                    W Offline
                                    W Offline
                                    warp735
                                    schrieb am zuletzt editiert von
                                    #146

                                    @miael
                                    Ja, das ist AC, bzw die interne WR Temp, nach der er selbst auch regelt

                                    1 Antwort Letzte Antwort
                                    0
                                    • W Offline
                                      W Offline
                                      warp735
                                      schrieb am zuletzt editiert von warp735
                                      #147

                                      Weiß jemand wie die "Tägliche Erzeugung" gerechnet wird? Ist da der Micro inkludiert oder nicht? Bei der oberen prozentualen Anzeige "Produktion" interessiert er auf jedenfall nicht. Bei diesem Beispiel müssten es ja 55% sein und nicht 41%

                                      Find nämlich auch kein Register für die kwh vom Microinverter 😞

                                      Snag_44ef76.png

                                      1 Antwort Letzte Antwort
                                      0
                                      • R Offline
                                        R Offline
                                        Ronny81
                                        schrieb am zuletzt editiert von
                                        #148

                                        Servus zusammen,

                                        ich bin neu hier und hoffe ihr könnt mir helfen.
                                        Ich muss ganz dringen ein Register am Deye setzen und zwar die ID bzw. Seriennummer.
                                        Leider hat mein Deye nach dem letzten Firmware Update seine ID verloren.
                                        Ich habe es schon über die RS232 versucht, aber der WR will nicht antworten.
                                        Kann man die ID über die RS485 ändern?
                                        Die ID müsste die Register 3,4,5,6 und 7 haben.
                                        Register 7, ID(SN), Stelle 2 + 1 ASCII
                                        Register 6, ID(SN), Stelle 4 + 3 ASCII
                                        Register 5, ID(SN), Stelle 6 + 5 ASCII
                                        Register 4, ID(SN), Stelle 8 + 7 ASCII
                                        Register 3, ID(SN), Stelle 10 + 9 ASCII
                                        Ich hoffe Ihr könnt mir helfen. Danke schon mal.
                                        Anbei noch ein Foto des Display ohne ID.

                                        Gruß Ronny

                                        20240406_174924.jpg 20240407_155125.jpg

                                        1 Antwort Letzte Antwort
                                        0
                                        • wendy2702W Offline
                                          wendy2702W Offline
                                          wendy2702
                                          schrieb am zuletzt editiert von
                                          #149

                                          Hi,

                                          ich schaffe es aktuell nicht meinen Deye SUN-12K-SG04LP3-EU pe Waveshare auszulesen.

                                          ich verwende diesen Waveshare:

                                          15a56c0a-df08-4f36-b038-41bcf06e6805-grafik.png

                                          mit diesen Einstellungen:

                                          ad83f715-b7d6-4abb-adb5-613b814a6e75-grafik.png

                                          636dd362-e0c0-47b0-98c1-4b4ca03fc7ec-grafik.png

                                          Wenn ich mit CAS Modbus Scanner per USB RS485 Adapter einen Test mache funktioniert die Verbindung:

                                          50611fe6-b361-4ec5-b918-04fb5d121f7e-grafik.png :

                                          Und mit Modbus Poll kann ich register auslesen.

                                          Iob ist so konfiguriert:

                                          49401faa-1116-48a2-8c29-861e6cc774ba-grafik.png

                                          Register aus dem Github Modbus Template von @TheBam

                                          9f3695a3-2a67-4fd6-baea-7a6977a7ea52-grafik.png

                                          Debug log hilft mir aktuell nicht weiter: (Gekürzt wegen Payload.)

                                          2024-05-24 10:49:09.547  - info: host.iobroker "system.adapter.modbus.4" enabled
                                          2024-05-24 10:49:10.972  - info: host.iobroker instance system.adapter.modbus.4 started with pid 213280
                                          2024-05-24 10:49:12.811  - debug: modbus.4 (213280) Redis Objects: Use Redis connection: 0.0.0.0:9001
                                          2024-05-24 10:49:12.924  - debug: modbus.4 (213280) Objects client ready ... initialize now
                                          2024-05-24 10:49:13.001  - debug: modbus.4 (213280) Objects create System PubSub Client
                                          2024-05-24 10:49:13.002  - debug: modbus.4 (213280) Objects create User PubSub Client
                                          2024-05-24 10:49:13.308  - debug: modbus.4 (213280) Objects client initialize lua scripts
                                          2024-05-24 10:49:13.332  - debug: modbus.4 (213280) Objects connected to redis: 0.0.0.0:9001
                                          2024-05-24 10:49:13.551  - debug: modbus.4 (213280) Redis States: Use Redis connection: 0.0.0.0:9000
                                          2024-05-24 10:49:13.669  - debug: modbus.4 (213280) States create System PubSub Client
                                          2024-05-24 10:49:13.670  - debug: modbus.4 (213280) States create User PubSub Client
                                          2024-05-24 10:49:13.848  - debug: modbus.4 (213280) States connected to redis: 0.0.0.0:9000
                                          2024-05-24 10:49:14.085  - debug: modbus.4 (213280) Plugin sentry Do not initialize Plugin (enabled=false)
                                          2024-05-24 10:49:14.141  - debug: modbus.4 (213280) Plugin sentry destroyed because not initialized correctly
                                          2024-05-24 10:49:14.599  - info: modbus.4 (213280) starting. Version 6.2.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                                          2024-05-24 10:49:15.614  - debug: modbus.4 (213280) Initialize Objects for disInputs: []
                                          2024-05-24 10:49:15.616  - debug: modbus.4 (213280) Initialize Objects for coils: []
                                          2024-05-24 10:49:15.617  - debug: modbus.4 (213280) Initialize Objects for inputRegs: []
                                          2024-05-24 10:49:15.626  - debug: modbus.4 (213280) Initialize Objects for holdingRegs: [{"_address":40001,"name":"Device type","description":"Gerätetyp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40001,"id":"holdingRegisters.40001_Device_type"},Gesamtscheinleistung","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40609,"id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power"},{"_address":40610,"name":"Grid-side frequency","description":"Grid Seite Frequenz","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40610,"id":"holdingRegisters.40610_Grid-side_frequency"},{"_address":40611,"name":"grid side inner current L1","description":"netzseitiger Innenstrom 1","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40678,"id":"holdingRegisters.40678_Dc_current_1"},{"_address":40679,"name":"Dc voltage 2","description":"Gleichspannung 2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40679,"id":"holdingRegisters.40679_Dc_voltage_2"},{"_address":40680,"name":"Dc current 2","description":"Gleichstrom 2","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":4,"address":40680,"id":"holdingRegisters.40680_Dc_current_2"}]
                                          2024-05-24 10:49:15.633  - debug: modbus.4 (213280) Add holdingRegisters.40001_Device_type: {"_id":"holdingRegisters.40001_Device_type","type":"state","common":{"name":"Gerätetyp","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40001,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.636  - debug: modbus.4 (213280) Add holdingRegisters.40004_Seriennummer: {"_id":"holdingRegisters.40004_Seriennummer","type":"state","common":{"name":"Seriennummer","role":"state","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":40004,"deviceId":4,"type":"string","len":5,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.637  - debug: modbus.4 (213280) Add holdingRegisters.40061_Fernsperre: {"_id":"holdingRegisters.40061_Fernsperre","type":"state","common":{"name":"Fernsperre","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40061,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40081_SchalterModus: {"_id":"holdingRegisters.40081_SchalterModus","type":"state","common":{"name":"SchalterModus","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40081,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.638  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.639  - debug: modbus.4 (213280) Add holdingRegisters.40105_ZeroExport_power: {"_id":"holdingRegisters.40105_ZeroExport_power","type":"state","common":{"name":"ZeroExport-Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40105,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40109_Max_A_Charge: {"_id":"holdingRegisters.40109_Max_A_Charge","type":"state","common":{"name":"Maximaler Ladestrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40109,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.640  - debug: modbus.4 (213280) Add holdingRegisters.40110_Max_A_discharge: {"_id":"holdingRegisters.40110_Max_A_discharge","type":"state","common":{"name":"Max A Entladung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40110,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40116_ShutDown_battery_capacity_ShutDown: {"_id":"holdingRegisters.40116_ShutDown_battery_capacity_ShutDown","type":"state","common":{"name":"Abschalten Batteriekapazität Herunterfahren","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40116,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40117_Restart_battery_capacityRestart: {"_id":"holdingRegisters.40117_Restart_battery_capacityRestart","type":"state","common":{"name":"Neu starten BatteriekapazitätNeustart","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40117,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.641  - debug: modbus.4 (213280) Add holdingRegisters.40118_LowBatt_battery_capacityLowBatt: {"_id":"holdingRegisters.40118_LowBatt_battery_capacityLowBatt","type":"state","common":{"name":"Low Batterie Anzeige zum Abschalten der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40118,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40130_Generator_is_charged_to_enable: {"_id":"holdingRegisters.40130_Generator_is_charged_to_enable","type":"state","common":{"name":"Generator is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40130,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.642  - debug: modbus.4 (213280) Add holdingRegisters.40131_Grid_is_charged_to_enable: {"_id":"holdingRegisters.40131_Grid_is_charged_to_enable","type":"state","common":{"name":"Grid is charged to enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40131,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection: {"_id":"holdingRegisters.40144_Max_Limit_Power_Output_Grid_Connection","type":"state","common":{"name":"Begrenzen Sie die maximale Ausgangsleistung des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40144,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40145_External_current_sensor_clamp_phase: {"_id":"holdingRegisters.40145_External_current_sensor_clamp_phase","type":"state","common":{"name":"Klemmphase des externen Stromsensors","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40145,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40146_Solar_sell: {"_id":"holdingRegisters.40146_Solar_sell","type":"state","common":{"name":"  Verkauf von Solar","role":"switch","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40146,"deviceId":4,"type":"floatbe","len":2,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.643  - debug: modbus.4 (213280) Add holdingRegisters.40149_Sell_mode_time_point_1: {"_id":"holdingRegisters.40149_Sell_mode_time_point_1","type":"state","common":{"name":"Sell mode time point 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40149,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40150_Sell_mode_time_point_2: {"_id":"holdingRegisters.40150_Sell_mode_time_point_2","type":"state","common":{"name":"Sell mode time point 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40150,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40151_Sell_mode_time_point_3: {"_id":"holdingRegisters.40151_Sell_mode_time_point_3","type":"state","common":{"name":"Sell mode time point 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40151,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40152_Sell_mode_time_point_4: {"_id":"holdingRegisters.40152_Sell_mode_time_point_4","type":"state","common":{"name":"Sell mode time point 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40152,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40153_Sell_mode_time_point_5: {"_id":"holdingRegisters.40153_Sell_mode_time_point_5","type":"state","common":{"name":"Sell mode time point 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40153,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40154_Sell_mode_time_point_6: {"_id":"holdingRegisters.40154_Sell_mode_time_point_6","type":"state","common":{"name":"Sell mode time point 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40154,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.644  - debug: modbus.4 (213280) Add holdingRegisters.40155_Sell_mode_Watt_time_1: {"_id":"holdingRegisters.40155_Sell_mode_Watt_time_1","type":"state","common":{"name":"Sell mode Watt time 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40155,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40156_Sell_mode_Watt_time_2: {"_id":"holdingRegisters.40156_Sell_mode_Watt_time_2","type":"state","common":{"name":"Sell mode Watt time 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40156,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40157_Sell_mode_Watt_time_3: {"_id":"holdingRegisters.40157_Sell_mode_Watt_time_3","type":"state","common":{"name":"Sell mode Watt time 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40157,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.645  - debug: modbus.4 (213280) Add holdingRegisters.40158_Sell_mode_Watt_time_4: {"_id":"holdingRegisters.40158_Sell_mode_Watt_time_4","type":"state","common":{"name":"Sell mode Watt time 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40158,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40159_Sell_mode_Watt_time_5: {"_id":"holdingRegisters.40159_Sell_mode_Watt_time_5","type":"state","common":{"name":"Sell mode Watt time 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40159,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40160_Sell_mode_Watt_time_6: {"_id":"holdingRegisters.40160_Sell_mode_Watt_time_6","type":"state","common":{"name":"Sell mode Watt time 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40160,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40167_TOF_Cell_SOC_1: {"_id":"holdingRegisters.40167_TOF_Cell_SOC_1","type":"state","common":{"name":"TOF_Cell SOC 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40167,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40168_TOF_Cell_SOC_2: {"_id":"holdingRegisters.40168_TOF_Cell_SOC_2","type":"state","common":{"name":"TOF_Cell SOC 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40168,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.646  - debug: modbus.4 (213280) Add holdingRegisters.40169_TOF_Cell_SOC_3: {"_id":"holdingRegisters.40169_TOF_Cell_SOC_3","type":"state","common":{"name":"TOF_Cell SOC 3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40169,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40170_TOF_Cell_SOC_4: {"_id":"holdingRegisters.40170_TOF_Cell_SOC_4","type":"state","common":{"name":"TOF_Cell SOC 4","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40170,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40171_TOF_Cell_SOC_5: {"_id":"holdingRegisters.40171_TOF_Cell_SOC_5","type":"state","common":{"name":"TOF_Cell SOC 5","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40171,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40172_TOF_Cell_SOC_6: {"_id":"holdingRegisters.40172_TOF_Cell_SOC_6","type":"state","common":{"name":"TOF_Cell SOC 6","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40172,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40173_Time_point_1_charge_enable: {"_id":"holdingRegisters.40173_Time_point_1_charge_enable","type":"state","common":{"name":"Time point 1 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40173,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.647  - debug: modbus.4 (213280) Add holdingRegisters.40174_Time_point_2_charge_enable: {"_id":"holdingRegisters.40174_Time_point_2_charge_enable","type":"state","common":{"name":"Time point 2 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40174,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40175_Time_point_3_charge_enable: {"_id":"holdingRegisters.40175_Time_point_3_charge_enable","type":"state","common":{"name":"Time point 3 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40175,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40176_Time_point_4_charge_enable: {"_id":"holdingRegisters.40176_Time_point_4_charge_enable","type":"state","common":{"name":"Time point 4 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40176,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40177_Time_point_5_charge_enable: {"_id":"holdingRegisters.40177_Time_point_5_charge_enable","type":"state","common":{"name":"Time point 5 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40177,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40178_Time_point_6_charge_enable: {"_id":"holdingRegisters.40178_Time_point_6_charge_enable","type":"state","common":{"name":"Time point 6 charge enable","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40178,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.648  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_at_Zero_grid","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei null einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in: {"_id":"holdingRegisters.40341_Max_Solar_Sell_Power_by_full_in","type":"state","common":{"name":"Maximale Solarverkaufsleistung bei einspeisung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40341,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40501_Status: {"_id":"holdingRegisters.40501_Status","type":"state","common":{"name":"Status (Standby, check, norm, altert, fault)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40501,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40521_Day_Grid_Buy_Power_Wh: {"_id":"holdingRegisters.40521_Day_Grid_Buy_Power_Wh","type":"state","common":{"name":"Tag Netzabnahme Strom Wh","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40521,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.649  - debug: modbus.4 (213280) Add holdingRegisters.40522_Day_GridSell_Power_Wh: {"_id":"holdingRegisters.40522_Day_GridSell_Power_Wh","type":"state","common":{"name":"Tages Verkaufs leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40522,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40530_Day_PV_Power_Wh: {"_id":"holdingRegisters.40530_Day_PV_Power_Wh","type":"state","common":{"name":"Tagesproduzierte leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40530,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40535_Total_PV_power_Wh_low_word: {"_id":"holdingRegisters.40535_Total_PV_power_Wh_low_word","type":"state","common":{"name":"Gesamt-PV-Leistung Wh niedriges Wort","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"kwh"},"native":{"regType":"holdingRegs","address":40535,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_AC_Relay: {"_id":"holdingRegisters.40553_AC_Relay","type":"state","common":{"name":"AC relay","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.650  - debug: modbus.4 (213280) Add holdingRegisters.40553_Ac_relay_2: {"_id":"holdingRegisters.40553_Ac_relay_2","type":"state","common":{"name":"AC relay2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40553,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40587_battery_temperature: {"_id":"holdingRegisters.40587_battery_temperature","type":"state","common":{"name":"Batterietemperatur","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":40587,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40588_battery_voltage: {"_id":"holdingRegisters.40588_battery_voltage","type":"state","common":{"name":"Batteriespannung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40588,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40589_battery_capacity: {"_id":"holdingRegisters.40589_battery_capacity","type":"state","common":{"name":"Batteriekapazität","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":40589,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40591_Battery_output_power: {"_id":"holdingRegisters.40591_Battery_output_power","type":"state","common":{"name":"Ausgangsleistung der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40591,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40592_Battery_output_current: {"_id":"holdingRegisters.40592_Battery_output_current","type":"state","common":{"name":"Ausgangsstrom der Batterie","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40592,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40593_Corrected_AH: {"_id":"holdingRegisters.40593_Corrected_AH","type":"state","common":{"name":"AH korrigiert","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"AH"},"native":{"regType":"holdingRegs","address":40593,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.651  - debug: modbus.4 (213280) Add holdingRegisters.40599_Grid_phase_voltage_A: {"_id":"holdingRegisters.40599_Grid_phase_voltage_A","type":"state","common":{"name":"Netzphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40599,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40600_Grid_phase_voltage_B: {"_id":"holdingRegisters.40600_Grid_phase_voltage_B","type":"state","common":{"name":"Netzphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40600,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40601_Grid_phase_voltage_C: {"_id":"holdingRegisters.40601_Grid_phase_voltage_C","type":"state","common":{"name":"Netzphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40601,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40605_L1_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L1 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40605,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40606_L2_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L2 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40606,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid: {"_id":"holdingRegisters.40607_L3_phase_power_on_the_inner_side_of_the_grid","type":"state","common":{"name":"L3 Phasenleistung auf der Innenseite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40607,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40608_active_power_from_side_to_side_of_the_grid: {"_id":"holdingRegisters.40608_active_power_from_side_to_side_of_the_grid","type":"state","common":{"name":"Wirkleistung von Seite zu Seite des Netzes","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40608,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40609_Grid_side_-_inside_total_apparent_power: {"_id":"holdingRegisters.40609_Grid_side_-_inside_total_apparent_power","type":"state","common":{"name":"Netzseite – innere Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40609,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.652  - debug: modbus.4 (213280) Add holdingRegisters.40610_Grid-side_frequency: {"_id":"holdingRegisters.40610_Grid-side_frequency","type":"state","common":{"name":"Grid Seite Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40610,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40611_grid_side_inner_current_L1: {"_id":"holdingRegisters.40611_grid_side_inner_current_L1","type":"state","common":{"name":"netzseitiger Innenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40611,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40612_grid_side_inner_current_L2: {"_id":"holdingRegisters.40612_grid_side_inner_current_L2","type":"state","common":{"name":"netzseitiger Innenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40612,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40613_grid_side_inner_current_L3: {"_id":"holdingRegisters.40613_grid_side_inner_current_L3","type":"state","common":{"name":"netzseitiger Innenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40613,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.653  - debug: modbus.4 (213280) Add holdingRegisters.40614_Out-of-grid_-_current_L1: {"_id":"holdingRegisters.40614_Out-of-grid_-_current_L1","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40614,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40615_Out-of-grid_-_current_L2: {"_id":"holdingRegisters.40615_Out-of-grid_-_current_L2","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40615,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40616_Out-of-grid_-_current_L3: {"_id":"holdingRegisters.40616_Out-of-grid_-_current_L3","type":"state","common":{"name":"Außerhalb des Netzes – aktuelles L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40616,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40617_A_Out-of-grid_-power_L1: {"_id":"holdingRegisters.40617_A_Out-of-grid_-power_L1","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40617,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40618_A_Out-of-grid_-power_L2: {"_id":"holdingRegisters.40618_A_Out-of-grid_-power_L2","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40618,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40619_A_Out-of-grid_-power_L3: {"_id":"holdingRegisters.40619_A_Out-of-grid_-power_L3","type":"state","common":{"name":"A Außerhalb des Netzes - Strom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40619,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.654  - debug: modbus.4 (213280) Add holdingRegisters.40620_Out-of-grid_–total_power: {"_id":"holdingRegisters.40620_Out-of-grid_–total_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40620,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40621_Out-of-grid_–total_apparent_power: {"_id":"holdingRegisters.40621_Out-of-grid_–total_apparent_power","type":"state","common":{"name":"Außerhalb des Netzes – Gesamtscheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40621,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40622_Grid-connected_power_factor_PF: {"_id":"holdingRegisters.40622_Grid-connected_power_factor_PF","type":"state","common":{"name":"Netzgekoppelter Leistungsfaktor PF","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40622,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40623_Grid_side_A-phase_power: {"_id":"holdingRegisters.40623_Grid_side_A-phase_power","type":"state","common":{"name":"Netzseitiger L1-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40623,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40624_Grid_side_B-phase_power: {"_id":"holdingRegisters.40624_Grid_side_B-phase_power","type":"state","common":{"name":"Netzseitiger L2-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40624,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40625_Grid_side_C-phase_power: {"_id":"holdingRegisters.40625_Grid_side_C-phase_power","type":"state","common":{"name":"Netzseitiger L3-Phasen-Strom","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40625,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40626_Grid_side_total_power: {"_id":"holdingRegisters.40626_Grid_side_total_power","type":"state","common":{"name":"Netzseitige Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40626,"deviceId":4,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.655  - debug: modbus.4 (213280) Add holdingRegisters.40628_Inverter_output_phase_voltage_A: {"_id":"holdingRegisters.40628_Inverter_output_phase_voltage_A","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40628,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40629_Inverter_output_phase_voltage_B: {"_id":"holdingRegisters.40629_Inverter_output_phase_voltage_B","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40629,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40630_Inverter_output_phase_voltage_C: {"_id":"holdingRegisters.40630_Inverter_output_phase_voltage_C","type":"state","common":{"name":"Wechselrichter-Ausgangsphasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40630,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40631_Inverter_output_phase_current_A: {"_id":"holdingRegisters.40631_Inverter_output_phase_current_A","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40631,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.656  - debug: modbus.4 (213280) Add holdingRegisters.40632_Inverter_output_phase_current_B: {"_id":"holdingRegisters.40632_Inverter_output_phase_current_B","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40632,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.657  - debug: modbus.4 (213280) Add holdingRegisters.40633_Inverter_output_phase_current_C: {"_id":"holdingRegisters.40633_Inverter_output_phase_current_C","type":"state","common":{"name":"Ausgangsphasenstrom des Wechselrichters L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40633,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.659  - debug: modbus.4 (213280) Add holdingRegisters.40634_Inverter_output_phase_power_A: {"_id":"holdingRegisters.40634_Inverter_output_phase_power_A","type":"state","common":{"name":"  Ausgangsphase des Wechselrichters Macht L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40634,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.660  - debug: modbus.4 (213280) Add holdingRegisters.40635_Inverter_output_phase_power_B: {"_id":"holdingRegisters.40635_Inverter_output_phase_power_B","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Macht L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40635,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40636_Inverter_output_phase_power_C: {"_id":"holdingRegisters.40636_Inverter_output_phase_power_C","type":"state","common":{"name":"Ausgangsphase des Wechselrichters Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40636,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40637_Inverter_output_total_power: {"_id":"holdingRegisters.40637_Inverter_output_total_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Leistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40637,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40638_Inverter_output_total_apparent_power: {"_id":"holdingRegisters.40638_Inverter_output_total_apparent_power","type":"state","common":{"name":"Gesamtleistung des Wechselrichters Scheinleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40638,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40639_Inverter_frequency: {"_id":"holdingRegisters.40639_Inverter_frequency","type":"state","common":{"name":"Wechselrichter frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40639,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.661  - debug: modbus.4 (213280) Add holdingRegisters.40641_UPS_load-side_phase_power_A: {"_id":"holdingRegisters.40641_UPS_load-side_phase_power_A","type":"state","common":{"name":"USV-lastseitige Phasenleistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40641,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40642_UPS_load-side_phase_power_B: {"_id":"holdingRegisters.40642_UPS_load-side_phase_power_B","type":"state","common":{"name":"USV-lastseitige Phasenleistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40642,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40643_UPS_load-side_phase_power_C: {"_id":"holdingRegisters.40643_UPS_load-side_phase_power_C","type":"state","common":{"name":"USV-lastseitige Phasenleistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40643,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40644_UPS_load-sidetotal_power: {"_id":"holdingRegisters.40644_UPS_load-sidetotal_power","type":"state","common":{"name":"Lastseitige Gesamtleistung der USV","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40644,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.662  - debug: modbus.4 (213280) Add holdingRegisters.40645_Load_phase_voltage_A: {"_id":"holdingRegisters.40645_Load_phase_voltage_A","type":"state","common":{"name":"Load phasenspannung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40645,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40646_Load_phase_voltage_B: {"_id":"holdingRegisters.40646_Load_phase_voltage_B","type":"state","common":{"name":"Load phasenspannung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40646,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.665  - debug: modbus.4 (213280) Add holdingRegisters.40647_Load_phase_voltage_C: {"_id":"holdingRegisters.40647_Load_phase_voltage_C","type":"state","common":{"name":"Load phasenspannung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40647,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40648_Load_phase_current_A: {"_id":"holdingRegisters.40648_Load_phase_current_A","type":"state","common":{"name":"Load phasenstrom L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40648,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40649_Load_phase_current_B: {"_id":"holdingRegisters.40649_Load_phase_current_B","type":"state","common":{"name":"Load phasenstrom L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40649,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40650_Load_phase_current_C: {"_id":"holdingRegisters.40650_Load_phase_current_C","type":"state","common":{"name":"Load phasenstrom L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40650,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.01,"poll":true}}
                                          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40651_Load_phase_power_A: {"_id":"holdingRegisters.40651_Load_phase_power_A","type":"state","common":{"name":"Load phase Leistung L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40651,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.666  - debug: modbus.4 (213280) Add holdingRegisters.40652_Load_phase_power_B: {"_id":"holdingRegisters.40652_Load_phase_power_B","type":"state","common":{"name":"Load phase Leistung L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40652,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40653_Load_phase_power_C: {"_id":"holdingRegisters.40653_Load_phase_power_C","type":"state","common":{"name":"Load phase Leistung L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40653,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.667  - debug: modbus.4 (213280) Add holdingRegisters.40654_Load_totalpower: {"_id":"holdingRegisters.40654_Load_totalpower","type":"state","common":{"name":"Load Gesamtleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40654,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40655_Load_phase_apparent_power: {"_id":"holdingRegisters.40655_Load_phase_apparent_power","type":"state","common":{"name":"Scheinleistung der Lastphase","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":40655,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40656_Load_frequency: {"_id":"holdingRegisters.40656_Load_frequency","type":"state","common":{"name":"Load Frequenz","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":40656,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40662_Phase_voltage_of_Gen_port_A: {"_id":"holdingRegisters.40662_Phase_voltage_of_Gen_port_A","type":"state","common":{"name":"Phasenspannung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40662,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40663_Phase_voltage_of_Gen_port_B: {"_id":"holdingRegisters.40663_Phase_voltage_of_Gen_port_B","type":"state","common":{"name":"Phasenspannung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40663,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40664_Phase_voltage_of_Gen_port_C: {"_id":"holdingRegisters.40664_Phase_voltage_of_Gen_port_C","type":"state","common":{"name":"Phasenspannung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40664,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.668  - debug: modbus.4 (213280) Add holdingRegisters.40665_Phase_power_of_Gen_port_A: {"_id":"holdingRegisters.40665_Phase_power_of_Gen_port_A","type":"state","common":{"name":"Phasenleistung von Gen-Port L1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40665,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40666_Phase_power_of_Gen_port_B: {"_id":"holdingRegisters.40666_Phase_power_of_Gen_port_B","type":"state","common":{"name":"Phasenleistung von Gen-Port L2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40666,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40667_Phase_power_of_Gen_port_C: {"_id":"holdingRegisters.40667_Phase_power_of_Gen_port_C","type":"state","common":{"name":"Phasenleistung von Gen-Port L3","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40667,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40668_total_power_of_Gen_port: {"_id":"holdingRegisters.40668_total_power_of_Gen_port","type":"state","common":{"name":"Gesamtleistung des Gen-Ports","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40668,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.669  - debug: modbus.4 (213280) Add holdingRegisters.40673_PV1_input_power: {"_id":"holdingRegisters.40673_PV1_input_power","type":"state","common":{"name":"PV1 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40673,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40674_PV2_input_power: {"_id":"holdingRegisters.40674_PV2_input_power","type":"state","common":{"name":"PV2 Eingangsleistung","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":40674,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40677_Dc_voltage_1: {"_id":"holdingRegisters.40677_Dc_voltage_1","type":"state","common":{"name":"Gleichspannung 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40677,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.670  - debug: modbus.4 (213280) Add holdingRegisters.40678_Dc_current_1: {"_id":"holdingRegisters.40678_Dc_current_1","type":"state","common":{"name":"Gleichstrom 1","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40678,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40679_Dc_voltage_2: {"_id":"holdingRegisters.40679_Dc_voltage_2","type":"state","common":{"name":"Gleichspannung 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":40679,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.671  - debug: modbus.4 (213280) Add holdingRegisters.40680_Dc_current_2: {"_id":"holdingRegisters.40680_Dc_current_2","type":"state","common":{"name":"Gleichstrom 2","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40680,"deviceId":4,"type":"uint16be","len":1,"offset":0,"factor":0.1,"poll":true}}
                                          2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                                          2024-05-24 10:49:15.802  - debug: modbus.4 (213280) Remove old object modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                                          2024-05-24 10:49:18.765  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40620_Out-of-grid_–total_power changed to modbus.4.holdingRegisters.40620_Out-of-grid__total_power
                                          2024-05-24 10:49:18.777  - warn: modbus.4 (213280) Used invalid characters: modbus.4.holdingRegisters.40621_Out-of-grid_–total_apparent_power changed to modbus.4.holdingRegisters.40621_Out-of-grid__total_apparent_power
                                          2024-05-24 10:49:22.213  - info: modbus.4 (213280) Connected to slave 192.168.178.238
                                          2024-05-24 10:49:22.214  - debug: modbus.4 (213280) [DevID_4] Poll start ---------------------
                                          2024-05-24 10:49:22.215  - debug: modbus.4 (213280) Initialization of scale factors done!
                                          2024-05-24 10:49:22.215  - debug: modbus.4 (213280) [DevID_4/holdingRegs] Poll address 40001 - 8 registers
                                          2024-05-24 10:49:27.221  - warn: modbus.4 (213280) Error: undefined
                                          2024-05-24 10:49:27.222  - error: modbus.4 (213280) Request timed out.
                                          2024-05-24 10:49:27.222  - error: modbus.4 (213280) Client in error state.
                                          2024-05-24 10:49:27.222  - warn: modbus.4 (213280) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                                          2024-05-24 10:49:27.223  - debug: modbus.4 (213280) Socket closed with error
                                          2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Clearing timeout of the current request.
                                          2024-05-24 10:49:27.224  - debug: modbus.4 (213280) Cleaning up request fifo.
                                          2024-05-24 10:49:28.222  - debug: modbus.4 (213280) Closing client on purpose.
                                          2024-05-24 10:49:28.223  - info: modbus.4 (213280) Disconnected from slave 192.168.178.238
                                          
                                          

                                          Angeschlossen am Deye Modbus Ausgang mit Firmware:
                                          d1a96c7e-2622-4aa6-bb76-06240a571d6a-grafik.png

                                          Der Waveshare funktioniert an einem anderen Modbus Device einwandfrei.

                                          Jemand noch eine Idee wo das Problem liegen könnte?

                                          Bitte keine Fragen per PN, die gehören ins Forum!

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          W 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          755

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe