  4. Modbus adapter

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.3k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.0k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    15
    1
    2.4k

Modbus adapter

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
modbus adaptermodbus
980 Beiträge 141 Kommentatoren 383.2k Aufrufe 64 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • arteckA arteck

    @sneak-l8 der wird mit der 0c079d60-6b0f-49ee-9008-a3a3cd81c2d2-grafik.png

    nicht klarkommen.. brauchst du eine sekunden Auflösung ??

    S Offline
    S Offline
    Sneak-L8
    schrieb am zuletzt editiert von
    #818

    @arteck Da hatte ich testweise mal 2000ms eingestellt, das hat auch nicht geholfen.
    Meine beiden Energy-Meter leifern die werte auch im Sekundentakt. Und wenn ich den hausinternen Verbrauch aus Regard/Surplus - Erzeugung berechne, dann wäre ein recht aktueller wert gut.

    Schon jetzt sehe ich mal negative Verbräcuhe, weil die Sonne gerade rauskommt und dann die Werte nicht ganz zusammenpassen. Da befürchte ich, dass es eben schlechter wird. Aber ich denke, mit 2-5 Sekunden könnte ich leben. Was würdest Du empfehlen?

    P.S. Mit diesne einstellungen läuft der Adater aber schon einige Jahre ...

    arteckA 1 Antwort Letzte Antwort
    0
    • S Sneak-L8

      @arteck Da hatte ich testweise mal 2000ms eingestellt, das hat auch nicht geholfen.
      Meine beiden Energy-Meter leifern die werte auch im Sekundentakt. Und wenn ich den hausinternen Verbrauch aus Regard/Surplus - Erzeugung berechne, dann wäre ein recht aktueller wert gut.

      Schon jetzt sehe ich mal negative Verbräcuhe, weil die Sonne gerade rauskommt und dann die Werte nicht ganz zusammenpassen. Da befürchte ich, dass es eben schlechter wird. Aber ich denke, mit 2-5 Sekunden könnte ich leben. Was würdest Du empfehlen?

      P.S. Mit diesne einstellungen läuft der Adater aber schon einige Jahre ...

      arteckA Offline
      arteckA Offline
      arteck
      Developer Most Active
      schrieb am zuletzt editiert von arteck
      #819

      @sneak-l8 wofür brraucht man die Werte .. nur für die Anzeige ?? wie oft steht du vor und schaust die dir sekündlichen Werte an ?
      für historie .. jede sekunde ?? wozu um die Kurve glatt zu bekommen.. ??

      ich hab den gleichen WR .. und frage die Werte alle 10 sek ab. das reicht vollkommen..

      wenn der Adapter seid jahren schon so lief . dann hat sich bei dir was geändert in der Netzerkinfrastruktur.. die Fehlermeldung besagt der WR antwortet nicht in der vorgegebenen zeit..

      was läuft auf modbus.0 ?? der gleiche WR.. ?? wird der sonst noch mit anfragen bombardiert ?? von http ??

      zigbee hab ich, zwave auch, nuc's genauso und HA auch

      S 1 Antwort Letzte Antwort
      0
      • arteckA arteck

        @sneak-l8 wofür brraucht man die Werte .. nur für die Anzeige ?? wie oft steht du vor und schaust die dir sekündlichen Werte an ?
        für historie .. jede sekunde ?? wozu um die Kurve glatt zu bekommen.. ??

        ich hab den gleichen WR .. und frage die Werte alle 10 sek ab. das reicht vollkommen..

        wenn der Adapter seid jahren schon so lief . dann hat sich bei dir was geändert in der Netzerkinfrastruktur.. die Fehlermeldung besagt der WR antwortet nicht in der vorgegebenen zeit..

        was läuft auf modbus.0 ?? der gleiche WR.. ?? wird der sonst noch mit anfragen bombardiert ?? von http ??

        S Offline
        S Offline
        Sneak-L8
        schrieb am zuletzt editiert von
        #820

        @arteck Also ich nutze die Werte, um den Überschuss fürs E-Auto-Laden zu berechnen, den WW-Boiler davon abhängig zu steuern.

        wenn der Adapter seid jahren schon so lief . dann hat sich bei dir was geändert in der Netzerkinfrastruktur.. die Fehlermeldung besagt der WR antwortet nicht in der vorgegebenen zeit..

        Also mein DSL wurde von 50 auf 100MBit/s erhöht und es gibt einen neuen Shelly im Netz. Sonst hat sich da nichts getan.

        was läuft auf modbus.0 ??

        Ausschließlich der modbus-Adapter. Und der geht ja über TCP/IP. Ich meine "echtes" Modbus gibt es keins. Der SummyHomeManager spricht ja auch über TCP/UDP mit dem WR und nicht per Modbus. Sonst müsste es da ja eine extra Verkabelung geben, oder?

        arteckA 1 Antwort Letzte Antwort
        0
        • S Sneak-L8

          @arteck Also ich nutze die Werte, um den Überschuss fürs E-Auto-Laden zu berechnen, den WW-Boiler davon abhängig zu steuern.

          wenn der Adapter seid jahren schon so lief . dann hat sich bei dir was geändert in der Netzerkinfrastruktur.. die Fehlermeldung besagt der WR antwortet nicht in der vorgegebenen zeit..

          Also mein DSL wurde von 50 auf 100MBit/s erhöht und es gibt einen neuen Shelly im Netz. Sonst hat sich da nichts getan.

          was läuft auf modbus.0 ??

          Ausschließlich der modbus-Adapter. Und der geht ja über TCP/IP. Ich meine "echtes" Modbus gibt es keins. Der SummyHomeManager spricht ja auch über TCP/UDP mit dem WR und nicht per Modbus. Sonst müsste es da ja eine extra Verkabelung geben, oder?

          arteckA Offline
          arteckA Offline
          arteck
          Developer Most Active
          schrieb am zuletzt editiert von arteck
          #821

          @sneak-l8 Modbus ist nur ein Kommunikationsprotokoll.. wie MQTT oder Zigbee.. wodrüber die Daten kommen ist wurscht..

          E-Auto-Laden zu berechnen, den WW-Boiler davon abhängig zu steuern

          und womit .. mit einem script oder wie ???
          ich hoffe nicht dass du alle sek den wagen penetrierst sollte die Sonne mal nicht da sein dann wieder doch dann wieder nicht..ist aber ein anderes Thema

          wie gesagt der WR antwortet nicht direkt.. deshalb die Meldung

          zigbee hab ich, zwave auch, nuc's genauso und HA auch

          S 1 Antwort Letzte Antwort
          0
          • arteckA arteck

            @sneak-l8 Modbus ist nur ein Kommunikationsprotokoll.. wie MQTT oder Zigbee.. wodrüber die Daten kommen ist wurscht..

            E-Auto-Laden zu berechnen, den WW-Boiler davon abhängig zu steuern

            und womit .. mit einem script oder wie ???
            ich hoffe nicht dass du alle sek den wagen penetrierst sollte die Sonne mal nicht da sein dann wieder doch dann wieder nicht..ist aber ein anderes Thema

            wie gesagt der WR antwortet nicht direkt.. deshalb die Meldung

            S Offline
            S Offline
            Sneak-L8
            schrieb am zuletzt editiert von
            #822

            @arteck Ah, ok. Danke für die Aufklärung. Dachte, es bräuchte für Modbus ne extra Verkabelung.

            Dann spricht vermutlich der SMH mit dem WR über Modbus. Sonst passiert bei Modbus aber nichts.

            Auto laden

            Ist der kecontact-Adapter. Ganz am Anfang hatte ich das per Skript gemacht und tatsächlich alle State abonniert und die Wallbox bei jeder Änderung bombadiert...
            Jetzt rechnet der Adapter alle 30 Sekunden aus, wie geregelt werden soll.

            Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

            Ich habe das Abfrageintervall mal auf 5 Sekunden erhöht, dann kamen erst diese Fehler:

            11:02:10.461	modbus.1	(COMPACT) Socket Error
            11:02:10.462	modbus.1	(COMPACT) Client in error state.
            11:02:10.462	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:02:15.591	modbus.1	(COMPACT) Socket Error
            11:02:15.592	modbus.1	(COMPACT) Client in error state.
            11:02:15.592	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:02:25.821	modbus.1	(COMPACT) Socket Error
            11:02:25.822	modbus.1	(COMPACT) Client in error state.
            11:02:25.822	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            

            8 Minuten später dann diese:

            11:09:35.901	modbus.1	(COMPACT) Socket Error
            11:09:35.903	modbus.1	(COMPACT) Client in error state.
            11:09:35.904	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:10:24.049	modbus.1	(COMPACT) Error: undefined
            11:10:24.067	modbus.1	(COMPACT) Request timed out.
            11:10:24.069	modbus.1	(COMPACT) Client in error state.
            11:10:24.075	modbus.1	(COMPACT) Poll error count: 1 code: {"err":"timeout","timeout":5000}
            11:10:29.720	modbus.1	(COMPACT) Error: undefined
            11:10:29.721	modbus.1	(COMPACT) Request timed out.
            11:10:29.722	modbus.1	(COMPACT) Client in error state.
            11:10:29.723	modbus.1	(COMPACT) Poll error count: 4621 code: {"err":"timeout","timeout":5000}
            11:10:29.725	modbus.1	(COMPACT) Reconnect did not help, restart adapter
            11:10:34.826	modbus.1	(COMPACT) Error: undefined
            11:10:34.828	modbus.1	(COMPACT) Request timed out.
            11:10:34.829	modbus.1	(COMPACT) Client in error state.
            11:10:34.830	modbus.1	(COMPACT) Poll error count: 39 code: {"err":"timeout","timeout":5000}
            11:10:34.832	modbus.1	(COMPACT) Reconnect did not help, restart adapter
            11:10:41.926	modbus.1	(COMPACT) Error: undefined
            11:10:41.928	modbus.1	(COMPACT) Request timed out.
            11:10:41.929	modbus.1	(COMPACT) Client in error state.
            11:10:41.930	modbus.1	(COMPACT) Poll error count: 15 code: {"err":"timeout","timeout":5000}
            11:10:41.933	modbus.1	(COMPACT) Reconnect did not help, restart adapter
            

            und nach einer Weile wieder die alt-bekannten:

            11:19:03.998	modbus.1	(COMPACT) Request timed out.
            11:19:03.999	modbus.1	(COMPACT) Client in error state.
            11:19:04.007	modbus.1	(COMPACT) Poll error count: 33 code: {"err":"timeout","timeout":5000}
            11:19:04.009	modbus.1	(COMPACT) Reconnect did not help, restart adapter
            11:19:12.232	modbus.1	(COMPACT) Error: undefined
            11:27:00.387	modbus.1	(COMPACT) Socket Error
            11:27:00.389	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:27:05.502	modbus.1	(COMPACT) Socket Error
            11:27:05.505	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:27:10.622	modbus.1	(COMPACT) Socket Error
            11:27:10.624	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:27:20.861	modbus.1	(COMPACT) Socket Error
            11:27:20.863	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
            11:27:31.101	modbus.1	(COMPACT) Socket Error
            

            Dazwischen waren aber auch mal ( Minuten oder Protokoll wie man sehen kann.

            HomoranH arteckA 3 Antworten Letzte Antwort
            0
            • S Sneak-L8

              @arteck Ah, ok. Danke für die Aufklärung. Dachte, es bräuchte für Modbus ne extra Verkabelung.

              Dann spricht vermutlich der SMH mit dem WR über Modbus. Sonst passiert bei Modbus aber nichts.

              Auto laden

              Ist der kecontact-Adapter. Ganz am Anfang hatte ich das per Skript gemacht und tatsächlich alle State abonniert und die Wallbox bei jeder Änderung bombadiert...
              Jetzt rechnet der Adapter alle 30 Sekunden aus, wie geregelt werden soll.

              Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

              Ich habe das Abfrageintervall mal auf 5 Sekunden erhöht, dann kamen erst diese Fehler:

              11:02:10.461	modbus.1	(COMPACT) Socket Error
              11:02:10.462	modbus.1	(COMPACT) Client in error state.
              11:02:10.462	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:02:15.591	modbus.1	(COMPACT) Socket Error
              11:02:15.592	modbus.1	(COMPACT) Client in error state.
              11:02:15.592	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:02:25.821	modbus.1	(COMPACT) Socket Error
              11:02:25.822	modbus.1	(COMPACT) Client in error state.
              11:02:25.822	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              

              8 Minuten später dann diese:

              11:09:35.901	modbus.1	(COMPACT) Socket Error
              11:09:35.903	modbus.1	(COMPACT) Client in error state.
              11:09:35.904	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:10:24.049	modbus.1	(COMPACT) Error: undefined
              11:10:24.067	modbus.1	(COMPACT) Request timed out.
              11:10:24.069	modbus.1	(COMPACT) Client in error state.
              11:10:24.075	modbus.1	(COMPACT) Poll error count: 1 code: {"err":"timeout","timeout":5000}
              11:10:29.720	modbus.1	(COMPACT) Error: undefined
              11:10:29.721	modbus.1	(COMPACT) Request timed out.
              11:10:29.722	modbus.1	(COMPACT) Client in error state.
              11:10:29.723	modbus.1	(COMPACT) Poll error count: 4621 code: {"err":"timeout","timeout":5000}
              11:10:29.725	modbus.1	(COMPACT) Reconnect did not help, restart adapter
              11:10:34.826	modbus.1	(COMPACT) Error: undefined
              11:10:34.828	modbus.1	(COMPACT) Request timed out.
              11:10:34.829	modbus.1	(COMPACT) Client in error state.
              11:10:34.830	modbus.1	(COMPACT) Poll error count: 39 code: {"err":"timeout","timeout":5000}
              11:10:34.832	modbus.1	(COMPACT) Reconnect did not help, restart adapter
              11:10:41.926	modbus.1	(COMPACT) Error: undefined
              11:10:41.928	modbus.1	(COMPACT) Request timed out.
              11:10:41.929	modbus.1	(COMPACT) Client in error state.
              11:10:41.930	modbus.1	(COMPACT) Poll error count: 15 code: {"err":"timeout","timeout":5000}
              11:10:41.933	modbus.1	(COMPACT) Reconnect did not help, restart adapter
              

              und nach einer Weile wieder die alt-bekannten:

              11:19:03.998	modbus.1	(COMPACT) Request timed out.
              11:19:03.999	modbus.1	(COMPACT) Client in error state.
              11:19:04.007	modbus.1	(COMPACT) Poll error count: 33 code: {"err":"timeout","timeout":5000}
              11:19:04.009	modbus.1	(COMPACT) Reconnect did not help, restart adapter
              11:19:12.232	modbus.1	(COMPACT) Error: undefined
              11:27:00.387	modbus.1	(COMPACT) Socket Error
              11:27:00.389	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:27:05.502	modbus.1	(COMPACT) Socket Error
              11:27:05.505	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:27:10.622	modbus.1	(COMPACT) Socket Error
              11:27:10.624	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:27:20.861	modbus.1	(COMPACT) Socket Error
              11:27:20.863	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
              11:27:31.101	modbus.1	(COMPACT) Socket Error
              

              Dazwischen waren aber auch mal ( Minuten oder Protokoll wie man sehen kann.

              HomoranH Nicht stören
              HomoranH Nicht stören
              Homoran
              Global Moderator Administrators
              schrieb am zuletzt editiert von
              #823

              @sneak-l8 sagte in Modbus adapter:

              Dachte, es bräuchte für Modbus ne extra Verkabelung.

              je nachdrm was dein Gerät anbietet.

              bei Modbus RTU ja, bei Modbus TCP nein, da braucht es nur das Netzwerk

              kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

              Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

              der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

              1 Antwort Letzte Antwort
              0
              • S Sneak-L8

                @arteck Ah, ok. Danke für die Aufklärung. Dachte, es bräuchte für Modbus ne extra Verkabelung.

                Dann spricht vermutlich der SMH mit dem WR über Modbus. Sonst passiert bei Modbus aber nichts.

                Auto laden

                Ist der kecontact-Adapter. Ganz am Anfang hatte ich das per Skript gemacht und tatsächlich alle State abonniert und die Wallbox bei jeder Änderung bombadiert...
                Jetzt rechnet der Adapter alle 30 Sekunden aus, wie geregelt werden soll.

                Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

                Ich habe das Abfrageintervall mal auf 5 Sekunden erhöht, dann kamen erst diese Fehler:

                11:02:10.461	modbus.1	(COMPACT) Socket Error
                11:02:10.462	modbus.1	(COMPACT) Client in error state.
                11:02:10.462	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:02:15.591	modbus.1	(COMPACT) Socket Error
                11:02:15.592	modbus.1	(COMPACT) Client in error state.
                11:02:15.592	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:02:25.821	modbus.1	(COMPACT) Socket Error
                11:02:25.822	modbus.1	(COMPACT) Client in error state.
                11:02:25.822	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                

                8 Minuten später dann diese:

                11:09:35.901	modbus.1	(COMPACT) Socket Error
                11:09:35.903	modbus.1	(COMPACT) Client in error state.
                11:09:35.904	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:10:24.049	modbus.1	(COMPACT) Error: undefined
                11:10:24.067	modbus.1	(COMPACT) Request timed out.
                11:10:24.069	modbus.1	(COMPACT) Client in error state.
                11:10:24.075	modbus.1	(COMPACT) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                11:10:29.720	modbus.1	(COMPACT) Error: undefined
                11:10:29.721	modbus.1	(COMPACT) Request timed out.
                11:10:29.722	modbus.1	(COMPACT) Client in error state.
                11:10:29.723	modbus.1	(COMPACT) Poll error count: 4621 code: {"err":"timeout","timeout":5000}
                11:10:29.725	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                11:10:34.826	modbus.1	(COMPACT) Error: undefined
                11:10:34.828	modbus.1	(COMPACT) Request timed out.
                11:10:34.829	modbus.1	(COMPACT) Client in error state.
                11:10:34.830	modbus.1	(COMPACT) Poll error count: 39 code: {"err":"timeout","timeout":5000}
                11:10:34.832	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                11:10:41.926	modbus.1	(COMPACT) Error: undefined
                11:10:41.928	modbus.1	(COMPACT) Request timed out.
                11:10:41.929	modbus.1	(COMPACT) Client in error state.
                11:10:41.930	modbus.1	(COMPACT) Poll error count: 15 code: {"err":"timeout","timeout":5000}
                11:10:41.933	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                

                und nach einer Weile wieder die alt-bekannten:

                11:19:03.998	modbus.1	(COMPACT) Request timed out.
                11:19:03.999	modbus.1	(COMPACT) Client in error state.
                11:19:04.007	modbus.1	(COMPACT) Poll error count: 33 code: {"err":"timeout","timeout":5000}
                11:19:04.009	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                11:19:12.232	modbus.1	(COMPACT) Error: undefined
                11:27:00.387	modbus.1	(COMPACT) Socket Error
                11:27:00.389	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:27:05.502	modbus.1	(COMPACT) Socket Error
                11:27:05.505	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:27:10.622	modbus.1	(COMPACT) Socket Error
                11:27:10.624	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:27:20.861	modbus.1	(COMPACT) Socket Error
                11:27:20.863	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                11:27:31.101	modbus.1	(COMPACT) Socket Error
                

                Dazwischen waren aber auch mal ( Minuten oder Protokoll wie man sehen kann.

                arteckA Offline
                arteckA Offline
                arteck
                Developer Most Active
                schrieb am zuletzt editiert von
                #824

                @sneak-l8 mach den mal an
                efdd7e85-cb82-4f63-8fb7-de99ad1bdee2-grafik.png

                zigbee hab ich, zwave auch, nuc's genauso und HA auch

                S 1 Antwort Letzte Antwort
                0
                • S Sneak-L8

                  @arteck Ah, ok. Danke für die Aufklärung. Dachte, es bräuchte für Modbus ne extra Verkabelung.

                  Dann spricht vermutlich der SMH mit dem WR über Modbus. Sonst passiert bei Modbus aber nichts.

                  Auto laden

                  Ist der kecontact-Adapter. Ganz am Anfang hatte ich das per Skript gemacht und tatsächlich alle State abonniert und die Wallbox bei jeder Änderung bombadiert...
                  Jetzt rechnet der Adapter alle 30 Sekunden aus, wie geregelt werden soll.

                  Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

                  Ich habe das Abfrageintervall mal auf 5 Sekunden erhöht, dann kamen erst diese Fehler:

                  11:02:10.461	modbus.1	(COMPACT) Socket Error
                  11:02:10.462	modbus.1	(COMPACT) Client in error state.
                  11:02:10.462	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:02:15.591	modbus.1	(COMPACT) Socket Error
                  11:02:15.592	modbus.1	(COMPACT) Client in error state.
                  11:02:15.592	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:02:25.821	modbus.1	(COMPACT) Socket Error
                  11:02:25.822	modbus.1	(COMPACT) Client in error state.
                  11:02:25.822	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  

                  8 Minuten später dann diese:

                  11:09:35.901	modbus.1	(COMPACT) Socket Error
                  11:09:35.903	modbus.1	(COMPACT) Client in error state.
                  11:09:35.904	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:10:24.049	modbus.1	(COMPACT) Error: undefined
                  11:10:24.067	modbus.1	(COMPACT) Request timed out.
                  11:10:24.069	modbus.1	(COMPACT) Client in error state.
                  11:10:24.075	modbus.1	(COMPACT) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  11:10:29.720	modbus.1	(COMPACT) Error: undefined
                  11:10:29.721	modbus.1	(COMPACT) Request timed out.
                  11:10:29.722	modbus.1	(COMPACT) Client in error state.
                  11:10:29.723	modbus.1	(COMPACT) Poll error count: 4621 code: {"err":"timeout","timeout":5000}
                  11:10:29.725	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                  11:10:34.826	modbus.1	(COMPACT) Error: undefined
                  11:10:34.828	modbus.1	(COMPACT) Request timed out.
                  11:10:34.829	modbus.1	(COMPACT) Client in error state.
                  11:10:34.830	modbus.1	(COMPACT) Poll error count: 39 code: {"err":"timeout","timeout":5000}
                  11:10:34.832	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                  11:10:41.926	modbus.1	(COMPACT) Error: undefined
                  11:10:41.928	modbus.1	(COMPACT) Request timed out.
                  11:10:41.929	modbus.1	(COMPACT) Client in error state.
                  11:10:41.930	modbus.1	(COMPACT) Poll error count: 15 code: {"err":"timeout","timeout":5000}
                  11:10:41.933	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                  

                  und nach einer Weile wieder die alt-bekannten:

                  11:19:03.998	modbus.1	(COMPACT) Request timed out.
                  11:19:03.999	modbus.1	(COMPACT) Client in error state.
                  11:19:04.007	modbus.1	(COMPACT) Poll error count: 33 code: {"err":"timeout","timeout":5000}
                  11:19:04.009	modbus.1	(COMPACT) Reconnect did not help, restart adapter
                  11:19:12.232	modbus.1	(COMPACT) Error: undefined
                  11:27:00.387	modbus.1	(COMPACT) Socket Error
                  11:27:00.389	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:27:05.502	modbus.1	(COMPACT) Socket Error
                  11:27:05.505	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:27:10.622	modbus.1	(COMPACT) Socket Error
                  11:27:10.624	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:27:20.861	modbus.1	(COMPACT) Socket Error
                  11:27:20.863	modbus.1	(COMPACT) On error: {"errno":-110,"code":"ETIMEDOUT","syscall":"connect","address":"192.168.97.46","port":502}
                  11:27:31.101	modbus.1	(COMPACT) Socket Error
                  

                  Dazwischen waren aber auch mal ( Minuten oder Protokoll wie man sehen kann.

                  HomoranH Nicht stören
                  HomoranH Nicht stören
                  Homoran
                  Global Moderator Administrators
                  schrieb am zuletzt editiert von
                  #825

                  @sneak-l8 sagte in Modbus adapter:

                  Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

                  ja und?
                  dein Auto regelt aber selber nicht in dem Tempo nach. Ob die Wallbox das schafft weiss ich nicht.

                  Arbeite doch mit Schieberegistern um den fließenden Mittelweer über eine bestimmte Zeit zu erhalten, oder die Differenz der kumulierten Energie.
                  Das gibt geglättete Werte.

                  Selbst 1 Minute bei 11kW wären lächerliche 183Wh = 7ct bei vollständigem Bezug zu 40ct/kWh.
                  Wenn du dir durch das ständige regeln etwas kaputtspielst wird das erheblich teurer

                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                  S 1 Antwort Letzte Antwort
                  1
                  • arteckA arteck

                    @sneak-l8 mach den mal an
                    efdd7e85-cb82-4f63-8fb7-de99ad1bdee2-grafik.png

                    S Offline
                    S Offline
                    Sneak-L8
                    schrieb am zuletzt editiert von
                    #826

                    @arteck Ok, hab ich probiert. Jetzt sind meine bisherigen States alle weg bzw. haben einen neuen Namen bekommen (modbus.1.inputRegisters.30531_Gesamtertrag => modbus.1.inputRegisters.1.30531_Gesamtertrag).

                    Die Werte sind aber nun alle "invalid", also high-value
                    06cfe626-a579-47bd-90e2-aab9b510cf68-grafik.png
                    und aktualisieren sich auch nicht mehr.... Ich gehe also wohl eher wieder zurück ... da kommen auch wieder alle Werte.

                    Die geloggten Werte der State sind durch das Löschen aber jetzt alle weg ...

                    arteckA HomoranH 2 Antworten Letzte Antwort
                    0
                    • HomoranH Homoran

                      @sneak-l8 sagte in Modbus adapter:

                      Wenn ich aber nur alle 30 Sekunden den WR abfragen lasse, dann kann der wert ja bis zu 30 Sekunden alt sein. Der Wert vom SMH/EnergyMeter ist aber aktuell. In 30 Sekunden kann viel sonne auftauchen/verschwinden. Daher sollten die Werte für EM und WR möglichst gleichzeitig ermittelt worden sein (auch ne Sekunde ist da eigentlich schon ungenau).

                      ja und?
                      dein Auto regelt aber selber nicht in dem Tempo nach. Ob die Wallbox das schafft weiss ich nicht.

                      Arbeite doch mit Schieberegistern um den fließenden Mittelweer über eine bestimmte Zeit zu erhalten, oder die Differenz der kumulierten Energie.
                      Das gibt geglättete Werte.

                      Selbst 1 Minute bei 11kW wären lächerliche 183Wh = 7ct bei vollständigem Bezug zu 40ct/kWh.
                      Wenn du dir durch das ständige regeln etwas kaputtspielst wird das erheblich teurer

                      S Offline
                      S Offline
                      Sneak-L8
                      schrieb am zuletzt editiert von
                      #827

                      @homoran Deswegen schrieb ich ja "am Anfang". Mein Auto meldete sogar irgendwann Ladefehler. Jetzt mit 30 Sekunden-Taktung läuft es prima.

                      Über Kumulation von Werten habe ich auch schon nachgedacht, um stetigere Werte zu erhalten.

                      1 Antwort Letzte Antwort
                      0
                      • S Sneak-L8

                        @arteck Ok, hab ich probiert. Jetzt sind meine bisherigen States alle weg bzw. haben einen neuen Namen bekommen (modbus.1.inputRegisters.30531_Gesamtertrag => modbus.1.inputRegisters.1.30531_Gesamtertrag).

                        Die Werte sind aber nun alle "invalid", also high-value
                        06cfe626-a579-47bd-90e2-aab9b510cf68-grafik.png
                        und aktualisieren sich auch nicht mehr.... Ich gehe also wohl eher wieder zurück ... da kommen auch wieder alle Werte.

                        Die geloggten Werte der State sind durch das Löschen aber jetzt alle weg ...

                        arteckA Offline
                        arteckA Offline
                        arteck
                        Developer Most Active
                        schrieb am zuletzt editiert von arteck
                        #828

                        @sneak-l8 wenn du mehrere Geräte hast die mit dem WR kommunizieren..dann solltest du das auch einstellen

                        dann kontrollireren..

                        5ec218ad-007f-4c74-b052-6ddbb6ba6be7-grafik.png

                        dass die auch hier steht..

                        und ja die bekommen nen neuen namen.. mit der zahl davor

                        zigbee hab ich, zwave auch, nuc's genauso und HA auch

                        S 2 Antworten Letzte Antwort
                        1
                        • arteckA arteck

                          @sneak-l8 wenn du mehrere Geräte hast die mit dem WR kommunizieren..dann solltest du das auch einstellen

                          dann kontrollireren..

                          5ec218ad-007f-4c74-b052-6ddbb6ba6be7-grafik.png

                          dass die auch hier steht..

                          und ja die bekommen nen neuen namen.. mit der zahl davor

                          S Offline
                          S Offline
                          Sneak-L8
                          schrieb am zuletzt editiert von Sneak-L8
                          #829

                          @arteck Danke für den Hinweis. Jetzt kommen die Werte auch bei "mehrere Geräte-IDs". Meine Scripte, die auf den Datenpunkt abfragen habe ch angepasst. Im Log ist erst mal nichts zu sehen (auch bei Abfrage jede Sekunde).

                          Vielleicht hat ein anderen Gerät jetzt modbus-Fähigkeiten und hat die Kommunikation gestört...

                          Danke!

                          1 Antwort Letzte Antwort
                          0
                          • S Sneak-L8

                            @arteck Ok, hab ich probiert. Jetzt sind meine bisherigen States alle weg bzw. haben einen neuen Namen bekommen (modbus.1.inputRegisters.30531_Gesamtertrag => modbus.1.inputRegisters.1.30531_Gesamtertrag).

                            Die Werte sind aber nun alle "invalid", also high-value
                            06cfe626-a579-47bd-90e2-aab9b510cf68-grafik.png
                            und aktualisieren sich auch nicht mehr.... Ich gehe also wohl eher wieder zurück ... da kommen auch wieder alle Werte.

                            Die geloggten Werte der State sind durch das Löschen aber jetzt alle weg ...

                            HomoranH Nicht stören
                            HomoranH Nicht stören
                            Homoran
                            Global Moderator Administrators
                            schrieb am zuletzt editiert von
                            #830

                            @sneak-l8 sagte in Modbus adapter:

                            Die geloggten Werte der State sind durch das Löschen aber jetzt alle weg ...

                            nein!
                            die sind noch bei den alten IDs.
                            einfach die History-Aliase verwenden

                            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                            S 1 Antwort Letzte Antwort
                            1
                            • HomoranH Homoran

                              @sneak-l8 sagte in Modbus adapter:

                              Die geloggten Werte der State sind durch das Löschen aber jetzt alle weg ...

                              nein!
                              die sind noch bei den alten IDs.
                              einfach die History-Aliase verwenden

                              S Offline
                              S Offline
                              Sneak-L8
                              schrieb am zuletzt editiert von
                              #831

                              @homoran Danke für den Hinweis.

                              Hatte kurzzeitig den Haken bei "mehrere Geräte-IDs" wieder entfernt. Da war auch keine History-Einstellung mehr zu den Datenpunkten da. Hatte ich dann vielleicht doch gar keine eingestellt? Denn wenn die noch in der History (bzw. SQL) da sind, dann sollten auch die Protokollier-einstellungen noch da sein, oder?

                              HomoranH 1 Antwort Letzte Antwort
                              -1
                              • arteckA arteck

                                @sneak-l8 wenn du mehrere Geräte hast die mit dem WR kommunizieren..dann solltest du das auch einstellen

                                dann kontrollireren..

                                5ec218ad-007f-4c74-b052-6ddbb6ba6be7-grafik.png

                                dass die auch hier steht..

                                und ja die bekommen nen neuen namen.. mit der zahl davor

                                S Offline
                                S Offline
                                Sneak-L8
                                schrieb am zuletzt editiert von
                                #832

                                @arteck Schade, jetzt geht es schon wieder mit den Fehlern los:

                                modbus.1
                                	2023-08-02 15:54:30.865	error	(COMPACT) Reconnect did not help, restart adapter
                                modbus.1
                                	2023-08-02 15:54:30.865	info	(COMPACT) setState not processed because States database not connected
                                modbus.1
                                	2023-08-02 15:54:30.864	warn	(COMPACT) Poll error count: 26 code: {"err":"timeout","timeout":5000}
                                modbus.1
                                	2023-08-02 15:54:30.863	error	(COMPACT) Client in error state.
                                modbus.1
                                	2023-08-02 15:54:30.862	error	(COMPACT) Request timed out.
                                modbus.1
                                	2023-08-02 15:54:30.861	warn	(COMPACT) Error: undefined
                                
                                1 Antwort Letzte Antwort
                                0
                                • S Sneak-L8

                                  @homoran Danke für den Hinweis.

                                  Hatte kurzzeitig den Haken bei "mehrere Geräte-IDs" wieder entfernt. Da war auch keine History-Einstellung mehr zu den Datenpunkten da. Hatte ich dann vielleicht doch gar keine eingestellt? Denn wenn die noch in der History (bzw. SQL) da sind, dann sollten auch die Protokollier-einstellungen noch da sein, oder?

                                  HomoranH Nicht stören
                                  HomoranH Nicht stören
                                  Homoran
                                  Global Moderator Administrators
                                  schrieb am zuletzt editiert von
                                  #833

                                  @sneak-l8 sagte in Modbus adapter:

                                  dann sollten auch die Protokollier-einstellungen noch da sein, oder?

                                  oder!

                                  Die Daten sind in der Datenbank unter der ID mit der sie geloggt wurden.
                                  Auch wenn du (oder wer/was auch immer) Das loggen deaktivierst.

                                  Loggst du wieder unter derselben ID kommst du auch wieder an die alten Daten.

                                  kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                  Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                  der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                  1 Antwort Letzte Antwort
                                  1
                                  • S Offline
                                    S Offline
                                    Sneak-L8
                                    schrieb am zuletzt editiert von
                                    #834

                                    So langsam verlässt mich der modbus-Adapter immer weiter. Bisher kamen ja Fehlermeldungen, aber es konnte denn noch der wert der PV-Leistung ausgelesne werden. Seit heutem orgen um 6 Uhr kommt kein Wert mehr. Damit kann ich keinen PV-Überschuss mehr für Wallbox und WW-Speicher nutzen.
                                    Ich habe mich mal ins Sunny-Portal eingeloggt. Dort werden die Daten weiterhin korrekt angezeigt.

                                    Nach dem 3. Neustart des Adapters geht es wieder.

                                    Was ich beim 3. Neustart anders gemacht habe? Ich hatte gesehen, dass der hm-rega auch gelb war und habe beide neu gestartet.

                                    Bin etwa ratlos, was ich noch tun kann, um der Quelle des Fehlers auf die Spur zu kommen.

                                    arteckA 1 Antwort Letzte Antwort
                                    0
                                    • S Sneak-L8

                                      So langsam verlässt mich der modbus-Adapter immer weiter. Bisher kamen ja Fehlermeldungen, aber es konnte denn noch der wert der PV-Leistung ausgelesne werden. Seit heutem orgen um 6 Uhr kommt kein Wert mehr. Damit kann ich keinen PV-Überschuss mehr für Wallbox und WW-Speicher nutzen.
                                      Ich habe mich mal ins Sunny-Portal eingeloggt. Dort werden die Daten weiterhin korrekt angezeigt.

                                      Nach dem 3. Neustart des Adapters geht es wieder.

                                      Was ich beim 3. Neustart anders gemacht habe? Ich hatte gesehen, dass der hm-rega auch gelb war und habe beide neu gestartet.

                                      Bin etwa ratlos, was ich noch tun kann, um der Quelle des Fehlers auf die Spur zu kommen.

                                      arteckA Offline
                                      arteckA Offline
                                      arteck
                                      Developer Most Active
                                      schrieb am zuletzt editiert von arteck
                                      #835

                                      @sneak-l8 schon mal Kabel getuscht zu dem WR ??

                                      und es liegt nocht an dem 3 Mal neustraten oder 50 mal

                                      wenn du den Adapter stoppst dauerst es so 1 min bis der WR dann den Modbus einstellt..

                                      nochaml was fragt den WR noch ab.. welche Software hast du noch im einsatz ?? du schreibst PV_Überschuss .. wie wird das gesteuert ??

                                      zigbee hab ich, zwave auch, nuc's genauso und HA auch

                                      S 1 Antwort Letzte Antwort
                                      0
                                      • arteckA arteck

                                        @sneak-l8 schon mal Kabel getuscht zu dem WR ??

                                        und es liegt nocht an dem 3 Mal neustraten oder 50 mal

                                        wenn du den Adapter stoppst dauerst es so 1 min bis der WR dann den Modbus einstellt..

                                        nochaml was fragt den WR noch ab.. welche Software hast du noch im einsatz ?? du schreibst PV_Überschuss .. wie wird das gesteuert ??

                                        S Offline
                                        S Offline
                                        Sneak-L8
                                        schrieb am zuletzt editiert von
                                        #836

                                        @arteck Guter Gedanke. Müsste ich temporär mal machen, da es recht lang durch diverse Rohre verlegt ist, die auch noch mit Dämmmaterial ausgestopft sind... Oder evtl. der Switch?

                                        nochaml was fragt den WR noch ab.. welche Software hast du noch im einsatz ?? du schreibst PV_Überschuss .. wie wird das gesteuert ??

                                        Nur der SunnyHomeManger und der modbus-Adapter. Sonst ist mir nichts bekannt. PV-Überschuss steuer ich zum einen über den kecontact-Adapter. Aber stimmt ,der liest nur den SHM aus und schaut, was für ein Überschuss da ist.
                                        Die WW-teuerung ist ein Skript, das anhand PV-Produktion - surplus + regard den Verbrauch im Haushaltsnetz errechnet, um darüber festzustellen, ob der WW-Speicher noch lädt.

                                        arteckA 1 Antwort Letzte Antwort
                                        0
                                        • S Sneak-L8

                                          @arteck Guter Gedanke. Müsste ich temporär mal machen, da es recht lang durch diverse Rohre verlegt ist, die auch noch mit Dämmmaterial ausgestopft sind... Oder evtl. der Switch?

                                          nochaml was fragt den WR noch ab.. welche Software hast du noch im einsatz ?? du schreibst PV_Überschuss .. wie wird das gesteuert ??

                                          Nur der SunnyHomeManger und der modbus-Adapter. Sonst ist mir nichts bekannt. PV-Überschuss steuer ich zum einen über den kecontact-Adapter. Aber stimmt ,der liest nur den SHM aus und schaut, was für ein Überschuss da ist.
                                          Die WW-teuerung ist ein Skript, das anhand PV-Produktion - surplus + regard den Verbrauch im Haushaltsnetz errechnet, um darüber festzustellen, ob der WW-Speicher noch lädt.

                                          arteckA Offline
                                          arteckA Offline
                                          arteck
                                          Developer Most Active
                                          schrieb am zuletzt editiert von
                                          #837

                                          @sneak-l8 sagte in Modbus adapter:

                                          Guter Gedanke. Müsste ich temporär mal machen, da es recht lang durch diverse Rohre verlegt ist, die auch noch mit Dämmmaterial ausgestopft sind... Oder evtl. der Switch?

                                          na guck haben wir es doch mal.. vielleicht parallel zur Stromführung das kabel gelegt .. und günstig Kabel gekauft ohne Abschirmung ??

                                          zigbee hab ich, zwave auch, nuc's genauso und HA auch

                                          S 1 Antwort Letzte Antwort
                                          0
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          748

                                          Online

                                          32.4k

                                          Benutzer

                                          81.4k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe