  3. Off Topic
  4. Synology als Nut-Server, SBC als Client
12 Beiträge 3 Kommentatoren 4.5k Aufrufe 3 Beobachtet
Dieses Thema wurde aufgespalten von [HowTo] USV: NUT Server auf SBC installieren Homoran
  • NegaleinN Offline
    NegaleinN Offline
    Negalein
    Hallo
    Ich hab die Synology als UPS-Server und am Proxmox-PC Nut-Client installiert.
    bei systemctl status nut-client bekomm ich folgende Fehler:
    ● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
         Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; preset: enabled)
         Active: active (running) since Mon 2026-04-27 18:10:56 CEST; 4min 19s ago
       Main PID: 632 (upsmon)
          Tasks: 2 (limit: 18831)
         Memory: 4.7M
            CPU: 19ms
         CGroup: /system.slice/nut-monitor.service
                 ├─632 /lib/nut/upsmon -F
                 └─643 /lib/nut/upsmon -F
    Apr 27 18:13:16 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
    Apr 27 18:13:21 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
    Apr 27 18:13:26 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
    Apr 27 18:13:31 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
    Apr 27 18:13:36 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
    Apr 27 18:13:41 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Server disconnected
    Apr 27 18:13:46 proxmox-3 nut-monitor[643]: Communications with UPS ups@10.0.1.21 established
    Apr 27 18:13:46 proxmox-3 nut-monitor[643]: UPS ups@10.0.1.21 on line power
    Apr 27 18:13:46 proxmox-3 nut-monitor[1421]: Network UPS Tools upsmon 2.8.0
    Apr 27 18:13:46 proxmox-3 nut-monitor[1423]: Network UPS Tools upsmon 2.8.0
    # Network UPS Tools: example nut.conf
    # General section
    # The MODE determines which part of the NUT is to be started, and which
    # configuration files must be modified.
    # This file try to standardize the various files being found in the field, like
    # /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based
    # systems, ... Distribution's init script should source this file to see which
    # component(s) has to be started.
    # The values of MODE can be:
    # - none: NUT is not configured, or use the Integrated Power Management, or use
    #   some external system to startup NUT components. So nothing is to be started.
    # - standalone: This mode address a local only configuration, with 1 UPS
    #   protecting the local system. This implies to start the 3 NUT layers (driver,
    #   upsd and upsmon) and the matching configuration files. This mode can also
    #   address UPS redundancy.
    # - netserver: same as for the standalone configuration, but also need
    #   some more network access controls (firewall, tcp-wrappers) and possibly a
    #   specific LISTEN directive in upsd.conf.
    #   Since this MODE is opened to the network, a special care should be applied
    #   to security concerns.
    # - netclient: this mode only requires upsmon.
    # IMPORTANT NOTE:
    #  This file is intended to be sourced by standard POSIX shell scripts (so
    #  there is no guaranteed `export VAR=VAL` syntax) and by systemd on Linux.
    #  You MUST NOT use spaces around the equal sign!
    MODE=netclient
    # Uncomment this to allow starting the service even if ups.conf has no device
    # sections at the moment. This environment variable overrides the built-in
    # "false" and an optional same-named default flag that can be set in upsd.conf:
    #ALLOW_NO_DEVICE=true
    #export ALLOW_NO_DEVICE
    # Network UPS Tools: example upsmon configuration
    # This file contains passwords, so keep it secure.
    # RUN_AS_USER <userid>
    # By default, upsmon splits into two processes.  One stays as root and
    # waits to run the SHUTDOWNCMD.  The other one switches to another userid
    # and does everything else.
    # The default unprivileged user is set at compile-time with the option
    #   'configure --with-user=...'
    # You can override it with '-u <user>' when starting upsmon, or just
    # define it here for convenience.
    # Note: if you plan to use the reload feature, this file (upsmon.conf)
    # must be readable by this user!  Since it contains passwords, DO NOT
    # make it world-readable.  Also, do not make it writable by the upsmon
    # user, since it creates an opportunity for an attack by changing the
    # SHUTDOWNCMD to something malicious.
    # For best results, you should create a new normal user like "nutmon",
    # and make it a member of a "nut" group or similar.  Then specify it
    # here and grant read access to the upsmon.conf for that group.
    # This user should not have write access to upsmon.conf.
    # RUN_AS_USER nut
    # MONITOR <system> <powervalue> <username> <password> ("primary"|"secondary")
    # List systems you want to monitor.  Not all of these may supply power
    # to the system running upsmon, but if you want to watch it, it has to
    # be in this section.
    # You must have at least one of these declared.
    # <system> is a UPS identifier in the form <upsname>@<hostname>[:<port>]
    # like ups@localhost, su700@mybox, etc.
    # Examples:
    #  - "su700@mybox" means a UPS called "su700" on a system called "mybox"
    #  - "fenton@bigbox:5678" is a UPS called "fenton" on a system called
    #    "bigbox" which runs upsd on port "5678".
    # The UPS names like "su700" and "fenton" are set in your ups.conf
    # in [brackets] which identify a section for a particular driver.
    # If the ups.conf on host "doghouse" has a section called "snoopy", the
    # identifier for it would be "snoopy@doghouse".
    # <powervalue> is an integer - the number of power supplies that this UPS
    # feeds on this system.  Most personal computers only have one power supply,
    # so this value is normally set to 1, while most modern servers have at least
    # two.  You need a pretty big or special box to have any other value here.
    # You can also set this to 0 for a system that doesn't take any power
    # from the MONITORed supply, which you still want to monitor (e.g. for an
    # administrative workstation fed from a different circuit than the datacenter
    # servers it monitors). Use <powervalue> if 0 when you want to hear about
    # changes for a given UPS without shutting down when it goes critical.
    # <username> and <password> must match an entry in that system's
    # upsd.users.  If your username is "upsmon" and your password is
    # "blah", the upsd.users would look like this:
    #	[upsmon]
    #		password  = blah
    #		upsmon primary 	# (or secondary)
    # "primary" means this system will shutdown last, allowing the secondary
    # systems time to shutdown first.
    # "secondary" means this system shuts down immediately when power goes
    # critical and less than MINSUPPLIES power sources have reliable input feeds.
    # The general assumption is that the "primary" system is the one with direct
    # connection to an UPS (such as serial or USB cable), so the primary system
    # runs the NUT driver and 'upsd' server locally and can manage the device,
    # and it would often tell the UPS to completely power itself off as a step
    # in power-race avoidance (see POWERDOWNFLAG for details).
    # Also, since the primary system stays up the longest, it suffers higher risks
    # of ungraceful shutdown if the estimation of remaining runtime (or of the
    # time it takes to shut down this system) was guessed wrong. By consequence,
    # the "secondary" systems typically monitor the power environment state
    # through the 'upsd' processes running on the remote (often "primary") systems
    # and do not directly interact with an UPS (no local NUT drivers are running
    # on the secondary systems). As such, secondaries typically shut down as
    # soon as there is a sufficiently long power outage, or a low-battery alert
    # from the UPS, or a loss of connection to the primary while the power was
    # last known to be missing.
    # This assumption and configuration can also make sense for networked UPSes,
    # where a rack full of servers might overload the communications capacity
    # of the networked management card on the UPS - in this case you might either
    # reduce the 'snmp-ups' or 'netxml-ups' driver polling rate, or dedicate a
    # "primary" server and set up the rest as "secondary" systems.
    # In case of such large setups as mentioned above, beware also that shutdown
    # times of the rack done all at once can substantially differ from smaller
    # scale experiments with single-server shutdowns, since systems can compete
    # for shared storage and other limited resources as they go down (and also
    # not everyone may safely shut down simultaneously - e.g. a NAS or DB server
    # would better go down after all its clients). You would be well served by
    # higher-end UPSes with manageable thresholds to declare a critical state.
    # Examples:
    # MONITOR myups@bigserver 1 upswired blah primary
    # MONITOR su700@server.example.com 1 upsmon secretpass secondary
    # MONITOR myups@localhost 1 upsmon pass primary	# (or secondary)
    MONITOR ups@10.0.1.21 1 monuser secret slave
    # MINSUPPLIES <num>
    # Give the number of power supplies that must be receiving power to keep
    # this system running.  Most systems have one power supply, so you would
    # put "1" in this field.
    # Large/expensive server type systems usually have more, and can run with
    # a few missing.  Some of these can run with 2 out of 4, for example,
    # so you'd set that to 2.  The idea is to keep the box running as long
    # as possible, right?
    # Obviously you have to put the redundant supplies on different UPS circuitsa
    # for this to make sense!  See big-servers.txt in the docs subdirectory
    # for more information and ideas on how to use this feature.
    MINSUPPLIES 1
    # SHUTDOWNCMD "<command>"
    # upsmon runs this command when the system needs to be brought down.
    # This should work just about everywhere ... if it doesn't, well, change it,
    # perhaps to a more complicated custom script.
    # Note that while you experiment with the initial setup and want to test how
    # your configuration reacts to power state changes and ultimately when power
    # is reported to go critical, but do not want your system to actually turn
    # off, consider setting the SHUTDOWNCMD temporarily to do something benign -
    # such as posting a message with 'logger' or 'wall' or 'mailx'. Do be careful
    # to plug the UPS back into the wall in a timely fashion.
    SHUTDOWNCMD "/sbin/shutdown -h +0"
    # NOTIFYCMD <command>
    # upsmon calls this to send messages when things happen
    # This command is called with the full text of the message (from NOTIFYMSG)
    # as one argument.
    # The environment string NOTIFYTYPE will contain the type string of
    # whatever caused this event to happen.
    # The environment string UPSNAME will contain the name of the system/device
    # that generated the change.
    # Note that this is only called for NOTIFY events that have EXEC set with
    # NOTIFYFLAG.  See NOTIFYFLAG below for more details.
    # Making this some sort of shell script might not be a bad idea.
    # Alternately you can use the upssched program as your NOTIFYCMD for some
    # more complex setups (e.g. to ease handling of notification storms).
    # For more information and ideas, see docs/scheduling.txt
    # Example:
    # NOTIFYCMD /bin/notifyme
    # POLLFREQ <n>
    # Polling frequency for normal activities, measured in seconds.
    # Adjust this to keep upsmon from flooding your network, but don't make
    # it too high or it may miss certain short-lived power events.
    POLLFREQ 5
    # POLLFREQALERT <n>
    # Polling frequency in seconds while UPS on battery.
    # You can make this number lower than POLLFREQ, which will make updates
    # faster when any UPS is running on battery.  This is a good way to tune
    # network load if you have a lot of these things running.
    # The default is 5 seconds for both this and POLLFREQ.
    POLLFREQALERT 5
    # HOSTSYNC - How long upsmon will wait before giving up on another upsmon
    # The primary upsmon process uses this number when waiting for secondary
    # systems to disconnect once it has set the forced shutdown (FSD) flag.
    # If they don't disconnect after this many seconds, it goes on without them.
    # Similarly, upsmon secondary processes wait up to this interval for the
    # primary upsmon to set FSD when an UPS they are monitoring goes critical -
    # that is, on battery and low battery.  If the primary doesn't do its job,
    # the secondaries will shut down anyway to avoid damage to the file systems.
    # This "wait for FSD" is done to avoid races where the status changes
    # to critical and back between polls by the primary.
    HOSTSYNC 15
    # DEADTIME - Interval to wait before declaring a stale ups "dead"
    # upsmon requires a UPS to provide status information every few seconds
    # (see POLLFREQ and POLLFREQALERT) to keep things updated.  If the status
    # fetch fails, the UPS is marked stale.  If it stays stale for more than
    # DEADTIME seconds, the UPS is marked dead.
    # A dead UPS that was last known to be on battery is assumed to have gone
    # to a low battery condition.  This may force a shutdown if it is providing
    # a critical amount of power to your system.
    # Note: DEADTIME should be a multiple of POLLFREQ and POLLFREQALERT.
    # Otherwise you'll have "dead" UPSes simply because upsmon isn't polling
    # them quickly enough.  Rule of thumb: take the larger of the two
    # POLLFREQ values, and multiply by 3.
    DEADTIME 15
    # POWERDOWNFLAG - Flag file for forcing UPS shutdown on the primary system
    # upsmon will create a file with this name in primary mode when it's time
    # to shut down the load.  You should check for this file's existence in
    # your shutdown scripts and run 'upsdrvctl shutdown' if it exists, to tell
    # the UPS(es) to power off.
    # See the config-notes.txt file in the docs subdirectory for more information.
    # Refer to the section:
    # [[UPS_shutdown]] "Configuring automatic shutdowns for low battery events"
    # or refer to the online version.
    POWERDOWNFLAG /etc/killpower
    # NOTIFYMSG - change messages sent by upsmon when certain events occur
    # You can change the default messages to something else if you like.
    # NOTIFYMSG <notify type> "message"
    # NOTIFYMSG ONLINE	"UPS %s on line power"
    # NOTIFYMSG ONBATT	"UPS %s on battery"
    # NOTIFYMSG LOWBATT	"UPS %s battery is low"
    # NOTIFYMSG FSD		"UPS %s: forced shutdown in progress"
    # NOTIFYMSG COMMOK	"Communications with UPS %s established"
    # NOTIFYMSG COMMBAD	"Communications with UPS %s lost"
    # NOTIFYMSG SHUTDOWN	"Auto logout and shutdown proceeding"
    # NOTIFYMSG REPLBATT	"UPS %s battery needs to be replaced"
    # NOTIFYMSG NOCOMM	"UPS %s is unavailable"
    # NOTIFYMSG NOPARENT	"upsmon parent process died - shutdown impossible"
    # Note that %s is replaced with the identifier of the UPS in question.
    # Possible values for <notify type>:
    # ONLINE   : UPS is back online
    # ONBATT   : UPS is on battery
    # LOWBATT  : UPS has a low battery (if also on battery, it's "critical")
    # FSD      : UPS is being shutdown by the primary (FSD = "Forced Shutdown")
    # COMMOK   : Communications established with the UPS
    # COMMBAD  : Communications lost to the UPS
    # SHUTDOWN : The system is being shutdown
    # REPLBATT : The UPS battery is bad and needs to be replaced
    # NOCOMM   : A UPS is unavailable (can't be contacted for monitoring)
    # NOPARENT : The process that shuts down the system has died (shutdown impossible)
    # NOTIFYFLAG - change behavior of upsmon when NOTIFY events occur
    # By default, upsmon sends walls (global messages to all logged in users)
    # and writes to the syslog when things happen.  You can change this.
    # NOTIFYFLAG <notify type> <flag>[+<flag>][+<flag>] ...
    # NOTIFYFLAG ONLINE	SYSLOG+WALL
    # NOTIFYFLAG ONBATT	SYSLOG+WALL
    # NOTIFYFLAG LOWBATT	SYSLOG+WALL
    # NOTIFYFLAG FSD	SYSLOG+WALL
    # NOTIFYFLAG COMMOK	SYSLOG+WALL
    # NOTIFYFLAG COMMBAD	SYSLOG+WALL
    # NOTIFYFLAG SHUTDOWN	SYSLOG+WALL
    # NOTIFYFLAG REPLBATT	SYSLOG+WALL
    # NOTIFYFLAG NOCOMM	SYSLOG+WALL
    # NOTIFYFLAG NOPARENT	SYSLOG+WALL
    # Possible values for the flags:
    # SYSLOG - Write the message in the syslog
    # WALL   - Write the message to all users on the system
    # EXEC   - Execute NOTIFYCMD (see above) with the message
    # IGNORE - Don't do anything
    # If you use IGNORE, don't use any other flags on the same line.
    # RBWARNTIME - replace battery warning time in seconds
    # upsmon will normally warn you about a battery that needs to be replaced
    # every 43200 seconds, which is 12 hours.  It does this by triggering a
    # NOTIFY_REPLBATT which is then handled by the usual notify structure
    # you've defined above.
    # If this number is not to your liking, override it here.
    RBWARNTIME 43200
    # NOCOMMWARNTIME - no communications warning time in seconds
    # upsmon will let you know through the usual notify system if it can't
    # talk to any of the UPS entries that are defined in this file.  It will
    # trigger a NOTIFY_NOCOMM by default every 300 seconds unless you
    # change the interval with this directive.
    NOCOMMWARNTIME 300
    # FINALDELAY - last sleep interval before shutting down the system
    # On a primary, upsmon will wait this long after sending the NOTIFY_SHUTDOWN
    # before executing your SHUTDOWNCMD.  If you need to do something in between
    # those events, increase this number.  Remember, at this point your UPS is
    # almost depleted, so don't make this too high.  If needed, on high-end UPS
    # devices you can usually configure when the low-battery state is announced
    # based on estimated remaining run-time or on charge level of the batteries.
    # Alternatively, you can set this very low so you don't wait around when
    # it's time to shut down.  Some UPSes don't give much warning for low
    # battery and will require a value of 0 here for a safe shutdown.
    # Note: If FINALDELAY on the secondary is greater than HOSTSYNC on the
    # primary, the primary will give up waiting for that secondary system
    # to disconnect.
    FINALDELAY 5
    # CERTPATH - path to certificates (database directory or directory with CA's)
    # When compiled with SSL support, you can enter the certificate path here.
    # With NSS:
    # Certificates are stored in a dedicated database (split into 3 files).
    # Specify the path of the database directory.
    # CERTPATH /etc/nut/cert/upsmon
    # With OpenSSL:
    # Directory containing CA certificates in PEM format, used to verify
    # the server certificate presented by the upsd server. The files each
    # contain one CA certificate. The files are looked up by the CA subject
    # name hash value, which must hence be available.
    # CERTPATH /usr/ssl/certs
    # See 'docs/security.txt' or the Security chapter of NUT user manual
    # for more information on the SSL support in NUT.
    # CERTIDENT - self certificate name and database password
    # CERTIDENT <certificate name> <database password>
    # When compiled with SSL support with NSS, you can specify the certificate
    # name to retrieve from database to authenticate itself and the password
    # required to access certificate related private key.
    # CERTIDENT "my nut monitor" "MyPasSw0rD"
    # CERTHOST - security properties for an host
    # CERTHOST <hostname> <certificate name> <certverify> <forcessl>
    # When compiled with SSL support with NSS, you can specify security directive
    # for each server you can contact.
    # Each entry maps server name with the expected certificate name and flags
    # indicating if the server certificate is verified and if the connection
    # must be secure.
    # CERTHOST localhost "My nut server" 1 1
    # CERTVERIFY - make upsmon verify all connections with certificates
    # CERTVERIFY 1
    # When compiled with SSL support, make upsmon verify all connections with
    # certificates.
    # Without this, there is no guarantee that the upsd is the right host.
    # Enabling this greatly reduces the risk of man in the middle attacks.
    # This effectively forces the use of SSL, so don't use this unless
    # all of your upsd hosts are ready for SSL and have their certificates
    # in order.
    # When compiled with NSS support of SSL, can be overridden for host
    # specified with a CERTHOST directive.
    # FORCESSL - force upsmon to use SSL
    # FORCESSL 1
    # When compiled with SSL, specify that a secured connection must be used
    # to communicate with upsd.
    # If you don't use 'CERTVERIFY 1', then this will at least make sure
    # that nobody can sniff your sessions without a large effort.  Setting
    # this will make upsmon drop connections if the remote upsd doesn't
    # support SSL, so don't use it unless all of them have it running.
    # DEBUG_MIN - specify minimal debugging level for upsmon daemon
    # e.g. DEBUG_MIN 6
    # Optionally specify a minimum debug level for `upsmon` daemon, e.g. for
    # troubleshooting a deployment, without impacting foreground or background
    # running mode directly, and without need to edit init-scripts or service
    # unit definitions. Note that command-line option `-D` can only increase
    # this verbosity level.
    # NOTE: if the running daemon receives a `reload` command, presence of the
    # `DEBUG_MIN NUMBER` value in the configuration file can be used to tune
    # debugging verbosity in the running service daemon (it is recommended to
    # comment it away or set the minimum to explicit zero when done, to avoid
    # huge journals and I/O system abuse). Keep in mind that for this run-time
    # tuning, the `DEBUG_MIN` value *present* in *reloaded* configuration files
    # is applied instantly and overrides any previously set value, from file
    # or CLI options, regardless of older logging level being higher or lower
    # than the newly found number; a missing (or commented away) value however
    # does not change the previously active logging verbosity.
    wo hab ich da noch einen Fehler?
    ° Fixer ---> iob fix
    • NegaleinN Negalein
      Hallo
           Memory: 4.7M
              CPU: 19ms
      # General section
      # IMPORTANT NOTE:
      MODE=netclient
      # RUN_AS_USER nut
      # Examples:
      #	[upsmon]
      #		password  = blah
      # Examples:
      # MINSUPPLIES <num>
      MINSUPPLIES 1
      # as one argument.
      # Example:
      # POLLFREQ <n>
      POLLFREQ 5
      # POLLFREQALERT <n>
      POLLFREQALERT 5
      HOSTSYNC 15
      DEADTIME 15
      RBWARNTIME 43200
      NOCOMMWARNTIME 300
      # to disconnect.
      FINALDELAY 5
      # With NSS:
      # With OpenSSL:
      # must be secure.
      # CERTVERIFY 1
      # certificates.
      # in order.
      # FORCESSL 1
      # e.g. DEBUG_MIN 6
      @Negalein hast du in der syno bei nut die IP des Proxmox freigegeben?
        NegaleinN Offline
        NegaleinN Offline
        Negalein
        @Homoran sagte:
        Ja, aber die falsche. Ich Döddl ;)
        Dürfte jetzt laufen
             Active: active (running) since Mon 2026-04-27 18:41:48 CEST; 10s ago
           Main PID: 6452 (upsmon)
             Memory: 844.0K
                CPU: 4ms
                     ├─6452 /lib/nut/upsmon -F
                     └─6453 /lib/nut/upsmon -F
        Apr 27 18:41:48 proxmox-3 systemd[1]: Started nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller.
        Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: fopen /run/nut/upsmon.pid: No such file or directory
        Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: Could not find PID file to see if previous upsmon instance is already running!
        Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: UPS: ups@10.0.1.21 (secondary) (power value 1)
        Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: Using power down flag file /etc/killpower
        Apr 27 18:41:48 proxmox-3 nut-monitor[6453]: Init SSL without certificate database
        brauch ich am Proxmox nun noch ein Script, damit er zuerst Lxc/VM und erst dann den Host runterfährt?
          @Homoran sagte:
          Dürfte jetzt laufen
               Memory: 844.0K
                  CPU: 4ms
          Meister MopperM Offline
          Meister Mopper
          schrieb am zuletzt editiert von Meister Mopper
          @Negalein sagte:
          Nein, das Herunterfahren des Node beinhaltet natürlich das saubere Herunterfahren aller virtuellen Maschinen und Container.
          Man stoppt doch auch nicht alle VM/LXC bei einem reboot des Node.
          Proxmox und HA ...
            @Negalein sagte:
            NegaleinN Offline
            NegaleinN Offline
            Negalein
            @Meister-Mopper sagte:
            stimmt auch wieder.
            Die Tuts im Netzt sind zT so aufgeblasen.
            • NegaleinN Offline
              NegaleinN Offline
              Negalein
              @meister-mopper
              noch eine Frage:
              Nut-Client muss nicht noch extra konfiguriert werden, damit er weiss, wann die Maschine heruntergefahren werden muss?
              Da nimmt er Zeit/Prozent von der Synology?
              • NegaleinN Negalein verschob dieses Thema von ioBroker Allgemein am
              • Meister MopperM Offline
                Meister Mopper
                Du musst die Synology natürlich in der /etc/nut/upsmon.conf mit Passwort bekanntgeben und den nut-client.service starten.
                Ich überwache den Status mit dem linux-control Adapter regelmäßig, da er sich bei mir ab und an grußlos abgemeldet hat:
                if systemctl is-active --quiet nut-client.service; then echo "true"; else echo "false"; fi
                Proxmox und HA ...
                  NegaleinN Offline
                  NegaleinN Offline
                  Negalein
                  Ja, das läuft. Status ist verbunden. :)
                  hast du den noch mit speziellen Kommandos konfiguriert oder nur den Host eingetragen?
                  Javascript??
                    Javascript??
                    Meister Mopper
                    @Negalein
                    Das wird im Adapter unter 'MEINE BEFEHLE' eingegeben:
                    aeb11249-78b4-4750-8847-de2836dce29a-image.jpeg .
                    Dann hast du einen Boolean-Datenpunkt auf den du triggern kannst..
                    Proxmox und HA ...
                    NegaleinN 2 Antworten Letzte Antwort
                      @Negalein
                      NegaleinN Offline
                      NegaleinN Offline
                      Negalein
                        @Negalein
                        NegaleinN Offline
                        NegaleinN Offline
                        Negalein
                        kann ich dan Dienst dann mit Linux-Control wieder starten?
                          Meister Mopper
                          @Negalein sagte:
                          Das muss durch ein Skript geschehen.
                          Wenn der DP auf false geht sudo systemctl restart nut-client.service
                          edit => @Negalein
                          Aber hier sollte auch eine großzügige zeitliche Komponente eingebaut werden, damit nicht bei jedem Neustart des Ziel-Host das "Gezappel" losgeht.
                          Proxmox und HA ...