<?xml version="1.0" encoding="UTF-8"?><rss xmlns:dc="http://purl.org/dc/elements/1.1/" xmlns:content="http://purl.org/rss/1.0/modules/content/" xmlns:atom="http://www.w3.org/2005/Atom" version="2.0"><channel><title><![CDATA[Synology als Nut-Server, SBC als Client]]></title><description><![CDATA[<p dir="auto">Hallo</p>
<p dir="auto">Ich hab die Synology als UPS-Server und am Proxmox-PC Nut-Client installiert.</p>
<p dir="auto">bei <code>systemctl status nut-client</code> bekomm ich folgende Fehler:</p>
<pre><code>● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
     Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; preset: enabled)
     Active: active (running) since Mon 2026-04-27 18:10:56 CEST; 4min 19s ago
   Main PID: 632 (upsmon)
      Tasks: 2 (limit: 18831)
     Memory: 4.7M
        CPU: 19ms
     CGroup: /system.slice/nut-monitor.service
             ├─632 /lib/nut/upsmon -F
             └─643 /lib/nut/upsmon -F

Apr 27 18:13:16 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
Apr 27 18:13:21 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
Apr 27 18:13:26 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
Apr 27 18:13:31 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
Apr 27 18:13:36 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Access denied
Apr 27 18:13:41 proxmox-3 nut-monitor[643]: Poll UPS [ups@10.0.1.21] failed - Server disconnected
Apr 27 18:13:46 proxmox-3 nut-monitor[643]: Communications with UPS ups@10.0.1.21 established
Apr 27 18:13:46 proxmox-3 nut-monitor[643]: UPS ups@10.0.1.21 on line power
Apr 27 18:13:46 proxmox-3 nut-monitor[1421]: Network UPS Tools upsmon 2.8.0
Apr 27 18:13:46 proxmox-3 nut-monitor[1423]: Network UPS Tools upsmon 2.8.0
</code></pre>
<p dir="auto"></p><section class="spoiler-wrapper"><button class="spoiler-control btn btn-default">nut.conf</button><section style="display:none" class="spoiler-content"><p></p>
<pre><code># Network UPS Tools: example nut.conf
#
##############################################################################
# General section
##############################################################################
# The MODE determines which part of the NUT is to be started, and which
# configuration files must be modified.
#
# This file try to standardize the various files being found in the field, like
# /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based
# systems, ... Distribution's init script should source this file to see which
# component(s) has to be started.
#
# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management, or use
#   some external system to startup NUT components. So nothing is to be started.
# - standalone: This mode address a local only configuration, with 1 UPS
#   protecting the local system. This implies to start the 3 NUT layers (driver,
#   upsd and upsmon) and the matching configuration files. This mode can also
#   address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
#   some more network access controls (firewall, tcp-wrappers) and possibly a
#   specific LISTEN directive in upsd.conf.
#   Since this MODE is opened to the network, a special care should be applied
#   to security concerns.
# - netclient: this mode only requires upsmon.
#
# IMPORTANT NOTE:
#  This file is intended to be sourced by standard POSIX shell scripts (so
#  there is no guaranteed `export VAR=VAL` syntax) and by systemd on Linux.
#  You MUST NOT use spaces around the equal sign!

MODE=netclient

# Uncomment this to allow starting the service even if ups.conf has no device
# sections at the moment. This environment variable overrides the built-in
# "false" and an optional same-named default flag that can be set in upsd.conf:
#ALLOW_NO_DEVICE=true
#export ALLOW_NO_DEVICE
</code></pre>
<p dir="auto"></p></section></section><p></p>
<p dir="auto"></p><section class="spoiler-wrapper"><button class="spoiler-control btn btn-default">upsmon.conf</button><section style="display:none" class="spoiler-content"><p></p>
<pre><code># Network UPS Tools: example upsmon configuration
#
# This file contains passwords, so keep it secure.

# --------------------------------------------------------------------------
# RUN_AS_USER &lt;userid&gt;
#
# By default, upsmon splits into two processes.  One stays as root and
# waits to run the SHUTDOWNCMD.  The other one switches to another userid
# and does everything else.
#
# The default unprivileged user is set at compile-time with the option
#   'configure --with-user=...'
#
# You can override it with '-u &lt;user&gt;' when starting upsmon, or just
# define it here for convenience.
#
# Note: if you plan to use the reload feature, this file (upsmon.conf)
# must be readable by this user!  Since it contains passwords, DO NOT
# make it world-readable.  Also, do not make it writable by the upsmon
# user, since it creates an opportunity for an attack by changing the
# SHUTDOWNCMD to something malicious.
#
# For best results, you should create a new normal user like "nutmon",
# and make it a member of a "nut" group or similar.  Then specify it
# here and grant read access to the upsmon.conf for that group.
#
# This user should not have write access to upsmon.conf.
#
# RUN_AS_USER nut

# --------------------------------------------------------------------------
# MONITOR &lt;system&gt; &lt;powervalue&gt; &lt;username&gt; &lt;password&gt; ("primary"|"secondary")
#
# List systems you want to monitor.  Not all of these may supply power
# to the system running upsmon, but if you want to watch it, it has to
# be in this section.
#
# You must have at least one of these declared.
#
# &lt;system&gt; is a UPS identifier in the form &lt;upsname&gt;@&lt;hostname&gt;[:&lt;port&gt;]
# like ups@localhost, su700@mybox, etc.
#
# Examples:
#
#  - "su700@mybox" means a UPS called "su700" on a system called "mybox"
#
#  - "fenton@bigbox:5678" is a UPS called "fenton" on a system called
#    "bigbox" which runs upsd on port "5678".
#
# The UPS names like "su700" and "fenton" are set in your ups.conf
# in [brackets] which identify a section for a particular driver.
#
# If the ups.conf on host "doghouse" has a section called "snoopy", the
# identifier for it would be "snoopy@doghouse".
#
# &lt;powervalue&gt; is an integer - the number of power supplies that this UPS
# feeds on this system.  Most personal computers only have one power supply,
# so this value is normally set to 1, while most modern servers have at least
# two.  You need a pretty big or special box to have any other value here.
#
# You can also set this to 0 for a system that doesn't take any power
# from the MONITORed supply, which you still want to monitor (e.g. for an
# administrative workstation fed from a different circuit than the datacenter
# servers it monitors). Use &lt;powervalue&gt; if 0 when you want to hear about
# changes for a given UPS without shutting down when it goes critical.
#
# &lt;username&gt; and &lt;password&gt; must match an entry in that system's
# upsd.users.  If your username is "upsmon" and your password is
# "blah", the upsd.users would look like this:
#
#	[upsmon]
#		password  = blah
#		upsmon primary 	# (or secondary)
#
# "primary" means this system will shutdown last, allowing the secondary
# systems time to shutdown first.
#
# "secondary" means this system shuts down immediately when power goes
# critical and less than MINSUPPLIES power sources have reliable input feeds.
#
# The general assumption is that the "primary" system is the one with direct
# connection to an UPS (such as serial or USB cable), so the primary system
# runs the NUT driver and 'upsd' server locally and can manage the device,
# and it would often tell the UPS to completely power itself off as a step
# in power-race avoidance (see POWERDOWNFLAG for details).
#
# Also, since the primary system stays up the longest, it suffers higher risks
# of ungraceful shutdown if the estimation of remaining runtime (or of the
# time it takes to shut down this system) was guessed wrong. By consequence,
# the "secondary" systems typically monitor the power environment state
# through the 'upsd' processes running on the remote (often "primary") systems
# and do not directly interact with an UPS (no local NUT drivers are running
# on the secondary systems). As such, secondaries typically shut down as
# soon as there is a sufficiently long power outage, or a low-battery alert
# from the UPS, or a loss of connection to the primary while the power was
# last known to be missing.
#
# This assumption and configuration can also make sense for networked UPSes,
# where a rack full of servers might overload the communications capacity
# of the networked management card on the UPS - in this case you might either
# reduce the 'snmp-ups' or 'netxml-ups' driver polling rate, or dedicate a
# "primary" server and set up the rest as "secondary" systems.
#
# In case of such large setups as mentioned above, beware also that shutdown
# times of the rack done all at once can substantially differ from smaller
# scale experiments with single-server shutdowns, since systems can compete
# for shared storage and other limited resources as they go down (and also
# not everyone may safely shut down simultaneously - e.g. a NAS or DB server
# would better go down after all its clients). You would be well served by
# higher-end UPSes with manageable thresholds to declare a critical state.
#
# Examples:
#
# MONITOR myups@bigserver 1 upswired blah primary
# MONITOR su700@server.example.com 1 upsmon secretpass secondary
# MONITOR myups@localhost 1 upsmon pass primary	# (or secondary)

MONITOR ups@10.0.1.21 1 monuser secret slave

# --------------------------------------------------------------------------
# MINSUPPLIES &lt;num&gt;
#
# Give the number of power supplies that must be receiving power to keep
# this system running.  Most systems have one power supply, so you would
# put "1" in this field.
#
# Large/expensive server type systems usually have more, and can run with
# a few missing.  Some of these can run with 2 out of 4, for example,
# so you'd set that to 2.  The idea is to keep the box running as long
# as possible, right?
#
# Obviously you have to put the redundant supplies on different UPS circuitsa
# for this to make sense!  See big-servers.txt in the docs subdirectory
# for more information and ideas on how to use this feature.

MINSUPPLIES 1

# --------------------------------------------------------------------------
# SHUTDOWNCMD "&lt;command&gt;"
#
# upsmon runs this command when the system needs to be brought down.
#
# This should work just about everywhere ... if it doesn't, well, change it,
# perhaps to a more complicated custom script.
#
# Note that while you experiment with the initial setup and want to test how
# your configuration reacts to power state changes and ultimately when power
# is reported to go critical, but do not want your system to actually turn
# off, consider setting the SHUTDOWNCMD temporarily to do something benign -
# such as posting a message with 'logger' or 'wall' or 'mailx'. Do be careful
# to plug the UPS back into the wall in a timely fashion.

SHUTDOWNCMD "/sbin/shutdown -h +0"

# --------------------------------------------------------------------------
# NOTIFYCMD &lt;command&gt;
#
# upsmon calls this to send messages when things happen
#
# This command is called with the full text of the message (from NOTIFYMSG)
# as one argument.
#
# The environment string NOTIFYTYPE will contain the type string of
# whatever caused this event to happen.
#
# The environment string UPSNAME will contain the name of the system/device
# that generated the change.
#
# Note that this is only called for NOTIFY events that have EXEC set with
# NOTIFYFLAG.  See NOTIFYFLAG below for more details.
#
# Making this some sort of shell script might not be a bad idea.
# Alternately you can use the upssched program as your NOTIFYCMD for some
# more complex setups (e.g. to ease handling of notification storms).
# For more information and ideas, see docs/scheduling.txt
#
# Example:
# NOTIFYCMD /bin/notifyme

# --------------------------------------------------------------------------
# POLLFREQ &lt;n&gt;
#
# Polling frequency for normal activities, measured in seconds.
#
# Adjust this to keep upsmon from flooding your network, but don't make
# it too high or it may miss certain short-lived power events.

POLLFREQ 5

# --------------------------------------------------------------------------
# POLLFREQALERT &lt;n&gt;
#
# Polling frequency in seconds while UPS on battery.
#
# You can make this number lower than POLLFREQ, which will make updates
# faster when any UPS is running on battery.  This is a good way to tune
# network load if you have a lot of these things running.
#
# The default is 5 seconds for both this and POLLFREQ.

POLLFREQALERT 5

# --------------------------------------------------------------------------
# HOSTSYNC - How long upsmon will wait before giving up on another upsmon
#
# The primary upsmon process uses this number when waiting for secondary
# systems to disconnect once it has set the forced shutdown (FSD) flag.
# If they don't disconnect after this many seconds, it goes on without them.
#
# Similarly, upsmon secondary processes wait up to this interval for the
# primary upsmon to set FSD when an UPS they are monitoring goes critical -
# that is, on battery and low battery.  If the primary doesn't do its job,
# the secondaries will shut down anyway to avoid damage to the file systems.
#
# This "wait for FSD" is done to avoid races where the status changes
# to critical and back between polls by the primary.

HOSTSYNC 15

# --------------------------------------------------------------------------
# DEADTIME - Interval to wait before declaring a stale ups "dead"
#
# upsmon requires a UPS to provide status information every few seconds
# (see POLLFREQ and POLLFREQALERT) to keep things updated.  If the status
# fetch fails, the UPS is marked stale.  If it stays stale for more than
# DEADTIME seconds, the UPS is marked dead.
#
# A dead UPS that was last known to be on battery is assumed to have gone
# to a low battery condition.  This may force a shutdown if it is providing
# a critical amount of power to your system.
#
# Note: DEADTIME should be a multiple of POLLFREQ and POLLFREQALERT.
# Otherwise you'll have "dead" UPSes simply because upsmon isn't polling
# them quickly enough.  Rule of thumb: take the larger of the two
# POLLFREQ values, and multiply by 3.

DEADTIME 15

# --------------------------------------------------------------------------
# POWERDOWNFLAG - Flag file for forcing UPS shutdown on the primary system
#
# upsmon will create a file with this name in primary mode when it's time
# to shut down the load.  You should check for this file's existence in
# your shutdown scripts and run 'upsdrvctl shutdown' if it exists, to tell
# the UPS(es) to power off.
#
# See the config-notes.txt file in the docs subdirectory for more information.
# Refer to the section:
# [[UPS_shutdown]] "Configuring automatic shutdowns for low battery events"
# or refer to the online version.

POWERDOWNFLAG /etc/killpower

# --------------------------------------------------------------------------
# NOTIFYMSG - change messages sent by upsmon when certain events occur
#
# You can change the default messages to something else if you like.
#
# NOTIFYMSG &lt;notify type&gt; "message"
#
# NOTIFYMSG ONLINE	"UPS %s on line power"
# NOTIFYMSG ONBATT	"UPS %s on battery"
# NOTIFYMSG LOWBATT	"UPS %s battery is low"
# NOTIFYMSG FSD		"UPS %s: forced shutdown in progress"
# NOTIFYMSG COMMOK	"Communications with UPS %s established"
# NOTIFYMSG COMMBAD	"Communications with UPS %s lost"
# NOTIFYMSG SHUTDOWN	"Auto logout and shutdown proceeding"
# NOTIFYMSG REPLBATT	"UPS %s battery needs to be replaced"
# NOTIFYMSG NOCOMM	"UPS %s is unavailable"
# NOTIFYMSG NOPARENT	"upsmon parent process died - shutdown impossible"
#
# Note that %s is replaced with the identifier of the UPS in question.
#
# Possible values for &lt;notify type&gt;:
#
# ONLINE   : UPS is back online
# ONBATT   : UPS is on battery
# LOWBATT  : UPS has a low battery (if also on battery, it's "critical")
# FSD      : UPS is being shutdown by the primary (FSD = "Forced Shutdown")
# COMMOK   : Communications established with the UPS
# COMMBAD  : Communications lost to the UPS
# SHUTDOWN : The system is being shutdown
# REPLBATT : The UPS battery is bad and needs to be replaced
# NOCOMM   : A UPS is unavailable (can't be contacted for monitoring)
# NOPARENT : The process that shuts down the system has died (shutdown impossible)

# --------------------------------------------------------------------------
# NOTIFYFLAG - change behavior of upsmon when NOTIFY events occur
#
# By default, upsmon sends walls (global messages to all logged in users)
# and writes to the syslog when things happen.  You can change this.
#
# NOTIFYFLAG &lt;notify type&gt; &lt;flag&gt;[+&lt;flag&gt;][+&lt;flag&gt;] ...
#
# NOTIFYFLAG ONLINE	SYSLOG+WALL
# NOTIFYFLAG ONBATT	SYSLOG+WALL
# NOTIFYFLAG LOWBATT	SYSLOG+WALL
# NOTIFYFLAG FSD	SYSLOG+WALL
# NOTIFYFLAG COMMOK	SYSLOG+WALL
# NOTIFYFLAG COMMBAD	SYSLOG+WALL
# NOTIFYFLAG SHUTDOWN	SYSLOG+WALL
# NOTIFYFLAG REPLBATT	SYSLOG+WALL
# NOTIFYFLAG NOCOMM	SYSLOG+WALL
# NOTIFYFLAG NOPARENT	SYSLOG+WALL
#
# Possible values for the flags:
#
# SYSLOG - Write the message in the syslog
# WALL   - Write the message to all users on the system
# EXEC   - Execute NOTIFYCMD (see above) with the message
# IGNORE - Don't do anything
#
# If you use IGNORE, don't use any other flags on the same line.

# --------------------------------------------------------------------------
# RBWARNTIME - replace battery warning time in seconds
#
# upsmon will normally warn you about a battery that needs to be replaced
# every 43200 seconds, which is 12 hours.  It does this by triggering a
# NOTIFY_REPLBATT which is then handled by the usual notify structure
# you've defined above.
#
# If this number is not to your liking, override it here.

RBWARNTIME 43200

# --------------------------------------------------------------------------
# NOCOMMWARNTIME - no communications warning time in seconds
#
# upsmon will let you know through the usual notify system if it can't
# talk to any of the UPS entries that are defined in this file.  It will
# trigger a NOTIFY_NOCOMM by default every 300 seconds unless you
# change the interval with this directive.

NOCOMMWARNTIME 300

# --------------------------------------------------------------------------
# FINALDELAY - last sleep interval before shutting down the system
#
# On a primary, upsmon will wait this long after sending the NOTIFY_SHUTDOWN
# before executing your SHUTDOWNCMD.  If you need to do something in between
# those events, increase this number.  Remember, at this point your UPS is
# almost depleted, so don't make this too high.  If needed, on high-end UPS
# devices you can usually configure when the low-battery state is announced
# based on estimated remaining run-time or on charge level of the batteries.
#
# Alternatively, you can set this very low so you don't wait around when
# it's time to shut down.  Some UPSes don't give much warning for low
# battery and will require a value of 0 here for a safe shutdown.
#
# Note: If FINALDELAY on the secondary is greater than HOSTSYNC on the
# primary, the primary will give up waiting for that secondary system
# to disconnect.

FINALDELAY 5

# --------------------------------------------------------------------------
# CERTPATH - path to certificates (database directory or directory with CA's)
#
# When compiled with SSL support, you can enter the certificate path here.
#
# With NSS:
# Certificates are stored in a dedicated database (split into 3 files).
# Specify the path of the database directory.
#
# CERTPATH /etc/nut/cert/upsmon
#
# With OpenSSL:
# Directory containing CA certificates in PEM format, used to verify
# the server certificate presented by the upsd server. The files each
# contain one CA certificate. The files are looked up by the CA subject
# name hash value, which must hence be available.
#
# CERTPATH /usr/ssl/certs
#
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTIDENT - self certificate name and database password
# CERTIDENT &lt;certificate name&gt; &lt;database password&gt;
#
# When compiled with SSL support with NSS, you can specify the certificate
# name to retrieve from database to authenticate itself and the password
# required to access certificate related private key.
#
# CERTIDENT "my nut monitor" "MyPasSw0rD"
#
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTHOST - security properties for an host
# CERTHOST &lt;hostname&gt; &lt;certificate name&gt; &lt;certverify&gt; &lt;forcessl&gt;
#
# When compiled with SSL support with NSS, you can specify security directive
# for each server you can contact.
# Each entry maps server name with the expected certificate name and flags
# indicating if the server certificate is verified and if the connection
# must be secure.
#
# CERTHOST localhost "My nut server" 1 1
#
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTVERIFY - make upsmon verify all connections with certificates
# CERTVERIFY 1
#
# When compiled with SSL support, make upsmon verify all connections with
# certificates.
# Without this, there is no guarantee that the upsd is the right host.
# Enabling this greatly reduces the risk of man in the middle attacks.
# This effectively forces the use of SSL, so don't use this unless
# all of your upsd hosts are ready for SSL and have their certificates
# in order.
# When compiled with NSS support of SSL, can be overridden for host
# specified with a CERTHOST directive.


# --------------------------------------------------------------------------
# FORCESSL - force upsmon to use SSL
# FORCESSL 1
#
# When compiled with SSL, specify that a secured connection must be used
# to communicate with upsd.
# If you don't use 'CERTVERIFY 1', then this will at least make sure
# that nobody can sniff your sessions without a large effort.  Setting
# this will make upsmon drop connections if the remote upsd doesn't
# support SSL, so don't use it unless all of them have it running.
# When compiled with NSS support of SSL, can be overridden for host
# specified with a CERTHOST directive.

# --------------------------------------------------------------------------
# DEBUG_MIN - specify minimal debugging level for upsmon daemon
# e.g. DEBUG_MIN 6
#
# Optionally specify a minimum debug level for `upsmon` daemon, e.g. for
# troubleshooting a deployment, without impacting foreground or background
# running mode directly, and without need to edit init-scripts or service
# unit definitions. Note that command-line option `-D` can only increase
# this verbosity level.
#
# NOTE: if the running daemon receives a `reload` command, presence of the
# `DEBUG_MIN NUMBER` value in the configuration file can be used to tune
# debugging verbosity in the running service daemon (it is recommended to
# comment it away or set the minimum to explicit zero when done, to avoid
# huge journals and I/O system abuse). Keep in mind that for this run-time
# tuning, the `DEBUG_MIN` value *present* in *reloaded* configuration files
# is applied instantly and overrides any previously set value, from file
# or CLI options, regardless of older logging level being higher or lower
# than the newly found number; a missing (or commented away) value however
# does not change the previously active logging verbosity.
</code></pre>
<p dir="auto"></p></section></section><p></p>
<p dir="auto">wo hab ich da noch einen Fehler?</p>
]]></description><link>https://forum.iobroker.net/topic/84415/synology-als-nut-server-sbc-als-client</link><generator>RSS for Node</generator><lastBuildDate>Sat, 02 May 2026 18:21:49 GMT</lastBuildDate><atom:link href="https://forum.iobroker.net/topic/84415.rss" rel="self" type="application/rss+xml"/><pubDate>Mon, 27 Apr 2026 16:28:04 GMT</pubDate><ttl>60</ttl><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 15:17:00 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/negalein" aria-label="Profile: Negalein">@<bdi>Negalein</bdi></a> <a href="/post/1336876">sagte</a>:</p>
<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: Meister-Mopper">@<bdi>Meister-Mopper</bdi></a> <a href="/post/1336856">sagte</a>:</p>
<p dir="auto">Dann hast du einen Boolean-Datenpunkt auf den du triggern kannst..</p>
</blockquote>
<p dir="auto">kann ich dan Dienst dann mit Linux-Control wieder starten?</p>
</blockquote>
<p dir="auto">Das muss durch ein Skript geschehen.<br />
Wenn der DP auf false geht <code> sudo systemctl restart nut-client.service</code></p>
<p dir="auto">edit =&gt; <a class="plugin-mentions-user plugin-mentions-a" href="/user/negalein" aria-label="Profile: Negalein">@<bdi>Negalein</bdi></a><br />
Aber hier sollte auch eine großzügige zeitliche Komponente eingebaut werden, damit nicht bei jedem Neustart des Ziel-Host das "Gezappel" losgeht.</p>
]]></description><link>https://forum.iobroker.net/post/1336890</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336890</guid><dc:creator><![CDATA[Meister Mopper]]></dc:creator><pubDate>Tue, 28 Apr 2026 15:17:00 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 11:07:01 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: Meister-Mopper">@<bdi>Meister-Mopper</bdi></a> <a href="/post/1336856">sagte</a>:</p>
<p dir="auto">Dann hast du einen Boolean-Datenpunkt auf den du triggern kannst..</p>
</blockquote>
<p dir="auto">kann ich dan Dienst dann mit Linux-Control wieder starten?</p>
]]></description><link>https://forum.iobroker.net/post/1336876</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336876</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Tue, 28 Apr 2026 11:07:01 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 10:14:36 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: Meister-Mopper">@<bdi>Meister-Mopper</bdi></a> <a href="/post/1336856">sagte</a>:</p>
<p dir="auto">Das wird im Adapter unter 'MEINE BEFEHLE' eingegeben:</p>
</blockquote>
<p dir="auto">Danke</p>
]]></description><link>https://forum.iobroker.net/post/1336859</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336859</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Tue, 28 Apr 2026 10:14:36 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 10:08:43 GMT]]></title><description><![CDATA[<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/negalein" aria-label="Profile: Negalein">@<bdi>Negalein</bdi></a></p>
<p dir="auto">Das wird im Adapter unter 'MEINE BEFEHLE' eingegeben:</p>
<p dir="auto"><img src="/assets/uploads/files/1777370882274-aeb11249-78b4-4750-8847-de2836dce29a-image.jpeg" alt="aeb11249-78b4-4750-8847-de2836dce29a-image.jpeg" class=" img-fluid img-markdown" /> .</p>
<p dir="auto">Dann hast du einen Boolean-Datenpunkt auf den du triggern kannst..</p>
]]></description><link>https://forum.iobroker.net/post/1336856</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336856</guid><dc:creator><![CDATA[Meister Mopper]]></dc:creator><pubDate>Tue, 28 Apr 2026 10:08:43 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 06:58:20 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: Meister-Mopper">@<bdi>Meister-Mopper</bdi></a> <a href="/post/1336804">sagte</a>:</p>
<p dir="auto">Du musst die Synology natürlich in der /etc/nut/upsmon.conf mit Passwort bekanntgeben und den nut-client.service starten.</p>
</blockquote>
<p dir="auto">Ja, das läuft. Status ist verbunden. :)</p>
<blockquote>
<p dir="auto">Ich überwache den Status mit dem linux-control Adapter regelmäßig, da er sich bei mir ab und an grußlos abgemeldet hat:</p>
</blockquote>
<p dir="auto">hast du den noch mit speziellen Kommandos konfiguriert oder nur den Host eingetragen?</p>
<blockquote>
<p dir="auto">if systemctl is-active --quiet nut-client.service; then echo "true"; else echo "false"; fi</p>
</blockquote>
<p dir="auto">Javascript??</p>
]]></description><link>https://forum.iobroker.net/post/1336808</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336808</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Tue, 28 Apr 2026 06:58:20 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Tue, 28 Apr 2026 06:49:21 GMT]]></title><description><![CDATA[<p dir="auto">Du musst die Synology natürlich in der <code>/etc/nut/upsmon.conf</code> mit Passwort bekanntgeben und den nut-client.service starten.</p>
<p dir="auto">Ich überwache den Status mit dem linux-control Adapter regelmäßig, da er sich bei mir ab und an grußlos abgemeldet hat:<br />
<code>if systemctl is-active --quiet nut-client.service; then echo "true"; else echo "false"; fi</code></p>
]]></description><link>https://forum.iobroker.net/post/1336804</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336804</guid><dc:creator><![CDATA[Meister Mopper]]></dc:creator><pubDate>Tue, 28 Apr 2026 06:49:21 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Mon, 27 Apr 2026 21:05:40 GMT]]></title><description><![CDATA[<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: meister-mopper">@<bdi>meister-mopper</bdi></a></p>
<p dir="auto">noch eine Frage:</p>
<p dir="auto">Nut-Client muss nicht noch extra konfiguriert werden, damit er weiss, wann die Maschine heruntergefahren werden muss?<br />
Da nimmt er Zeit/Prozent von der Synology?</p>
]]></description><link>https://forum.iobroker.net/post/1336785</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336785</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Mon, 27 Apr 2026 21:05:40 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Mon, 27 Apr 2026 16:55:09 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/meister-mopper" aria-label="Profile: Meister-Mopper">@<bdi>Meister-Mopper</bdi></a> <a href="/post/1336711">sagte</a>:</p>
<p dir="auto">Man stoppt doch auch nicht alle VM/LXC bei einem reboot des Node.</p>
</blockquote>
<p dir="auto">stimmt auch wieder.</p>
<p dir="auto">Die Tuts im Netzt sind zT so aufgeblasen.</p>
]]></description><link>https://forum.iobroker.net/post/1336715</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336715</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Mon, 27 Apr 2026 16:55:09 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Mon, 27 Apr 2026 16:53:19 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/negalein" aria-label="Profile: Negalein">@<bdi>Negalein</bdi></a> <a href="/post/1336707">sagte</a>:</p>
<p dir="auto">brauch ich am Proxmox nun noch ein Script, damit er zuerst Lxc/VM und erst dann den Host runterfährt?</p>
</blockquote>
<p dir="auto">Nein, das Herunterfahren des Node beinhaltet natürlich das saubere Herunterfahren aller virtuellen Maschinen und Container.<br />
Man stoppt doch auch nicht alle VM/LXC bei einem reboot des Node.</p>
]]></description><link>https://forum.iobroker.net/post/1336711</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336711</guid><dc:creator><![CDATA[Meister Mopper]]></dc:creator><pubDate>Mon, 27 Apr 2026 16:53:19 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Mon, 27 Apr 2026 16:47:27 GMT]]></title><description><![CDATA[<blockquote>
<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/homoran" aria-label="Profile: Homoran">@<bdi>Homoran</bdi></a> <a href="/post/1336704">sagte</a>:</p>
<p dir="auto">hast du in der syno bei nut die IP des Proxmox freigegeben?</p>
</blockquote>
<p dir="auto">Ja, aber die falsche. Ich Döddl ;)</p>
<p dir="auto">Dürfte jetzt laufen</p>
<pre><code>● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
     Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; preset: enabled)
     Active: active (running) since Mon 2026-04-27 18:41:48 CEST; 10s ago
   Main PID: 6452 (upsmon)
      Tasks: 2 (limit: 18831)
     Memory: 844.0K
        CPU: 4ms
     CGroup: /system.slice/nut-monitor.service
             ├─6452 /lib/nut/upsmon -F
             └─6453 /lib/nut/upsmon -F

Apr 27 18:41:48 proxmox-3 systemd[1]: Started nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller.
Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: fopen /run/nut/upsmon.pid: No such file or directory
Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: Could not find PID file to see if previous upsmon instance is already running!
Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: UPS: ups@10.0.1.21 (secondary) (power value 1)
Apr 27 18:41:48 proxmox-3 nut-monitor[6452]: Using power down flag file /etc/killpower
Apr 27 18:41:48 proxmox-3 nut-monitor[6453]: Init SSL without certificate database
</code></pre>
<p dir="auto">brauch ich am Proxmox nun noch ein Script, damit er zuerst Lxc/VM und erst dann den Host runterfährt?</p>
]]></description><link>https://forum.iobroker.net/post/1336707</link><guid isPermaLink="true">https://forum.iobroker.net/post/1336707</guid><dc:creator><![CDATA[Negalein]]></dc:creator><pubDate>Mon, 27 Apr 2026 16:47:27 GMT</pubDate></item><item><title><![CDATA[Reply to Synology als Nut-Server, SBC als Client on Mon, 27 Apr 2026 16:34:39 GMT]]></title><description><![CDATA[<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/negalein" aria-label="Profile: Negalein">@<bdi>Negalein</bdi></a> hast du in der syno bei nut die IP des Proxmox freigegeben?</p>