Skip to content
  • Home
  • Recent
  • Tags
  • 0 Unread 0
  • Categories
  • Unreplied
  • Popular
  • GitHub
  • Docu
  • Hilfe
Skins
  • Light
  • Brite
  • Cerulean
  • Cosmo
  • Flatly
  • Journal
  • Litera
  • Lumen
  • Lux
  • Materia
  • Minty
  • Morph
  • Pulse
  • Sandstone
  • Simplex
  • Sketchy
  • Spacelab
  • United
  • Yeti
  • Zephyr
  • Dark
  • Cyborg
  • Darkly
  • Quartz
  • Slate
  • Solar
  • Superhero
  • Vapor

  • Default (No Skin)
  • No Skin
Collapse
ioBroker Logo

Community Forum

donate donate
  1. ioBroker Community Home
  2. Deutsch
  3. Tester
  4. Test Adapter HeatingControl v2.12.x

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.8k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.4k

Test Adapter HeatingControl v2.12.x

Scheduled Pinned Locked Moved Tester
heating
3.2k Posts 236 Posters 2.0m Views 205 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • Palm_ManiacP Palm_Maniac

    @dominik-f Hmmm, als dort Auto WindowOpen stand, wurde die Temp nach einiger Zeit wieder hochgesetzt, obwohl das Fenster noch auf war. Erst jetzt, wo dort Manual OpenWindow stand, war alles stabil. Eben habe ich die Fenster zu gemacht, die Temp geht hoch, aber es steht im State immer noch manual... Da die HMs alle auf Manuell stehen, funkt von dort eigentlich nichts dazwischen, ich wüßte zumindest nicht was.

    Rene_HMR Offline
    Rene_HMR Offline
    Rene_HM
    Developer
    wrote on last edited by
    #2643

    @palm_maniac sagte in Test Adapter HeatingControl v2.8.x:

    aber es steht im State immer noch manual.

    Bis zum nächsten Profilpunkt ...

    Palm_ManiacP 1 Reply Last reply
    0
    • Rene_HMR Rene_HM

      @palm_maniac sagte in Test Adapter HeatingControl v2.8.x:

      aber es steht im State immer noch manual.

      Bis zum nächsten Profilpunkt ...

      Palm_ManiacP Offline
      Palm_ManiacP Offline
      Palm_Maniac
      wrote on last edited by
      #2644

      @rene_hm Wie ich weiter oben schrieb, hab ich die Fenster dem Adapter in einem Test bekannt gemacht und nach einigen hinundher hat es damit dauerhaft funktioniert. Aber komisch ist, dass es nur dann geht, wenn im State aus auto nach dem öffnen des Fensters ein manual open window wird. Der Hack bei Thermostat behandelt Fenster offen ist gesetzt.

      Ich stelle morgen die entsprechenden Instanzen nochmal auf Debug und beobachte es. Sollte es sich wieder verstellen, poste ich dann nochmal das Log, da dann die Fensterkontakte erfasst werden.

      Vielen Dank schon mal für die Hilfe bei der Fehlersuche.

      Dominik F.D 1 Reply Last reply
      0
      • Palm_ManiacP Palm_Maniac

        @rene_hm Wie ich weiter oben schrieb, hab ich die Fenster dem Adapter in einem Test bekannt gemacht und nach einigen hinundher hat es damit dauerhaft funktioniert. Aber komisch ist, dass es nur dann geht, wenn im State aus auto nach dem öffnen des Fensters ein manual open window wird. Der Hack bei Thermostat behandelt Fenster offen ist gesetzt.

        Ich stelle morgen die entsprechenden Instanzen nochmal auf Debug und beobachte es. Sollte es sich wieder verstellen, poste ich dann nochmal das Log, da dann die Fensterkontakte erfasst werden.

        Vielen Dank schon mal für die Hilfe bei der Fehlersuche.

        Dominik F.D Offline
        Dominik F.D Offline
        Dominik F.
        wrote on last edited by
        #2645

        @palm_maniac

        Wenn bei dir auf manual gestellt ist, stellt sich der Adapter erst beim nächsten Profilpunkt wieder auf Auto, daher wird es bei dir denke ich keine Veränderung geben bis der nächste Profilpunkt erreicht ist.

        Eine Idee wäre noch, die Verknüpfung der Fensterkontakte mit dem Thermostaten/Wandthermostat zu lösen. Die Verknüpfung brauchst du ja theoretisch nicht. Ich hab bei mir nur die Thermostate mit dem Wandthermostat verknüpft und die Fenstersensoren (sind bei mir nicht von hm) ganz normal dem Adapter bekannt gemacht. Das sollte dann definitiv das Problem mit Auto und Manual Modus beheben.

        Palm_ManiacP 1 Reply Last reply
        0
        • Dominik F.D Dominik F.

          @palm_maniac

          Wenn bei dir auf manual gestellt ist, stellt sich der Adapter erst beim nächsten Profilpunkt wieder auf Auto, daher wird es bei dir denke ich keine Veränderung geben bis der nächste Profilpunkt erreicht ist.

          Eine Idee wäre noch, die Verknüpfung der Fensterkontakte mit dem Thermostaten/Wandthermostat zu lösen. Die Verknüpfung brauchst du ja theoretisch nicht. Ich hab bei mir nur die Thermostate mit dem Wandthermostat verknüpft und die Fenstersensoren (sind bei mir nicht von hm) ganz normal dem Adapter bekannt gemacht. Das sollte dann definitiv das Problem mit Auto und Manual Modus beheben.

          Palm_ManiacP Offline
          Palm_ManiacP Offline
          Palm_Maniac
          wrote on last edited by
          #2646

          @dominik-f Mein Problem ist ja nicht die Auto oder Manu Problematik, sondern das die Fenster Offen Temp trotz offenem Fenster irgendwann übersteuert wird.

          Wenn der Fensterkontakt in der Heizgruppe mit drin ist und ein Fenster geöffnet wird, dann wird das mit einem Symbol im Wand- und Heizkörperthermostat zusätzlich angezeigt als optische Kontrolle. Da würde ich ungern drauf verzichten und die Funktion würde bei Ausfall von iobroker verloren gehen. Ich werde es aber mal testen und darüber nachdenken.

          1 Reply Last reply
          0
          • Palm_ManiacP Offline
            Palm_ManiacP Offline
            Palm_Maniac
            wrote on last edited by
            #2647

            Heute klappt es wunderbar. Im State steht auto windowopen und die Thermostate bleiben auf 12 Grad. Nichts überschreibt die Temp. Ich habe nichts geändert. Das einzige was heute anders ist als gestern, heute ist kein Feiertag.

            1 Reply Last reply
            0
            • Palm_ManiacP Offline
              Palm_ManiacP Offline
              Palm_Maniac
              wrote on last edited by
              #2648

              Verdammt, leider zu früh gefreut. Als um 17Uhr die Temp im Bad laut Profil geändert werden sollte, wurde aus auto windowopen ein auto im state und die Temp ging trotz offenem Fenster und WindowIsOpen auf True auf 22,5 Grad. Leider hatte ich 1 Stunde vorher das Debug-Log abgeschaltet, so dass ich davon kein Log habe. Morgen versuche ich es erneut MIT laufendem Debug-Log.

              1 Reply Last reply
              0
              • Palm_ManiacP Offline
                Palm_ManiacP Offline
                Palm_Maniac
                wrote on last edited by
                #2649

                Heute ist es wieder passiert und ich hab das Log. :)

                2022-04-20 16:58:18.317 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE {"val":21.9,"ack":true,"ts":1650466698315,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543}
                2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Current to {"val":21.9,"ack":true,"ts":1650466698315,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543} in auto
                2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) Change Status current temperature in Bad to 21.9
                2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                2022-04-20 16:58:18.333 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto WindowOpen 12°C
                2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE {"val":12,"ack":true,"ts":1650466698362,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650459008565}
                2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 17:00:00.010 - debug: heatingcontrol.2 (4014) ChangeStatus fired with [{"room":"Bad","target":22.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"17:00","CurrentTimePeriodFull":"Period 3 17:00"}]
                2022-04-20 17:00:00.010 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus ProfilPoint to {"room":"Bad","target":22.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"17:00","CurrentTimePeriodFull":"Period 3 17:00"} in auto
                2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) ChangeStatus by cron Profilepoint in Bad target 22.5
                2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) CalculateRoomTemperature for Bad auto
                2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) Bad auto mode: target 22.5
                2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) Bad auto mode (incl. reduced): target 22.5
                2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) SetRoomTemperature started for Bad target 22.5 with offset 0
                2022-04-20 17:00:00.035 - debug: heatingcontrol.2 (4014) unsubscribe linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 17:00:00.038 - debug: heatingcontrol.2 (4014) Bad set thermostat target linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE to 22.5
                2022-04-20 17:00:00.101 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                2022-04-20 17:00:05.038 - debug: heatingcontrol.2 (4014) subscribe linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE {"val":21.9,"ack":true,"ts":1650466847811,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543}
                2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Current to {"val":21.9,"ack":true,"ts":1650466847811,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543} in auto
                2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) Change Status current temperature in Bad to 21.9
                2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                2022-04-20 17:00:47.828 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095}
                2022-04-20 17:00:47.828 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 17:00:47.829 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                2022-04-20 17:00:47.829 - debug: heatingcontrol.2 (4014) ChangeStatus called, while already changing, push to list Bad Thermostats_Target {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} (1)
                2022-04-20 17:00:47.841 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto 22.5°C
                2022-04-20 17:00:47.850 - debug: heatingcontrol.2 (4014) ChangeStatus recall cmd from list Bad Thermostats_Target {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} (0)
                2022-04-20 17:00:47.850 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Target to {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} in auto
                2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) Change Status target temperature in Bad to 22.5 (profile 22.5) in auto
                2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) CheckManualMode Bad target 22.5 current manual target 18 state auto
                2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                2022-04-20 17:00:47.915 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto 22.5°C
                

                Die Luke/das Fenster wurde nicht geschlossen. Ich hoffe der Logausschnitt reicht.

                Rene_HMR 1 Reply Last reply
                0
                • Palm_ManiacP Palm_Maniac

                  Heute ist es wieder passiert und ich hab das Log. :)

                  2022-04-20 16:58:18.317 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE {"val":21.9,"ack":true,"ts":1650466698315,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543}
                  2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                  2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                  2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Current to {"val":21.9,"ack":true,"ts":1650466698315,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543} in auto
                  2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) Change Status current temperature in Bad to 21.9
                  2022-04-20 16:58:18.318 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                  2022-04-20 16:58:18.333 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto WindowOpen 12°C
                  2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE {"val":12,"ack":true,"ts":1650466698362,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650459008565}
                  2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 16:58:18.364 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 17:00:00.010 - debug: heatingcontrol.2 (4014) ChangeStatus fired with [{"room":"Bad","target":22.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"17:00","CurrentTimePeriodFull":"Period 3 17:00"}]
                  2022-04-20 17:00:00.010 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus ProfilPoint to {"room":"Bad","target":22.5,"currentTimePeriod":3,"ActiveTimeSlot":3,"CurrentTimePeriodTime":"17:00","CurrentTimePeriodFull":"Period 3 17:00"} in auto
                  2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) ChangeStatus by cron Profilepoint in Bad target 22.5
                  2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) CalculateRoomTemperature for Bad auto
                  2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) Bad auto mode: target 22.5
                  2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) Bad auto mode (incl. reduced): target 22.5
                  2022-04-20 17:00:00.019 - debug: heatingcontrol.2 (4014) SetRoomTemperature started for Bad target 22.5 with offset 0
                  2022-04-20 17:00:00.035 - debug: heatingcontrol.2 (4014) unsubscribe linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 17:00:00.038 - debug: heatingcontrol.2 (4014) Bad set thermostat target linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE to 22.5
                  2022-04-20 17:00:00.101 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                  2022-04-20 17:00:05.038 - debug: heatingcontrol.2 (4014) subscribe linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE {"val":21.9,"ack":true,"ts":1650466847811,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543}
                  2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                  2022-04-20 17:00:47.815 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.ACTUAL_TEMPERATURE
                  2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Current to {"val":21.9,"ack":true,"ts":1650466847811,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650461948543} in auto
                  2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) Change Status current temperature in Bad to 21.9
                  2022-04-20 17:00:47.816 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                  2022-04-20 17:00:47.828 - debug: heatingcontrol.2 (4014) ### handle state change acked linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095}
                  2022-04-20 17:00:47.828 - debug: heatingcontrol.2 (4014) HandleStateChangeDevices linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 17:00:47.829 - debug: heatingcontrol.2 (4014) CheckStateChangeDevice linkeddevices.0.Heizung.OG.Bad.SET_TEMPERATURE
                  2022-04-20 17:00:47.829 - debug: heatingcontrol.2 (4014) ChangeStatus called, while already changing, push to list Bad Thermostats_Target {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} (1)
                  2022-04-20 17:00:47.841 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto 22.5°C
                  2022-04-20 17:00:47.850 - debug: heatingcontrol.2 (4014) ChangeStatus recall cmd from list Bad Thermostats_Target {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} (0)
                  2022-04-20 17:00:47.850 - debug: heatingcontrol.2 (4014) Bad ### ChangeStatus Thermostats_Target to {"val":22.5,"ack":true,"ts":1650466847825,"q":0,"from":"system.adapter.linkeddevices.0","user":"system.user.admin","lc":1650466800095} in auto
                  2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) Change Status target temperature in Bad to 22.5 (profile 22.5) in auto
                  2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) CheckManualMode Bad target 22.5 current manual target 18 state auto
                  2022-04-20 17:00:47.851 - debug: heatingcontrol.2 (4014) UpdateDPs for Bad auto
                  2022-04-20 17:00:47.915 - debug: heatingcontrol.2 (4014) AddStatusToLog skip Bad auto 22.5°C
                  

                  Die Luke/das Fenster wurde nicht geschlossen. Ich hoffe der Logausschnitt reicht.

                  Rene_HMR Offline
                  Rene_HMR Offline
                  Rene_HM
                  Developer
                  wrote on last edited by Rene_HM
                  #2650

                  @palm_maniac ja, ich denke da ist noch ein Fehler im Adapter. So wie es aussieht, wird hier das WindowIsOpen ignoriert, wenn der Profilpunkt wechselt. Muss ich mir mal genauer anschauen...

                  https://github.com/rg-engineering/ioBroker.heatingcontrol/issues/312

                  Rene_HMR 1 Reply Last reply
                  1
                  • Palm_ManiacP Offline
                    Palm_ManiacP Offline
                    Palm_Maniac
                    wrote on last edited by
                    #2651

                    Eine schnelle Frage.

                    Da ein Kurzer im Fensterkontakt die Batterien immer in wenigen Tagen leer gesaugt hat, habe ich heute diesen und das Wandthermostat gegen neue HM-IP Produkte ausgetauscht. Jetzt ist das Problem, dass der Fensterkontakt nicht mehr True und False liefert, sondern Open(1) und Closed(0). Wie muß ich jetzt den FK in den Adapter eintragen, damit dieser weiterhin den Fensterzustand mitbekommt? Momentan steht er auf Offen, egal was der neue FK liefert.

                    P T 2 Replies Last reply
                    0
                    • Palm_ManiacP Palm_Maniac

                      Eine schnelle Frage.

                      Da ein Kurzer im Fensterkontakt die Batterien immer in wenigen Tagen leer gesaugt hat, habe ich heute diesen und das Wandthermostat gegen neue HM-IP Produkte ausgetauscht. Jetzt ist das Problem, dass der Fensterkontakt nicht mehr True und False liefert, sondern Open(1) und Closed(0). Wie muß ich jetzt den FK in den Adapter eintragen, damit dieser weiterhin den Fensterzustand mitbekommt? Momentan steht er auf Offen, egal was der neue FK liefert.

                      P Offline
                      P Offline
                      Pittini
                      Developer
                      wrote on last edited by
                      #2652

                      @palm_maniac Einmal in die Einstellungen geguggt und es hätte sich von selber erklärt. Also geh in die Fensterkontakteinstellungen, stell von Boolean auf Number und gib rechts davon Dein 0 und 1 ein. Fertsch.

                      Palm_ManiacP 1 Reply Last reply
                      0
                      • P Pittini

                        @palm_maniac Einmal in die Einstellungen geguggt und es hätte sich von selber erklärt. Also geh in die Fensterkontakteinstellungen, stell von Boolean auf Number und gib rechts davon Dein 0 und 1 ein. Fertsch.

                        Palm_ManiacP Offline
                        Palm_ManiacP Offline
                        Palm_Maniac
                        wrote on last edited by
                        #2653

                        @pittini Genau das habe ich gemacht, aber da bleibt er Offen und ignoriert die Änderungen. Auch mit der Einstellung String habe ich es versucht.

                        Rene_HMR 1 Reply Last reply
                        0
                        • Palm_ManiacP Palm_Maniac

                          @pittini Genau das habe ich gemacht, aber da bleibt er Offen und ignoriert die Änderungen. Auch mit der Einstellung String habe ich es versucht.

                          Rene_HMR Offline
                          Rene_HMR Offline
                          Rene_HM
                          Developer
                          wrote on last edited by
                          #2654

                          @palm_maniac so geht es auf jeden Fall bei mir:

                          bild1.PNG

                          Palm_ManiacP 1 Reply Last reply
                          1
                          • Rene_HMR Rene_HM

                            @palm_maniac so geht es auf jeden Fall bei mir:

                            bild1.PNG

                            Palm_ManiacP Offline
                            Palm_ManiacP Offline
                            Palm_Maniac
                            wrote on last edited by
                            #2655

                            @rene_hm Bingo. Dann reagiert er also auch auf Boolean, obwohl die Ausgabe keine True/False Geschichte ist. Hätte ich es also so gelassen und nur das Gerät getauscht, hätte es direkt funktioniert. Oh mann.....

                            Nochmal Danke für den Schubser in die richtige Richtung.

                            1 Reply Last reply
                            0
                            • Rene_HMR Rene_HM

                              @palm_maniac ja, ich denke da ist noch ein Fehler im Adapter. So wie es aussieht, wird hier das WindowIsOpen ignoriert, wenn der Profilpunkt wechselt. Muss ich mir mal genauer anschauen...

                              https://github.com/rg-engineering/ioBroker.heatingcontrol/issues/312

                              Rene_HMR Offline
                              Rene_HMR Offline
                              Rene_HM
                              Developer
                              wrote on last edited by
                              #2656

                              @Palm_Maniac

                              ja, ich denke da ist noch ein Fehler im Adapter. So wie es aussieht, wird hier das WindowIsOpen ignoriert, wenn der Profilpunkt wechselt. Muss ich mir mal genauer anschauen...

                              Endlich ist die Simulation nun fehlerfrei:

                              bild1.PNG

                              Kurz vor 16:00 Uhr geht das Fenster auf (gelb), das Thermostat senkt auf 5°C. Um 16:00 Uhr wechselt der Profilpunkt, der wird aber erst genutzt, wenn das Fenster wieder zu geht...

                              Nur zur Info:

                              • blau -> Soll-Temperatur am Thermostat
                              • gelb -> Fenster auf / zu
                              • grün -> simulierte Ist-Temperatur am Thermostat
                              • rot -> Aktor - Status (ein /aus)

                              Ich erstelle eine neue Version (2.8.7), die wird dann morgen im latest-repo sein...

                              1 Reply Last reply
                              1
                              • Palm_ManiacP Palm_Maniac

                                Eine schnelle Frage.

                                Da ein Kurzer im Fensterkontakt die Batterien immer in wenigen Tagen leer gesaugt hat, habe ich heute diesen und das Wandthermostat gegen neue HM-IP Produkte ausgetauscht. Jetzt ist das Problem, dass der Fensterkontakt nicht mehr True und False liefert, sondern Open(1) und Closed(0). Wie muß ich jetzt den FK in den Adapter eintragen, damit dieser weiterhin den Fensterzustand mitbekommt? Momentan steht er auf Offen, egal was der neue FK liefert.

                                T Offline
                                T Offline
                                TurboSasch
                                wrote on last edited by TurboSasch
                                #2657

                                Hallo zusammen,

                                Mein Heatingcontrol lief bisher ansich top. Nur jetzt stimmt irgendwas mit der Zeit nicht. Die Programmierung steht auf 6:00 Uhr, obwohl mittlerweile wesentlich später. Hat jemand eine Idee was zu tun ist?

                                Das steht im Log:

                                heatingcontrol.0
                                2022-04-24 16:13:25.995 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                heatingcontrol.0
                                2022-04-24 16:13:25.023 error copy from vis

                                heatingcontrol.0
                                2022-04-24 16:13:25.022 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                heatingcontrol.0
                                2022-04-24 16:13:17.630 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                heatingcontrol.0
                                2022-04-24 16:07:37.969 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                Sorry @Palm_Maniac ,ich habe irgendwie versehentlich auf dich bei Antwort geklickt :-)

                                E3515031-7ECD-4484-B5CF-D9A5CCA5313F.jpeg

                                Rene_HMR 1 Reply Last reply
                                0
                                • T TurboSasch

                                  Hallo zusammen,

                                  Mein Heatingcontrol lief bisher ansich top. Nur jetzt stimmt irgendwas mit der Zeit nicht. Die Programmierung steht auf 6:00 Uhr, obwohl mittlerweile wesentlich später. Hat jemand eine Idee was zu tun ist?

                                  Das steht im Log:

                                  heatingcontrol.0
                                  2022-04-24 16:13:25.995 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                  heatingcontrol.0
                                  2022-04-24 16:13:25.023 error copy from vis

                                  heatingcontrol.0
                                  2022-04-24 16:13:25.022 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                  heatingcontrol.0
                                  2022-04-24 16:13:17.630 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                  heatingcontrol.0
                                  2022-04-24 16:07:37.969 error exception in SetVis [TypeError: Cannot read properties of null (reading 'val')]

                                  Sorry @Palm_Maniac ,ich habe irgendwie versehentlich auf dich bei Antwort geklickt :-)

                                  E3515031-7ECD-4484-B5CF-D9A5CCA5313F.jpeg

                                  Rene_HMR Offline
                                  Rene_HMR Offline
                                  Rene_HM
                                  Developer
                                  wrote on last edited by
                                  #2658

                                  @turbosasch sagte in Test Adapter HeatingControl v2.8.x:

                                  Nur jetzt stimmt irgendwas mit der Zeit nicht.

                                  Laut deinem log sürzt der Adapter ab. Die Frage ist nun, was hast du gemacht? update? andere Änderungen? welche Version des Adapters? welche Einstellungen?
                                  Evtl. mal auf debug-log umschalten und das log (als Code) hier posten...

                                  T 1 Reply Last reply
                                  0
                                  • Rene_HMR Rene_HM

                                    @turbosasch sagte in Test Adapter HeatingControl v2.8.x:

                                    Nur jetzt stimmt irgendwas mit der Zeit nicht.

                                    Laut deinem log sürzt der Adapter ab. Die Frage ist nun, was hast du gemacht? update? andere Änderungen? welche Version des Adapters? welche Einstellungen?
                                    Evtl. mal auf debug-log umschalten und das log (als Code) hier posten...

                                    T Offline
                                    T Offline
                                    TurboSasch
                                    wrote on last edited by
                                    #2659

                                    @rene_hm Hi Rene,

                                    warum auch immer, ging es nach einem kompletten Neustart wieder. Frag mich nicht, was das war. Aber wenn alles so einfach zu lösen sei, wäre ich glücklich :joy:

                                    1 Reply Last reply
                                    0
                                    • kBrausewK Offline
                                      kBrausewK Offline
                                      kBrausew
                                      wrote on last edited by
                                      #2660

                                      Nach einem kleinen Tippfehler habe ich den ioBroker komplett neu aufsetzen müssen (disaster & recover wäre jetzt mal getestet ;-) ) ...
                                      Hat auch alles funktioniert!

                                      Jetzt fehlen mir ein paar Übersetzungen im vis von Pittini die ich nicht mehr herstellen kann (Beispiel siehe Bild)
                                      Wie bekomme ich die zurück? Adapter & vis neu installieren bzw Upload brachten keine Besserung :-(

                                      4c7d25dd-aa01-48ee-b41c-48cac7106cca-image.png

                                      Pi 4/8GB + SSD + Docker \ DebMatic HM-IP + HM-RF \ ioBroker
                                      HikVision InterCom \ tedee SmartLook
                                      Wiegand - TCP/IP Door Access Controller \ MF-549 Fingerprint/Code/RFID \ FP100 Fingerprint/Code

                                      Fritz 7590 (ohne SmartHome)

                                      P 1 Reply Last reply
                                      0
                                      • kBrausewK kBrausew

                                        Nach einem kleinen Tippfehler habe ich den ioBroker komplett neu aufsetzen müssen (disaster & recover wäre jetzt mal getestet ;-) ) ...
                                        Hat auch alles funktioniert!

                                        Jetzt fehlen mir ein paar Übersetzungen im vis von Pittini die ich nicht mehr herstellen kann (Beispiel siehe Bild)
                                        Wie bekomme ich die zurück? Adapter & vis neu installieren bzw Upload brachten keine Besserung :-(

                                        4c7d25dd-aa01-48ee-b41c-48cac7106cca-image.png

                                        P Offline
                                        P Offline
                                        Pittini
                                        Developer
                                        wrote on last edited by
                                        #2661

                                        @kbrausew Das wär der Fireplacemode. Gugg mal ob Du den Datenpunkt heatingcontrol.0.vis.translations.cardHzngProfilParam.FireplaceModeDecrease hast und was da drin steht.

                                        kBrausewK 1 Reply Last reply
                                        0
                                        • P Pittini

                                          @kbrausew Das wär der Fireplacemode. Gugg mal ob Du den Datenpunkt heatingcontrol.0.vis.translations.cardHzngProfilParam.FireplaceModeDecrease hast und was da drin steht.

                                          kBrausewK Offline
                                          kBrausewK Offline
                                          kBrausew
                                          wrote on last edited by
                                          #2662

                                          @pittini
                                          DP ist nicht da

                                          Pi 4/8GB + SSD + Docker \ DebMatic HM-IP + HM-RF \ ioBroker
                                          HikVision InterCom \ tedee SmartLook
                                          Wiegand - TCP/IP Door Access Controller \ MF-549 Fingerprint/Code/RFID \ FP100 Fingerprint/Code

                                          Fritz 7590 (ohne SmartHome)

                                          P 1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          331

                                          Online

                                          32.4k

                                          Users

                                          81.5k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Home
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe