    Test Adapter pid (pid-Regler) V1.0.x

    This topic has been deleted. Only users with topic management privileges can see it.
    • fu_zhou
      fu_zhou @mcm1957 last edited by fu_zhou

      @mcm57 cool, schaffe ich aber erst heute Abend, auch wenn mich das aktuell mehr juckt, als die Arbeit 😉

      1 Reply Last reply Reply Quote 0
      • mcm1957
        mcm1957 @fu_zhou last edited by

        @fu_zhou said in Test neuer Adapter pid (pid-Regler) V0.0.3-alpha.x:

        @mcm57 Der ganze PID-Algorithmus in der S7 ist eine Kombination aus Funktions-Aufrufen. Ist es hilfreich, wenn ich das alles mal zusammensuche? Ich glaube eher nicht, dazu sind wir hier schon weit genug, würde ich sagen.

        Danke für das Angebot.
        Aber ich glaube auch, dass wir das nur (mehr) machen sollten, wenn es hier Probleme gibt die am Algorithmus liegen könnten.

        McM

        Ben1983 2 Replies Last reply Reply Quote 0
        • Ben1983
          Ben1983 @mcm1957 last edited by Ben1983

          @mcm57 Jetzt ist es aber so, wenn man während hold einen Reset macht, passiert nichts => OK
          setzt man dann hold wieder auf false, beginnt der Regler mit y = 0 neu zu regeln.

          Wäre es keine Option, wenn Hold = true ist den rst state einfach zu bestätigen, aber nichts zu machen?

          mcm1957 1 Reply Last reply Reply Quote 0
          • Ben1983
            Ben1983 @mcm1957 last edited by

            @mcm57 Liegt das am Hold bit, dass die diff nicht passt?
            798b2fe6-49cd-480c-8d74-9a99658b744a-image.png

            mcm1957 1 Reply Last reply Reply Quote 0
            • mcm1957
              mcm1957 @Ben1983 last edited by mcm1957

              @ben1983 said in Test neuer Adapter pid (pid-Regler) V0.0.3-alpha.x:

              @mcm57 Jetzt ist es aber so, wenn man während hold einen Reset macht, passiert nichts => OK
              setzt man dann hold wieder auf false, beginnt der Regler mit y = 0 neu zu regeln.

              Wäre es keine Option, wenn Hold = true ist den rst state einfach zu bestätigen, aber nichts zu machen?

              RST sollte keine außertourliche Neubrechnung auslösen, genausowenig wie das Ändern von act, set, ... RST mcht genau eines - der Integralspeicher wird resetted. Damit wird die Vorgeschuchte vergessen und beim nächsten Rechenzyklus wie bei einem ersten Start berechnet.

              Das bei hold=true keine Reaktion auf y zu sehen ist ist daher gewunschen und m.E. ok.

              Beim Restart (hold=false) wird y auf set-act/kp + offset gesetzt. Beim ersten Zyklus gibt es keinen Integralteil da dt mangels Vorgängerwert null ist. Wenn also am Ausgang y 0 angelegt wird, dann muss err = 0 sein (bzw. err*kp-off).

              Bitte ggef das Loggend er Berechnungen aktivieren:
              02ec3f3a-0bb7-421c-82ca-900e7c0724fa-image.png

              Dann sollten die Berechnungszyklen im Log auftauchen:

              0ea9f8f0-5958-4bde-9d93-40356208f58f-image.png

              RST während eines Holds zu ignorieren wäre m.E. unlogisch.

              1 Reply Last reply Reply Quote 0
              • mcm1957
                mcm1957 @Ben1983 last edited by

                @ben1983 said in Test neuer Adapter pid (pid-Regler) V0.0.3-alpha.x:

                @mcm57 Liegt das am Hold bit, dass die diff nicht passt?
                798b2fe6-49cd-480c-8d74-9a99658b744a-image.png

                Ich gehe mal davon aus, dass act nach dem letzen Update von y (und diff) sich wieder geändert hat. Diff wird NICHT ständig aktualisiert sondern spiegelt jenen diff Wert dar der bei der letzen Berechnung verwendet wurde. Act und Set können sich dann bis zur nächsten Berechnung ändern.

                Änderungen von Act oder Set lösen keine extra Neuberechnung aus.

                Ansonsten bitte wie oben die Berechnungslogs aktivieren und den zugehörigen Output posten.

                MartinP 1 Reply Last reply Reply Quote 0
                • MartinP
                  MartinP @mcm1957 last edited by

                  Instinktiv habe ich gewisse Vorbehalte, einen Regler zu weit weg von der zu regelnden Strecke zu implementieren.

                  Dass bei gutmütigen Regelkreisen auch eventuelle Latenz, die beim Durchschleusen durch den iobroker entstehen kann kein Problem ist, ist sicherlich einleuchtend. Schwieriger wird es, wenn schneller nachgeregelt werden muss.

                  Kennt noch jemand den "Magnet-Schweberegler"?

                  https://www.mikrocontroller.net/attachment/43883/Artikel_zum_Magnet-Schweberegler.pdf

                  Wäre ein so zeitkritischer Regelkreis auch mit einem iobroker Regler-Adapter möglich?

                  mcm1957 1 Reply Last reply Reply Quote 0
                  • mcm1957
                    mcm1957 @MartinP last edited by

                    @martinp
                    Sorry, dass kann ich dir nicht beantworten.

                    Die Entfernung spielt wahrscheinlich keine Rolle - wenn schon die Laufzeit des Signals am Kabel relevant wird, dann bruachen wir über Regler in Software wohl nicht sprechen. Prinzipiell ist aber ioBroker sicher nicht als Echtzeitsystem zu sehen.

                    1 Reply Last reply Reply Quote 0
                    • fu_zhou
                      fu_zhou last edited by fu_zhou

                      Das Verhalten von y bei Änderung von Tn bei laufendem Regler ist jetzt so, wie ich es mir gewünscht habe - danke! Die Kombinationen aus man, hold, rst, die ich jetzt mal so beim Rumspielen probiert habe, sind nachvollziehbar. @Ben1983 was meinst du?
                      Philosophiefrage ist folgendes Szenario: Regler auf hold, dann rst = true => y bleibt stehen, dann hold = false => rst wird jetzt ausgeführt und der Regler fängt bei 0 an bzw. mit der Kp Sprungantwort. Heißt also, solange der Regler auf hold ist, bleibt das y stehen, das zum Zeitpunkt von hold ausgegeben wurde, selbst wenn rst = true gesetzt wird. Die philosophische Frage ist jetzt: so lassen oder bei hold = true führt ein rst = true zu y = 0 (das dann stehen bleibt, weil ja hold = true). Wenn dann hold = false gesetzt wird, ist das Ergebnis das gleiche (Regler startet y zu verändern ab 0), nur sieht man durch y = 0, dass rst betätigt wurde. Der Unterschied ist der Zeitpunkt, wann y = 0 wird. Einmal bei rst = true, das andere mal bei hold = false.

                      Ah sehe gerade, dass das weiter oben schon diskutiert wurde, lasse es trotzdem mal stehen...

                      mcm1957 1 Reply Last reply Reply Quote 0
                      • mcm1957
                        mcm1957 @fu_zhou last edited by

                        @fu_zhou
                        Ich möchte eigentlich konsequent den Y Ausgang nur bei einer Neuberechnung ändern.
                        Warum?
                        hold = true y=bleibt unverändert ist klar nachvollziehbar

                        Wenn man bei hold=true auf RST reagiert, dann kommt als nächstes die Frage warum ein Ändern vion OFFS, MAN, MIN nichts ändert. Und warum sich die Änderung von SET, ACT nichts auswirkt.
                        Das führt in einen Teufelskreis - meiner Ansicht nach.

                        Und bei JEDER Änderung von Eingangsgrößen sofort neu zu berechnen führt bei einer Regelstrecke mit kurzer Verzögkerung (z.B. Y wirkt unverzögert auf act) zu einer Dauerberechnungsloop die den iob potenziell lahmlegt. Also auch nicht so toll.

                        Ich würde das Ganze mal so lassen.
                        Falls es wirklich Bedarf für ein erweitertes (!), soll heißen explizit einstellbares oder auslösbares und kompatibles Verhalten gibt, kann man natürlich über einer Erweiterung reden. Denkbar wäre z.B. ein Calculate Now Triggerstate. Ich bezweifle nur dass der Bedarf hier nennenswert ist.

                        Insofern bitte mal den aktuellen Stand anschaun und allfällige Fehler melden. (Oder auch kurz, dass nix aufgefallen ist).

                        Ich werde - sofern keine Probleme hier auftauchen - nach Update der Doku den Stand mal in den regularäen Beta Test (incl. Lates Request) schicken.

                        fu_zhou 2 Replies Last reply Reply Quote 0
                        • fu_zhou
                          fu_zhou @mcm1957 last edited by

                          @mcm57

                          @mcm57 sagte in Test neuer Adapter pid (pid-Regler) V0.0.3-alpha.x:

                          Ich würde das Ganze mal so lassen.

                          👍

                          Ansonsten läuft das Ding jetzt bei mir ohne Auffälligkeiten und ich nehme den Adapter mit dem aktuellen Stand mal produktiv.

                          1 Reply Last reply Reply Quote 0
                          • fu_zhou
                            fu_zhou @mcm1957 last edited by

                            @mcm57 jetzt fällt mir im Produktivbetrieb doch was auf: wenn max erreicht ist (lim = 1), in meinem Fall unten 11, wird i_sumerr schlagartig auf den 10-fachen Wert vom vorherigen Wert gesetzt und trotz großer Regelabweichung hält der Regler y bei max, obwohl y schnell kleiner werden müsste. Bei 10.9 war i_sumerr z.B. 110, dann springt i_sumerr bei Erreichen vom Limit (11) auf 1100. Und von dort kommt der Regler dann nicht mehr weg, weil vom hohen i_sumerr verhältnismäßig kleine Werte abgezogen werden bei einer Regelabweichung in die andere Richtung.

                            564598eb-197e-41e6-b5c8-55df93993097-image.png

                            mcm1957 1 Reply Last reply Reply Quote 0
                            • mcm1957
                              mcm1957 @fu_zhou last edited by mcm1957

                              @fu_zhou
                              Bitte aktiviere "log calculation" und poste mal die logs

                              (https://forum.iobroker.net/topic/64250/test-neuer-adapter-pid-pid-regler-v0-0-3-alpha-x/191)

                              Ich schau derweil mal in den Code

                              Und fährst du "normal" oder "inverted" ?

                              fu_zhou 3 Replies Last reply Reply Quote 0
                              • fu_zhou
                                fu_zhou @mcm1957 last edited by fu_zhou

                                @mcm57 ich fahre normal, nicht invertiert.
                                hier das log beim erreichen von max:

                                pid.0
                                2023-04-14 18:12:24.112	info	[C-TestRegler2] update() - {"ts":1681488744112,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":11,"lim":true,"dt":501,"differr":null,"sumerr":1085,"supr":false}
                                
                                pid.0
                                2023-04-14 18:12:23.612	info	[C-TestRegler2] update() - {"ts":1681488743611,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":11,"lim":true,"dt":500,"differr":null,"sumerr":1085,"supr":false}
                                
                                pid.0
                                2023-04-14 18:12:23.111	info	[C-TestRegler2] update() - {"ts":1681488743111,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":10.999374999999967,"lim":false,"dt":501,"differr":null,"sumerr":108.49374999999966,"supr":false}
                                
                                pid.0
                                2023-04-14 18:12:22.611	info	[C-TestRegler2] update() - {"ts":1681488742610,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":10.991859999999969,"lim":false,"dt":500,"differr":null,"sumerr":108.41859999999967,"supr":false}
                                

                                und hier das log , wenn ich von act -2 auf act +3 springe, dann müsste y von max weg wieder kleiner werden, passiert aber nicht:

                                pid.0
                                2023-04-14 18:15:03.311	info	[C-TestRegler2] update() - {"ts":1681488903311,"act":3,"set":-0.5,"diff":-3.5,"off":0,"err":-3.5,"y":11,"lim":true,"dt":501,"differr":null,"sumerr":1135,"supr":false}
                                
                                pid.0
                                2023-04-14 18:15:02.810	info	[C-TestRegler2] update() - {"ts":1681488902810,"act":3,"set":-0.5,"diff":-3.5,"off":0,"err":-3.5,"y":11,"lim":true,"dt":501,"differr":null,"sumerr":1135,"supr":false}
                                
                                pid.0
                                2023-04-14 18:15:02.309	info	[C-TestRegler2] update() - {"ts":1681488902309,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":11,"lim":true,"dt":501,"differr":null,"sumerr":1085,"supr":false}
                                
                                pid.0
                                2023-04-14 18:15:01.808	info	[C-TestRegler2] update() - {"ts":1681488901808,"act":-2,"set":-0.5,"diff":1.5,"off":0,"err":1.5,"y":11,"lim":true,"dt":500,"differr":null,"sumerr":1085,"supr":false}
                                

                                und 2 Minuten später sieht es noch genauso aus:

                                pid.0
                                2023-04-14 18:17:57.000	info	[C-TestRegler2] update() - {"ts":1681489077000,"act":3,"set":-0.5,"diff":-3.5,"off":0,"err":-3.5,"y":11,"lim":true,"dt":500,"differr":null,"sumerr":1135,"supr":false}
                                
                                pid.0
                                2023-04-14 18:17:56.500	info	[C-TestRegler2] update() - {"ts":1681489076500,"act":3,"set":-0.5,"diff":-3.5,"off":0,"err":-3.5,"y":11,"lim":true,"dt":501,"differr":null,"sumerr":1135,"supr":false}
                                
                                pid.0
                                2023-04-14 18:17:55.999	info	[C-TestRegler2] update() - {"ts":1681489075999,"act":3,"set":-0.5,"diff":-3.5,"off":0,"err":-3.5,"y":11,"lim":true,"dt":500,"differr":null,"sumerr":1135,"supr":false}
                                
                                1 Reply Last reply Reply Quote 0
                                • fu_zhou
                                  fu_zhou @mcm1957 last edited by fu_zhou

                                  @mcm57 noch was: wenn min erreicht wird und die Regelabweichung bleibt, wird bei max weitergemacht und von da läuft der Regler wieder Richtung min. (Tn > 1)

                                  pid.0
                                  2023-04-14 18:46:22.892	info	[C-TestRegler2] update() - {"ts":1681490782892,"act":0.5,"set":-0.5,"diff":-1,"off":0,"err":-1,"y":10.889980000000001,"lim":false,"dt":501,"differr":null,"sumerr":109.8998,"supr":false}
                                  
                                  pid.0
                                  2023-04-14 18:46:22.391	info	[C-TestRegler2] update() - {"ts":1681490782391,"act":0.5,"set":-0.5,"diff":-1,"off":0,"err":-1,"y":10.894990000000002,"lim":false,"dt":501,"differr":null,"sumerr":109.9499,"supr":false}
                                  
                                  pid.0
                                  2023-04-14 18:46:21.890	info	[C-TestRegler2] update() - {"ts":1681490781890,"act":0.5,"set":-0.5,"diff":-1,"off":0,"err":-1,"y":1,"lim":true,"dt":501,"differr":null,"sumerr":110,"supr":false}
                                  
                                  pid.0
                                  2023-04-14 18:46:21.389	info	[C-TestRegler2] update() - {"ts":1681490781389,"act":0.5,"set":-0.5,"diff":-1,"off":0,"err":-1,"y":1.0047899999999956,"lim":false,"dt":501,"differr":null,"sumerr":11.047899999999956,"supr":false}
                                  
                                  pid.0
                                  2023-04-14 18:46:20.888	info	[C-TestRegler2] update() - {"ts":1681490780888,"act":0.5,"set":-0.5,"diff":-1,"off":0,"err":-1,"y":1.0097999999999956,"lim":false,"dt":501,"differr":null,"sumerr":11.097999999999956,"supr":false}
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • fu_zhou
                                    fu_zhou @mcm1957 last edited by

                                    @mcm57 sagte in Test neuer Adapter pid (pid-Regler) V0.0.3-alpha.x:

                                    Ich dachte eigentlich, dass ich nur mal schnell den node-pid code in einen Adapter integriere.

                                    🤣🤣🤣🤣🙌

                                    1 Reply Last reply Reply Quote 0
                                    • fu_zhou
                                      fu_zhou @mcm1957 last edited by fu_zhou

                                      @mcm57 es scheint so zu sein, dass bei Tn >1 der Regler sich bei max festhängt und bei Tn < 1 sich der Regler bei min festhängt. Nur bei Tn = 1 funktioniert's. Wenn der Regler mal hängt, bekommt man ihn wieder in Gang, indem man Tn = 1 setzt.

                                      Und bei Tn < 1 läuft der Regler Richtung max, bleibt nicht stehen und fängt wieder bei min an (bei Regelabweichung mit entsprechendem Vorzeichen), habe als max diesmal 3, nicht 11 drin:

                                      pid.0
                                      2023-04-14 19:36:19.924	info	[C-TestRegler2] update() - {"ts":1681493779924,"act":-1,"set":-0.5,"diff":0.5,"off":0,"err":0.5,"y":1.6251,"lim":false,"dt":501,"differr":null,"sumerr":15.751,"supr":false}
                                      
                                      pid.0
                                      2023-04-14 19:36:19.423	info	[C-TestRegler2] update() - {"ts":1681493779423,"act":-1,"set":-0.5,"diff":0.5,"off":0,"err":0.5,"y":1.5750000000000002,"lim":false,"dt":500,"differr":null,"sumerr":15.25,"supr":false}
                                      
                                      pid.0
                                      2023-04-14 19:36:18.923	info	[C-TestRegler2] update() - {"ts":1681493778923,"act":-1,"set":-0.5,"diff":0.5,"off":0,"err":0.5,"y":3,"lim":true,"dt":501,"differr":null,"sumerr":14.75,"supr":false}
                                      
                                      pid.0
                                      2023-04-14 19:36:18.422	info	[C-TestRegler2] update() - {"ts":1681493778422,"act":-1,"set":-0.5,"diff":0.5,"off":0,"err":0.5,"y":2.977000000000001,"lim":false,"dt":501,"differr":null,"sumerr":29.270000000000014,"supr":false}
                                      
                                      pid.0
                                      2023-04-14 19:36:17.921	info	[C-TestRegler2] update() - {"ts":1681493777921,"act":-1,"set":-0.5,"diff":0.5,"off":0,"err":0.5,"y":2.926900000000001,"lim":false,"dt":501,"differr":null,"sumerr":28.769000000000013,"supr":false}
                                      
                                      mcm1957 1 Reply Last reply Reply Quote 0
                                      • mcm1957
                                        mcm1957 @fu_zhou last edited by mcm1957

                                        @fu_zhou
                                        Ja ich glaub ich hab den Fehler schon. Die Umstellung dass sumErr schon beim integrieren tn berücksichtigt dürfte nicht in die Limitierung eingeflossen sein,

                                        Kannst du mir bitte noch deine Parametereinstelliung (kp, tn, tv, max, min, gff off) schicken? Ich will das mal in Excel nachrechnen was ich codiere 🙂

                                        sumErr wird nämlich beim begrenzen auch limitiert. Nur muss das zurückgerechnet werden dass sumErr xxx ganu y == lime rgibt. Und dürfte der Wurm drinnen sein.

                                        fu_zhou 1 Reply Last reply Reply Quote 0
                                        • fu_zhou
                                          fu_zhou @mcm1957 last edited by

                                          @mcm57
                                          Kp = 0,1
                                          Tn = > 1 oder < 1 (10 im Produktivbetrieb, wird sich aber noch ändern, wenn der Regler min/max richtig verarbeitet 😉 ) oder = 1 um den Regler wieder in Gang zu setzen
                                          Tv = 0
                                          max = 3 (11 im Produktivbetrieb)
                                          min = 1
                                          off = 0
                                          sup = 0,2

                                          mcm1957 1 Reply Last reply Reply Quote 0
                                          • mcm1957
                                            mcm1957 @fu_zhou last edited by

                                            @fu_zhou
                                            Bitte teste mal die neueste Release (0.0.6).

                                            Lt. Excel sollt es nun passen. Der Sprung um 10 den du beobachtet hast passt auch zu tn=10

                                            fu_zhou 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            900
                                            Online

                                            31.6k
                                            Users

                                            79.6k
                                            Topics

                                            1.3m
                                            Posts

                                            15
                                            303
                                            35608
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes