  2. English
  3. ioBroker general
  4. Zigbee adapter stopped running
    6.0k
Geplant Angeheftet Gesperrt Verschoben ioBroker general
zigbee
43 Beiträge 5 Kommentatoren 9.5k Aufrufe 5 Beobachtet
  • AsgothianA Asgothian
    @ap2017 sagte in Zigbee adapter stopped running:
    Plugged Zigbee adapter to a different USB port on controller, now can see all three USB ports:
    ap@AP-Tiny:~$ ls -l /dev/serial/by-id
    total 0
    lrwxrwxrwx 1 root root 13 Jul 14 13:34 usb-0658_0200-if00 -> ../../ttyACM0
    lrwxrwxrwx 1 root root 13 Jul 14 13:33 usb-1a86_USB2.0-Serial-if00-port0 -> ../../ttyUSB0
    lrwxrwxrwx 1 root root 13 Jul 14 13:37 usb-Texas_Instruments_TI_CC2531_USB_CDC___0X00124B0018E2EC73-if00 -> ../../ttyACM1
    Zigbee adapter still does not work after reboot:
    2022-07-14 13:46:08.303 - info: zigbee.0 (2610) Starting Zigbee npm ...
    2022-07-14 13:46:08.524 - info: zigbee.0 (2610) Installed Version: iobroker.zigbee@1.7.5
    2022-07-14 13:46:14.661 - info: mysensors.0 (2275) disconnected
    2022-07-14 13:46:21.257 - info: mysensors.0 (2275) Connected
    2022-07-14 13:46:21.258 - info: mysensors.0 (2275) STARTED
    2022-07-14 13:46:28.818 - error: zigbee.0 (2610) Starting zigbee-herdsman problem : "Failed to connect to the adapter (Error: SRSP - SYS - ping after 6000ms)"
    2022-07-14 13:46:28.820 - error: zigbee.0 (2610) Failed to start Zigbee
    2022-07-14 13:46:28.820 - error: zigbee.0 (2610) Error herdsman start
    2022-07-14 13:46:38.821 - info: zigbee.0 (2610) Try to reconnect. 1 attempts left
    2022-07-14 13:46:38.822 - info: zigbee.0 (2610) Starting Zigbee npm ...
    2022-07-14 13:46:38.833 - info: zigbee.0 (2610) Installed Version: iobroker.zigbee@1.7.5
    2022-07-14 13:46:38.920 - error: zigbee.0 (2610) Starting zigbee-herdsman problem : "Error while opening serialport 'Error: Error Resource temporarily unavailable Cannot lock port'"
    2022-07-14 13:46:38.921 - error: zigbee.0 (2610) Failed to start Zigbee
    2022-07-14 13:46:38.921 - error: zigbee.0 (2610) Error herdsman start
    You have an issue with the stick. The port is opened but the firmware does not respond (as per this message)
    The message about not being able to open the port is from a later start attempt which fails as the previous attempt did not manage to close the port after the firmware did not respond.
    You need to check:
    • which USB port the stick is plugged into (USB2 or USB3)
    • do you have any disks or SSD's plugged into a USB3 port ?
    • does the Stick have the correct firmware flashed
    A.
    ap2017
    @asgothian
    Not sure how to check which USB port is which, don't know Linux enough.
    Nothing is connected to USB ports except MySensors gateway, Zwave adapter and Zigbee adapter.
    There is certainly a chance that Zigbee adapter failed, but it was working fine for many months, this is not new setup. I think that it uses firmware version 20190608.
      @ap2017
      It the other way round...
      Setting ACM1 in the adapter means nothing in the 'real world' of the Operating System.
      The linux kernel and/or systemd decides where your devices end up in /dev/tty* and sets the correct link in /dev/serial/by-id pointing to the device.
      So you need to find out which of your two devices in /dev/serial/by-id is the ZigBee Adapter. Try and Error. I think it is the second entry.
      BTW: Set da different Extended PAN-Id. The one you use is too simple and only a place holder for an individual Id .
      ap2017
      schrieb am zuletzt editiert von ap2017
      Thank you found where is PAN-id, changing it caused many new error messages even after reboot, so I restored the default one.
        This 'problem' is exactly the reason why you should never set /dev/ttyDEVICE but always the link that you find in /dev/serial/by-id
        /dev/ttyDEVICE is generated during system start and may change at anytime, the link in /dev/serial/by-id will always point to the correct hardware.
        ap2017
        I changed all serial ports definitions with /dev/serial/by-id settings. MySensors and Zwave (USB) adapters work, but Zwave still does not
        2022-07-14 20:45:46.201 - error: zigbee.0 (3605) Starting zigbee-herdsman problem : "Failed to connect to the adapter (Error: SRSP - SYS - ping after 6000ms)"
        2022-07-14 20:45:46.202 - error: zigbee.0 (3605) Failed to start Zigbee
        2022-07-14 20:45:46.202 - error: zigbee.0 (3605) Error herdsman start
        total 0
        lrwxrwxrwx 1 root root 13 Jul 14 18:07 usb-0658_0200-if00 -> ../../ttyACM0
        lrwxrwxrwx 1 root root 13 Jul 14 20:38 usb-1a86_USB2.0-Serial-if00-port0 -> ../../ttyUSB0
        lrwxrwxrwx 1 root root 13 Jul 14 20:43 usb-Texas_Instruments_TI_CC2531_USB_CDC___0X00124B0018E2EC73-if00 -> ../..                 /ttyACM1
          ap2017
          Nobody responded if it is important that serialport version of Zigbee is older than serialport of other adapters (assuming that 9.2.8 is a version number)
          ap@AP-Tiny:/opt/iobroker$ npm list serialport
          [sudo] password for ap:
          iobroker.inst@2.0.3 /opt/iobroker
          ├─┬ iobroker.discovery@3.0.5
          │ └── serialport@10.4.0
          ├─┬ iobroker.mysensors@3.0.0
          │ └── serialport@10.4.0 deduped
          ├─┬ iobroker.zigbee@1.7.5
          │ └─┬ zigbee-herdsman@0.14.34
          │   └── serialport@9.2.8
          └─┬ iobroker.zwave2@2.6.0
            └─┬ zwave-js@9.6.0
              ├─┬ @zwave-js/serial@9.6.0
          • A ap2017
            @asgothian
            AsgothianA Offline
            AsgothianA Offline
            Asgothian
            @asgothian
            Please test:
            remove the MySensors gateway and the Zwave adapter and see if the zigbee adapter starts. Please be on the lookout for the first log message containing Starting zigbee-herdsman problem :, ignoring all messages after info: zigbee.0 (2610) Try to reconnect. as they will point you to a wrong direction.
            If the zigbee adapter starts in this configuration there might be some interference between either the mysensors gateway and the zigbee stick or the zwave stick and the zigbee stick. If it does not start in this configuration, the firmware on the stick has become corrupted and should be refreshed.
            The Zigbee-Herdsman Library which is used by the zigbee adapter requires a specific serialport library version, which is why it is completely normal to have a separate installation of the serial port library.
            A.
              @asgothian
              Please test:
              A.
              ap2017
              @asgothian
              I disabled MySensors and Zwave then restarted controller. Here is what I am getting:
              2022-07-15 15:49:58.005 - error: zigbee.0 (20495) Starting zigbee-herdsman problem : "Error while opening serialport 'Error: Error Resource temporarily unavailable Cannot lock port'"
              2022-07-15 15:49:58.006 - error: zigbee.0 (20495) Failed to start Zigbee
              2022-07-15 15:49:58.006 - error: zigbee.0 (20495) Error herdsman start
              • A ap2017
                @asgothian
                AsgothianA Offline
                AsgothianA Offline
                Asgothian
                @ap2017 Please reread my previous post and check for the correct message. I am 99% certain that this message is the one i explicitly told you was a false flag.
                A.
                  A.
                  ap2017
                  @asgothian
                  2022-07-15 18:26:04.695 - info: zigbee.0 (25872) Starting Zigbee npm ...
                  2022-07-15 18:26:04.921 - info: zigbee.0 (25872) Installed Version: iobroker.zigbee@1.7.5
                  2022-07-15 18:26:09.726 - info: mysensors.0 (21245) STARTED
                  2022-07-15 18:26:24.873 - error: zigbee.0 (25872) Starting zigbee-herdsman problem : "Failed to connect to the adapter (Error: SRSP - SYS - ping after 6000ms)"
                  2022-07-15 18:26:24.875 - error: zigbee.0 (25872) Failed to start Zigbee
                  2022-07-15 18:26:24.875 - error: zigbee.0 (25872) Error herdsman start
                  2022-07-15 18:26:34.876 - info: zigbee.0 (25872) Try to reconnect. 1 attempts left
                  2022-07-15 18:26:34.877 - info: zigbee.0 (25872) Starting Zigbee npm ...
                  2022-07-15 18:26:34.889 - info: zigbee.0 (25872) Installed Version: iobroker.zigbee@1.7.5
                  2022-07-15 18:26:34.989 - error: zigbee.0 (25872) Starting zigbee-herdsman problem : "Error while opening serialport 'Error: Error Resource temporarily unavailable Cannot lock port'"
                  2022-07-15 18:26:34.990 - error: zigbee.0 (25872) Failed to start Zigbee
                  2022-07-15 18:26:34.990 - error: zigbee.0 (25872) Error herdsman start
                  • A ap2017
                    @asgothian
                    @ap2017
                    I quote:
                    So try to reflash the Firmware.
                      @ap2017
                      I quote:
                      ap2017
                      @thomas-braun After reflashing the firmware Zigbeee adapter started to behave differently. It works for some seconds then shuts down with error code. After restarting the adapter is does it again - works for a short time then shuts down with error code. I received another stick, reflashed it as well, but system behaves same way.
                      2022-07-17 21:10:10.373 - info: zigbee.0 (2538) Zigbee started
                      2022-07-17 21:10:12.539 - info: admin.0 (1256) ==> Connected system.user.admin from ::ffff:192.168.1.244
                      2022-07-17 21:10:21.356 - warn: zigbee.0 (2538) DeviceAvailability:Failed to ping 0x90fd9ffffe2bad6b TRADFRI bulb E26 W opal 1000lm
                      2022-07-17 21:10:40.020 - warn: zigbee.0 (2538) Device '0x90fd9ffffe2baf88' announced itself
                      2022-07-17 21:10:40.023 - error: zigbee.0 (2538) Unhandled promise rejection. This error originated either by throwing inside of an async function without a catch block, or by rejecting a promise which was not handled with .catch().
                      2022-07-17 21:10:40.024 - error: zigbee.0 (2538) unhandled promise rejection: Cannot read properties of undefined (reading 'color_options')
                      2022-07-17 21:10:40.024 - error: zigbee.0 (2538) TypeError: Cannot read properties of undefined (reading 'color_options')
                      at Object.bulbOnEvent [as onEvent] (/opt/iobroker/node_modules/zigbee-herdsman-converters/devices/ikea.js:39:19)
                      at DeviceEvent.callOnEvent (/opt/iobroker/node_modules/iobroker.zigbee/lib/zbDeviceEvent.js:44:26)
                      at DeviceEvent.onZigbeeEvent (/opt/iobroker/node_modules/iobroker.zigbee/lib/zbDeviceEvent.js:26:18)
                      at ZigbeeController.callExtensionMethod (/opt/iobroker/node_modules/iobroker.zigbee/lib/zigbeecontroller.js:236:54)
                      at ZigbeeController.handleDeviceAnnounce (/opt/iobroker/node_modules/iobroker.zigbee/lib/zigbeecontroller.js:560:18)
                      2022-07-17 21:10:40.025 - error: zigbee.0 (2538) Cannot read properties of undefined (reading 'color_options')
                      2022-07-17 21:10:40.028 - info: zigbee.0 (2538) cleaned everything up...
                      2022-07-17 21:10:40.056 - info: zigbee.0 (2538) Zigbee: disabling joining new devices.
                      2022-07-17 21:10:40.528 - info: zigbee.0 (2538) terminating
                      2022-07-17 21:10:40.529 - warn: zigbee.0 (2538) Terminated (UNCAUGHT_EXCEPTION): Without reason
                      2022-07-17 21:10:41.035 - warn: zigbee.0 (2538) get state error: Connection is closed.
                      2022-07-17 21:10:41.101 - error: host.AP-Tiny instance system.adapter.zigbee.0 terminated with code 6 (UNCAUGHT_EXCEPTION)
                      2022-07-17 21:10:41.102 - info: host.AP-Tiny Restart adapter system.adapter.zigbee.0 because enabled
                      2022-07-17 21:10:41.102 - warn: host.AP-Tiny Do not restart adapter system.adapter.zigbee.0 because restart loop detected
                      2022-07-17 21:10:43.459 - info: mysensors.0 (2199) STARTED
                      2022-07-17 21:10:43.460 - info: mysensors.0 (2199) STARTED
                      2022-07-17 21:10:48.629 - info: admin.0 (1256) <== Disconnect system.user.admin from ::ffff:192.168.1.244
                      • A ap2017
                        AsgothianA Offline
                        AsgothianA Offline
                        Asgothian
                        @ap2017 Please see here for cause and temporary fix:
                        https://forum.iobroker.net/topic/55346/zigbee-stürzt-beim-schalten-von-birnen-über-shalter-ab/7?_=1658123566370
                        A.
                          A.
                          ap2017
                          @asgothian
                          Thanks if I can figure out how to edit file in terminal mode...
                          • A ap2017
                            @asgothian
                            AsgothianA Offline
                            AsgothianA Offline
                            Asgothian
                            @ap2017 you should be able to use the "nano" command. You may have to use sudo to be able to write the file, or have to modify the access rights via sudo chmod a+w
                            A.
                            A 2 Antworten Letzte Antwort
                              A.
                              ap2017
                              @asgothian I did not have a chance to manually change the code, but noticed new version of adapter just released with fixed IKEA interface. Unfortunately it does not work for me, see log. It starts fine adapter is operational but it is not able to ping devices
                              2022-07-24 18:48:09.741 - info: host.AP-Tiny stopInstance system.adapter.zigbee.0 (force=false, process=true)
                              2022-07-24 18:48:09.745 - info: zigbee.0 (2399) Got terminate signal TERMINATE_YOURSELF
                              2022-07-24 18:48:09.746 - info: zigbee.0 (2399) cleaned everything up...
                              2022-07-24 18:48:09.755 - info: zigbee.0 (2399) Zigbee: disabling joining new devices.
                              2022-07-24 18:48:09.792 - info: host.AP-Tiny stopInstance system.adapter.zigbee.0 send kill signal
                              2022-07-24 18:48:10.237 - info: zigbee.0 (2399) terminating
                              2022-07-24 18:48:10.238 - info: zigbee.0 (2399) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                              2022-07-24 18:48:10.795 - info: host.AP-Tiny instance system.adapter.zigbee.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                              2022-07-24 18:48:12.834 - info: host.AP-Tiny instance system.adapter.zigbee.0 started with pid 2431
                              2022-07-24 18:48:14.205 - info: zigbee.0 (2431) Plugin sentry Sentry Plugin disabled for this process because sending of statistic data is disabled for the system
                              2022-07-24 18:48:14.356 - info: zigbee.0 (2431) starting. Version 1.7.6 in /opt/iobroker/node_modules/iobroker.zigbee, node: v16.16.0, js-controller: 4.0.23
                              2022-07-24 18:48:14.401 - info: zigbee.0 (2431) delete old Backup files. keep only last 10
                              2022-07-24 18:48:14.402 - info: zigbee.0 (2431) Starting Zigbee npm ...
                              2022-07-24 18:48:14.633 - info: zigbee.0 (2431) Installed Version: iobroker.zigbee@1.7.6
                              2022-07-24 18:48:15.005 - info: zigbee.0 (2431) Coordinator firmware version: {"type":"zStack12","meta":{"transportrev":2,"product":0,"majorrel":2,"minorrel":6,"maintrel":3,"revision":20190608}}
                              2022-07-24 18:48:15.009 - info: zigbee.0 (2431) Disable LED
                              2022-07-24 18:48:15.010 - info: zigbee.0 (2431) Unable to disable LED, unsupported function.
                              2022-07-24 18:48:15.011 - info: zigbee.0 (2431) --> transmitPower : normal
                              2022-07-24 18:48:15.018 - info: zigbee.0 (2431) Currently 15 devices are joined:
                              2022-07-24 18:48:15.037 - info: zigbee.0 (2431) 0x90fd9ffffe2bad6b (addr 43852): LED1622G12 - IKEA TRADFRI LED bulb E26 1000 lumen, dimmable, opal white (Router)
                              2022-07-24 18:48:15.041 - info: zigbee.0 (2431) 0x00158d00044678ff (addr 48528): WXKG12LM - Xiaomi Aqara wireless switch (with gyroscope) (EndDevice)
                              2022-07-24 18:48:15.041 - info: zigbee.0 (2431) 0x00124b001f90ed15 (addr 54998): SA-003-Zigbee - eWeLink Zigbee smart plug (Router)
                              2022-07-24 18:48:15.042 - info: zigbee.0 (2431) 0xd0cf5efffedaa37c (addr 43246): LED1622G12 - IKEA TRADFRI LED bulb E26 1000 lumen, dimmable, opal white (Router)
                              2022-07-24 18:48:15.042 - info: zigbee.0 (2431) 0x000b57fffebcfc39 (addr 38662): LED1622G12 - IKEA TRADFRI LED bulb E26 1000 lumen, dimmable, opal white (Router)
                              2022-07-24 18:48:15.043 - info: zigbee.0 (2431) 0x00124b0022658a2b (addr 33323): SNZB-01 - SONOFF Wireless button (EndDevice)
                              2022-07-24 18:48:15.043 - info: zigbee.0 (2431) 0xd0cf5efffe7d475c (addr 30129): LED1622G12 - IKEA TRADFRI LED bulb E26 1000 lumen, dimmable, opal white (Router)
                              2022-07-24 18:48:15.044 - info: zigbee.0 (2431) 0x00158d00045a362e (addr 24701): SJCGQ11LM - Xiaomi Aqara water leak sensor (EndDevice)
                              2022-07-24 18:48:15.045 - info: zigbee.0 (2431) 0xbc33acfffeff263f (addr 65507): SM-AZ713 - UseeLink Smart water/gas valve (Router)
                              2022-07-24 18:48:15.046 - info: zigbee.0 (2431) 0x90fd9ffffe2baf88 (addr 53737): LED1622G12 - IKEA TRADFRI LED bulb E26 1000 lumen, dimmable, opal white (Router)
                              2022-07-24 18:48:15.046 - info: zigbee.0 (2431) 0x000b57fffe8b9e9c (addr 56023): LED1650R5 - IKEA TRADFRI LED bulb GU10 400 lumen, dimmable (Router)
                              2022-07-24 18:48:15.047 - info: zigbee.0 (2431) 0x00124b0022419f47 (addr 23822): SA-003-Zigbee - eWeLink Zigbee smart plug (Router)
                              2022-07-24 18:48:15.047 - info: zigbee.0 (2431) 0xccccccfffe939035 (addr 18190): E1525/E1745 - IKEA TRADFRI motion sensor (EndDevice)
                              2022-07-24 18:48:15.048 - info: zigbee.0 (2431) 0x04cf8cdf3c79009e (addr 52418): GZCGQ01LM - Xiaomi MiJia light intensity sensor (EndDevice)
                              2022-07-24 18:48:15.048 - info: zigbee.0 (2431) 0x00158d0006ea578f (addr 63873): SJCGQ11LM - Xiaomi Aqara water leak sensor (EndDevice)
                              2022-07-24 18:48:15.049 - info: zigbee.0 (2431) Zigbee started
                              2022-07-24 18:48:38.963 - info: mysensors.0 (2339) STARTED
                              2022-07-24 18:49:01.024 - info: admin.0 (1527) ==> Connected system.user.admin from ::ffff:192.168.1.244
                              2022-07-24 18:49:19.328 - info: admin.0 (1527) <== Disconnect system.user.admin from ::ffff:192.168.1.244
                              2022-07-24 18:49:23.126 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0x00124b001f90ed15 SA-003-Zigbee
                              2022-07-24 18:49:23.750 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0xd0cf5efffedaa37c TRADFRI bulb E26 W opal 1000lm
                              2022-07-24 18:49:24.226 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0x000b57fffebcfc39 TRADFRI bulb E26 W opal 1000lm
                              2022-07-24 18:49:33.874 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0xd0cf5efffe7d475c TRADFRI bulb E26 W opal 1000lm
                              2022-07-24 18:49:34.415 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0x000b57fffe8b9e9c TRADFRI bulb GU10 W 400lm
                              2022-07-24 18:49:34.858 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0x90fd9ffffe2baf88 TRADFRI bulb E26 W opal 1000lm
                              2022-07-24 18:49:35.014 - warn: zigbee.0 (2431) DeviceAvailability:Failed to ping 0x00124b0022419f47 SA-003-Zigbee
                                A.
                                ap2017
                                @asgothian Do you still recommend to manually edit the file or the latest adapter update incorporate all the changes?
                                • A ap2017
                                  AsgothianA Offline
                                  AsgothianA Offline
                                  Asgothian
                                  @ap2017 the latest version should contain the edit.
                                  A.
                                    A.
                                    ap2017
                                    @asgothian It does not work for me see my message from July 24
                                    • A ap2017
                                      AsgothianA Offline
                                      AsgothianA Offline
                                      Asgothian
                                      @ap2017 Please check if you have duplicate zigbee-herdsman-converters libraries installed, or if their permissions do not allow overwriting.
                                      if need be, follow this method:
                                      • stop the zigbee adapter
                                      • remove the zigbee-herdsman-converters library
                                      • remove the zigbee-herdsman library
                                      • reinstall the zigbee adapter.
                                      A.
                                        A.
                                        ap2017
                                        @asgothian Thanks, but it I don't know how to:
                                        • reinstall the zigbee adapter. How to reinstall? Delete and then install new adapter? Will all devices configuration stay?
                                        • A ap2017
                                          ap2017
                                          @ap2017 Please help