Modbus EasyCharge Einstellungen
-
modbus.0 2025-02-09 19:55:11.275 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:10.222 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:09.167 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:08.114 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:07.062 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:06.009 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:04.957 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:03.904 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:02.852 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:01.799 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:55:00.747 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:59.695 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:58.642 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:57.586 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:56.532 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:55.479 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:54.422 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 19:54:54.419 info Connected to slave modbus.0 2025-02-09 19:54:54.403 debug connect to serial /dev/ttyUSB0 with 9600 modbus.0 2025-02-09 19:54:53.834 debug Add holdingRegisters.40035_Temp: {"_id":"holdingRegisters.40035_Temp","type":"state","common":{"name":"Temp","role":"value","type":"number","read":false,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":40035,"deviceId":2,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":""}} modbus.0 2025-02-09 19:54:53.833 debug Initialize Objects for holdingRegs: [{"_address":"40035","name":"Temp","description":"Temp","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":"","wp":"","cw":"","isScale":"","address":40035,"deviceId":2,"id":"holdingRegisters.40035_Temp"}] modbus.0 2025-02-09 19:54:53.831 debug Initialize Objects for inputRegs: [] modbus.0 2025-02-09 19:54:53.830 debug Initialize Objects for coils: [] modbus.0 2025-02-09 19:54:53.827 debug Initialize Objects for disInputs: [] modbus.0 2025-02-09 19:54:53.504 info starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.17.1, js-controller: 7.0.6 modbus.0 2025-02-09 19:54:52.592 debug Plugin sentry Initialize Plugin (enabled=true) modbus.0 2025-02-09 19:54:52.524 debug States connected to redis: 127.0.0.1:9000 modbus.0 2025-02-09 19:54:52.499 debug States create User PubSub Client modbus.0 2025-02-09 19:54:52.495 debug States create System PubSub Client modbus.0 2025-02-09 19:54:52.478 debug Redis States: Use Redis connection: 127.0.0.1:9000 modbus.0 2025-02-09 19:54:52.435 debug Objects connected to redis: 127.0.0.1:9001 modbus.0 2025-02-09 19:54:52.417 debug Objects client initialize lua scripts modbus.0 2025-02-09 19:54:52.372 debug Objects create User PubSub Client modbus.0 2025-02-09 19:54:52.369 debug Objects create System PubSub Client modbus.0 2025-02-09 19:54:52.338 debug Objects client ready ... initialize now modbus.0 2025-02-09 19:54:52.275 debug Redis Objects: Use Redis connection: 127.0.0.1:9001 host.michi 2025-02-09 19:54:48.339 info instance system.adapter.modbus.0 in version "6.3.2" started with pid 2514 host.michi 2025-02-09 19:54:47.367 info "system.adapter.modbus.0" enabled
So richtig?
-
@mark sagte in Modbus EasyCharge Einstellungen:
Bin ich da richtig im Holding-Register oder muss das wo anders rein?
das sollte eigentlich in der Anleitung zum Gerät stehen.
Üblich sind Eingangsregister zum Lesen und Holdingregister zum Schreiben.
40000er sind aber Holdingregister.
bei dir fehlt daher der Haken bei Abfrage, wenn du einen Holdingregister auslesen willst.
-
@homoran Wenn ich den Haken bei Abfrage setze startert der Adapter und geht kurz darauf auf gelb
modbus.0 2025-02-09 20:08:22.493 debug Cleaning up request fifo. modbus.0 2025-02-09 20:08:22.492 debug Clearing timeout of the current request. modbus.0 2025-02-09 20:08:22.488 info Disconnected from slave modbus.0 2025-02-09 20:08:21.488 warn [DevID_2] Poll error count: 2 code: {"err":"timeout","timeout":5000} modbus.0 2025-02-09 20:08:21.486 error Request timed out. modbus.0 2025-02-09 20:08:21.483 warn Error: undefined modbus.0 2025-02-09 20:08:16.479 debug [DevID_2/holdingRegs] Poll address 40035 - 1 registers modbus.0 2025-02-09 20:08:16.478 debug [DevID_2] Poll start --------------------- modbus.0 2025-02-09 20:08:16.474 info Connected to slave modbus.0 2025-02-09 20:08:16.468 debug connect to serial /dev/ttyUSB0 with 9600
-
@mark zeig mal die Grundeinstellungen!
-
@mark Stimmen die Serial Einstellungen zwischen Instanz und Gerät überein und stimmt die Device ID?
Kannst auch mal versuchen das eine Register bei Eingangsregister einzutragen.
Wer weiss ob der Hersteller sich an die Regeln gehalten hat.
-
@homoran
Ich hoffe du meinst diese:In der Beschreibung steht:
In der Modbus Register-Map (gleiche Homepage) steht:
Sowohl none als auch even liefern mir das selbe Ergebnis (mit oder ohne Haken bei Abfrage)
-
@mark sagte in Modbus EasyCharge Einstellungen:
Ich hoffe du meinst diese:
ja!
hat dein Gerät wirklich ID = 2?
@mark sagte in Modbus EasyCharge Einstellungen:
In der Beschreibung steht:
und warum dann 8,1,even?
-
@homoran
ID:
Laut der Modbus Register Map ist die Standard-Adresse 2. Daher hab ich bei ID 2 eingetragen und bin davon ausgegangen dass es stimmt, weil der Adapter auf Grün und conect auf true war. Gibt es eine Möglichkeit die ID abzufragen, falls die 2 falsch ist?8,1,even war der letzt Versuch. hat das selbe Ergebnis gebracht wie 8,1,none.
Was muss ich da einstellen?Hab ja schon widersprüchliche Aussagen in der Beschreibung (falls ich die richtig Verstehe, wenn nicht, bitte korrigiert mich)
-
@mark ich verstehe den fettgedruckten Zusatz nicht "Modbus Kit erforderlich"
hast du den?
muss es dann so heißen, oder kann man es erst dann umstellen -
Beim Gerät selber war kein Modbuskit dabei. Auf der Homepage steht, dass man einen RS485 Adapter braucht, den hab ich mir gekauft und angeschlossen.
-
@mark jetzt hab ich was auf dem Screenshot erkannt
Dann scheinen deine Einstellungen zu passen.
der USB-Port wird richtig sein
Vielleicht gibst du trotzdem mal die ausgabe von
ls /dev/serial/ by-id/
da müsste dann so etwas rauskommen
pi@ioBrokerpi5:~ $ ls /dev/serial/by-id/ usb-FTDI_FT232R_USB_UART_A10NBMVW-if00-port0 usb-FTDI_FT232R_USB_UART_AB0OH9QR-if00-port0 usb-Silicon_Labs_CP2104_USB_to_UART_Bridge_Controller_01066523-if00-port0 pi@ioBrokerpi5:~ $
die ersten beiden sind auch rs485toUSB
-
@homoran said in Modbus EasyCharge Einstellungen:
ls /dev/serial/ by-id/
usb-1a86_USB2.0-Ser_-if00-port0
Aber dafür ist mir jetzt bei deiner Ausgabe was aufgefallen:
Bei dir steht: usb-FTDI...
In der Beschreibung steht auch Modbus mit FTDI. Bei meinem steht das nicht! -
@mark sagte in Modbus EasyCharge Einstellungen:
@homoran said in Modbus EasyCharge Einstellungen:
ls /dev/serial/ by-id/
usb-1a86_USB2.0-Ser_-if00-port0
Das kannst du such statt des USB-Ports eingeben
also
/dev/serial/by-id/usb-1a86_USB2.0-Ser_-if00-port0
dann läuft es auch, wenn die USB Schnittstellen nach einem Neustart anders durchnummeriert werden -
Welchen Adapter hast du denn?
-
-
-
@wendy2702
Um ehrlich zu sein hab ich keinen extra gekauft, sondern vom Pi-Starterset genommen. Müsst der hier sein:
SertronicsUnd wenn ich das auf der Seite gerade richtig lese dann hat er den Chipsatz: CH340C und wenn du mir jetzt noch sagst, dass das kein FTDI Chip hat, dann haben wir den Fehler wohl gefunden und ich darf einen anderen Adapter kaufen
-
@wendy2702 ok!
aber das alte Bild hat noch eine Markierung.
Das erinnert mich gerade @Mark zu fragen wie seine Verdrahtung aussieht. -
@homoran said in Modbus EasyCharge Einstellungen:
@wendy2702 ok!
aber das alte Bild hat noch eine Markierung.
Das erinnert mich gerade @Mark zu fragen wie seine Verdrahtung aussieht.Vom Raspi über RS485 Adapter zum Easycharger Modbus - GND
-
@homoran ja, die beiden Adern könnte man mal auf einer Seite drehen zum Testen