  4. Modbus Adapter für Fronius Wechselrichter geeignet

NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.7k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.1k

Modbus Adapter für Fronius Wechselrichter geeignet

Geplant Angeheftet Gesperrt Verschoben ioBroker Allgemein
103 Beiträge 24 Kommentatoren 26.0k Aufrufe 15 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • HomoranH Homoran

    @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

    wenn‘s um den Modbus-Adapter geht?

    allesxwas du bisher geschrieben hast, bei dem du Probleme hast, hat nichts mit dem modbus-Adapter zu tun.
    der läuft ja bei dir

    L Online
    L Online
    legro
    schrieb am zuletzt editiert von
    #84

    @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

    @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

    wenn‘s um den Modbus-Adapter geht?

    allesxwas du bisher geschrieben hast, bei dem du Probleme hast, hat nichts mit dem modbus-Adapter zu tun.
    der läuft ja bei dir

    Der läuft zwar, aber eben nicht fehlerfrei. Es geht doch auch um die Einstellungen, die ich im Modus-Adapter vornehmen muss, damit ich die Daten und vor allem die richtigen Werte erhalte. Wozu soll das Forum den sonst gut sein?

    Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
    Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

    HomoranH 1 Antwort Letzte Antwort
    0
    • L legro

      @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      wenn‘s um den Modbus-Adapter geht?

      allesxwas du bisher geschrieben hast, bei dem du Probleme hast, hat nichts mit dem modbus-Adapter zu tun.
      der läuft ja bei dir

      Der läuft zwar, aber eben nicht fehlerfrei. Es geht doch auch um die Einstellungen, die ich im Modus-Adapter vornehmen muss, damit ich die Daten und vor allem die richtigen Werte erhalte. Wozu soll das Forum den sonst gut sein?

      HomoranH Nicht stören
      HomoranH Nicht stören
      Homoran
      Global Moderator Administrators
      schrieb am zuletzt editiert von
      #85

      @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      Der läuft zwar, aber eben nicht fehlerfrei.

      doch!

      @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      Es geht doch auch um die Einstellungen, die ich im Modus-Adapter vornehmen muss, damit ich die Daten und vor allem die richtigen Werte erhalte.

      ich kann mich nur wiederholen:

      die sind gerätespezifisch und

      @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      das müsste in der Registerbeschreibung

      des jeweiligen Gerätes stehen.

      @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

      Wozu soll das Forum den sonst gut sein?

      damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

      L 1 Antwort Letzte Antwort
      0
      • HomoranH Homoran

        @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

        Der läuft zwar, aber eben nicht fehlerfrei.

        doch!

        @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

        Es geht doch auch um die Einstellungen, die ich im Modus-Adapter vornehmen muss, damit ich die Daten und vor allem die richtigen Werte erhalte.

        ich kann mich nur wiederholen:

        die sind gerätespezifisch und

        @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

        das müsste in der Registerbeschreibung

        des jeweiligen Gerätes stehen.

        @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

        Wozu soll das Forum den sonst gut sein?

        damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

        L Online
        L Online
        legro
        schrieb am zuletzt editiert von
        #86

        @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

        damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

        Das habe ich hier bereits schon getan.

        Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
        Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

        HomoranH 1 Antwort Letzte Antwort
        0
        • L legro

          @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

          damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

          Das habe ich hier bereits schon getan.

          HomoranH Nicht stören
          HomoranH Nicht stören
          Homoran
          Global Moderator Administrators
          schrieb am zuletzt editiert von
          #87

          @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

          @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

          damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

          Das habe ich hier bereits schon getan.

          Den Thread hab ich nicht gesehen.
          ich lese zwar seeehr viel, aber um alles lesen zu können, müsste ich mich mehrfach klonen.

          Hatte deinen Thread sowieso wie besprochen in offtopic erwartet.

          kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

          der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

          T 1 Antwort Letzte Antwort
          0
          • HomoranH Homoran

            @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

            @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

            damit du diese Informationen zusammen mit de7nen Einstellungen zur Verfügung stellst, damit die Helfenden die eventuellen Fehler sehen helfen.

            Das habe ich hier bereits schon getan.

            Den Thread hab ich nicht gesehen.
            ich lese zwar seeehr viel, aber um alles lesen zu können, müsste ich mich mehrfach klonen.

            Hatte deinen Thread sowieso wie besprochen in offtopic erwartet.

            T Offline
            T Offline
            topsurfer
            schrieb am zuletzt editiert von topsurfer
            #88

            Ich ziehe meinen Hut für all die tolle Arbeit, die hier gemacht wird, um Daten vom Fronius WR in ioBroker zu integrieren! Danke!

            Ich erhalte in den nächsten Wochen meinen Fronius WR incl. einem Smart Meter TS.

            Jetzt habe ich hier (https://www.fronius.com/de/solarenergie/installateure-partner/technische-daten/alle-produkte/anlagen-monitoring/hardware/fronius-smart-meter/fronius-smart-meter-63a-3) gesehen, dass es ja einige verschiedene Modell vom Smart Meter gibt, speziell der Unterschied mit "TS" und "IP" am Ende.
            Der "TS" hat bei "Schnittstelle zum WR: Modbus RTU (RS485)"
            Der "IP" hat dort: "Schnittstelle zum WR: Modbus RTU (RS485), Modbus TCP (Wifi, LAN)"

            Funktioniert das Auslesen für ioBroker mit beiden, oder sollte man eine spezielle Version vom Smart-Meter bevorzugen?
            (Im Technikraum habe ich LAN und WLAN zur Verfügung)

            L 1 Antwort Letzte Antwort
            0
            • T topsurfer

              Ich ziehe meinen Hut für all die tolle Arbeit, die hier gemacht wird, um Daten vom Fronius WR in ioBroker zu integrieren! Danke!

              Ich erhalte in den nächsten Wochen meinen Fronius WR incl. einem Smart Meter TS.

              Jetzt habe ich hier (https://www.fronius.com/de/solarenergie/installateure-partner/technische-daten/alle-produkte/anlagen-monitoring/hardware/fronius-smart-meter/fronius-smart-meter-63a-3) gesehen, dass es ja einige verschiedene Modell vom Smart Meter gibt, speziell der Unterschied mit "TS" und "IP" am Ende.
              Der "TS" hat bei "Schnittstelle zum WR: Modbus RTU (RS485)"
              Der "IP" hat dort: "Schnittstelle zum WR: Modbus RTU (RS485), Modbus TCP (Wifi, LAN)"

              Funktioniert das Auslesen für ioBroker mit beiden, oder sollte man eine spezielle Version vom Smart-Meter bevorzugen?
              (Im Technikraum habe ich LAN und WLAN zur Verfügung)

              L Online
              L Online
              legro
              schrieb am zuletzt editiert von legro
              #89

              @topsurfer

              Funktioniert das Auslesen für ioBroker mit beiden, oder sollte man eine spezielle Version vom Smart-Meter bevorzugen?

              Das von dir referenzierte Smartmeter ist ein älteres, aber durchaus noch aktuelles Modell. Heute wird üblicherweise das TS 65A-3 verbaut, wobei TS für die Bedienung mittels Bildschirm (touch ..) steht. Das von dir zitierte Gerät hat dieselben Funktionen, ist jedoch breiter und belegt auf der Hutschiene vier (statt drei) Einheiten.

              Wenn du das Teil später einmal per Modbus ansteuern willst, solltest du hier einmal vorbeischauen. Zur Zeit bin ich dabei, im Modbus-Adapter von ioBroker die Register für Smartmeter und Wechselrichter (GEN24) zu editieren.

              Du musst jedoch nicht mittels Modbus deinen Wechselrichter verwalten. Der verfügbare Adapter lässt auch in der derzeit vorliegenden Form kaum Wünsche offen, es sei denn, du möchtest selbst wichtige Funktionen des Wechselrichters und der Batterie steuern. Über den sog. Fronius-Adapter kannst du über die Netzwerkschnittstelle des GEN24 auf Wechselrichter selbst und das über RTU mit dem GEN24 verbundene Smartmeter zugreifen. Was ich so alles damit angestellt/realisiert habe, kannst du hier dir anschauen.

              Derzeit wird an einer neuen Version des Adapters gearbeitet. Näheres findest du hier.

              Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
              Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

              1 Antwort Letzte Antwort
              0
              • T Offline
                T Offline
                topsurfer
                schrieb am zuletzt editiert von
                #90

                @legro Danke dir,
                und ja, im Angebot steht der (aktuelle) TS 65A-3 auch drin!
                (hab ich nur falsch verlinkt)

                L 1 Antwort Letzte Antwort
                0
                • T topsurfer

                  @legro Danke dir,
                  und ja, im Angebot steht der (aktuelle) TS 65A-3 auch drin!
                  (hab ich nur falsch verlinkt)

                  L Online
                  L Online
                  legro
                  schrieb am zuletzt editiert von legro
                  #91

                  @topsurfer

                  Was für einen Wechselrichter bekommst du denn?

                  Lass‘ dir in jedem Fall auch das sog. Technician Passwort nennen! Schließlich gehört dir ja das Gerät. Im Gegensatz zu vielen Herstellern gibt es bei Fronius keine Zankereien bei den Passwörtern.

                  Leider suchen viele Hersteller heutzutage ihre Pfründe und die der Fachbetriebe zu schützen. Dabei gehen einige soweit, dass die Fachbetriebe „personalisierte“ Passwörter erhalten und die zuweilen auch nur, wenn sie zuvor kostenpflichtige Lehrgänge beim Hersteller durchlaufen haben.

                  Zwei Beispiele aus unserer Familie und Bekanntenkreis ..

                  Um die 70%-Grenze für Anlagen mit weniger als 7KWp zu entfernen, musste der Installateur anrücken. Selbstverständlich rechnete der das Ganze zu günstigen Tageshöchstpreisen ab.

                  Um Einstellungen in der Batteriekonfiguration an eigene Bedürfnisse anzupassen, dasselbe miese Spiel.

                  Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
                  Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

                  HomoranH 1 Antwort Letzte Antwort
                  0
                  • L legro

                    @topsurfer

                    Was für einen Wechselrichter bekommst du denn?

                    Lass‘ dir in jedem Fall auch das sog. Technician Passwort nennen! Schließlich gehört dir ja das Gerät. Im Gegensatz zu vielen Herstellern gibt es bei Fronius keine Zankereien bei den Passwörtern.

                    Leider suchen viele Hersteller heutzutage ihre Pfründe und die der Fachbetriebe zu schützen. Dabei gehen einige soweit, dass die Fachbetriebe „personalisierte“ Passwörter erhalten und die zuweilen auch nur, wenn sie zuvor kostenpflichtige Lehrgänge beim Hersteller durchlaufen haben.

                    Zwei Beispiele aus unserer Familie und Bekanntenkreis ..

                    Um die 70%-Grenze für Anlagen mit weniger als 7KWp zu entfernen, musste der Installateur anrücken. Selbstverständlich rechnete der das Ganze zu günstigen Tageshöchstpreisen ab.

                    Um Einstellungen in der Batteriekonfiguration an eigene Bedürfnisse anzupassen, dasselbe miese Spiel.

                    HomoranH Nicht stören
                    HomoranH Nicht stören
                    Homoran
                    Global Moderator Administrators
                    schrieb am zuletzt editiert von
                    #92

                    @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                    Um die 70%-Grenze für Anlagen mit weniger als 7KWp zu entfernen, musste der Installateur anrücken

                    das ist Hoheitsgebiet der Netzbetreiber und genau der Grund warum diese Parameter, die netzrelevant sind, nicht von jedem User verstellt werden können und dürfen.

                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                    L 1 Antwort Letzte Antwort
                    0
                    • HomoranH Homoran

                      @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                      Um die 70%-Grenze für Anlagen mit weniger als 7KWp zu entfernen, musste der Installateur anrücken

                      das ist Hoheitsgebiet der Netzbetreiber und genau der Grund warum diese Parameter, die netzrelevant sind, nicht von jedem User verstellt werden können und dürfen.

                      L Online
                      L Online
                      legro
                      schrieb am zuletzt editiert von legro
                      #93

                      @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                      das ist Hoheitsgebiet der Netzbetreiber und genau der Grund warum diese Parameter, die netzrelevant sind, nicht von jedem User verstellt werden können und dürfen.

                      Das ist schlichtweg nicht richtig. Die von dir vermutlich gemeinten „sensiblen“ Netzparameter sind selbstverständlich (mittlerweile) auch bei Fronius geschützt. Darüber hinaus sollte jeder (freie) Bürger dieses Landes wissen, wo seine Grenzen liegen. Aber ich habe keine Lust hierüber jetzt eine Diskussion vom Zaun zu brechen.

                      Mein Rat bleibt: Das Technician Passwort gehört dem Kunden mitgeteilt!

                      Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
                      Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

                      A 1 Antwort Letzte Antwort
                      0
                      • L legro

                        @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                        das ist Hoheitsgebiet der Netzbetreiber und genau der Grund warum diese Parameter, die netzrelevant sind, nicht von jedem User verstellt werden können und dürfen.

                        Das ist schlichtweg nicht richtig. Die von dir vermutlich gemeinten „sensiblen“ Netzparameter sind selbstverständlich (mittlerweile) auch bei Fronius geschützt. Darüber hinaus sollte jeder (freie) Bürger dieses Landes wissen, wo seine Grenzen liegen. Aber ich habe keine Lust hierüber jetzt eine Diskussion vom Zaun zu brechen.

                        Mein Rat bleibt: Das Technician Passwort gehört dem Kunden mitgeteilt!

                        A Online
                        A Online
                        Alex4
                        schrieb am zuletzt editiert von
                        #94

                        hat schon jemand probiert Modbus TCP als Slave Smartmeter einzubinden?

                        Damit könnte man im Solarweb auch den Verbrauch der Waschmaschine, Ladestation und anderen Dingen die man im ioBroker hat visualisieren.

                        Die dafür nötigen Modbus Adressen sind ja bekannt.

                        Gen24 to Fronuis Smart Meter Registers
                        Polled at startup, haven't reversed those yet
                        
                        0, [2336,0]     AC Voltage mean?
                        11, [731]
                        770, [1,3)
                        20480, [50, 51, 48, 50, 53, 54, 87, 31973, 1450]    S/N?
                        20496, [2022]
                        4098, [0]
                        4355, [1]
                        4356, [1,0]
                        
                        
                        Polled constantly:
                        
                        Read holding register for device ID 1 , Start address = 258 Quantity = 16
                        Read holding register for device ID 1 , Start address = 286 Quantity = 42
                        
                        
                        
                        The values are encoded as 32-bit integers, with an odd coding of negative values (see python code below)
                        
                        258 - 2340      234.0 AC Voltage Mean?
                        259 - 0
                        260 - 4053      405.3 AC Voltage Mean?
                        261 - 0 
                        262 - 47739     -1780.6W - Power total
                        263 - 65535
                        264 - 17799     1779.9 VA - Apparent Power total
                        265 - 0           
                        266 - 254       -2.54 VA - Reactive Power total
                        267 - 0
                        268 - 1000      Power factor
                        269 - 0
                        270 - 0
                        271 - 0
                        272 - 499       49.9 Hz - Frequency
                        273 - 0
                        
                        286 - 4053      405.3 V - AC Voltage P1
                        287 - 0
                        288 - 2343      234.3 - AC Voltage L1
                        289 - 0
                        290 - 63001     -2.534A - AC Current L1
                        291 - 65535
                        292 - 59598     -593.7W - Power L1    
                        293 - 65535 
                        294 - 5938      593.3 - Apparent Power L1
                        295 - 0
                        296 - 22        2.2 VA - Reactive Power L1
                        297 - 0 
                        298 - 1000      Power factor
                        299 - 0 
                        
                        300 - 4027      402.7 - AC Voltage P2
                        301 - 0
                        302 - 2338      233.8 - AC Voltage L2
                        303 - 0
                        304 - 62991     -2.544A - AC Current L2
                        305 - 65535
                        306 - 59589     -594.6W - Power L2
                        307 - 65535
                        308 - 5948      594.8 - Apparent Power L2
                        309 - 0
                        310 - 109       10.9 VA - Reactive Power L2
                        311 - 0
                        312 - 1000      Power factor = 1 (64537 = 0.999)
                        313 - 0
                        
                        314 - 4072      407.2 - AC Voltage P3
                        315 - 0
                        316 - 2336      233.6 - AC Voltage L3
                        317 - 0
                        318 - 63005     -2.530A - AC Current L3 (65535-63005 mA)
                        319 - 65535
                        320 - 59626     -590.9W - Power L3 ( (65535-59626)/10 )
                        321 - 65535
                        322 - 5911      591.1 - Apparent Power L3
                        323 - 0
                        324 - 122       12.2 VA - Reactive Power L3
                        325 - 0
                        326 - 1000      Power factor
                        327 - 0
                        
                        
                        
                        Polled every 10 seconds:
                        
                        2023-03-20 17:19:30.073269 Read holding register for device ID 1 , Start address = 1024 Quantity = 16```
                        
                        
                        
                        Values below were confirmed by looking at the actual meter display
                        
                        1024 - 2005     Energy consumed (2005.163 kWh)
                        1025 - 0
                        1026 - 163       
                        1027 - 0
                        1028 - 43       Energy reactive consumed (43.801 kVArh)
                        1029 - 0
                        1030 - 801     
                        1031 - 0
                        1032 - 1722     Energy produced (1722.232 kWh)
                        1033 - 0
                        1034 - 232      
                        1035 - 0
                        1036 - 8        Energy reactive produced (8.203 kVArh)
                        1037 - 0      
                        1038 - 203
                        1039 - 0
                        
                        
                        
                        
                        
                        Python to code/decode values
                        Two consecutive 16-bit registers are used. If MSB in r2 is 1, then it's a negative number.
                        
                        def get_value_from_32bits(r1,r2):
                        
                          v = r1 + (r2 & 32767) * 65536
                          if r2 > 32768:
                            v = - ((65535 - r1) + (65535 - r2) * 65536)
                          print("v:",v)
                          return v
                        
                        def get_32bits_from_value(value):
                          if value > 0:
                            r1 = value & 65535
                            r2 = value >> 16
                          if value < 0:
                            value = - value
                            r1 = 65535 - (value & 65535)
                            r2 = 65535 - (value >> 16)
                          print("v,r1,r2:",value,r1,r2)
                          print("")
                          return [r1,r2]
                        
                        
                        v = get_value_from_32bits(64657,1) # 130193
                        new_regs = get_32bits_from_value(v // 1) 
                        
                        v = get_value_from_32bits(17799,0) # 17799
                        new_regs = get_32bits_from_value(v // 1) 
                        
                        v = get_value_from_32bits(47739,65535) # -17796
                        new_regs = get_32bits_from_value(v // 1) 
                        
                        v = get_value_from_32bits(31071,65534) # -100000 
                        new_regs = get_32bits_from_value(-100000 // 1) 
                        
                        1 Antwort Letzte Antwort
                        0
                        • L Online
                          L Online
                          legro
                          schrieb am zuletzt editiert von legro
                          #95

                          @alex4 sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                          hat schon jemand probiert Modbus TCP als Slave Smartmeter einzubinden?

                          Damit könnte man im Solarweb auch den Verbrauch der Waschmaschine, Ladestation und anderen Dingen die man im ioBroker hat visualisieren.

                          Die dafür nötigen Modbus Adressen sind ja bekannt.

                          Es ist mir ein Rätsel, wie du mittels der Modbus-Register diese Verbräuche ermitteln willst. Hierzu müsstest du ja vor jedem Verbraucher ein Smartmeter installieren. Oder habe ich dich grundlegend falsch verstanden?

                          Apropos Register ..

                          Nachdem ich die vielen Hürden überwunden hatte, wie man diese einrichtet, habe ich die Strafarbeit auf mich genommen und diese editiert. Hier habe ich sie zum Herunterladen zur Verfügung gestellt.

                          Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
                          Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

                          HomoranH 1 Antwort Letzte Antwort
                          0
                          • L legro

                            @alex4 sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                            hat schon jemand probiert Modbus TCP als Slave Smartmeter einzubinden?

                            Damit könnte man im Solarweb auch den Verbrauch der Waschmaschine, Ladestation und anderen Dingen die man im ioBroker hat visualisieren.

                            Die dafür nötigen Modbus Adressen sind ja bekannt.

                            Es ist mir ein Rätsel, wie du mittels der Modbus-Register diese Verbräuche ermitteln willst. Hierzu müsstest du ja vor jedem Verbraucher ein Smartmeter installieren. Oder habe ich dich grundlegend falsch verstanden?

                            Apropos Register ..

                            Nachdem ich die vielen Hürden überwunden hatte, wie man diese einrichtet, habe ich die Strafarbeit auf mich genommen und diese editiert. Hier habe ich sie zum Herunterladen zur Verfügung gestellt.

                            HomoranH Nicht stören
                            HomoranH Nicht stören
                            Homoran
                            Global Moderator Administrators
                            schrieb am zuletzt editiert von
                            #96

                            @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                            wie du mittels der Modbus-Register diese Verbräuche ermitteln willst.

                            er will Werte an den Fronius liefern!
                            um sie dort visualisieren zu können.
                            @Alex4
                            und ja, versucht iobroker für solche Fälle als modbus slave zu missbrauchen gab es. hab aberr nicht weiterverfolgt mit welchem Ausgang.
                            Da musst du mal suchen.

                            kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                            L A 2 Antworten Letzte Antwort
                            0
                            • HomoranH Homoran

                              @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                              wie du mittels der Modbus-Register diese Verbräuche ermitteln willst.

                              er will Werte an den Fronius liefern!
                              um sie dort visualisieren zu können.
                              @Alex4
                              und ja, versucht iobroker für solche Fälle als modbus slave zu missbrauchen gab es. hab aberr nicht weiterverfolgt mit welchem Ausgang.
                              Da musst du mal suchen.

                              L Online
                              L Online
                              legro
                              schrieb am zuletzt editiert von legro
                              #97

                              @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                              er will Werte an den Fronius liefern! um sie dort visualisieren zu können. .. Da musst du mal suchen.

                              Gewiss nicht. Ich bin heil froh, die vielen Register editiert zu haben. Visualisiert wird bei mir selbstverständlich mit VIS im ioBroker.

                              Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
                              Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

                              HomoranH 1 Antwort Letzte Antwort
                              0
                              • L legro

                                @homoran sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                                er will Werte an den Fronius liefern! um sie dort visualisieren zu können. .. Da musst du mal suchen.

                                Gewiss nicht. Ich bin heil froh, die vielen Register editiert zu haben. Visualisiert wird bei mir selbstverständlich mit VIS im ioBroker.

                                HomoranH Nicht stören
                                HomoranH Nicht stören
                                Homoran
                                Global Moderator Administrators
                                schrieb am zuletzt editiert von
                                #98

                                @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                                Gewiss nicht

                                was?

                                kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                                1 Antwort Letzte Antwort
                                0
                                • HomoranH Homoran

                                  @legro sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                                  wie du mittels der Modbus-Register diese Verbräuche ermitteln willst.

                                  er will Werte an den Fronius liefern!
                                  um sie dort visualisieren zu können.
                                  @Alex4
                                  und ja, versucht iobroker für solche Fälle als modbus slave zu missbrauchen gab es. hab aberr nicht weiterverfolgt mit welchem Ausgang.
                                  Da musst du mal suchen.

                                  A Online
                                  A Online
                                  Alex4
                                  schrieb am zuletzt editiert von
                                  #99

                                  @homoran wir haben das inzwischen als Slave Smartmeter am laufen, nur muss man aufpassen, dass man die Seriennummern im statischen Register 20480 ändert, da der gen24 keine smartmeter mit gleichen Seriennummern mag.

                                  Der Hintergrund ist, dass ich mit einem Smartmeter derzeit 3 gen24 dazu bringe parallel auch 3 Batterien zu laden/entladen und da es Tesla Batterien mit 77-100kwh sind (gesamt 310Kwh), kam mir dann die Idee, dass auch von anderen Verbrauchern zur Verfügung zu stellen. Im Prinzip wären bei vielen von uns die Daten schon da und müssten nur ,,genutzt“ werden.

                                  Da ich selbst grafisch eine komplette Niete bin und keine Vis auf die Reihe bekomme, ist das via solarweb eine gute Alternative.

                                  P 1 Antwort Letzte Antwort
                                  0
                                  • B Offline
                                    B Offline
                                    Bender275
                                    schrieb am zuletzt editiert von
                                    #100

                                    Hallo zusammen,
                                    ich brauche mal eure Hilfe. Ich schaffe es nicht, per Modbus auf meinen Gen24 Wechselrichter zu kommen.
                                    Konfig im Adapter:
                                    2.png 1.png

                                    Konfig im WR:
                                    3.png

                                    In der Tabelle steht, welchen Wert ich lesen will. Ich habe die Adresse um eins reduziert, wie beschrieben.

                                    Im Log erscheint aber immer nur:

                                    modbus.0	2023-10-10 09:50:12.261	info	Disconnected from slave 10.0.0.4
                                    modbus.0	2023-10-10 09:50:12.207	warn	Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:11.149	warn	Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:10.090	warn	Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:09.032	warn	Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:07.972	warn	Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:06.911	warn	Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                    modbus.0	2023-10-10 09:50:06.887	info	Connected to slave 10.0.0.4
                                    

                                    Lasse ich die Holding-Register leer, kommt nur Connected und Disconnected. Ich gehe also davon aus, dass die Verbindung an sich funktioniert.

                                    WR-Firmware ist die aktuelle 1.27.3-1.

                                    Hat jemand eine Idee? Danke!

                                    B 1 Antwort Letzte Antwort
                                    0
                                    • B Bender275

                                      Hallo zusammen,
                                      ich brauche mal eure Hilfe. Ich schaffe es nicht, per Modbus auf meinen Gen24 Wechselrichter zu kommen.
                                      Konfig im Adapter:
                                      2.png 1.png

                                      Konfig im WR:
                                      3.png

                                      In der Tabelle steht, welchen Wert ich lesen will. Ich habe die Adresse um eins reduziert, wie beschrieben.

                                      Im Log erscheint aber immer nur:

                                      modbus.0	2023-10-10 09:50:12.261	info	Disconnected from slave 10.0.0.4
                                      modbus.0	2023-10-10 09:50:12.207	warn	Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:11.149	warn	Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:10.090	warn	Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:09.032	warn	Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:07.972	warn	Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:06.911	warn	Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      modbus.0	2023-10-10 09:50:06.887	info	Connected to slave 10.0.0.4
                                      

                                      Lasse ich die Holding-Register leer, kommt nur Connected und Disconnected. Ich gehe also davon aus, dass die Verbindung an sich funktioniert.

                                      WR-Firmware ist die aktuelle 1.27.3-1.

                                      Hat jemand eine Idee? Danke!

                                      B Offline
                                      B Offline
                                      Bender275
                                      schrieb am zuletzt editiert von
                                      #101

                                      Keiner eine Idee? Oder einen Tipp, wie es bei ihm/ihr selbst funktioniert?

                                      L 1 Antwort Letzte Antwort
                                      0
                                      • B Bender275

                                        Keiner eine Idee? Oder einen Tipp, wie es bei ihm/ihr selbst funktioniert?

                                        L Online
                                        L Online
                                        legro
                                        schrieb am zuletzt editiert von
                                        #102

                                        @bender275 sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                                        Keiner eine Idee? Oder einen Tipp, wie es bei ihm/ihr selbst funktioniert?

                                        Wer suchet, der findet.:slightly_smiling_face: Hier habe ich ausführlich beschrieben, welche Ressourcen Fronius bereitstellt und wie ich das Ganze umgesetzt habe.

                                        Nach über vier Jahren Leidenszeit unter Qivicon/MSH vor den Telekomikern zu ioBroker geflüchtet.
                                        Raspberry Pi 4 mit 8GB + ArgonOneM.2 + 120GB SSD + Coordinator CC26X2R1 + ioBroker + piVCCU3

                                        1 Antwort Letzte Antwort
                                        0
                                        • A Alex4

                                          @homoran wir haben das inzwischen als Slave Smartmeter am laufen, nur muss man aufpassen, dass man die Seriennummern im statischen Register 20480 ändert, da der gen24 keine smartmeter mit gleichen Seriennummern mag.

                                          Der Hintergrund ist, dass ich mit einem Smartmeter derzeit 3 gen24 dazu bringe parallel auch 3 Batterien zu laden/entladen und da es Tesla Batterien mit 77-100kwh sind (gesamt 310Kwh), kam mir dann die Idee, dass auch von anderen Verbrauchern zur Verfügung zu stellen. Im Prinzip wären bei vielen von uns die Daten schon da und müssten nur ,,genutzt“ werden.

                                          Da ich selbst grafisch eine komplette Niete bin und keine Vis auf die Reihe bekomme, ist das via solarweb eine gute Alternative.

                                          P Offline
                                          P Offline
                                          passuff
                                          schrieb am zuletzt editiert von
                                          #103

                                          @alex4 sagte in Modbus Adapter für Fronius Wechselrichter geeignet:

                                          @homoran wir haben das inzwischen als Slave Smartmeter am laufen, nur muss man aufpassen, dass man die Seriennummern im statischen Register 20480 ändert, da der gen24 keine smartmeter mit gleichen Seriennummern mag.

                                          Kann ich irgendwo nachlesen, wie du das realisiert hast einen SmartMeter zu "simulieren"?

                                          1 Antwort Letzte Antwort
                                          1
                                          Antworten
                                          • In einem neuen Thema antworten
                                          Anmelden zum Antworten
                                          • Älteste zuerst
                                          • Neuste zuerst
                                          • Meiste Stimmen


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate
                                          FAQ Cloud / IOT
                                          HowTo: Node.js-Update
                                          HowTo: Backup/Restore
                                          Downloads
                                          BLOG

                                          558

                                          Online

                                          32.4k

                                          Benutzer

                                          81.5k

                                          Themen

                                          1.3m

                                          Beiträge
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Anmelden

                                          • Du hast noch kein Konto? Registrieren

                                          • Anmelden oder registrieren, um zu suchen
                                          • Erster Beitrag
                                            Letzter Beitrag
                                          0
                                          • Home
                                          • Aktuell
                                          • Tags
                                          • Ungelesen 0
                                          • Kategorien
                                          • Unreplied
                                          • Beliebt
                                          • GitHub
                                          • Docu
                                          • Hilfe