    Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox

    This topic has been deleted. Only users with topic management privileges can see it.
    • A
      AndreasK last edited by AndreasK

      Hallo.
      Ich lese schon einige Werte über den Modbus Adapter aus meiner Mennekes Amtron 4You 560 Wallbox aus.
      Da ich dienstlich und privat lade, möchte ich die ID-Karte auch auslesen, damit ich weiß, ob ich gerade privat oder dienstlich lade.
      Damit habe ich aber ein Problem.
      Laut der Modbus Register Tabelle von Mennekes sind das diese Nummern
      Bildschirmfoto 2025-05-06 um 19.57.51.png
      Diese wollte, ich wie alle anderen Werte, welche ich schon auslese, ins Holding-Register eintragen.
      Leider bekomme ich dann folgende Fehlermeldung

      
      modbus.0
      2025-05-06 19:54:47.271	warn	[DevID_1] Poll error count: 6 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      
      modbus.0
      2025-05-06 19:54:46.191	warn	[DevID_1] Poll error count: 5 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      
      modbus.0
      2025-05-06 19:54:45.132	warn	[DevID_1] Poll error count: 4 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      
      modbus.0
      2025-05-06 19:54:44.077	warn	[DevID_1] Poll error count: 3 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      
      modbus.0
      2025-05-06 19:54:43.017	warn	[DevID_1] Poll error count: 2 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      
      modbus.0
      2025-05-06 19:54:41.335	warn	[DevID_1] Poll error count: 1 code: {"errorCode":129,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
      

      Hier noch meine Einstellungen

      Bildschirmfoto 2025-05-06 um 20.54.08.png

      Register

      Bildschirmfoto 2025-05-06 um 20.39.17.png

      Was passt hier nicht?

      Gruß
      Andreas

      Homoran 1 Reply Last reply Reply Quote 0
      • Homoran
        Homoran Global Moderator Administrators @AndreasK last edited by

        @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

        Was mache ich falsch?

        du zeigst das log als Screenshot und nicht als Text in code-tags.
        Als Ausgleich gibt es die Modbus Einstellungen gar nicht.

        A 1 Reply Last reply Reply Quote 0
        • A
          AndreasK @Homoran last edited by

          @homoran sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

          du zeigst das log als Screenshot und nicht als Text in code-tags.
          Als Ausgleich gibt es die Modbus Einstellungen gar nicht.

          Danke für das Feedback. Habe ich angepasst

          Homoran 1 Reply Last reply Reply Quote 0
          • Homoran
            Homoran Global Moderator Administrators @AndreasK last edited by

            @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

            @homoran sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

            du zeigst das log als Screenshot und nicht als Text in code-tags.
            Als Ausgleich gibt es die Modbus Einstellungen gar nicht.

            Danke für das Feedback. Habe ich angepasst

            Danke!
            die Register Einstellungen wären noch sehr sinnvoll zu kennen, wenn due Meldung entsprechend ausfällt

            A 1 Reply Last reply Reply Quote 0
            • A
              AndreasK @Homoran last edited by

              @homoran Auch das ist hinzugefügt

              Homoran 1 Reply Last reply Reply Quote 0
              • Homoran
                Homoran Global Moderator Administrators @AndreasK last edited by

                @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

                @homoran Auch das ist hinzugefügt

                Die

                @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

                anderen Werte, welche ich schon auslese, ins Holding-Register

                hast du genau so eingetragen?
                3-stellige Ziffern, und das ohne Haken bei Alias verwenden?
                Und funktionieren trotzdem?

                hast du ein debug-log vom Aufruf?
                da müsste die letztlich effektiv abgefragte Registernummer zu sehen sein.

                Ansonsten ist es keine Zahl
                Screenshot_20250506-205306_Firefox.jpg

                Ob alle 5 Tags zeitgleich ausgelesen werden und zerlegt werden müssen kann ich nicht beurteilen

                A 1 Reply Last reply Reply Quote 0
                • A
                  AndreasK @Homoran last edited by

                  @homoran
                  Alias hatte ich eigentlich aktiviert. Heute aber raus genommen. Ich habe es jetzt wieder aktiviert.
                  Dann sehen die Register Einträge so aus:
                  Bildschirmfoto 2025-05-06 um 21.22.33.png

                  Hier der Debug-Log:

                  
                  modbus.0
                  2025-05-06 21:19:05.875	debug	Closing client on purpose.
                  
                  modbus.0
                  2025-05-06 21:19:04.875	debug	Cleaning up request fifo.
                  
                  modbus.0
                  2025-05-06 21:19:04.874	debug	Socket closed with error
                  
                  modbus.0
                  2025-05-06 21:19:04.869	info	Disconnected from slave 192.168.30.242
                  
                  modbus.0
                  2025-05-06 21:19:04.868	debug	Closing client on purpose.
                  
                  modbus.0
                  2025-05-06 21:19:04.817	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:19:04.816	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:19:04.809	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:19:04.808	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:19:04.800	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:19:04.799	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:19:03.745	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:19:03.745	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:19:03.740	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:19:03.736	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:19:03.719	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:19:03.718	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:19:02.666	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:19:02.665	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:19:02.656	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:19:02.653	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:19:02.647	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:19:02.646	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:19:01.594	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:19:01.593	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:19:01.588	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:19:01.587	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:19:01.575	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:19:01.575	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:19:00.523	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:19:00.522	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:19:00.517	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:19:00.516	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:19:00.506	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:19:00.505	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:18:59.452	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                  
                  modbus.0
                  2025-05-06 21:18:59.450	debug	Received pdu describes an error.
                  
                  modbus.0
                  2025-05-06 21:18:59.447	debug	[DevID_1/holdingRegs] Poll address 716 - 14 registers
                  
                  modbus.0
                  2025-05-06 21:18:59.441	debug	[DevID_1/holdingRegs] Poll address 206 DONE
                  
                  modbus.0
                  2025-05-06 21:18:59.428	debug	[DevID_1/holdingRegs] Poll address 206 - 16 registers
                  
                  modbus.0
                  2025-05-06 21:18:59.427	debug	Initialization of scale factors done!
                  
                  modbus.0
                  2025-05-06 21:18:59.425	debug	[DevID_1] Poll start ---------------------
                  
                  modbus.0
                  2025-05-06 21:18:59.423	info	Connected to slave 192.168.30.242
                  
                  modbus.0
                  2025-05-06 21:18:59.014	debug	Add holdingRegisters.40729_IDTAG_5: {"_id":"holdingRegisters.40729_IDTAG_5","type":"state","common":{"name":"RFID Tag Teil 5","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":728,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.014	debug	Add holdingRegisters.40727_IDTAG_4: {"_id":"holdingRegisters.40727_IDTAG_4","type":"state","common":{"name":"RFID Tag Teil 4","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":726,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.013	debug	Add holdingRegisters.40725_IDTAG_3: {"_id":"holdingRegisters.40725_IDTAG_3","type":"state","common":{"name":"RFID Tag Teil 3","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":724,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.012	debug	Add holdingRegisters.40723_IDTAG_2: {"_id":"holdingRegisters.40723_IDTAG_2","type":"state","common":{"name":"RFID Tag Teil 2","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":722,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.011	debug	Add holdingRegisters.40721_IDTAG_1: {"_id":"holdingRegisters.40721_IDTAG_1","type":"state","common":{"name":"RFID Tag Teil 1","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":720,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.011	debug	Add holdingRegisters.40719_Ladedauer: {"_id":"holdingRegisters.40719_Ladedauer","type":"state","common":{"name":"Ladedauer","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"s"},"native":{"regType":"holdingRegs","address":718,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.010	debug	Add holdingRegisters.40717_CHARGED_ENERGY: {"_id":"holdingRegisters.40717_CHARGED_ENERGY","type":"state","common":{"name":"Wert aktueller Ladevorgang","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":716,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.010	debug	Add holdingRegisters.40221_Aktuelle_Leistung: {"_id":"holdingRegisters.40221_Aktuelle_Leistung","type":"state","common":{"name":"Aktuell gezogene Leistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":220,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.009	debug	Add holdingRegisters.40219_Total_Energy_: {"_id":"holdingRegisters.40219_Total_Energy_","type":"state","common":{"name":"Zählerstand","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":218,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.009	debug	Add holdingRegisters.40217_Strom_L3: {"_id":"holdingRegisters.40217_Strom_L3","type":"state","common":{"name":"Aktueller Strom über L3","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mA"},"native":{"regType":"holdingRegs","address":216,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.008	debug	Add holdingRegisters.40215_Strom_L2: {"_id":"holdingRegisters.40215_Strom_L2","type":"state","common":{"name":"Aktueller Strom über L2","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mA"},"native":{"regType":"holdingRegs","address":214,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.007	debug	Add holdingRegisters.40213_Strom_L1: {"_id":"holdingRegisters.40213_Strom_L1","type":"state","common":{"name":"Aktueller Strom über L1","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"mA"},"native":{"regType":"holdingRegs","address":212,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.007	debug	Add holdingRegisters.40211_Leistung_L3: {"_id":"holdingRegisters.40211_Leistung_L3","type":"state","common":{"name":"Aktuelle Leistung über L3","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":210,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.006	debug	Add holdingRegisters.40209_Leistung_L2: {"_id":"holdingRegisters.40209_Leistung_L2","type":"state","common":{"name":"Aktuelle Leistung über L2","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":208,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.006	debug	Add holdingRegisters.40207_Leistung_L1: {"_id":"holdingRegisters.40207_Leistung_L1","type":"state","common":{"name":"Aktuelle Leistung über L1","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":206,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                  
                  modbus.0
                  2025-05-06 21:18:59.005	debug	Initialize Objects for holdingRegs: [{"_address":40207,"name":"Leistung L1","description":"Aktuelle Leistung über L1","unit":"W","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":206,"id":"holdingRegisters.40207_Leistung_L1"},{"_address":40209,"name":"Leistung L2","description":"Aktuelle Leistung über L2","unit":"W","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":208,"id":"holdingRegisters.40209_Leistung_L2"},{"_address":40211,"name":"Leistung L3","description":"Aktuelle Leistung über L3","unit":"W","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":210,"id":"holdingRegisters.40211_Leistung_L3"},{"_address":40213,"name":"Strom L1","description":"Aktueller Strom über L1","unit":"mA","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":212,"id":"holdingRegisters.40213_Strom_L1"},{"_address":40215,"name":"Strom L2","description":"Aktueller Strom über L2","unit":"mA","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":214,"id":"holdingRegisters.40215_Strom_L2"},{"_address":40217,"name":"Strom L3","description":"Aktueller Strom über L3","unit":"mA","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":216,"id":"holdingRegisters.40217_Strom_L3"},{"_address":40219,"name":"Total Energy ","description":"Zählerstand","unit":"Wh","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","address":218,"deviceId":1,"id":"holdingRegisters.40219_Total_Energy_"},{"_address":40221,"name":"Aktuelle Leistung","description":"Aktuell gezogene Leistung","unit":"W","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":220,"id":"holdingRegisters.40221_Aktuelle_Leistung"},{"_address":40717,"name":"CHARGED_ENERGY","description":"Wert aktueller Ladevorgang","unit":"Wh","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":716,"id":"holdingRegisters.40717_CHARGED_ENERGY"},{"_address":40719,"name":"Ladedauer","description":"Ladedauer","unit":"s","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":718,"id":"holdingRegisters.40719_Ladedauer"},{"_address":40721,"name":"IDTAG_1","description":"RFID Tag Teil 1","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":720,"id":"holdingRegisters.40721_IDTAG_1"},{"_address":40723,"name":"IDTAG_2","description":"RFID Tag Teil 2","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":722,"id":"holdingRegisters.40723_IDTAG_2"},{"_address":40725,"name":"IDTAG_3","description":"RFID Tag Teil 3","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":724,"id":"holdingRegisters.40725_IDTAG_3"},{"_address":40727,"name":"IDTAG_4","description":"RFID Tag Teil 4","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":726,"id":"holdingRegisters.40727_IDTAG_4"},{"_address":40729,"name":"IDTAG_5","description":"RFID Tag Teil 5","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":"","isScale":"","deviceId":1,"address":728,"id":"holdingRegisters.40729_IDTAG_5"}]
                  
                  modbus.0
                  2025-05-06 21:18:59.004	debug	Initialize Objects for inputRegs: []
                  
                  modbus.0
                  2025-05-06 21:18:59.003	debug	Initialize Objects for coils: []
                  
                  modbus.0
                  2025-05-06 21:18:59.002	debug	Initialize Objects for disInputs: []
                  
                  modbus.0
                  2025-05-06 21:18:58.775	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.0, js-controller: 7.0.6
                  
                  Homoran 1 Reply Last reply Reply Quote 0
                  • Homoran
                    Homoran Global Moderator Administrators @AndreasK last edited by

                    @andreask du hast aber immer noch Zahl und nicht text drin.

                    Die Register stimmen jetzt, der Errorcode hat sich geändert.
                    Leider hilft mir das nicht.

                    Wenn es mit Text/String auch nicht klappt, weiß ich nicht weiter

                    A 1 Reply Last reply Reply Quote 0
                    • A
                      AndreasK @Homoran last edited by

                      @homoran
                      Danke für die Unterstützung.
                      Leider funktioniert auch kein String. Ich habe alle durchprobiert.
                      Ist es richtig, dass bei den Springs die Länge auch immer 2 ist? Auch bei den 16 Bit Varianten? Normalerweise hat doch 16 Bit nur eine Länge von 1

                      Homoran 1 Reply Last reply Reply Quote 0
                      • Homoran
                        Homoran Global Moderator Administrators @AndreasK last edited by

                        @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

                        Leider funktioniert auch kein String.

                        heisst was?

                        @andreask sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

                        Ist es richtig, dass bei den Springs die Länge auch immer 2 ist? Auch bei den 16 Bit Varianten? Normalerweise hat doch 16 Bit nur eine Länge von 1

                        Meines Wissens gilt das für Zahlen um einen entsprechenden Wertebereich abzudecken.

                        Bei String müsste die Länge variabel sein, hab ich aber noch nie probiert.

                        1 Reply Last reply Reply Quote 0
                        • A
                          AndreasK last edited by

                          @homoran sagte in Probleme Auslesen Modbus Mennekes Amtron 4You Wallbox:

                          heisst was?

                          Soll heissen, dass ich alle String Typen durchprobiert habe. Immer mit der vergebenen Länge von 2
                          Bildschirmfoto 2025-05-07 um 19.08.16.png

                          Und immer erhalte ich die gleiche Fehlermeldung im Log

                          
                          modbus.0
                          2025-05-07 19:03:42.599	info	Disconnected from slave 192.168.30.242
                          
                          modbus.0
                          2025-05-07 19:03:42.547	warn	[DevID_1] Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:41.484	warn	[DevID_1] Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:40.420	warn	[DevID_1] Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:39.361	warn	[DevID_1] Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:38.300	warn	[DevID_1] Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:37.216	warn	[DevID_1] Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                          
                          modbus.0
                          2025-05-07 19:03:37.187	info	Connected to slave 192.168.30.242
                          
                          modbus.0
                          2025-05-07 19:03:36.591	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.0, js-controller: 7.0.6
                          
                          Homoran 1 Reply Last reply Reply Quote 0
                          • Homoran
                            Homoran Global Moderator Administrators @AndreasK last edited by

                            @andreask Dann weiss ich auch nichts mehr, sorry.

                            Möglicherweise ist auch mit "non-null string...." ein "non-0 string" gemeint, und (zero-end) passt dann nicht.

                            1 Reply Last reply Reply Quote 0
                            • First post
                              Last post

                            Support us

                            ioBroker
                            Community Adapters
                            Donate
                            FAQ Cloud / IOT
                            HowTo: Node.js-Update
                            HowTo: Backup/Restore
                            Downloads
                            BLOG

                            857
                            Online

                            31.7k
                            Users

                            79.7k
                            Topics

                            1.3m
                            Posts

                            2
                            12
                            138
                            Loading More Posts
                            • Oldest to Newest
                            • Newest to Oldest
                            • Most Votes
                            Reply
                            • Reply as topic
                            Log in to reply
                            Community
                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                            The ioBroker Community 2014-2023
                            logo