  4. Kaco Blueplanet NX3 M2->RS485 TO POE ETH an Modbus Problem
    5.1k
31 Beiträge 6 Kommentatoren 5.0k Aufrufe 6 Beobachtet
  • wendy2702W wendy2702
    @stronoff Haken bei Aliase raus. Speichern, Register kontrollieren/korrigieren, Speichern, log zeigen
    Willst du mehrere Geräte über den BUS auslesen?
    S Online
    S Online
    stronoff
    @wendy2702
    Ich hab den Haken bei "Mehrere Geräte IDs" entfernt.
    v6.3.5
    1818
    Log-Größe: 261.0 KB
    Zeit
    Nachricht
    modbus.1
    	2023-03-12 10:05:05.625	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:05:05.624	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:05:04.629	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:05:04.629	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:05:04.628	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:05:04.626	warn	Poll error count: 4 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:05:04.624	error	Client in error state.
    modbus.1
    	2023-03-12 10:05:04.624	error	Request timed out.
    modbus.1
    	2023-03-12 10:05:04.623	warn	Error: undefined
    modbus.1
    	2023-03-12 10:04:59.621	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:04:59.621	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:04:59.620	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:03:59.618	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:03:59.617	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:03:58.621	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:03:58.621	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:03:58.621	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:03:58.618	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:03:58.617	error	Client in error state.
    modbus.1
    	2023-03-12 10:03:58.616	error	Request timed out.
    modbus.1
    	2023-03-12 10:03:58.615	warn	Error: undefined
    modbus.1
    	2023-03-12 10:03:53.614	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:03:53.614	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:03:53.612	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:02:53.610	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:02:53.609	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:02:52.614	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:02:52.613	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:02:52.613	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:02:52.610	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:02:52.609	error	Client in error state.
    modbus.1
    	2023-03-12 10:02:52.609	error	Request timed out.
    modbus.1
    	2023-03-12 10:02:52.608	warn	Error: undefined
    modbus.1
    	2023-03-12 10:02:47.606	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:02:47.606	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:02:47.605	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:01:47.601	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:01:47.600	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:01:46.605	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:01:46.604	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:01:46.604	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:01:46.601	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:01:46.599	error	Client in error state.
    modbus.1
    	2023-03-12 10:01:46.599	error	Request timed out.
    modbus.1
    	2023-03-12 10:01:46.598	warn	Error: undefined
    modbus.1
    	2023-03-12 10:01:41.590	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:01:41.589	debug	Initialization of scale factors done!
    modbus.1
    	2023-03-12 10:01:41.587	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:01:41.586	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:01:41.302	debug	Initialize Objects for holdingRegs: []
    modbus.1
    	2023-03-12 10:01:41.302	debug	Add inputRegisters.40072_Amps: {"_id":"inputRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.1
    	2023-03-12 10:01:41.301	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.40072_Amps"}]
    modbus.1
    	2023-03-12 10:01:41.300	debug	Initialize Objects for coils: []
    modbus.1
    	2023-03-12 10:01:41.299	debug	Initialize Objects for disInputs: []
    modbus.1
    	2023-03-12 10:01:41.102	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
    modbus.1
    	2023-03-12 10:01:40.683	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.1
    	2023-03-12 10:01:40.557	debug	States connected to redis: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:01:40.479	debug	States create User PubSub Client
    modbus.1
    	2023-03-12 10:01:40.477	debug	States create System PubSub Client
    modbus.1
    	2023-03-12 10:01:40.453	debug	Redis States: Use Redis connection: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:01:40.404	debug	Objects connected to redis: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:01:40.396	debug	Objects client initialize lua scripts
    modbus.1
    	2023-03-12 10:01:40.319	debug	Objects create User PubSub Client
    modbus.1
    	2023-03-12 10:01:40.317	debug	Objects create System PubSub Client
    modbus.1
    	2023-03-12 10:01:40.314	debug	Objects client ready ... initialize now
    modbus.1
    	2023-03-12 10:01:40.251	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:01:35.727	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.1
    	2023-03-12 10:01:35.727	debug	Plugin sentry destroyed
    modbus.1
    	2023-03-12 10:01:35.725	info	terminating
    modbus.1
    	2023-03-12 10:01:35.723	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:01:35.721	info	Got terminate signal TERMINATE_YOURSELF
    modbus.1
    	2023-03-12 10:01:31.930	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:01:31.928	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:01:30.935	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:01:30.934	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:01:30.933	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:01:30.930	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:01:30.928	error	Client in error state.
    modbus.1
    	2023-03-12 10:01:30.928	error	Request timed out.
    modbus.1
    	2023-03-12 10:01:30.927	warn	Error: undefined
    modbus.1
    	2023-03-12 10:01:25.919	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:01:25.919	debug	Initialization of scale factors done!
    modbus.1
    	2023-03-12 10:01:25.917	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:01:25.915	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:01:25.649	debug	Remove old object modbus.1.inputRegisters.3.40072_Amps
    modbus.1
    	2023-03-12 10:01:25.597	debug	Initialize Objects for holdingRegs: []
    modbus.1
    	2023-03-12 10:01:25.596	debug	Add inputRegisters.40072_Amps: {"_id":"inputRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.1
    	2023-03-12 10:01:25.595	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.40072_Amps"}]
    modbus.1
    	2023-03-12 10:01:25.594	debug	Initialize Objects for coils: []
    modbus.1
    	2023-03-12 10:01:25.593	debug	Initialize Objects for disInputs: []
    modbus.1
    	2023-03-12 10:01:25.398	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
    modbus.1
    	2023-03-12 10:01:24.970	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.1
    	2023-03-12 10:01:24.828	debug	States connected to redis: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:01:24.747	debug	States create User PubSub Client
    modbus.1
    	2023-03-12 10:01:24.745	debug	States create System PubSub Client
    modbus.1
    	2023-03-12 10:01:24.720	debug	Redis States: Use Redis connection: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:01:24.676	debug	Objects connected to redis: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:01:24.668	debug	Objects client initialize lua scripts
    modbus.1
    	2023-03-12 10:01:24.578	debug	Objects create User PubSub Client
    modbus.1
    	2023-03-12 10:01:24.577	debug	Objects create System PubSub Client
    modbus.1
    	2023-03-12 10:01:24.574	debug	Objects client ready ... initialize now
    modbus.1
    	2023-03-12 10:01:24.516	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:01:19.975	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.1
    	2023-03-12 10:01:19.975	debug	Plugin sentry destroyed
    modbus.1
    	2023-03-12 10:01:19.973	info	terminating
    modbus.1
    	2023-03-12 10:01:19.971	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:01:19.969	info	Got terminate signal TERMINATE_YOURSELF
    modbus.1
    	2023-03-12 10:00:49.061	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:00:49.060	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:00:48.067	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:00:48.066	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:00:48.065	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:00:48.062	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:00:48.060	error	Client in error state.
    modbus.1
    	2023-03-12 10:00:48.059	error	Request timed out.
    modbus.1
    	2023-03-12 10:00:48.059	warn	Error: undefined
    modbus.1
    	2023-03-12 10:00:43.051	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:00:43.051	debug	Initialization of scale factors done!
    modbus.1
    	2023-03-12 10:00:43.048	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:00:43.047	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:00:42.756	debug	Initialize Objects for holdingRegs: []
    modbus.1
    	2023-03-12 10:00:42.756	debug	Add inputRegisters.3.40072_Amps: {"_id":"inputRegisters.3.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.1
    	2023-03-12 10:00:42.754	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.3.40072_Amps"}]
    modbus.1
    	2023-03-12 10:00:42.754	debug	Initialize Objects for coils: []
    modbus.1
    	2023-03-12 10:00:42.753	debug	Initialize Objects for disInputs: []
    modbus.1
    	2023-03-12 10:00:42.564	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
    modbus.1
    	2023-03-12 10:00:42.142	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.1
    	2023-03-12 10:00:42.018	debug	States connected to redis: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:00:41.937	debug	States create User PubSub Client
    modbus.1
    	2023-03-12 10:00:41.934	debug	States create System PubSub Client
    modbus.1
    	2023-03-12 10:00:41.911	debug	Redis States: Use Redis connection: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:00:41.867	debug	Objects connected to redis: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:00:41.859	debug	Objects client initialize lua scripts
    modbus.1
    	2023-03-12 10:00:41.783	debug	Objects create User PubSub Client
    modbus.1
    	2023-03-12 10:00:41.781	debug	Objects create System PubSub Client
    modbus.1
    	2023-03-12 10:00:41.733	debug	Objects client ready ... initialize now
    modbus.1
    	2023-03-12 10:00:41.674	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:00:37.089	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.1
    	2023-03-12 10:00:37.088	debug	Plugin sentry destroyed
    modbus.1
    	2023-03-12 10:00:37.087	info	terminating
    modbus.1
    	2023-03-12 10:00:37.083	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:00:37.080	info	Got terminate signal TERMINATE_YOURSELF
    modbus.1
    	2023-03-12 10:00:19.692	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 10:00:19.690	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:00:18.701	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 10:00:18.700	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 10:00:18.699	debug	Socket closed with error
    modbus.1
    	2023-03-12 10:00:18.694	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 10:00:18.691	error	Client in error state.
    modbus.1
    	2023-03-12 10:00:18.690	error	Request timed out.
    modbus.1
    	2023-03-12 10:00:18.689	warn	Error: undefined
    modbus.1
    	2023-03-12 10:00:13.677	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
    modbus.1
    	2023-03-12 10:00:13.675	debug	Initialization of scale factors done!
    modbus.1
    	2023-03-12 10:00:13.672	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 10:00:13.670	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 10:00:13.216	debug	Remove old object modbus.1.inputRegisters.3.10071_Amps
    modbus.1
    	2023-03-12 10:00:13.144	debug	Initialize Objects for holdingRegs: []
    modbus.1
    	2023-03-12 10:00:13.143	debug	Add inputRegisters.3.40072_Amps: {"_id":"inputRegisters.3.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.1
    	2023-03-12 10:00:13.141	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.3.40072_Amps"}]
    modbus.1
    	2023-03-12 10:00:13.140	debug	Initialize Objects for coils: []
    modbus.1
    	2023-03-12 10:00:13.135	debug	Initialize Objects for disInputs: []
    modbus.1
    	2023-03-12 10:00:12.801	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
    modbus.1
    	2023-03-12 10:00:12.019	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.1
    	2023-03-12 10:00:11.851	debug	States connected to redis: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:00:11.726	debug	States create User PubSub Client
    modbus.1
    	2023-03-12 10:00:11.717	debug	States create System PubSub Client
    modbus.1
    	2023-03-12 10:00:11.682	debug	Redis States: Use Redis connection: 127.0.0.1:9000
    modbus.1
    	2023-03-12 10:00:11.615	debug	Objects connected to redis: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:00:11.598	debug	Objects client initialize lua scripts
    modbus.1
    	2023-03-12 10:00:11.506	debug	Objects create User PubSub Client
    modbus.1
    	2023-03-12 10:00:11.503	debug	Objects create System PubSub Client
    modbus.1
    	2023-03-12 10:00:11.496	debug	Objects client ready ... initialize now
    modbus.1
    	2023-03-12 10:00:11.365	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
    modbus.1
    	2023-03-12 10:00:06.092	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.1
    	2023-03-12 10:00:06.091	debug	Plugin sentry destroyed
    modbus.1
    	2023-03-12 10:00:06.090	info	terminating
    modbus.1
    	2023-03-12 10:00:06.086	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 10:00:06.084	info	Got terminate signal TERMINATE_YOURSELF
    modbus.1
    	2023-03-12 09:59:50.034	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 09:59:50.032	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 09:59:49.039	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 09:59:49.038	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 09:59:49.037	debug	Socket closed with error
    modbus.1
    	2023-03-12 09:59:49.034	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 09:59:49.033	error	Client in error state.
    modbus.1
    	2023-03-12 09:59:49.032	error	Request timed out.
    modbus.1
    	2023-03-12 09:59:49.031	warn	Error: undefined
    modbus.1
    	2023-03-12 09:59:44.023	debug	[DevID_3/inputRegs] Poll address 10071 - 1 registers
    modbus.1
    	2023-03-12 09:59:44.022	debug	Initialization of scale factors done!
    modbus.1
    	2023-03-12 09:59:44.020	debug	[DevID_3] Poll start ---------------------
    modbus.1
    	2023-03-12 09:59:44.019	info	Connected to slave 192.168.1.97
    modbus.1
    	2023-03-12 09:59:43.765	debug	Remove old object modbus.1.inputRegisters.3.40072_Amps
    modbus.1
    	2023-03-12 09:59:43.711	debug	Initialize Objects for holdingRegs: []
    modbus.1
    	2023-03-12 09:59:43.710	debug	Add inputRegisters.3.10071_Amps: {"_id":"inputRegisters.3.10071_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":10071,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
    modbus.1
    	2023-03-12 09:59:43.709	debug	Initialize Objects for inputRegs: [{"_address":10071,"deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":10071,"id":"inputRegisters.3.10071_Amps"}]
    modbus.1
    	2023-03-12 09:59:43.708	debug	Initialize Objects for coils: []
    modbus.1
    	2023-03-12 09:59:43.707	debug	Initialize Objects for disInputs: []
    modbus.1
    	2023-03-12 09:59:43.496	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
    modbus.1
    	2023-03-12 09:59:43.105	debug	Plugin sentry Initialize Plugin (enabled=true)
    modbus.1
    	2023-03-12 09:59:42.973	debug	States connected to redis: 127.0.0.1:9000
    modbus.1
    	2023-03-12 09:59:42.880	debug	States create User PubSub Client
    modbus.1
    	2023-03-12 09:59:42.878	debug	States create System PubSub Client
    modbus.1
    	2023-03-12 09:59:42.855	debug	Redis States: Use Redis connection: 127.0.0.1:9000
    modbus.1
    	2023-03-12 09:59:42.812	debug	Objects connected to redis: 127.0.0.1:9001
    modbus.1
    	2023-03-12 09:59:42.804	debug	Objects client initialize lua scripts
    modbus.1
    	2023-03-12 09:59:42.714	debug	Objects create User PubSub Client
    modbus.1
    	2023-03-12 09:59:42.713	debug	Objects create System PubSub Client
    modbus.1
    	2023-03-12 09:59:42.710	debug	Objects client ready ... initialize now
    modbus.1
    	2023-03-12 09:59:42.655	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
    modbus.1
    	2023-03-12 09:59:38.175	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
    modbus.1
    	2023-03-12 09:59:38.175	debug	Plugin sentry destroyed
    modbus.1
    	2023-03-12 09:59:38.173	info	terminating
    modbus.1
    	2023-03-12 09:59:38.170	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 09:59:38.168	info	Got terminate signal TERMINATE_YOURSELF
    modbus.1
    	2023-03-12 09:59:16.633	info	Disconnected from slave 192.168.1.97
    modbus.1
    	2023-03-12 09:59:16.632	debug	Closing client on purpose.
    modbus.1
    	2023-03-12 09:59:15.636	debug	Cleaning up request fifo.
    modbus.1
    	2023-03-12 09:59:15.635	debug	Clearing timeout of the current request.
    modbus.1
    	2023-03-12 09:59:15.635	debug	Socket closed with error
    modbus.1
    	2023-03-12 09:59:15.633	warn	Poll error count: 7 code: {"err":"timeout","timeout":5000}
    modbus.1
    	2023-03-12 09:59:15.632	error	Client in error state.
    modbus.1
    	2023-03-12 09:59:15.631	error	Request timed out.
    modbus.1
    	2023-03-12 09:59:15.631	warn	Error: undefined
    modbus.1
    	2023-03-12 09:59:10.630	debug	[DevID_3/inputRegs] Poll address 10071 - 1 registers
    modbus.1
    	2023-03-12 09:59:10.629	debug	[DevID_3] Poll start ---------------------
    • wendy2702W Offline
      wendy2702W Offline
      Jetzt noch das Register bei Holding und nicht Input eintragen, wie im Beispiel aus dem Link, und haken bei "Abfrage".
      Dann mal log bitte.
        Dann mal log bitte.
        S Online
        S Online
        stronoff
        @wendy2702
        v6.3.5
        2424
        Log-Größe: 299.8 KB
        Zeit
        Nachricht
        modbus.1
        	2023-03-12 10:22:06.962	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:22:06.961	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:22:05.964	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:22:05.964	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:22:05.963	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:22:05.961	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:22:05.960	error	Client in error state.
        modbus.1
        	2023-03-12 10:22:05.960	error	Request timed out.
        modbus.1
        	2023-03-12 10:22:05.959	warn	Error: undefined
        modbus.1
        	2023-03-12 10:22:00.958	debug	[DevID_3/holdingRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:22:00.958	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:22:00.957	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:21:00.954	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:21:00.953	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:20:59.958	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:20:59.958	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:20:59.957	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:20:59.955	warn	Poll error count: 2 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:20:59.954	error	Client in error state.
        modbus.1
        	2023-03-12 10:20:59.953	error	Request timed out.
        modbus.1
        	2023-03-12 10:20:59.952	warn	Error: undefined
        modbus.1
        	2023-03-12 10:20:54.950	debug	[DevID_3/holdingRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:20:54.950	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:20:54.948	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:54.945	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:54.944	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:19:53.950	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:19:53.949	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:19:53.948	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:19:53.945	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:19:53.944	error	Client in error state.
        modbus.1
        	2023-03-12 10:19:53.943	error	Request timed out.
        modbus.1
        	2023-03-12 10:19:53.942	warn	Error: undefined
        modbus.1
        	2023-03-12 10:19:48.934	debug	[DevID_3/holdingRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:19:48.933	debug	Initialization of scale factors done!
        modbus.1
        	2023-03-12 10:19:48.931	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:19:48.930	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:48.652	debug	Remove old object modbus.1.inputRegisters.40072_Amps
        modbus.1
        	2023-03-12 10:19:48.598	debug	Add holdingRegisters.40072_Amps: {"_id":"holdingRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
        modbus.1
        	2023-03-12 10:19:48.597	debug	Initialize Objects for holdingRegs: [{"_address":"40072","name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40072,"deviceId":3,"id":"holdingRegisters.40072_Amps"}]
        modbus.1
        	2023-03-12 10:19:48.596	debug	Initialize Objects for inputRegs: []
        modbus.1
        	2023-03-12 10:19:48.595	debug	Initialize Objects for coils: []
        modbus.1
        	2023-03-12 10:19:48.595	debug	Initialize Objects for disInputs: []
        modbus.1
        	2023-03-12 10:19:48.380	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
        modbus.1
        	2023-03-12 10:19:47.900	debug	Plugin sentry Initialize Plugin (enabled=true)
        modbus.1
        	2023-03-12 10:19:47.748	debug	States connected to redis: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:19:47.669	debug	States create User PubSub Client
        modbus.1
        	2023-03-12 10:19:47.667	debug	States create System PubSub Client
        modbus.1
        	2023-03-12 10:19:47.644	debug	Redis States: Use Redis connection: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:19:47.598	debug	Objects connected to redis: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:19:47.590	debug	Objects client initialize lua scripts
        modbus.1
        	2023-03-12 10:19:47.516	debug	Objects create User PubSub Client
        modbus.1
        	2023-03-12 10:19:47.514	debug	Objects create System PubSub Client
        modbus.1
        	2023-03-12 10:19:47.512	debug	Objects client ready ... initialize now
        modbus.1
        	2023-03-12 10:19:47.456	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:19:42.915	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
        modbus.1
        	2023-03-12 10:19:42.914	debug	Plugin sentry destroyed
        modbus.1
        	2023-03-12 10:19:42.913	info	terminating
        modbus.1
        	2023-03-12 10:19:42.910	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:19:42.908	info	Got terminate signal TERMINATE_YOURSELF
        modbus.1
        	2023-03-12 10:19:18.533	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:18.532	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:19:17.539	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:19:17.538	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:19:17.537	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:19:17.533	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:19:17.532	error	Client in error state.
        modbus.1
        	2023-03-12 10:19:17.531	error	Request timed out.
        modbus.1
        	2023-03-12 10:19:17.530	warn	Error: undefined
        modbus.1
        	2023-03-12 10:19:12.523	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:19:12.522	debug	Initialization of scale factors done!
        modbus.1
        	2023-03-12 10:19:12.519	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:19:12.518	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:12.206	debug	Add holdingRegisters.40072_Amps: {"_id":"holdingRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
        modbus.1
        	2023-03-12 10:19:12.206	debug	Initialize Objects for holdingRegs: [{"_address":"40072","name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40072,"deviceId":3,"id":"holdingRegisters.40072_Amps"}]
        modbus.1
        	2023-03-12 10:19:12.205	debug	Add inputRegisters.40072_Amps: {"_id":"inputRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
        modbus.1
        	2023-03-12 10:19:12.204	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.40072_Amps"}]
        modbus.1
        	2023-03-12 10:19:12.204	debug	Initialize Objects for coils: []
        modbus.1
        	2023-03-12 10:19:12.203	debug	Initialize Objects for disInputs: []
        modbus.1
        	2023-03-12 10:19:12.009	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
        modbus.1
        	2023-03-12 10:19:11.576	debug	Plugin sentry Initialize Plugin (enabled=true)
        modbus.1
        	2023-03-12 10:19:11.449	debug	States connected to redis: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:19:11.370	debug	States create User PubSub Client
        modbus.1
        	2023-03-12 10:19:11.368	debug	States create System PubSub Client
        modbus.1
        	2023-03-12 10:19:11.344	debug	Redis States: Use Redis connection: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:19:11.300	debug	Objects connected to redis: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:19:11.291	debug	Objects client initialize lua scripts
        modbus.1
        	2023-03-12 10:19:11.216	debug	Objects create User PubSub Client
        modbus.1
        	2023-03-12 10:19:11.214	debug	Objects create System PubSub Client
        modbus.1
        	2023-03-12 10:19:11.211	debug	Objects client ready ... initialize now
        modbus.1
        	2023-03-12 10:19:11.152	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:19:06.520	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
        modbus.1
        	2023-03-12 10:19:06.520	debug	Plugin sentry destroyed
        modbus.1
        	2023-03-12 10:19:06.518	info	terminating
        modbus.1
        	2023-03-12 10:19:06.515	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:19:06.513	info	Got terminate signal TERMINATE_YOURSELF
        modbus.1
        	2023-03-12 10:19:01.898	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:19:01.897	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:19:00.904	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:19:00.904	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:19:00.903	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:19:00.898	warn	Poll error count: 1 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:19:00.896	error	Client in error state.
        modbus.1
        	2023-03-12 10:19:00.896	error	Request timed out.
        modbus.1
        	2023-03-12 10:19:00.895	warn	Error: undefined
        modbus.1
        	2023-03-12 10:18:55.888	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:18:55.887	debug	Initialization of scale factors done!
        modbus.1
        	2023-03-12 10:18:55.885	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:18:55.884	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:18:55.579	debug	Add holdingRegisters.40072_Amps: {"_id":"holdingRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":40072,"deviceId":3,"type":"int16le","len":1,"offset":0,"factor":1,"poll":true}}
        modbus.1
        	2023-03-12 10:18:55.578	debug	Initialize Objects for holdingRegs: [{"_address":"40072","name":"Amps","description":"Amps","unit":"A","type":"int16le","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":"","cw":"","isScale":"","address":40072,"deviceId":3,"id":"holdingRegisters.40072_Amps"}]
        modbus.1
        	2023-03-12 10:18:55.578	debug	Add inputRegisters.40072_Amps: {"_id":"inputRegisters.40072_Amps","type":"state","common":{"name":"Amps","role":"level","type":"number","read":true,"write":false,"def":0,"unit":"A"},"native":{"regType":"inputRegs","address":40072,"deviceId":3,"type":"uint16be","len":1,"offset":0,"factor":1}}
        modbus.1
        	2023-03-12 10:18:55.576	debug	Initialize Objects for inputRegs: [{"_address":"40072","deviceId":3,"name":"Amps","description":"Amps","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":40072,"id":"inputRegisters.40072_Amps"}]
        modbus.1
        	2023-03-12 10:18:55.576	debug	Initialize Objects for coils: []
        modbus.1
        	2023-03-12 10:18:55.575	debug	Initialize Objects for disInputs: []
        modbus.1
        	2023-03-12 10:18:55.369	info	starting. Version 5.0.11 in /opt/iobroker/node_modules/iobroker.modbus, node: v16.19.0, js-controller: 4.0.23
        modbus.1
        	2023-03-12 10:18:54.876	debug	Plugin sentry Initialize Plugin (enabled=true)
        modbus.1
        	2023-03-12 10:18:54.752	debug	States connected to redis: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:18:54.706	debug	States create User PubSub Client
        modbus.1
        	2023-03-12 10:18:54.703	debug	States create System PubSub Client
        modbus.1
        	2023-03-12 10:18:54.639	debug	Redis States: Use Redis connection: 127.0.0.1:9000
        modbus.1
        	2023-03-12 10:18:54.590	debug	Objects connected to redis: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:18:54.581	debug	Objects client initialize lua scripts
        modbus.1
        	2023-03-12 10:18:54.501	debug	Objects create User PubSub Client
        modbus.1
        	2023-03-12 10:18:54.499	debug	Objects create System PubSub Client
        modbus.1
        	2023-03-12 10:18:54.497	debug	Objects client ready ... initialize now
        modbus.1
        	2023-03-12 10:18:54.436	debug	Redis Objects: Use Redis connection: 127.0.0.1:9001
        modbus.1
        	2023-03-12 10:18:49.962	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
        modbus.1
        	2023-03-12 10:18:49.961	debug	Plugin sentry destroyed
        modbus.1
        	2023-03-12 10:18:49.960	info	terminating
        modbus.1
        	2023-03-12 10:18:49.956	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:18:49.954	info	Got terminate signal TERMINATE_YOURSELF
        modbus.1
        	2023-03-12 10:17:50.318	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:17:50.318	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:17:49.322	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:17:49.321	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:17:49.321	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:17:49.319	warn	Poll error count: 10 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:17:49.319	error	Client in error state.
        modbus.1
        	2023-03-12 10:17:49.318	error	Request timed out.
        modbus.1
        	2023-03-12 10:17:49.318	warn	Error: undefined
        modbus.1
        	2023-03-12 10:17:44.317	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:17:44.316	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:17:44.315	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:16:44.313	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:16:44.313	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:16:43.323	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:16:43.322	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:16:43.322	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:16:43.314	warn	Poll error count: 9 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:16:43.313	error	Client in error state.
        modbus.1
        	2023-03-12 10:16:43.313	error	Request timed out.
        modbus.1
        	2023-03-12 10:16:43.312	warn	Error: undefined
        modbus.1
        	2023-03-12 10:16:38.311	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:16:38.310	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:16:38.309	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:15:38.307	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:15:38.307	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:15:37.311	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:15:37.311	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:15:37.310	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:15:37.308	warn	Poll error count: 8 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:15:37.307	error	Client in error state.
        modbus.1
        	2023-03-12 10:15:37.307	error	Request timed out.
        modbus.1
        	2023-03-12 10:15:37.306	warn	Error: undefined
        modbus.1
        	2023-03-12 10:15:32.304	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:15:32.303	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:15:32.302	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:14:32.299	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:14:32.299	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:14:31.303	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:14:31.303	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:14:31.302	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:14:31.300	warn	Poll error count: 7 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:14:31.299	error	Client in error state.
        modbus.1
        	2023-03-12 10:14:31.299	error	Request timed out.
        modbus.1
        	2023-03-12 10:14:31.298	warn	Error: undefined
        modbus.1
        	2023-03-12 10:14:26.297	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:14:26.296	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:14:26.296	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:13:26.292	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:13:26.292	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:13:25.300	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:13:25.299	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:13:25.299	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:13:25.293	warn	Poll error count: 6 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:13:25.292	error	Client in error state.
        modbus.1
        	2023-03-12 10:13:25.291	error	Request timed out.
        modbus.1
        	2023-03-12 10:13:25.291	warn	Error: undefined
        modbus.1
        	2023-03-12 10:13:20.288	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:13:20.288	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:13:20.287	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:12:20.284	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:12:20.283	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:12:19.287	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:12:19.286	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:12:19.286	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:12:19.284	warn	Poll error count: 5 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:12:19.283	error	Client in error state.
        modbus.1
        	2023-03-12 10:12:19.283	error	Request timed out.
        modbus.1
        	2023-03-12 10:12:19.282	warn	Error: undefined
        modbus.1
        	2023-03-12 10:12:14.281	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:12:14.280	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:12:14.279	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:11:14.277	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:11:14.276	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:11:13.280	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:11:13.280	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:11:13.280	debug	Socket closed with error
        modbus.1
        	2023-03-12 10:11:13.277	warn	Poll error count: 4 code: {"err":"timeout","timeout":5000}
        modbus.1
        	2023-03-12 10:11:13.276	error	Client in error state.
        modbus.1
        	2023-03-12 10:11:13.276	error	Request timed out.
        modbus.1
        	2023-03-12 10:11:13.275	warn	Error: undefined
        modbus.1
        	2023-03-12 10:11:08.274	debug	[DevID_3/inputRegs] Poll address 40072 - 1 registers
        modbus.1
        	2023-03-12 10:11:08.273	debug	[DevID_3] Poll start ---------------------
        modbus.1
        	2023-03-12 10:11:08.273	info	Connected to slave 192.168.1.97
        modbus.1
        	2023-03-12 10:10:08.270	info	Disconnected from slave 192.168.1.97
        modbus.1
        	2023-03-12 10:10:08.269	debug	Closing client on purpose.
        modbus.1
        	2023-03-12 10:10:07.275	debug	Cleaning up request fifo.
        modbus.1
        	2023-03-12 10:10:07.275	debug	Clearing timeout of the current request.
        modbus.1
        	2023-03-12 10:10:07.274	debug	Socket closed with error
        • S stronoff
          @wendy2702
          v6.3.5
          2424
          Log-Größe: 299.8 KB
          Zeit
          Nachricht
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          modbus.1
          wendy2702W Offline
          wendy2702W Offline
          @stronoff Hm,
          die Auswahl Anzahl Bits im Waveshare mit "8" ist ja nirgendwo dokumentiert, könnte also falsch sein.
          Wie ist die Verbindung zwischen Waveshare und Kaco aufgebaut?
            @stronoff Hm,
            S Online
            S Online
            stronoff
            schrieb am zuletzt editiert von stronoff
            @wendy2702
            Der Elektriker hat ein Patch Kabel aufgeschnitten und den Stecker am Kaco eingesteckt und PIN1 und 2 am Waveshare "verschraubt".
            Der Waveshare blinkt auch immer "Active" wenn am Kaco die Kommunikations LED blinkt.
            • S stronoff
              @wendy2702
              wendy2702W Offline
              wendy2702W Offline
              @stronoff wäre ein Versuch wert am Waveshare mal zu tauschen.
              S 3 Antworten Letzte Antwort
                S Online
                S Online
                stronoff
                @wendy2702
                Habe ich auch schon überlegt.
                Werd's mal probieren.
                  S Online
                  S Online
                  stronoff
                  @wendy2702
                  Danke Dir auf jeden Fall schon mal für Deine Unterstützung!
                    S Online
                    S Online
                    stronoff
                    @wendy2702
                    Heute war der Elektriker da und ich konnte das erste Mal hinter die Abdeckung sehen ;-)
                    Wir haben die Anschlüsse "durchgepiepst" und es war erst mal alles so, wie es gemäß Kaco Beschreibung sein sollte:
                    Mir fiel allerdings auf, dass die Ummantelung des Netzwerkkabels nicht am Waveshare angeschlossen war. Laut Elektriker unrelevant, ich wollte es aber trotzdem austesten und habe daher die Ummantelung (siehe Pfeile) anbringen lassen:
                    Ich habe die Anschlüsse daher jetzt erstmal nicht tauschen lassen. Ich kann leider erst am Samstag und Sonntag wieder testen. Wenn's nicht funktioniert, würde ich als nächstes 485A und 485B tauschen.
                    Was meinst Du? Ist die Verkabelung soweit OK oder ist aus Deiner Sicht ein Fehler vorhanden?
                    In der Anleitung stand noch was von einem Abschlusswiderstand.
                    Ist das für meine Verkabelung relevant? Laut Elektriker nicht, ich werde daraus aber nicht schlüssig...
                    • S stronoff
                      @wendy2702
                      wendy2702W Offline
                      wendy2702W Offline
                      @stronoff Weiss nicht wie lang das Kabel zwischen Waveshare und Kaco ist aber eigentlich reichen dann zwei drähte.
                      Ich habe bei mir ca. 1m dazwischen, alte IYSTY Kabel und davon ein Adernpaar genommen.
                        S Online
                        S Online
                        stronoff
                        @wendy2702
                        Ist bei mir auch nur ein Meter.
                        Werde morgen und am Sonntag weiter testen...
                        • wierer-sigiW Offline
                          wierer-sigi
                          Hallo in die Runde,
                          seit Ihr mit der installation weiter gekommen, und läuft diese Lösung mit KACO und iobroker?
                          Überlege auch den KACO 10 NX2 mit Waveshare in den Iobroker zu bekommen, gefällt mir besser als mit Shelly EM3 und Zangen auszulesen.
                          • wierer-sigiW wierer-sigi
                            Hallo in die Runde,
                            HomoranH Offline
                            HomoranH Offline
                            @wierer-sigi warum in zwei Threads?
                            wierer-sigiW 1 Antwort Letzte Antwort
                              wierer-sigi
                              @homoran sagte in Kaco Blueplanet NX3 M2->RS485 TO POE ETH an Modbus Problem:
                              Sorry - hatte erst wegen der Anbindung zur direkten Anbindung via Modbus Adapter im iobroker gefragt. Dann aber in diesem Teil erfahren das dies direkt wohl nicht klappt aber über in diesen Thread beschriebenen Waveshare RS485 TO POE adapter doch eine Möglichkeit gibt.
                                Mitch23
                                @wierer-sigi
                                Der Kaco WR lässt sich direkt abfragen, wenn eine WLAN-Verbindung eingerichtet ist. Ein RS485 Adapter auf TCP ist nicht nötig. Die Einstellung habe ich in deinem anderen Thread gepostet.
                                • M Mitch23
                                  @wierer-sigi
                                  jvkronenberg78
                                  @mitch23 sagte in Kaco Blueplanet NX3 M2->RS485 TO POE ETH an Modbus Problem:
                                  @wierer-sigi
                                  Hi, ich nutze den WLAN Stick von Kaco. Kannst du mir sagen, wie ich per WLAN die Daten in den ioBroker bekomme? Habe keinen Adapter dafür gefunden, oder verstehe ich dich da falsch?