  4. Heidelberg Wallbox Energy Control per Modbus verbunden?

NEWS

  • Neuer Blogbeitrag: Monatsrückblick - Dezember 2025 🎄
    BluefoxB
    Bluefox
    11
    1
    324

  • Weihnachtsangebot 2025! 🎄
    BluefoxB
    Bluefox
    24
    1
    1.5k

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    9.5k

Heidelberg Wallbox Energy Control per Modbus verbunden?

Geplant Angeheftet Gesperrt Verschoben Hardware
16 Beiträge 8 Kommentatoren 9.8k Aufrufe 8 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • H herr_kuschel

    Hallo,

    eigentlich sagt der Titel schon alles.... Nein, im Ernst. Da sicherlich viele Menschen zukünftig Wallboxen installieren und diese intelligent sein sollen (Stichwort PV; Nachtstrom ..) wäre es sehr hilfreich, wenn dazu Anleitungen und Hilfestellungen hier anzuschauen wären. Auch Hinweise auf funktionierende Hardware wären Gold wert.

    Deshalb, die Frage, wer hat schon installiert und würde seine Erfahrungen hier posten, damit auch Anfänger wie ich, eine Installation bewerkstelligen können..... :)

    LG

    H Offline
    H Offline
    herr_kuschel
    schrieb am zuletzt editiert von
    #2

    @herr_kuschel
    Ist keiner bereit?

    N 2 Antworten Letzte Antwort
    0
    • H herr_kuschel

      @herr_kuschel
      Ist keiner bereit?

      N Offline
      N Offline
      NewPaint2
      schrieb am zuletzt editiert von
      #3

      @herr_kuschel Steht bei mir nächstes WE auf dem Plan, versuche mich im Modbus-Netz mit Zwischenstromzählern und der Heidelberg EC Europa an einem Modbus über W-Lan. Die Europa-Box sollte gleich der EC sein. Wenn ich was zum "klingeln" gebracht habe poste ich alles, ich hoffe mal das der Modbus-Adapter Einstellungssicherungen dafür bereithält. Die Registereintragungen scheinen hier eher das Problem zu sein wo keiner so recht durchsteigt.
      Also etwas Geduld - ich denke hier werden noch mehr dieses Problem bekommen und ohne den teuren "Sunnyboy" was stricken zu wollen, wenn Iobroker schon da ist. Es gibt eine recht gute Beschreibung von Matthias Kleine (haus-automatisierung.com) auf Youtube wo aber leider die falsche Box dahinter ist, aber man kann sich ja lang hangeln und seine Filme sind echt sehenswert. Mein Elektriker hat schon abgewunken wo er nur BUS gehört hat (Corona bedingt sind alle Weiterbildungen ausgefallen). Also selber forschen... Teile sind alle bestellt... kann also losgehen.

      1 Antwort Letzte Antwort
      0
      • H herr_kuschel

        @herr_kuschel
        Ist keiner bereit?

        N Offline
        N Offline
        NewPaint2
        schrieb am zuletzt editiert von
        #4

        @herr_kuschel so geschafft, mal wieder was zum knaubeln gehabt (-; :

        Hardware:

        • Zweirichtungszähler (60A) mit Modbus Schnittstelle. Ich habe den Eastron SDM72D-M für knapp 60 Euro gekauft.
        • Modbus TCP/IP Master WIFI (230V) von Hösi (kam auch um die 60 Euro)
        • FI Schalter, Sicherungen usw. für eine kleine Unterverteilung
        • Die Heidelberg EC-Wallbox
        • Cat6 Kabel (bitte nehmt kein Ysti)

        948f6db1-b26d-4bf2-9c21-b6768c4a3d96.jpg 740ba995-718e-4393-8814-00d3cd7089ce.jpg

        Über das Verkabeln von Zähler, Fi-Schalter und Sicherungen lasse ich mich nicht aus, das sollte bekannt sein. Bitte darauf achten, dass der Cat6-Schirm einen geerdeten Nullleiter bekommt und nur an einer Seite des RS485-Buses verklemmt wird. Der Zwischenzähler und die Wallbox haben einen Anschluss dafür. Bitte messt auch, ob ihr die 120 Ohm am Anfang und am Ende eurer Busverkabelung messen könnt. Hier gibt es leider keine richtige Handhabe, das muss man echt messen und versuchen.

        Software, eine laufende Instanz von IOBrocker.Modbus (Version 3.4.14)
        mit folgenden Einstellungen kommen die Werte vom Zwischenzähler (ID3) und von der Heidelberg Wallbox EC (ID2):

        Im Modbus-Adapter auf TCP..., die IP Nummer eintragen, und bei Gerätetyp auf Master. Nur den Haken bei "Aliases benutzen" setzen,

        Bildschirmfoto 2021-10-31 um 11.13.24.png

        dann zum Reiter Eingangsregister wechseln

        Bildschirmfoto 2021-10-31 um 11.13.47.png

        auf den "Kopf" drücken und danach auf die "Pfeile" und die Daten einfügen:

        _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
        30005	2	Modbus Register-Layouts Version	Modbus Register-Layouts Version		uint16be	1	1	0		value		true	false
        30006	2	charging state	charging state		uint16be	1	1	0		value		true	false
        30007	2	L1 - Current RMS	L1 - Current RMS		uint16be	1	1	0		value		true	false
        30008	2	L2 - Current RMS	L2 - Current RMS		uint16be	1	1	0		value		true	false
        30009	2	L3 - Current RMS	L3 - Current RMS		uint16be	1	1	0		value		true	false
        30010	2	PCB-Temperatur	PCB-Temperatur	°C	int16be	1	0,1	0		value		true	false
        30011	2	Voltage L1 - N rms in Volt	Voltage L1 - N rms in Volt	V	uint16be	1	1	0		value		true	false
        30012	2	Voltage L2 - N rms in Volt	Voltage L2 - N rms in Volt	V	uint16be	1	1	0		value		true	false
        30013	2	Voltage L3 - N rms in Volt	Voltage L3 - N rms in Volt	V	uint16be	1	1	0		value		true	false
        30014	2	extern lock state	extern lock state		uint16be	1	1	0		value		true	false
        30015	2	Power (L1+L2+L3) in VA	Power (L1+L2+L3) in VA	VA	uint16be	1	1	0		value		true	false
        30016	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
        30017	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
        30018	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
        30019	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
        30101	2	Hardware configuration maximal current	Hardware configuration maximal current	A	uint16be	1	1	0		value		true	false
        30102	2	Hardware configuration minimal current	Hardware configuration minimal current	A	uint16be	1	1	0		value		true	false
        30201	2	Hardware-Variant	Hardware-Variant		uint16be	1	1	0		value		true	false
        30204	2	Application Software svn-revNo	Application Software svn-revNo		uint16be	1	1	0		value		true	false
        30001	3	Phase 1 line neutral volts	Phase 1 line neutral volts	V	floatbe	2	1	0		state		true	false
        30003	3	Phase 2 line neutral volts	Phase 2 line neutral volts	V	floatbe	2	1	0		state		true	false
        30005	3	Phase 3 line neutral volts	Phase 3 line neutral volts	V	floatbe	2	1	0		state		true	false
        30007	3	Phase 1 current	Phase 1 current	A	floatbe	2	1	0		state		true	false
        30009	3	Phase 2 current	Phase 2 current	A	floatbe	2	1	0		state		true	false
        30011	3	Phase 3 current	Phase 3 current	A	floatbe	2	1	0		state		true	false
        30013	3	Phase 1 activ power	Phase 1 activ power	W	floatbe	2	1	0		state		true	false
        30015	3	Phase 2 activ power	Phase 2 activ power	W	floatbe	2	1	0		state		true	false
        30017	3	Phase 3 activ power	Phase 3 activ power	W	floatbe	2	1	0		state		true	false
        30019	3	Phase 1 apparent power	Phase 1 apparent power	VA	floatbe	2	1	0		state		true	false
        30021	3	Phase 2 apparent power	Phase 2 apparent power	VA	floatbe	2	1	0		state		true	false
        30023	3	Phase 3 apparent power	Phase 3 apparent power	VA	floatbe	2	1	0		state		true	false
        30025	3	Phase 1 reactiv power	Phase 1 reactiv power	VAr	floatbe	2	1	0		state		true	false
        30027	3	Phase 2 reactiv power	Phase 2 reactiv power	VAr	floatbe	2	1	0		state		true	false
        30029	3	Phase 3 reactiv power	Phase 3 reactiv power	VAr	floatbe	2	1	0		state		true	false
        30031	3	Phase 1 power factor (1)	Phase 1 power factor (1)		floatbe	2	1	0		state		true	false
        30033	3	Phase 2 power factor (1)	Phase 2 power factor (1)		floatbe	2	1	0		state		true	false
        30035	3	Phase 3 power factor (1)	Phase 3 power factor (1)		floatbe	2	1	0		state		true	false
        30043	3	Average line to neutral volts	Average line to neutral volts	V	floatbe	2	1	0		state		true	false
        30047	3	Averange line current	Averange line current	A	floatbe	2	1	0		state		true	false
        30049	3	Sum of line currents	Sum of line currents	A	floatbe	2	1	0		state		true	false
        30053	3	Total system power	Total system power	W	floatbe	2	1	0		state		true	false
        30057	3	Total system volt amps	Total system volt amps	VA	floatbe	2	1	0		state		true	false
        30061	3	Total system VAr	Total system VAr	VAr	floatbe	2	1	0		state		true	false
        30063	3	Total systems power factor (1)	Total systems power factor (1)		floatbe	2	1	0		state		true	false
        30071	3	Frequency of supply voltages	Total systems power factor (1)	Hz	floatbe	2	1	0		state		true	false
        30073	3	Import active energy	Import active energy	kWh	floatbe	2	1	0		state		true	false
        30075	3	Export active energy	Export active energy	kWh	floatbe	2	1	0		state		true	false
        30201	3	Line 1 to Line 2 volts	Line 1 to Line 2 volts	V	floatbe	2	1	0		state		true	false
        30203	3	Line 2 to Line 3 volts	Line 2 to Line 3 volts	V	floatbe	2	1	0		state		true	false
        30205	3	Line 3 to Line 1 volts	Line 3 to Line 1 volts	V	floatbe	2	1	0		state		true	false
        30207	3	Average line to line volts	Average line to line volts	V	floatbe	2	1	0		state		true	false
        30225	3	Neutral current	Neutral current	A	floatbe	2	1	0		state		true	false
        30343	3	Total active Energy (2)	Total active Energy (2)	kWh	floatbe	2	1	0		state		true	false
        30345	3	Total reactive energy	Total reactive energy	kVArh	floatbe	2	1	0		state		true	false
        30385	3	resettable total active energy	resettable total active energy	kWh	floatbe	2	1	0		state		true	false
        30389	3	resettable import active energy	resettable import active energy	kWh	floatbe	2	1	0		state		true	false
        30391	3	resettable export active energy	resettable export active energy	kWh	floatbe	2	1	0		state		true	false
        30397	3	Net kWh (Import - Export)	Net kWh (Import - Export)	kWh	floatbe	2	1	0		state		true	false
        31281	3	Total import active power	Total import active power	W	floatbe	2	1	0		state		true	false
        31283	3	Total export active power	Total export active power	W	floatbe	2	1	0		state		true	false
        

        Solltet ihr andere Geräte-ID's verwenden, diese dann bitte anpassen!

        Inhalt für das Holdingregister:

        Bildschirmfoto 2021-10-31 um 11.13.59.png

        wieder wie oben, auf den "Kopf" klicken und dann auf die "Pfeile":

        _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
        40258	2	ModBus-Master WatchDog Timeout in ms	ModBus-Master WatchDog Timeout in ms		uint16be	1	1	15000		value		true	false	false	false
        40259	2	Standby FunktionControl	Standby FunktionControl		uint16be	1	1	4		value		false	false	true	false
        40260	2	Remote Look	Remote Look		uint16be	1	1	1		value		true	false	false	false
        40262	2	Maximal current command	Maximal current command		uint16be	1	1	60		value		true	false	true	false
        40263	2	FailSafe Current configuration	FailSafe Current configuration		uint16be	1	1	60		value		true	false	false	false
        

        Wie oben auch ändert die Geräte ID's nach euren Einstellungen!

        So, jetzt wird es etwas kompliziert: Die Box geht nach etwa 5 Minuten in den Standbye, wenn kein Fahrzeug dran steckt: Im Standbye meldet sich die Box ab und der Modbus-Adapter schaut etwa jede Minute nach, ob sich was tut und überträgt Daten vom Zwischenzähler. Werte von der Box kommen nur, wenn ihr diese frisch mit Strom versorgt oder ein Fahrzeug dran ist.

        Da ich noch keine PV-Überschuss-Ladung machen kann, sollte der Wert bei Maximal Current Command eingetragen werden.

        So, ich hoffe, dass ihr etwas schneller als ich zum Erfolg kommt!
        Beste Grüße aus Zwickau!

        H M 2 Antworten Letzte Antwort
        1
        • N NewPaint2

          @herr_kuschel so geschafft, mal wieder was zum knaubeln gehabt (-; :

          Hardware:

          • Zweirichtungszähler (60A) mit Modbus Schnittstelle. Ich habe den Eastron SDM72D-M für knapp 60 Euro gekauft.
          • Modbus TCP/IP Master WIFI (230V) von Hösi (kam auch um die 60 Euro)
          • FI Schalter, Sicherungen usw. für eine kleine Unterverteilung
          • Die Heidelberg EC-Wallbox
          • Cat6 Kabel (bitte nehmt kein Ysti)

          948f6db1-b26d-4bf2-9c21-b6768c4a3d96.jpg 740ba995-718e-4393-8814-00d3cd7089ce.jpg

          Über das Verkabeln von Zähler, Fi-Schalter und Sicherungen lasse ich mich nicht aus, das sollte bekannt sein. Bitte darauf achten, dass der Cat6-Schirm einen geerdeten Nullleiter bekommt und nur an einer Seite des RS485-Buses verklemmt wird. Der Zwischenzähler und die Wallbox haben einen Anschluss dafür. Bitte messt auch, ob ihr die 120 Ohm am Anfang und am Ende eurer Busverkabelung messen könnt. Hier gibt es leider keine richtige Handhabe, das muss man echt messen und versuchen.

          Software, eine laufende Instanz von IOBrocker.Modbus (Version 3.4.14)
          mit folgenden Einstellungen kommen die Werte vom Zwischenzähler (ID3) und von der Heidelberg Wallbox EC (ID2):

          Im Modbus-Adapter auf TCP..., die IP Nummer eintragen, und bei Gerätetyp auf Master. Nur den Haken bei "Aliases benutzen" setzen,

          Bildschirmfoto 2021-10-31 um 11.13.24.png

          dann zum Reiter Eingangsregister wechseln

          Bildschirmfoto 2021-10-31 um 11.13.47.png

          auf den "Kopf" drücken und danach auf die "Pfeile" und die Daten einfügen:

          _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
          30005	2	Modbus Register-Layouts Version	Modbus Register-Layouts Version		uint16be	1	1	0		value		true	false
          30006	2	charging state	charging state		uint16be	1	1	0		value		true	false
          30007	2	L1 - Current RMS	L1 - Current RMS		uint16be	1	1	0		value		true	false
          30008	2	L2 - Current RMS	L2 - Current RMS		uint16be	1	1	0		value		true	false
          30009	2	L3 - Current RMS	L3 - Current RMS		uint16be	1	1	0		value		true	false
          30010	2	PCB-Temperatur	PCB-Temperatur	°C	int16be	1	0,1	0		value		true	false
          30011	2	Voltage L1 - N rms in Volt	Voltage L1 - N rms in Volt	V	uint16be	1	1	0		value		true	false
          30012	2	Voltage L2 - N rms in Volt	Voltage L2 - N rms in Volt	V	uint16be	1	1	0		value		true	false
          30013	2	Voltage L3 - N rms in Volt	Voltage L3 - N rms in Volt	V	uint16be	1	1	0		value		true	false
          30014	2	extern lock state	extern lock state		uint16be	1	1	0		value		true	false
          30015	2	Power (L1+L2+L3) in VA	Power (L1+L2+L3) in VA	VA	uint16be	1	1	0		value		true	false
          30016	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
          30017	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
          30018	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
          30019	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
          30101	2	Hardware configuration maximal current	Hardware configuration maximal current	A	uint16be	1	1	0		value		true	false
          30102	2	Hardware configuration minimal current	Hardware configuration minimal current	A	uint16be	1	1	0		value		true	false
          30201	2	Hardware-Variant	Hardware-Variant		uint16be	1	1	0		value		true	false
          30204	2	Application Software svn-revNo	Application Software svn-revNo		uint16be	1	1	0		value		true	false
          30001	3	Phase 1 line neutral volts	Phase 1 line neutral volts	V	floatbe	2	1	0		state		true	false
          30003	3	Phase 2 line neutral volts	Phase 2 line neutral volts	V	floatbe	2	1	0		state		true	false
          30005	3	Phase 3 line neutral volts	Phase 3 line neutral volts	V	floatbe	2	1	0		state		true	false
          30007	3	Phase 1 current	Phase 1 current	A	floatbe	2	1	0		state		true	false
          30009	3	Phase 2 current	Phase 2 current	A	floatbe	2	1	0		state		true	false
          30011	3	Phase 3 current	Phase 3 current	A	floatbe	2	1	0		state		true	false
          30013	3	Phase 1 activ power	Phase 1 activ power	W	floatbe	2	1	0		state		true	false
          30015	3	Phase 2 activ power	Phase 2 activ power	W	floatbe	2	1	0		state		true	false
          30017	3	Phase 3 activ power	Phase 3 activ power	W	floatbe	2	1	0		state		true	false
          30019	3	Phase 1 apparent power	Phase 1 apparent power	VA	floatbe	2	1	0		state		true	false
          30021	3	Phase 2 apparent power	Phase 2 apparent power	VA	floatbe	2	1	0		state		true	false
          30023	3	Phase 3 apparent power	Phase 3 apparent power	VA	floatbe	2	1	0		state		true	false
          30025	3	Phase 1 reactiv power	Phase 1 reactiv power	VAr	floatbe	2	1	0		state		true	false
          30027	3	Phase 2 reactiv power	Phase 2 reactiv power	VAr	floatbe	2	1	0		state		true	false
          30029	3	Phase 3 reactiv power	Phase 3 reactiv power	VAr	floatbe	2	1	0		state		true	false
          30031	3	Phase 1 power factor (1)	Phase 1 power factor (1)		floatbe	2	1	0		state		true	false
          30033	3	Phase 2 power factor (1)	Phase 2 power factor (1)		floatbe	2	1	0		state		true	false
          30035	3	Phase 3 power factor (1)	Phase 3 power factor (1)		floatbe	2	1	0		state		true	false
          30043	3	Average line to neutral volts	Average line to neutral volts	V	floatbe	2	1	0		state		true	false
          30047	3	Averange line current	Averange line current	A	floatbe	2	1	0		state		true	false
          30049	3	Sum of line currents	Sum of line currents	A	floatbe	2	1	0		state		true	false
          30053	3	Total system power	Total system power	W	floatbe	2	1	0		state		true	false
          30057	3	Total system volt amps	Total system volt amps	VA	floatbe	2	1	0		state		true	false
          30061	3	Total system VAr	Total system VAr	VAr	floatbe	2	1	0		state		true	false
          30063	3	Total systems power factor (1)	Total systems power factor (1)		floatbe	2	1	0		state		true	false
          30071	3	Frequency of supply voltages	Total systems power factor (1)	Hz	floatbe	2	1	0		state		true	false
          30073	3	Import active energy	Import active energy	kWh	floatbe	2	1	0		state		true	false
          30075	3	Export active energy	Export active energy	kWh	floatbe	2	1	0		state		true	false
          30201	3	Line 1 to Line 2 volts	Line 1 to Line 2 volts	V	floatbe	2	1	0		state		true	false
          30203	3	Line 2 to Line 3 volts	Line 2 to Line 3 volts	V	floatbe	2	1	0		state		true	false
          30205	3	Line 3 to Line 1 volts	Line 3 to Line 1 volts	V	floatbe	2	1	0		state		true	false
          30207	3	Average line to line volts	Average line to line volts	V	floatbe	2	1	0		state		true	false
          30225	3	Neutral current	Neutral current	A	floatbe	2	1	0		state		true	false
          30343	3	Total active Energy (2)	Total active Energy (2)	kWh	floatbe	2	1	0		state		true	false
          30345	3	Total reactive energy	Total reactive energy	kVArh	floatbe	2	1	0		state		true	false
          30385	3	resettable total active energy	resettable total active energy	kWh	floatbe	2	1	0		state		true	false
          30389	3	resettable import active energy	resettable import active energy	kWh	floatbe	2	1	0		state		true	false
          30391	3	resettable export active energy	resettable export active energy	kWh	floatbe	2	1	0		state		true	false
          30397	3	Net kWh (Import - Export)	Net kWh (Import - Export)	kWh	floatbe	2	1	0		state		true	false
          31281	3	Total import active power	Total import active power	W	floatbe	2	1	0		state		true	false
          31283	3	Total export active power	Total export active power	W	floatbe	2	1	0		state		true	false
          

          Solltet ihr andere Geräte-ID's verwenden, diese dann bitte anpassen!

          Inhalt für das Holdingregister:

          Bildschirmfoto 2021-10-31 um 11.13.59.png

          wieder wie oben, auf den "Kopf" klicken und dann auf die "Pfeile":

          _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
          40258	2	ModBus-Master WatchDog Timeout in ms	ModBus-Master WatchDog Timeout in ms		uint16be	1	1	15000		value		true	false	false	false
          40259	2	Standby FunktionControl	Standby FunktionControl		uint16be	1	1	4		value		false	false	true	false
          40260	2	Remote Look	Remote Look		uint16be	1	1	1		value		true	false	false	false
          40262	2	Maximal current command	Maximal current command		uint16be	1	1	60		value		true	false	true	false
          40263	2	FailSafe Current configuration	FailSafe Current configuration		uint16be	1	1	60		value		true	false	false	false
          

          Wie oben auch ändert die Geräte ID's nach euren Einstellungen!

          So, jetzt wird es etwas kompliziert: Die Box geht nach etwa 5 Minuten in den Standbye, wenn kein Fahrzeug dran steckt: Im Standbye meldet sich die Box ab und der Modbus-Adapter schaut etwa jede Minute nach, ob sich was tut und überträgt Daten vom Zwischenzähler. Werte von der Box kommen nur, wenn ihr diese frisch mit Strom versorgt oder ein Fahrzeug dran ist.

          Da ich noch keine PV-Überschuss-Ladung machen kann, sollte der Wert bei Maximal Current Command eingetragen werden.

          So, ich hoffe, dass ihr etwas schneller als ich zum Erfolg kommt!
          Beste Grüße aus Zwickau!

          H Offline
          H Offline
          herr_kuschel
          schrieb am zuletzt editiert von
          #5

          @newpaint2
          Das sieht sehr gut aus. Ich habe auch einen Eaton installiert. Von diesem hole ich mir die Daten per Modbus (über den Elfin-ee11) in den Iobroker.
          Es hängt nur die WB an dem Zähler.

          Nun werde ich mich daran wagen, die WB an den Elfin-ee11 anzuklemmen....

          Danke für deine Unterstützung 😊😊😊👍

          S 1 Antwort Letzte Antwort
          1
          • H herr_kuschel

            @newpaint2
            Das sieht sehr gut aus. Ich habe auch einen Eaton installiert. Von diesem hole ich mir die Daten per Modbus (über den Elfin-ee11) in den Iobroker.
            Es hängt nur die WB an dem Zähler.

            Nun werde ich mich daran wagen, die WB an den Elfin-ee11 anzuklemmen....

            Danke für deine Unterstützung 😊😊😊👍

            S Offline
            S Offline
            steff393
            schrieb am zuletzt editiert von
            #6

            Ganz einfach geht das auch mit wbec für bis zu 16 Wallboxen:
            https://github.com/steff393/wbec

            1 Antwort Letzte Antwort
            0
            • N NewPaint2

              @herr_kuschel so geschafft, mal wieder was zum knaubeln gehabt (-; :

              Hardware:

              • Zweirichtungszähler (60A) mit Modbus Schnittstelle. Ich habe den Eastron SDM72D-M für knapp 60 Euro gekauft.
              • Modbus TCP/IP Master WIFI (230V) von Hösi (kam auch um die 60 Euro)
              • FI Schalter, Sicherungen usw. für eine kleine Unterverteilung
              • Die Heidelberg EC-Wallbox
              • Cat6 Kabel (bitte nehmt kein Ysti)

              948f6db1-b26d-4bf2-9c21-b6768c4a3d96.jpg 740ba995-718e-4393-8814-00d3cd7089ce.jpg

              Über das Verkabeln von Zähler, Fi-Schalter und Sicherungen lasse ich mich nicht aus, das sollte bekannt sein. Bitte darauf achten, dass der Cat6-Schirm einen geerdeten Nullleiter bekommt und nur an einer Seite des RS485-Buses verklemmt wird. Der Zwischenzähler und die Wallbox haben einen Anschluss dafür. Bitte messt auch, ob ihr die 120 Ohm am Anfang und am Ende eurer Busverkabelung messen könnt. Hier gibt es leider keine richtige Handhabe, das muss man echt messen und versuchen.

              Software, eine laufende Instanz von IOBrocker.Modbus (Version 3.4.14)
              mit folgenden Einstellungen kommen die Werte vom Zwischenzähler (ID3) und von der Heidelberg Wallbox EC (ID2):

              Im Modbus-Adapter auf TCP..., die IP Nummer eintragen, und bei Gerätetyp auf Master. Nur den Haken bei "Aliases benutzen" setzen,

              Bildschirmfoto 2021-10-31 um 11.13.24.png

              dann zum Reiter Eingangsregister wechseln

              Bildschirmfoto 2021-10-31 um 11.13.47.png

              auf den "Kopf" drücken und danach auf die "Pfeile" und die Daten einfügen:

              _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
              30005	2	Modbus Register-Layouts Version	Modbus Register-Layouts Version		uint16be	1	1	0		value		true	false
              30006	2	charging state	charging state		uint16be	1	1	0		value		true	false
              30007	2	L1 - Current RMS	L1 - Current RMS		uint16be	1	1	0		value		true	false
              30008	2	L2 - Current RMS	L2 - Current RMS		uint16be	1	1	0		value		true	false
              30009	2	L3 - Current RMS	L3 - Current RMS		uint16be	1	1	0		value		true	false
              30010	2	PCB-Temperatur	PCB-Temperatur	°C	int16be	1	0,1	0		value		true	false
              30011	2	Voltage L1 - N rms in Volt	Voltage L1 - N rms in Volt	V	uint16be	1	1	0		value		true	false
              30012	2	Voltage L2 - N rms in Volt	Voltage L2 - N rms in Volt	V	uint16be	1	1	0		value		true	false
              30013	2	Voltage L3 - N rms in Volt	Voltage L3 - N rms in Volt	V	uint16be	1	1	0		value		true	false
              30014	2	extern lock state	extern lock state		uint16be	1	1	0		value		true	false
              30015	2	Power (L1+L2+L3) in VA	Power (L1+L2+L3) in VA	VA	uint16be	1	1	0		value		true	false
              30016	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
              30017	2	Energy since PowerOn	Energy since PowerOn		uint16be	1	1	0		value		true	false
              30018	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
              30019	2	Energy since Installation	Energy since Installation		uint16be	1	1	0		value		true	false
              30101	2	Hardware configuration maximal current	Hardware configuration maximal current	A	uint16be	1	1	0		value		true	false
              30102	2	Hardware configuration minimal current	Hardware configuration minimal current	A	uint16be	1	1	0		value		true	false
              30201	2	Hardware-Variant	Hardware-Variant		uint16be	1	1	0		value		true	false
              30204	2	Application Software svn-revNo	Application Software svn-revNo		uint16be	1	1	0		value		true	false
              30001	3	Phase 1 line neutral volts	Phase 1 line neutral volts	V	floatbe	2	1	0		state		true	false
              30003	3	Phase 2 line neutral volts	Phase 2 line neutral volts	V	floatbe	2	1	0		state		true	false
              30005	3	Phase 3 line neutral volts	Phase 3 line neutral volts	V	floatbe	2	1	0		state		true	false
              30007	3	Phase 1 current	Phase 1 current	A	floatbe	2	1	0		state		true	false
              30009	3	Phase 2 current	Phase 2 current	A	floatbe	2	1	0		state		true	false
              30011	3	Phase 3 current	Phase 3 current	A	floatbe	2	1	0		state		true	false
              30013	3	Phase 1 activ power	Phase 1 activ power	W	floatbe	2	1	0		state		true	false
              30015	3	Phase 2 activ power	Phase 2 activ power	W	floatbe	2	1	0		state		true	false
              30017	3	Phase 3 activ power	Phase 3 activ power	W	floatbe	2	1	0		state		true	false
              30019	3	Phase 1 apparent power	Phase 1 apparent power	VA	floatbe	2	1	0		state		true	false
              30021	3	Phase 2 apparent power	Phase 2 apparent power	VA	floatbe	2	1	0		state		true	false
              30023	3	Phase 3 apparent power	Phase 3 apparent power	VA	floatbe	2	1	0		state		true	false
              30025	3	Phase 1 reactiv power	Phase 1 reactiv power	VAr	floatbe	2	1	0		state		true	false
              30027	3	Phase 2 reactiv power	Phase 2 reactiv power	VAr	floatbe	2	1	0		state		true	false
              30029	3	Phase 3 reactiv power	Phase 3 reactiv power	VAr	floatbe	2	1	0		state		true	false
              30031	3	Phase 1 power factor (1)	Phase 1 power factor (1)		floatbe	2	1	0		state		true	false
              30033	3	Phase 2 power factor (1)	Phase 2 power factor (1)		floatbe	2	1	0		state		true	false
              30035	3	Phase 3 power factor (1)	Phase 3 power factor (1)		floatbe	2	1	0		state		true	false
              30043	3	Average line to neutral volts	Average line to neutral volts	V	floatbe	2	1	0		state		true	false
              30047	3	Averange line current	Averange line current	A	floatbe	2	1	0		state		true	false
              30049	3	Sum of line currents	Sum of line currents	A	floatbe	2	1	0		state		true	false
              30053	3	Total system power	Total system power	W	floatbe	2	1	0		state		true	false
              30057	3	Total system volt amps	Total system volt amps	VA	floatbe	2	1	0		state		true	false
              30061	3	Total system VAr	Total system VAr	VAr	floatbe	2	1	0		state		true	false
              30063	3	Total systems power factor (1)	Total systems power factor (1)		floatbe	2	1	0		state		true	false
              30071	3	Frequency of supply voltages	Total systems power factor (1)	Hz	floatbe	2	1	0		state		true	false
              30073	3	Import active energy	Import active energy	kWh	floatbe	2	1	0		state		true	false
              30075	3	Export active energy	Export active energy	kWh	floatbe	2	1	0		state		true	false
              30201	3	Line 1 to Line 2 volts	Line 1 to Line 2 volts	V	floatbe	2	1	0		state		true	false
              30203	3	Line 2 to Line 3 volts	Line 2 to Line 3 volts	V	floatbe	2	1	0		state		true	false
              30205	3	Line 3 to Line 1 volts	Line 3 to Line 1 volts	V	floatbe	2	1	0		state		true	false
              30207	3	Average line to line volts	Average line to line volts	V	floatbe	2	1	0		state		true	false
              30225	3	Neutral current	Neutral current	A	floatbe	2	1	0		state		true	false
              30343	3	Total active Energy (2)	Total active Energy (2)	kWh	floatbe	2	1	0		state		true	false
              30345	3	Total reactive energy	Total reactive energy	kVArh	floatbe	2	1	0		state		true	false
              30385	3	resettable total active energy	resettable total active energy	kWh	floatbe	2	1	0		state		true	false
              30389	3	resettable import active energy	resettable import active energy	kWh	floatbe	2	1	0		state		true	false
              30391	3	resettable export active energy	resettable export active energy	kWh	floatbe	2	1	0		state		true	false
              30397	3	Net kWh (Import - Export)	Net kWh (Import - Export)	kWh	floatbe	2	1	0		state		true	false
              31281	3	Total import active power	Total import active power	W	floatbe	2	1	0		state		true	false
              31283	3	Total export active power	Total export active power	W	floatbe	2	1	0		state		true	false
              

              Solltet ihr andere Geräte-ID's verwenden, diese dann bitte anpassen!

              Inhalt für das Holdingregister:

              Bildschirmfoto 2021-10-31 um 11.13.59.png

              wieder wie oben, auf den "Kopf" klicken und dann auf die "Pfeile":

              _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
              40258	2	ModBus-Master WatchDog Timeout in ms	ModBus-Master WatchDog Timeout in ms		uint16be	1	1	15000		value		true	false	false	false
              40259	2	Standby FunktionControl	Standby FunktionControl		uint16be	1	1	4		value		false	false	true	false
              40260	2	Remote Look	Remote Look		uint16be	1	1	1		value		true	false	false	false
              40262	2	Maximal current command	Maximal current command		uint16be	1	1	60		value		true	false	true	false
              40263	2	FailSafe Current configuration	FailSafe Current configuration		uint16be	1	1	60		value		true	false	false	false
              

              Wie oben auch ändert die Geräte ID's nach euren Einstellungen!

              So, jetzt wird es etwas kompliziert: Die Box geht nach etwa 5 Minuten in den Standbye, wenn kein Fahrzeug dran steckt: Im Standbye meldet sich die Box ab und der Modbus-Adapter schaut etwa jede Minute nach, ob sich was tut und überträgt Daten vom Zwischenzähler. Werte von der Box kommen nur, wenn ihr diese frisch mit Strom versorgt oder ein Fahrzeug dran ist.

              Da ich noch keine PV-Überschuss-Ladung machen kann, sollte der Wert bei Maximal Current Command eingetragen werden.

              So, ich hoffe, dass ihr etwas schneller als ich zum Erfolg kommt!
              Beste Grüße aus Zwickau!

              M Offline
              M Offline
              Martin12
              schrieb am zuletzt editiert von
              #7

              @newpaint2
              Hallo,
              Vielen Dank für deinen Post hier. Ich habe es mit mehreren Modus USB Sticks in der Vergangenheit versucht und nie eine Kommunikation erreicht. Mit dem RS485/TCP Converter von Hösi hat es dann einwandfrei und einfach funktioniert.
              Nur die Holdingregister habe ich bei etwas anders konfiguriert, damit diese schreibar waren.
              Ich habe aktuell 2 Heidelberg Wallboxen angeschlossen und die Kommunikation funktioniert.
              Die Überschussladung konnte ich ebenso mit einem Blockly Script realisieren.
              Zur Ermittlung des Überschuss habe ich separat einen Shelly 3EM im Einsatz.

              Objects.PNG Config3.PNG Config2.PNG Config1.PNG

              N 1 Antwort Letzte Antwort
              1
              • M Martin12

                @newpaint2
                Hallo,
                Vielen Dank für deinen Post hier. Ich habe es mit mehreren Modus USB Sticks in der Vergangenheit versucht und nie eine Kommunikation erreicht. Mit dem RS485/TCP Converter von Hösi hat es dann einwandfrei und einfach funktioniert.
                Nur die Holdingregister habe ich bei etwas anders konfiguriert, damit diese schreibar waren.
                Ich habe aktuell 2 Heidelberg Wallboxen angeschlossen und die Kommunikation funktioniert.
                Die Überschussladung konnte ich ebenso mit einem Blockly Script realisieren.
                Zur Ermittlung des Überschuss habe ich separat einen Shelly 3EM im Einsatz.

                Objects.PNG Config3.PNG Config2.PNG Config1.PNG

                N Offline
                N Offline
                NewPaint2
                schrieb am zuletzt editiert von
                #8

                @martin12 Hallo Martin, kannst du die veränderten Registereinstellungen hier mit reinstellen, Damit bleiben vielleicht Andere auch aktuell. Wenn du das PV-Script noch dazu packst wäre das für später super. Wenn es dir geholfen hat freue ich mich sehr etwas zurückgeben zu können.

                M 1 Antwort Letzte Antwort
                0
                • N NewPaint2

                  @martin12 Hallo Martin, kannst du die veränderten Registereinstellungen hier mit reinstellen, Damit bleiben vielleicht Andere auch aktuell. Wenn du das PV-Script noch dazu packst wäre das für später super. Wenn es dir geholfen hat freue ich mich sehr etwas zurückgeben zu können.

                  M Offline
                  M Offline
                  Martin12
                  schrieb am zuletzt editiert von
                  #9

                  @newpaint2
                  Config3.PNG
                  Im Holdingregister habe ich die Haken bei CW weggelassen. Die Werte wurden sonst sofort wieder auf 0 gesetzt.
                  Das Script muss ich zuerst noch bei Sonnenschein testen, die letzten Tage war dazu noch keine Gelgenheit

                  H R 2 Antworten Letzte Antwort
                  1
                  • H herr_kuschel

                    Hallo,

                    eigentlich sagt der Titel schon alles.... Nein, im Ernst. Da sicherlich viele Menschen zukünftig Wallboxen installieren und diese intelligent sein sollen (Stichwort PV; Nachtstrom ..) wäre es sehr hilfreich, wenn dazu Anleitungen und Hilfestellungen hier anzuschauen wären. Auch Hinweise auf funktionierende Hardware wären Gold wert.

                    Deshalb, die Frage, wer hat schon installiert und würde seine Erfahrungen hier posten, damit auch Anfänger wie ich, eine Installation bewerkstelligen können..... :)

                    LG

                    N Offline
                    N Offline
                    nitrox9
                    schrieb am zuletzt editiert von nitrox9
                    #10

                    @herr_kuschel sagte in Heidelberg Wallbox Energy Control per Modbus verbunden?:

                    Deshalb, die Frage, wer hat schon installiert und würde seine Erfahrungen hier posten, damit auch Anfänger wie ich, eine Installation bewerkstelligen können..... :)

                    Einen Artikel über meine erfolgreiche Inbetriebnahme von
                    "PV-Überschussladen mit Wallbox Heidelberg Energy Control über Modbus, ioBroker und Blockly"
                    ist hier zu finden:
                    https://forum.iobroker.net/topic/51751/heidelberg-energy-control-pv-laden-modbus-blockly

                    1 Antwort Letzte Antwort
                    0
                    • M Martin12

                      @newpaint2
                      Config3.PNG
                      Im Holdingregister habe ich die Haken bei CW weggelassen. Die Werte wurden sonst sofort wieder auf 0 gesetzt.
                      Das Script muss ich zuerst noch bei Sonnenschein testen, die letzten Tage war dazu noch keine Gelgenheit

                      H Offline
                      H Offline
                      Hefo
                      schrieb am zuletzt editiert von
                      #11

                      @martin12 @NewPaint2
                      Danke erst mal für die Register-Copy-Paste-Vorlagen! Das hat die Einrichtung stark vereinfacht.

                      Bei meinen zwei Wallboxen trat das Problem auf, dass sobald die Wallbox mit Modbus ID 1 in den Standby ging die Wallbox mit ID2 zwar noch regelmäßig ihre Daten in den Input Registern aktualisiert hat, ich aber keine Werte in den Holding Registern (z.B. Maximal Current) schreiben konnte.

                      Abhilfe waren zwei einzelne Modbus-Instanzen eine nur für ID1, die andere nur für ID2.

                      Ob das mit allen Modbus-Adaptern geht kann ich nicht sagen, mit meinem Waveshare RS485 to ETH (B) (äußerlich baugleich zu dem HöSi-Adapter) ging es auf jeden Fall.
                      Ob es nötig ist diesen mit dem VirCOM Programm auf "Device Client & Slave mode" zu stellen kann ich nach dem ganzen hin und herstellen nicht definitiv sagen, so klappt es auf jeden Fall.

                      Einzig störend ist es jetzt noch, dass im Standby der IOBroker Modbus-Adapter das Log vollpustet wegen "Request timed out" und nach 13 Fehlversuchen jedesmal neustartet.
                      Außerdem unschön ist, dass das Logging der Werte in die InfluxDB trotz Standby mit den alten Werten weiterläuft...

                      Wer hierzu Lösungen hat: Immer her damit!
                      So tendiere ich eher dazu das Ganze über kurz oder lang mit einem Python-Skript zu lösen.
                      Ja, ich weiß, der Unterschied im Stromverbrauch zwischen "Standby" und "Normal" ist nicht sooo groß, aber nur weil die Programmierung es nicht hergibt? Da siegt der Ehrgeiz...

                      N InterimoI 2 Antworten Letzte Antwort
                      0
                      • H Hefo

                        @martin12 @NewPaint2
                        Danke erst mal für die Register-Copy-Paste-Vorlagen! Das hat die Einrichtung stark vereinfacht.

                        Bei meinen zwei Wallboxen trat das Problem auf, dass sobald die Wallbox mit Modbus ID 1 in den Standby ging die Wallbox mit ID2 zwar noch regelmäßig ihre Daten in den Input Registern aktualisiert hat, ich aber keine Werte in den Holding Registern (z.B. Maximal Current) schreiben konnte.

                        Abhilfe waren zwei einzelne Modbus-Instanzen eine nur für ID1, die andere nur für ID2.

                        Ob das mit allen Modbus-Adaptern geht kann ich nicht sagen, mit meinem Waveshare RS485 to ETH (B) (äußerlich baugleich zu dem HöSi-Adapter) ging es auf jeden Fall.
                        Ob es nötig ist diesen mit dem VirCOM Programm auf "Device Client & Slave mode" zu stellen kann ich nach dem ganzen hin und herstellen nicht definitiv sagen, so klappt es auf jeden Fall.

                        Einzig störend ist es jetzt noch, dass im Standby der IOBroker Modbus-Adapter das Log vollpustet wegen "Request timed out" und nach 13 Fehlversuchen jedesmal neustartet.
                        Außerdem unschön ist, dass das Logging der Werte in die InfluxDB trotz Standby mit den alten Werten weiterläuft...

                        Wer hierzu Lösungen hat: Immer her damit!
                        So tendiere ich eher dazu das Ganze über kurz oder lang mit einem Python-Skript zu lösen.
                        Ja, ich weiß, der Unterschied im Stromverbrauch zwischen "Standby" und "Normal" ist nicht sooo groß, aber nur weil die Programmierung es nicht hergibt? Da siegt der Ehrgeiz...

                        N Offline
                        N Offline
                        NewPaint2
                        schrieb am zuletzt editiert von NewPaint2
                        #12

                        @hefo
                        Ich kann den Fehler leider nicht nachvollziehen, ich habe nur eine Box dran. Ich habe mir auch nur behelfen können die Box mit dem "Hösi" direkt anzusteuern. Wie ich schon oben beschrieben hatte wenn der Standby anspringt wirft der Bus Fehler. Bei meiner Steuerung mit Durchlauferhitzer habe ich einen zweiten RS485-TTL-ESP32 mit einer eigenen Instanz wegen der örtlichen Entfernung zum Zähler benutzen müssen, also arbeite ich auch mit 2 Modbus-Adaptern. Das Standby in der Box ist recht nervig weil dann echt der Bus zum stehen kommt. Gut bei 5Watt... naja schön ist das nicht, aber so richtig eine Lösung habe ich im Moment auch nicht auf Lager, ich laß die Box in den Standby springen. Tut mir leid, ich denke Heidelberg läßt die Boxen mit ihren Corntroler einfach nicht ins Standby rutschen, wenn der Controler von ihnen dran ist und mehr als eine Box installiert ist.

                        1 Antwort Letzte Antwort
                        0
                        • M Martin12

                          @newpaint2
                          Config3.PNG
                          Im Holdingregister habe ich die Haken bei CW weggelassen. Die Werte wurden sonst sofort wieder auf 0 gesetzt.
                          Das Script muss ich zuerst noch bei Sonnenschein testen, die letzten Tage war dazu noch keine Gelgenheit

                          R Offline
                          R Offline
                          Roetty
                          schrieb am zuletzt editiert von
                          #13

                          @martin12
                          Hey danke für Deine Infos! Mal ne (doofe?) Frage: Warum sind die Registernummern um 1 Erhöht? In der WallBox-Doku steht z.B. Max. Current mit "261" bei Euch ist es 262 ?!

                          Ich tüxel mich gerade in das Thema Modbus usw. rein und hab noch nicht den Überblick und sauge alles auf was ich finde. Also das hat doch bestimmt einen Grund, oder?

                          VG Rötty

                          N 1 Antwort Letzte Antwort
                          0
                          • R Roetty

                            @martin12
                            Hey danke für Deine Infos! Mal ne (doofe?) Frage: Warum sind die Registernummern um 1 Erhöht? In der WallBox-Doku steht z.B. Max. Current mit "261" bei Euch ist es 262 ?!

                            Ich tüxel mich gerade in das Thema Modbus usw. rein und hab noch nicht den Überblick und sauge alles auf was ich finde. Also das hat doch bestimmt einen Grund, oder?

                            VG Rötty

                            N Offline
                            N Offline
                            NewPaint2
                            schrieb am zuletzt editiert von NewPaint2
                            #14

                            @roetty Weil der Adapter die Nummern im "Alias-Modus immer Registernummer+1" will. machst du den Alias-Modus aus, kommen die "echten" Registernummern. Leider kannst das nur probieren, manche Hersteller haben die Registeradressierung schon mit der addierten "1", Heidelberg leider nicht.

                            1 Antwort Letzte Antwort
                            0
                            • H Hefo

                              @martin12 @NewPaint2
                              Danke erst mal für die Register-Copy-Paste-Vorlagen! Das hat die Einrichtung stark vereinfacht.

                              Bei meinen zwei Wallboxen trat das Problem auf, dass sobald die Wallbox mit Modbus ID 1 in den Standby ging die Wallbox mit ID2 zwar noch regelmäßig ihre Daten in den Input Registern aktualisiert hat, ich aber keine Werte in den Holding Registern (z.B. Maximal Current) schreiben konnte.

                              Abhilfe waren zwei einzelne Modbus-Instanzen eine nur für ID1, die andere nur für ID2.

                              Ob das mit allen Modbus-Adaptern geht kann ich nicht sagen, mit meinem Waveshare RS485 to ETH (B) (äußerlich baugleich zu dem HöSi-Adapter) ging es auf jeden Fall.
                              Ob es nötig ist diesen mit dem VirCOM Programm auf "Device Client & Slave mode" zu stellen kann ich nach dem ganzen hin und herstellen nicht definitiv sagen, so klappt es auf jeden Fall.

                              Einzig störend ist es jetzt noch, dass im Standby der IOBroker Modbus-Adapter das Log vollpustet wegen "Request timed out" und nach 13 Fehlversuchen jedesmal neustartet.
                              Außerdem unschön ist, dass das Logging der Werte in die InfluxDB trotz Standby mit den alten Werten weiterläuft...

                              Wer hierzu Lösungen hat: Immer her damit!
                              So tendiere ich eher dazu das Ganze über kurz oder lang mit einem Python-Skript zu lösen.
                              Ja, ich weiß, der Unterschied im Stromverbrauch zwischen "Standby" und "Normal" ist nicht sooo groß, aber nur weil die Programmierung es nicht hergibt? Da siegt der Ehrgeiz...

                              InterimoI Offline
                              InterimoI Offline
                              Interimo
                              schrieb am zuletzt editiert von
                              #15

                              @hefo ich habe auch den Waveshare Adapter bekomme allerdings keine Verbindung zur Wallbox ist es möglich einmal die Konfiguration von dem Adapter zu zeigen?

                              H 1 Antwort Letzte Antwort
                              0
                              • InterimoI Interimo

                                @hefo ich habe auch den Waveshare Adapter bekomme allerdings keine Verbindung zur Wallbox ist es möglich einmal die Konfiguration von dem Adapter zu zeigen?

                                H Offline
                                H Offline
                                Hefo
                                schrieb am zuletzt editiert von
                                #16

                                @interimo Bei mir sieht es im Web-Frontend so aus:
                                Modbus_settings_3.PNG

                                Da ich gelesen hatte, dass über das Web-Frontend nicht alle Parameter zur Verfügung stehen, habe ich es dann mit VirCom auch nochmal eingestellt:
                                Modbus_settings_1.PNG

                                Modbus_settings_2.PNG

                                Ob die Einstellungen so 100% "richtig" sind weiß ich nicht, es funktioniert so auf jeden Fall ohne Probleme oder Ausfälle.

                                Gruß
                                Hefo

                                1 Antwort Letzte Antwort
                                0
                                Antworten
                                • In einem neuen Thema antworten
                                Anmelden zum Antworten
                                • Älteste zuerst
                                • Neuste zuerst
                                • Meiste Stimmen


                                Support us

                                ioBroker
                                Community Adapters
                                Donate

                                538

                                Online

                                32.5k

                                Benutzer

                                81.7k

                                Themen

                                1.3m

                                Beiträge
                                Community
                                Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                ioBroker Community 2014-2025
                                logo
                                • Anmelden

                                • Du hast noch kein Konto? Registrieren

                                • Anmelden oder registrieren, um zu suchen
                                • Erster Beitrag
                                  Letzter Beitrag
                                0
                                • Home
                                • Aktuell
                                • Tags
                                • Ungelesen 0
                                • Kategorien
                                • Unreplied
                                • Beliebt
                                • GitHub
                                • Docu
                                • Hilfe