      ChrisL @lisalisa last edited by ChrisL

      Danke schon mal allen für die schnellen Antworten!
      @hennerich - den Thread hatte ich gefunden, und war/ist meine Vorlage - leider bisher ohne Erfolg 😞
      @lisalisa - ja, Port 502, Status "klar", wird so auf dem SolarEdge angezeigt // betreffend Zugang schreibe ich dir gleich noch zurück 🙂
      @Glasfaser - siehe anbei einen Screenshot aus dem Log - ping geht vom PC aus als auch von Linux Host wo ioBroker drauf läuft - aktuell sind die Netze fürs normale "Home Netzwerk" sowie das "Smart Home Netzwerk" nicht getrennt

      Edit, ich sehe jetzt gerade, dass die App keinen Verbrauch mehr anzeigt - auch aus der Vergangenheit nicht mehr... (was sie bis vor kurzem garantiert noch tat... kA was ich da nun gemacht habe :()

      solardedge_03.png

      Glasfaser 1 Reply Last reply Reply Quote 0
      • Glasfaser
        Glasfaser @ChrisL last edited by Glasfaser

        @chrisl sagte in Solaredge Adapter (Photovoltaikanlage):

        siehe anbei einen Screenshot aus dem Log

        Bitte keine Log´s als Screenshot , sondern die Ausgabe in Code-Tags </> setzen .

        und du solltest :

        @glasfaser sagte in Solaredge Adapter (Photovoltaikanlage):
        was steht im LOG ( Logstufe der Instanz auf DEBUG )

        Expertenmodus einschalten , in der Adapter Instanz Modbus gehen , dann die Logstufe auf DEBUG stellen :

        BEISPIEL :

        98657e7b-b613-44d6-8cbf-4ebaf18b0aad-grafik.png

        C 1 Reply Last reply Reply Quote 0
        • C
          ChrisL @Glasfaser last edited by

          @glasfaser Salü, so, hoffe ist jetzt korrekt 🙂

          Was mich gearde wirklich auch noch etwas beunruhigt ist eben die Tatsache, dass die SolardEdge App nun auch kein Verbrauch mehr anzeigt... Habe ich da evtl. dummerweise irgendwie beim Rumdrückem am SolardEdge den "Stromzähler" abgehängt...? 😞

          2022-01-06 12:38:03.126 - warn: modbus.0 (240342) Poll error count: 8 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:38:03.177 - info: modbus.0 (240342) Disconnected from slave 192.168.100.162
          2022-01-06 12:38:27.778 - error: go-e.0 (206653) getaddrinfo EAI_AGAIN go-echarger
          2022-01-06 12:38:30.812 - info: shelly.0 (206154) State value to set for "shelly.0.SHSW-PM#E8DB84D2FAB6#1.Relay0.longpush" has to be type "string" but received type "boolean"
          2022-01-06 12:38:45.814 - info: shelly.0 (206154) State value to set for "shelly.0.SHSW-PM#E8DB84D2FAB6#1.Relay0.longpush" has to be type "string" but received type "boolean"
          2022-01-06 12:39:00.815 - info: shelly.0 (206154) State value to set for "shelly.0.SHSW-PM#E8DB84D2FAB6#1.Relay0.longpush" has to be type "string" but received type "boolean"
          2022-01-06 12:39:03.178 - info: modbus.0 (240342) Connected to slave 192.168.100.162
          2022-01-06 12:39:03.318 - warn: modbus.0 (240342) Poll error count: 9 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:03.369 - info: modbus.0 (240342) Disconnected from slave 192.168.100.162
          2022-01-06 12:39:27.778 - error: go-e.0 (206653) getaddrinfo EAI_AGAIN go-echarger
          2022-01-06 12:39:38.947 - info: host.iobroker01 stopInstance system.adapter.modbus.0 (force=false, process=true)
          2022-01-06 12:39:38.950 - info: host.iobroker01 stopInstance system.adapter.modbus.0 send kill signal
          2022-01-06 12:39:38.950 - info: modbus.0 (240342) Got terminate signal TERMINATE_YOURSELF
          2022-01-06 12:39:38.952 - info: modbus.0 (240342) terminating
          2022-01-06 12:39:38.953 - info: modbus.0 (240342) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
          2022-01-06 12:39:39.487 - info: host.iobroker01 instance system.adapter.modbus.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
          2022-01-06 12:39:41.980 - info: host.iobroker01 instance system.adapter.modbus.0 started with pid 240363
          2022-01-06 12:39:42.368 - debug: modbus.0 (240363) Redis Objects: Use Redis connection: 127.0.0.1:9001
          2022-01-06 12:39:42.394 - debug: modbus.0 (240363) Objects client ready ... initialize now
          2022-01-06 12:39:42.395 - debug: modbus.0 (240363) Objects create System PubSub Client
          2022-01-06 12:39:42.398 - debug: modbus.0 (240363) Objects create User PubSub Client
          2022-01-06 12:39:42.399 - debug: modbus.0 (240363) Objects client initialize lua scripts
          2022-01-06 12:39:42.405 - debug: modbus.0 (240363) Objects connected to redis: 127.0.0.1:9001
          2022-01-06 12:39:42.409 - debug: modbus.0 (240363) objectDB connected
          2022-01-06 12:39:42.410 - debug: modbus.0 (240363) Redis States: Use Redis connection: 127.0.0.1:9000
          2022-01-06 12:39:42.413 - debug: modbus.0 (240363) States create System PubSub Client
          2022-01-06 12:39:42.414 - debug: modbus.0 (240363) States create User PubSub Client
          2022-01-06 12:39:42.417 - debug: modbus.0 (240363) States connected to redis: 127.0.0.1:9000
          2022-01-06 12:39:42.418 - debug: modbus.0 (240363) statesDB connected
          2022-01-06 12:39:42.497 - debug: modbus.0 (240363) Plugin sentry Initialize Plugin (enabled=true)
          2022-01-06 12:39:42.591 - info: modbus.0 (240363) starting. Version 3.4.14 in /opt/iobroker/node_modules/iobroker.modbus, node: v12.22.1, js-controller: 3.3.22
          2022-01-06 12:39:42.641 - debug: modbus.0 (240363) Initialize Objects for disInputs: [{"_address":0,"name":"","description":"","formula":"","role":"level","room":"","cw":"","isScale":"","address":0,"deviceId":1,"id":"discreteInputs.0","len":1}]
          2022-01-06 12:39:42.642 - debug: modbus.0 (240363) Add discreteInputs.0: {"_id":"discreteInputs.0","type":"state","common":{"name":"","role":"level","type":"boolean","read":true,"write":false,"def":false},"native":{"regType":"disInputs","address":0,"deviceId":1}}
          2022-01-06 12:39:42.642 - debug: modbus.0 (240363) Initialize Objects for coils: [{"_address":0,"name":"","description":"","formula":"","role":"level","room":"","poll":"","wp":"","cw":"","isScale":"","address":0,"deviceId":1,"id":"coils.0"}]
          2022-01-06 12:39:42.642 - debug: modbus.0 (240363) Add coils.0: {"_id":"coils.0","type":"state","common":{"name":"","role":"level","type":"boolean","read":false,"write":true,"def":false},"native":{"regType":"coils","address":0,"deviceId":1,"poll":"","wp":""}}
          2022-01-06 12:39:42.642 - debug: modbus.0 (240363) Initialize Objects for inputRegs: [{"_address":0,"name":"","description":"","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"level","room":"","cw":"","isScale":"","address":0,"deviceId":1,"id":"inputRegisters.0"}]
          2022-01-06 12:39:42.642 - debug: modbus.0 (240363) Add inputRegisters.0: {"_id":"inputRegisters.0","type":"state","common":{"name":"","role":"level","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":0,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1}}
          2022-01-06 12:39:42.643 - debug: modbus.0 (240363) Initialize Objects for holdingRegs: [{"_address":"40071","name":"I_AC_Current","description":"AC-Verbrauch gesamt","unit":"Amp","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":"","cw":false,"isScale":"","address":40071,"deviceId":1,"id":"holdingRegisters.40071_I_AC_Current"}]
          2022-01-06 12:39:42.643 - debug: modbus.0 (240363) Add holdingRegisters.40071_I_AC_Current: {"_id":"holdingRegisters.40071_I_AC_Current","type":"state","common":{"name":"AC-Verbrauch gesamt","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Amp"},"native":{"regType":"holdingRegs","address":40071,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
          2022-01-06 12:39:42.792 - info: modbus.0 (240363) Connected to slave 192.168.100.162
          2022-01-06 12:39:42.793 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:42.793 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:42.886 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:42.887 - warn: modbus.0 (240363) Poll error count: 1 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:43.938 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:43.939 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:43.984 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:43.984 - warn: modbus.0 (240363) Poll error count: 2 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:45.036 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:45.036 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:45.073 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:45.074 - warn: modbus.0 (240363) Poll error count: 3 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:46.124 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:46.125 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:46.130 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:46.131 - warn: modbus.0 (240363) Poll error count: 4 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:47.181 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:47.182 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:47.292 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:47.293 - warn: modbus.0 (240363) Poll error count: 5 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:48.343 - debug: modbus.0 (240363) [DevID_1] Poll start ---------------------
          2022-01-06 12:39:48.345 - debug: modbus.0 (240363) [DevID_1/disInputs] Poll address 0 - 16 bits
          2022-01-06 12:39:48.393 - debug: modbus.0 (240363) Received pdu describes an error.
          2022-01-06 12:39:48.393 - warn: modbus.0 (240363) Poll error count: 6 code: {"errorCode":130,"exceptionCode":1,"message":"ILLEGAL FUNCTION"}
          2022-01-06 12:39:48.444 - debug: modbus.0 (240363) Closing client on purpose.
          2022-01-06 12:39:48.444 - info: modbus.0 (240363) Disconnected from slave 192.168.100.162
          2022-01-06 12:39:48.550 - debug: modbus.0 (240363) Socket closed with error
          2022-01-06 12:39:48.550 - debug: modbus.0 (240363) Cleaning up request fifo.
          2022-01-06 12:39:49.552 - debug: modbus.0 (240363) Closing client on purpose.
          
          Glasfaser 1 Reply Last reply Reply Quote 0
          • Glasfaser
            Glasfaser @ChrisL last edited by Glasfaser

            @chrisl

            Du hast aber nur im Holding etwas eingetragen !?...,, schau mal bei den anderen , Direct Input usw. hast du da was drin stehen .

            Was ergibt jetzt , von ioBroker aus :

            @glasfaser sagte in Solaredge Adapter (Photovoltaikanlage):
            Was sagt :
            nmap -sU -p 502 192.168.xxx.xx

            Bzw.

            auch die Ausgabe :

            nmap -Pn  192.168.xxx.xx
            

            Wieviel Teilnehmer Fragen den Modbus zum WR per Lan ab !?

            C 1 Reply Last reply Reply Quote 0
            • C
              ChrisL @Glasfaser last edited by

              @glasfaser said in Solaredge Adapter (Photovoltaikanlage):

              nmap -sU -p 502 192.168.xxx.xx

              ich nehme an, ausgeführt einfach von der Commandline vom Host, oder?
              Siehe below.

              Es dürfte niemand sonst mit dem SolarEdge abfragen...

              Ja, nur der eine Eintrag im Holding, die anderen sind leer.

              ioadmin@iobroker01:~$ sudo nmap -sU -p 502 192.168.100.163
              Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:00 UTC
              dnet: Failed to open device ens3
              QUITTING!
              ioadmin@iobroker01:~$ sudo nmap -Pn 192.168.100.163
              Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:01 UTC
              dnet: Failed to open device ens3
              QUITTING!
              ioadmin@iobroker01:~$
              
              
              Glasfaser 2 Replies Last reply Reply Quote 0
              • Glasfaser
                Glasfaser @ChrisL last edited by

                @chrisl

                Da stimmt was nicht .

                Ping geht hast du oben geschrieben !?

                C 1 Reply Last reply Reply Quote 0
                • Glasfaser
                  Glasfaser @ChrisL last edited by

                  @chrisl

                  ohne sudo !?

                  C 1 Reply Last reply Reply Quote 0
                  • C
                    ChrisL @Glasfaser last edited by

                    @glasfaser ok, ascha auf mein Haupt, hatte mich in der IP vertippt (im ioBroker ist aber die richtige eingetragen!)

                    ioadmin@iobroker01:~$ sudo nmap -sU -p 502 192.168.100.162
                    Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:19 UTC
                    dnet: Failed to open device ens3
                    QUITTING!
                    ioadmin@iobroker01:~$ sudo nmap -Pn 192.168.100.162
                    Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:19 UTC
                    dnet: Failed to open device ens3
                    QUITTING!
                    ioadmin@iobroker01:~$ ping 192.168.100.162
                    PING 192.168.100.162 (192.168.100.162) 56(84) bytes of data.
                    64 bytes from 192.168.100.162: icmp_seq=1 ttl=64 time=0.537 ms
                    64 bytes from 192.168.100.162: icmp_seq=2 ttl=64 time=0.428 ms
                    64 bytes from 192.168.100.162: icmp_seq=3 ttl=64 time=0.480 ms
                    64 bytes from 192.168.100.162: icmp_seq=4 ttl=64 time=0.436 ms
                    64 bytes from 192.168.100.162: icmp_seq=5 ttl=64 time=0.438 ms
                    ^[64 bytes from 192.168.100.162: icmp_seq=6 ttl=64 time=0.568 ms
                    64 bytes from 192.168.100.162: icmp_seq=7 ttl=64 time=0.626 ms
                    ^C
                    --- 192.168.100.162 ping statistics ---
                    7 packets transmitted, 7 received, 0% packet loss, time 6126ms
                    rtt min/avg/max/mdev = 0.428/0.501/0.626/0.071 ms
                    
                    
                    
                    1 Reply Last reply Reply Quote 0
                    • C
                      ChrisL @Glasfaser last edited by

                      @glasfaser - als ich das erste mal probierte motze mit das Terminal an, nmap brauche sudo... jetzt gehts auch ohne...

                      ioadmin@iobroker01:~$ nmap -Pn 192.168.100.162
                      Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:20 UTC
                      Nmap scan report for 192.168.100.162
                      Host is up (0.00087s latency).
                      All 1000 scanned ports on 192.168.100.162 are in ignored states.
                      Not shown: 1000 closed tcp ports (conn-refused)
                      
                      Nmap done: 1 IP address (1 host up) scanned in 4.24 seconds
                      ioadmin@iobroker01:~$ nmap -Pn 192.168.100.162
                      Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:20 UTC
                      Nmap scan report for 192.168.100.162
                      Host is up (0.00075s latency).
                      All 1000 scanned ports on 192.168.100.162 are in ignored states.
                      Not shown: 1000 closed tcp ports (conn-refused)
                      
                      Nmap done: 1 IP address (1 host up) scanned in 5.02 seconds
                      
                      
                      Glasfaser 1 Reply Last reply Reply Quote 0
                      • Glasfaser
                        Glasfaser @ChrisL last edited by

                        @chrisl

                        Du hast das vergessen , Port Abfrage

                        nmap -sU -p 502 192.168.100.162
                        
                        C 1 Reply Last reply Reply Quote 0
                        • C
                          ChrisL @Glasfaser last edited by

                          @glasfaser - dann kommt das hier, deswegen bin ich wohl auf sudo umgestiegen vorher 🙂

                          ioadmin@iobroker01:~$ nmap -sU -p 502 192.168.100.162
                          You requested a scan type which requires root privileges.
                          QUITTING!
                          
                          
                          Glasfaser 1 Reply Last reply Reply Quote 0
                          • Glasfaser
                            Glasfaser @ChrisL last edited by

                            @chrisl

                            Ja , aber ich finde keine Ausgabe davon , nur mit der falschen IP .... !?

                            C 1 Reply Last reply Reply Quote 0
                            • C
                              ChrisL @Glasfaser last edited by

                              @glasfaser wenn ich es mit sudo ausführe, kommt das hier raus... 😞

                              ioadmin@iobroker01:~$ sudo nmap -sU -p 502 192.168.100.162
                              Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 13:29 UTC
                              dnet: Failed to open device ens3
                              QUITTING!
                              
                              
                              Glasfaser 1 Reply Last reply Reply Quote 0
                              • Glasfaser
                                Glasfaser @ChrisL last edited by

                                @chrisl sagte in Solaredge Adapter (Photovoltaikanlage):

                                dnet: Failed to open device ens3

                                Und da ist mein ? .... auch schon oben gewesen

                                C 1 Reply Last reply Reply Quote 0
                                • C
                                  ChrisL @Glasfaser last edited by

                                  @glasfaser - ich komme etwas weiter...

                                  Allerdings kann ich jetzt gerade nicht den Modbus Status am Wechselrichter anschauen gehen, da SolardEdge irgendwas zurück gesetzt hat - die Kommunikation mit dem Zähler geht nun wieder, aber auf dem Display ist er noch in irgendeinem Menü, wo ich ned einfach so raus komme... Stupide 1 Knopf Bedienung... -.-

                                  ioadmin@iobroker01:~$ sudo snap connect nmap:network-control
                                  ioadmin@iobroker01:~$ sudo nmap -sU -p 502 192.168.100.162
                                  Starting Nmap 7.92 ( https://nmap.org ) at 2022-01-06 14:15 UTC
                                  Nmap scan report for 192.168.100.162
                                  Host is up (0.00058s latency).
                                  
                                  PORT    STATE  SERVICE
                                  502/udp closed mbap
                                  MAC Address: 00:27:02:14:54:89 (SolarEdge Technologies)
                                  
                                  Nmap done: 1 IP address (1 host up) scanned in 0.29 seconds
                                  ioadmin@iobroker01:~$
                                  
                                  
                                  Glasfaser 1 Reply Last reply Reply Quote 0
                                  • Glasfaser
                                    Glasfaser @ChrisL last edited by Glasfaser

                                    @chrisl

                                    Neue Modbus Instanz.1 anlegen , ( instanz.0 ausschalten )

                                    Einstellungen machen und dann dieses Register bei Holding importieren

                                    https://forum.iobroker.net/topic/38322/tutorial-solaredge-modbus-iobroker-grafana/92?_=1641479982903

                                    .
                                    9dcf1b3c-3340-4247-908c-f70f8d50e234-grafik.png

                                    C 1 Reply Last reply Reply Quote 0
                                    • C
                                      ChrisL @Glasfaser last edited by

                                      @glasfaser said in Solaredge Adapter (Photovoltaikanlage):

                                      eue Modbus Instanz.1 anleg

                                      ok, jetzt gehts vorwärts - wenn ich nun die Instanz.1 starte, ist sie ganz kurz auf Grün, wechselt dann aber sofort wieder auf Orange zurück - nun der laaaaange Log...

                                      2022-01-06 15:12:24.094 - debug: modbus.1 (2542) Redis Objects: Use Redis connection: 127.0.0.1:9001
                                      2022-01-06 15:12:24.119 - debug: modbus.1 (2542) Objects client ready ... initialize now
                                      2022-01-06 15:12:24.120 - debug: modbus.1 (2542) Objects create System PubSub Client
                                      2022-01-06 15:12:24.123 - debug: modbus.1 (2542) Objects create User PubSub Client
                                      2022-01-06 15:12:24.124 - debug: modbus.1 (2542) Objects client initialize lua scripts
                                      2022-01-06 15:12:24.130 - debug: modbus.1 (2542) Objects connected to redis: 127.0.0.1:9001
                                      2022-01-06 15:12:24.134 - debug: modbus.1 (2542) objectDB connected
                                      2022-01-06 15:12:24.135 - debug: modbus.1 (2542) Redis States: Use Redis connection: 127.0.0.1:9000
                                      2022-01-06 15:12:24.139 - debug: modbus.1 (2542) States create System PubSub Client
                                      2022-01-06 15:12:24.139 - debug: modbus.1 (2542) States create User PubSub Client
                                      2022-01-06 15:12:24.143 - debug: modbus.1 (2542) States connected to redis: 127.0.0.1:9000
                                      2022-01-06 15:12:24.143 - debug: modbus.1 (2542) statesDB connected
                                      2022-01-06 15:12:24.257 - debug: modbus.1 (2542) Plugin sentry Initialize Plugin (enabled=true)
                                      2022-01-06 15:12:24.346 - info: modbus.1 (2542) starting. Version 3.4.14 in /opt/iobroker/node_modules/iobroker.modbus, node: v12.22.8, js-controller: 3.3.22
                                      2022-01-06 15:12:24.411 - debug: modbus.1 (2542) Initialize Objects for disInputs: []
                                      2022-01-06 15:12:24.411 - debug: modbus.1 (2542) Initialize Objects for coils: []
                                      2022-01-06 15:12:24.411 - debug: modbus.1 (2542) Initialize Objects for inputRegs: []
                                      2022-01-06 15:12:24.412 - debug: modbus.1 (2542) Initialize Objects for holdingRegs: [{"_address":40000,"name":"C_SunSpec_ID","description":"Wert = \"SunS\" (0x53756e53). Identifiziert dies eindeutig als eine SunSpec Modbus-Karte","unit":"","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":null,"id":"holdingRegisters.NaN_C_SunSpec_ID"},{"_address":40002,"name":"C_SunSpec_DID","description":"Wert = 0x0001. Identifiziert dies eindeutig als einen SunSpec “Common Block“","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":1,"id":"holdingRegisters.40002_C_SunSpec_DID"},{"_address":40003,"name":"C_SunSpec_Länge","description":"65 = Länge eines Blocks in 16-bit Registern","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":2,"id":"holdingRegisters.40003_C_SunSpec_Länge"},{"_address":40004,"name":"C_Hersteller","description":"Bei SunSpec eingetragener Wert = \"SolarEdge\"","unit":"","type":"string","len":16,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":3,"id":"holdingRegisters.40004_C_Hersteller"},{"_address":40020,"name":"C_Modell","description":"Spezifischer SolarEdge Wert","unit":"","type":"string","len":16,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":19,"id":"holdingRegisters.40020_C_Modell"},{"_address":40044,"name":"C_Version","description":"Spezifischer SolarEdge Wert","unit":"","type":"string","len":8,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":43,"id":"holdingRegisters.40044_C_Version"},{"_address":40052,"name":"C_Seriennummer","description":"Eindeutiger SolarEdge Wert","unit":"","type":"string","len":16,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":51,"id":"holdingRegisters.40052_C_Seriennummer"},{"_address":40068,"name":"C_Geräteadresse","description":"Modbus-ID der entsprechenden Einheit","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":67,"id":"holdingRegisters.40068_C_Geräteadresse"},{"_address":40069,"name":"C_SunSpec_DID","description":"101 = Einphasig, 102 = Spaltphase, 103 = Dreiphasig","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":68,"id":"holdingRegisters.40069_C_SunSpec_DID"},{"_address":40070,"name":"C_SunSpec_Länge","description":"50 = Länge des Modellblocks","unit":"Register","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":69,"id":"holdingRegisters.40070_C_SunSpec_Länge"},{"_address":40071,"name":"I_AC_Strom","description":"AC-Gesamtstromwert","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":70,"id":"holdingRegisters.40071_I_AC_Strom"},{"_address":40072,"name":"I_AC_StromA","description":"AC-Phase A (L1) Stromwert","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":71,"id":"holdingRegisters.40072_I_AC_StromA"},{"_address":40073,"name":"I_AC_StromB","description":"AC-Phase B (L2) Stromwert","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":72,"id":"holdingRegisters.40073_I_AC_StromB"},{"_address":40074,"name":"I_AC_StromC","description":"AC-Phase C (L3) Stromwert","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":73,"id":"holdingRegisters.40074_I_AC_StromC"},{"_address":40075,"name":"I_AC_Strom_SF","description":"AC-Strom Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":74,"id":"holdingRegisters.40075_I_AC_Strom_SF"},{"_address":40076,"name":"I_AC_SpannungAB","description":"AC-Spannung Phase AB (L1-L2) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":75,"id":"holdingRegisters.40076_I_AC_SpannungAB"},{"_address":40077,"name":"I_AC_SpannungBC","description":"AC-Spannung Phase BC (L2-L3) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":76,"id":"holdingRegisters.40077_I_AC_SpannungBC"},{"_address":40078,"name":"I_AC_SpannungCA","description":"AC-Spannung Phase CA (L3-L1) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":77,"id":"holdingRegisters.40078_I_AC_SpannungCA"},{"_address":40079,"name":"I_AC_SpannungAN","description":"AC-Spannung Phase A-N (L1-N) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":78,"id":"holdingRegisters.40079_I_AC_SpannungAN"},{"_address":40080,"name":"I_AC_SpannungBN","description":"AC-Spannung Phase B-N (L2-N) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":79,"id":"holdingRegisters.40080_I_AC_SpannungBN"},{"_address":40081,"name":"I_AC_SpannungCN","description":"AC-Spannung Phase C-N (L3-N) Wert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":80,"id":"holdingRegisters.40081_I_AC_SpannungCN"},{"_address":40082,"name":"I_AC_Spannung_SF","description":"AC-Spannung Skalierungsfaktor","unit":"V","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":81,"id":"holdingRegisters.40082_I_AC_Spannung_SF"},{"_address":40083,"name":"I_AC_Leistung","description":"AC-Leistungswert","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":82,"id":"holdingRegisters.40083_I_AC_Leistung"},{"_address":40084,"name":"I_AC_Leistung_SF","description":"AC-Leistung Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":83,"id":"holdingRegisters.40084_I_AC_Leistung_SF"},{"_address":40085,"name":"I_AC_Frequenz","description":"Frequenzwert","unit":"Hz","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":84,"id":"holdingRegisters.40085_I_AC_Frequenz"},{"_address":40086,"name":"I_AC_Frequenz_SF","description":"Frequenz Skalierungsfaktor","unit":"","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":85,"id":"holdingRegisters.40086_I_AC_Frequenz_SF"},{"_address":40087,"name":"I_AC_VA","description":"Scheinleistung","unit":"VA","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":86,"id":"holdingRegisters.40087_I_AC_VA"},{"_address":40088,"name":"I_AC_VA_SF","description":"Scheinleistung Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":87,"id":"holdingRegisters.40088_I_AC_VA_SF"},{"_address":40089,"name":"I_AC_VAR","description":"Blindleistung","unit":"VAR","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":88,"id":"holdingRegisters.40089_I_AC_VAR"},{"_address":40090,"name":"I_AC_VAR_SF","description":"Blindleistung Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":89,"id":"holdingRegisters.40090_I_AC_VAR_SF"},{"_address":40091,"name":"I_AC_PF","description":"Leistungsfaktor","unit":"%","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":90,"id":"holdingRegisters.40091_I_AC_PF"},{"_address":40092,"name":"I_AC_PF_SF","description":"Leistungsfaktor Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":91,"id":"holdingRegisters.40092_I_AC_PF_SF"},{"_address":40093,"name":"I_AC_Energie_WH","description":"AC Gesamt-Energieproduktion","unit":"Wh","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":92,"id":"holdingRegisters.40093_I_AC_Energie_WH"},{"_address":40095,"name":"I_AC_Energie_WH_SF","description":"AC Gesamtenergie Skalierungsfaktor","unit":"SF","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":94,"id":"holdingRegisters.40095_I_AC_Energie_WH_SF"},{"_address":40096,"name":"I_DC_Strom","description":"DC-Stromwert","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":95,"id":"holdingRegisters.40096_I_DC_Strom"},{"_address":40097,"name":"I_DC_Strom_SF","description":"DC-Strom Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":96,"id":"holdingRegisters.40097_I_DC_Strom_SF"},{"_address":40098,"name":"I_DC_Spannung","description":"DC-Spannungswert","unit":"V","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":97,"id":"holdingRegisters.40098_I_DC_Spannung"},{"_address":40099,"name":"I_DC_Spannung_SF","description":"DC-Spannung Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":98,"id":"holdingRegisters.40099_I_DC_Spannung_SF"},{"_address":40100,"name":"I_DC_Leistung","description":"DC-Leistungswert","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":99,"id":"holdingRegisters.40100_I_DC_Leistung"},{"_address":40101,"name":"I_DC_Leistung_SF","description":"DC-Leistung Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":100,"id":"holdingRegisters.40101_I_DC_Leistung_SF"},{"_address":40103,"name":"I_Temp_Kühler","description":"Kühlkörpertemperatur","unit":"°C","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":102,"id":"holdingRegisters.40103_I_Temp_Kühler"},{"_address":40106,"name":"I_Temp_SF","description":"Kühlkörpertemperatur Skalierungsfaktor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":105,"id":"holdingRegisters.40106_I_Temp_SF"},{"_address":40107,"name":"I_Status","description":"Betriebszustand (1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup)","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":106,"id":"holdingRegisters.40107_I_Status"},{"_address":40108,"name":"I_Status_Anbieter","description":"Anbieter-spezifischer Betriebszustand sowie Fehlercodes: 1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":107,"id":"holdingRegisters.40108_I_Status_Anbieter"},{"_address":40123,"name":"C_Manufacturer","description":"Meter manufacturer","unit":"","type":"string","len":32,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":122,"id":"holdingRegisters.40123_C_Manufacturer"},{"_address":40139,"name":"C_Model","description":"Meter model","unit":"","type":"string","len":32,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":138,"id":"holdingRegisters.40139_C_Model"},{"_address":40155,"name":"C_Option","description":"Export + Import, Production, consumption","unit":"","type":"string","len":16,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":154,"id":"holdingRegisters.40155_C_Option"},{"_address":40190,"name":"M_AC_Current","description":"AC Current (sum of active phases)","unit":"A","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":189,"id":"holdingRegisters.40190_M_AC_Current"},{"_address":40194,"name":"M_AC_Current_S F","description":"AC Current Scale Factor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":193,"id":"holdingRegisters.40194_M_AC_Current_S_F"},{"_address":40206,"name":"M_AC_Power","description":"Total Real Power (sum of active phases)","unit":"W","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":205,"id":"holdingRegisters.40206_M_AC_Power"},{"_address":40210,"name":"M_AC_Power_SF","description":"AC Real Power Scale Factor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":209,"id":"holdingRegisters.40210_M_AC_Power_SF"},{"_address":40226,"name":"M_Exported","description":"Total Exported Real Energy","unit":"Wh","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":225,"id":"holdingRegisters.40226_M_Exported"},{"_address":40234,"name":"M_Imported","description":"Total Imported Real Energy","unit":"Wh","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":233,"id":"holdingRegisters.40234_M_Imported"},{"_address":40242,"name":"M_Energy_W_SF","description":"Real Energy Scale Factor","unit":"SF","type":"int16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":241,"id":"holdingRegisters.40242_M_Energy_W_SF"},{"_address":57664,"name":"Battery 1 Device ID","description":"Batterie Geräte ID","unit":"","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17663,"id":"holdingRegisters.57664_Battery_1 Device ID"},{"_address":57666,"name":"Battery 1 Rated Energy","description":"Batterie Nennkapazität","unit":"Wh","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17665,"id":"holdingRegisters.57666_Battery_1 Rated Energy"},{"_address":57668,"name":"Battery 1 Max Charge Continues Power","description":"Batterie maximale Ladeleistung","unit":"W","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17667,"id":"holdingRegisters.57668_Battery_1 Max Charge Continues Power"},{"_address":57670,"name":"Battery 1 Max Discharge Continues Power","description":"Batterie maximale Entladeleistung","unit":"W","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17669,"id":"holdingRegisters.57670_Battery_1 Max Discharge Continues Power"},{"_address":57672,"name":"Battery 1 Max Charge Peak Power","description":"Batterie maximale Ladespitzenleistung","unit":"W","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17671,"id":"holdingRegisters.57672_Battery_1 Max Charge Peak Power"},{"_address":57674,"name":"Battery 1 Max Discharge Peak Power","description":"Batterie maximale Entladespitzenleistung","unit":"W","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17673,"id":"holdingRegisters.57674_Battery_1 Max Discharge Peak Power"},{"_address":57708,"name":"Battery 1 Average Temperature","description":"Batterie Durchschnittstemperatur","unit":"°C","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17707,"id":"holdingRegisters.57708_Battery_1 Average Temperature"},{"_address":57710,"name":"Battery 1 Max Temperature","description":"Batterie maximale Temperatur","unit":"°C","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17709,"id":"holdingRegisters.57710_Battery_1 Max Temperature"},{"_address":57712,"name":"Battery 1 Instantaneous Voltage","description":"Batterie momentane Spannung","unit":"V","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17711,"id":"holdingRegisters.57712_Battery_1 Instantaneous Voltage"},{"_address":57714,"name":"Battery 1 Instantaneous Current","description":"Batterie momentane Stromstärke","unit":"A","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17713,"id":"holdingRegisters.57714_Battery_1 Instantaneous Current"},{"_address":57716,"name":"Battery 1 Instantaneous Power","description":"Batterie momentane Leistung","unit":"W","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17715,"id":"holdingRegisters.57716_Battery_1 Instantaneous Power"},{"_address":57718,"name":"Battery 1 Lifetime Export Energy Counter","description":"Batterie Gesamtenergie entladen","unit":"Wh","type":"uint64le","len":4,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17717,"id":"holdingRegisters.57718_Battery_1 Lifetime Export Energy Counter"},{"_address":57722,"name":"Battery 1 Lifetime Import Energy Counter","description":"Batterie Gesamtenergie geladen","unit":"Wh","type":"uint64le","len":4,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17721,"id":"holdingRegisters.57722_Battery_1 Lifetime Import Energy Counter"},{"_address":57726,"name":"Battery 1 Max Energy","description":"Batteriekapazität aktualisiert nach Alterung","unit":"Wh","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17725,"id":"holdingRegisters.57726_Battery_1 Max Energy"},{"_address":57728,"name":"Battery 1 Available Energy","description":"Batterie verfügbare Energie","unit":"Wh","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17727,"id":"holdingRegisters.57728_Battery_1 Available Energy"},{"_address":57730,"name":"Battery 1 State of Health (SOH)","description":"Batterie Verhältnis von Nennkapazität zu Batteriekapazität nach Alterung","unit":"%","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17729,"id":"holdingRegisters.57730_Battery_1 State of Health (SOH)"},{"_address":57732,"name":"Battery 1 State of Energy (SOE)","description":"Batterie Ladezustand (verfügbare Energie zu mögliche Kapazität)","unit":"%","type":"floatsw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17731,"id":"holdingRegisters.57732_Battery_1 State of Energy (SOE)"},{"_address":57734,"name":"Battery 1 Status","description":"Batterie Zustand (0 = Aus, 1 = Standby, 2 = Initialisierung, 3 = Laden, 4 = Entladen, 5 = Fehler, 6 = Leerlauf)","unit":"","type":"uint32sw","len":2,"factor":1,"offset":0,"formula":"","role":"level","room":"","poll":true,"wp":false,"cw":false,"isScale":false,"deviceId":1,"address":17733,"id":"holdingRegisters.57734_Battery_1 Status"}]
                                      2022-01-06 15:12:24.413 - debug: modbus.1 (2542) Add holdingRegisters.NaN_C_SunSpec_ID: {"_id":"holdingRegisters.NaN_C_SunSpec_ID","type":"state","common":{"name":"Wert = \"SunS\" (0x53756e53). Identifiziert dies eindeutig als eine SunSpec Modbus-Karte","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":null,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.413 - debug: modbus.1 (2542) Add holdingRegisters.40002_C_SunSpec_DID: {"_id":"holdingRegisters.40002_C_SunSpec_DID","type":"state","common":{"name":"Wert = 0x0001. Identifiziert dies eindeutig als einen SunSpec “Common Block“","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":1,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.414 - debug: modbus.1 (2542) Add holdingRegisters.40003_C_SunSpec_Länge: {"_id":"holdingRegisters.40003_C_SunSpec_Länge","type":"state","common":{"name":"65 = Länge eines Blocks in 16-bit Registern","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":2,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.414 - debug: modbus.1 (2542) Add holdingRegisters.40004_C_Hersteller: {"_id":"holdingRegisters.40004_C_Hersteller","type":"state","common":{"name":"Bei SunSpec eingetragener Wert = \"SolarEdge\"","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":3,"deviceId":1,"type":"string","len":16,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.414 - debug: modbus.1 (2542) Add holdingRegisters.40020_C_Modell: {"_id":"holdingRegisters.40020_C_Modell","type":"state","common":{"name":"Spezifischer SolarEdge Wert","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":19,"deviceId":1,"type":"string","len":16,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.414 - debug: modbus.1 (2542) Add holdingRegisters.40044_C_Version: {"_id":"holdingRegisters.40044_C_Version","type":"state","common":{"name":"Spezifischer SolarEdge Wert","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":43,"deviceId":1,"type":"string","len":8,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.415 - debug: modbus.1 (2542) Add holdingRegisters.40052_C_Seriennummer: {"_id":"holdingRegisters.40052_C_Seriennummer","type":"state","common":{"name":"Eindeutiger SolarEdge Wert","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":51,"deviceId":1,"type":"string","len":16,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.415 - debug: modbus.1 (2542) Add holdingRegisters.40068_C_Geräteadresse: {"_id":"holdingRegisters.40068_C_Geräteadresse","type":"state","common":{"name":"Modbus-ID der entsprechenden Einheit","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":67,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.415 - debug: modbus.1 (2542) Add holdingRegisters.40069_C_SunSpec_DID: {"_id":"holdingRegisters.40069_C_SunSpec_DID","type":"state","common":{"name":"101 = Einphasig, 102 = Spaltphase, 103 = Dreiphasig","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":68,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.415 - debug: modbus.1 (2542) Add holdingRegisters.40070_C_SunSpec_Länge: {"_id":"holdingRegisters.40070_C_SunSpec_Länge","type":"state","common":{"name":"50 = Länge des Modellblocks","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Register"},"native":{"regType":"holdingRegs","address":69,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.415 - debug: modbus.1 (2542) Add holdingRegisters.40071_I_AC_Strom: {"_id":"holdingRegisters.40071_I_AC_Strom","type":"state","common":{"name":"AC-Gesamtstromwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":70,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.416 - debug: modbus.1 (2542) Add holdingRegisters.40072_I_AC_StromA: {"_id":"holdingRegisters.40072_I_AC_StromA","type":"state","common":{"name":"AC-Phase A (L1) Stromwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":71,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.416 - debug: modbus.1 (2542) Add holdingRegisters.40073_I_AC_StromB: {"_id":"holdingRegisters.40073_I_AC_StromB","type":"state","common":{"name":"AC-Phase B (L2) Stromwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":72,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.416 - debug: modbus.1 (2542) Add holdingRegisters.40074_I_AC_StromC: {"_id":"holdingRegisters.40074_I_AC_StromC","type":"state","common":{"name":"AC-Phase C (L3) Stromwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":73,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.416 - debug: modbus.1 (2542) Add holdingRegisters.40075_I_AC_Strom_SF: {"_id":"holdingRegisters.40075_I_AC_Strom_SF","type":"state","common":{"name":"AC-Strom Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":74,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.416 - debug: modbus.1 (2542) Add holdingRegisters.40076_I_AC_SpannungAB: {"_id":"holdingRegisters.40076_I_AC_SpannungAB","type":"state","common":{"name":"AC-Spannung Phase AB (L1-L2) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":75,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.417 - debug: modbus.1 (2542) Add holdingRegisters.40077_I_AC_SpannungBC: {"_id":"holdingRegisters.40077_I_AC_SpannungBC","type":"state","common":{"name":"AC-Spannung Phase BC (L2-L3) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":76,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.417 - debug: modbus.1 (2542) Add holdingRegisters.40078_I_AC_SpannungCA: {"_id":"holdingRegisters.40078_I_AC_SpannungCA","type":"state","common":{"name":"AC-Spannung Phase CA (L3-L1) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":77,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.417 - debug: modbus.1 (2542) Add holdingRegisters.40079_I_AC_SpannungAN: {"_id":"holdingRegisters.40079_I_AC_SpannungAN","type":"state","common":{"name":"AC-Spannung Phase A-N (L1-N) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":78,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.417 - debug: modbus.1 (2542) Add holdingRegisters.40080_I_AC_SpannungBN: {"_id":"holdingRegisters.40080_I_AC_SpannungBN","type":"state","common":{"name":"AC-Spannung Phase B-N (L2-N) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":79,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.417 - debug: modbus.1 (2542) Add holdingRegisters.40081_I_AC_SpannungCN: {"_id":"holdingRegisters.40081_I_AC_SpannungCN","type":"state","common":{"name":"AC-Spannung Phase C-N (L3-N) Wert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":80,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40082_I_AC_Spannung_SF: {"_id":"holdingRegisters.40082_I_AC_Spannung_SF","type":"state","common":{"name":"AC-Spannung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":81,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40083_I_AC_Leistung: {"_id":"holdingRegisters.40083_I_AC_Leistung","type":"state","common":{"name":"AC-Leistungswert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":82,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40084_I_AC_Leistung_SF: {"_id":"holdingRegisters.40084_I_AC_Leistung_SF","type":"state","common":{"name":"AC-Leistung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":83,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40085_I_AC_Frequenz: {"_id":"holdingRegisters.40085_I_AC_Frequenz","type":"state","common":{"name":"Frequenzwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Hz"},"native":{"regType":"holdingRegs","address":84,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40086_I_AC_Frequenz_SF: {"_id":"holdingRegisters.40086_I_AC_Frequenz_SF","type":"state","common":{"name":"Frequenz Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":85,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.418 - debug: modbus.1 (2542) Add holdingRegisters.40087_I_AC_VA: {"_id":"holdingRegisters.40087_I_AC_VA","type":"state","common":{"name":"Scheinleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"VA"},"native":{"regType":"holdingRegs","address":86,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.419 - debug: modbus.1 (2542) Add holdingRegisters.40088_I_AC_VA_SF: {"_id":"holdingRegisters.40088_I_AC_VA_SF","type":"state","common":{"name":"Scheinleistung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":87,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.419 - debug: modbus.1 (2542) Add holdingRegisters.40089_I_AC_VAR: {"_id":"holdingRegisters.40089_I_AC_VAR","type":"state","common":{"name":"Blindleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"VAR"},"native":{"regType":"holdingRegs","address":88,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.419 - debug: modbus.1 (2542) Add holdingRegisters.40090_I_AC_VAR_SF: {"_id":"holdingRegisters.40090_I_AC_VAR_SF","type":"state","common":{"name":"Blindleistung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":89,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.424 - debug: modbus.1 (2542) Add holdingRegisters.40091_I_AC_PF: {"_id":"holdingRegisters.40091_I_AC_PF","type":"state","common":{"name":"Leistungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":90,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.424 - debug: modbus.1 (2542) Add holdingRegisters.40092_I_AC_PF_SF: {"_id":"holdingRegisters.40092_I_AC_PF_SF","type":"state","common":{"name":"Leistungsfaktor Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":91,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.424 - debug: modbus.1 (2542) Add holdingRegisters.40093_I_AC_Energie_WH: {"_id":"holdingRegisters.40093_I_AC_Energie_WH","type":"state","common":{"name":"AC Gesamt-Energieproduktion","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":92,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.424 - debug: modbus.1 (2542) Add holdingRegisters.40095_I_AC_Energie_WH_SF: {"_id":"holdingRegisters.40095_I_AC_Energie_WH_SF","type":"state","common":{"name":"AC Gesamtenergie Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":94,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.424 - debug: modbus.1 (2542) Add holdingRegisters.40096_I_DC_Strom: {"_id":"holdingRegisters.40096_I_DC_Strom","type":"state","common":{"name":"DC-Stromwert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":95,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40097_I_DC_Strom_SF: {"_id":"holdingRegisters.40097_I_DC_Strom_SF","type":"state","common":{"name":"DC-Strom Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":96,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40098_I_DC_Spannung: {"_id":"holdingRegisters.40098_I_DC_Spannung","type":"state","common":{"name":"DC-Spannungswert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":97,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40099_I_DC_Spannung_SF: {"_id":"holdingRegisters.40099_I_DC_Spannung_SF","type":"state","common":{"name":"DC-Spannung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":98,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40100_I_DC_Leistung: {"_id":"holdingRegisters.40100_I_DC_Leistung","type":"state","common":{"name":"DC-Leistungswert","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":99,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40101_I_DC_Leistung_SF: {"_id":"holdingRegisters.40101_I_DC_Leistung_SF","type":"state","common":{"name":"DC-Leistung Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":100,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.425 - debug: modbus.1 (2542) Add holdingRegisters.40103_I_Temp_Kühler: {"_id":"holdingRegisters.40103_I_Temp_Kühler","type":"state","common":{"name":"Kühlkörpertemperatur","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":102,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40106_I_Temp_SF: {"_id":"holdingRegisters.40106_I_Temp_SF","type":"state","common":{"name":"Kühlkörpertemperatur Skalierungsfaktor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":105,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40107_I_Status: {"_id":"holdingRegisters.40107_I_Status","type":"state","common":{"name":"Betriebszustand (1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":106,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40108_I_Status_Anbieter: {"_id":"holdingRegisters.40108_I_Status_Anbieter","type":"state","common":{"name":"Anbieter-spezifischer Betriebszustand sowie Fehlercodes: 1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":107,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40123_C_Manufacturer: {"_id":"holdingRegisters.40123_C_Manufacturer","type":"state","common":{"name":"Meter manufacturer","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":122,"deviceId":1,"type":"string","len":32,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40139_C_Model: {"_id":"holdingRegisters.40139_C_Model","type":"state","common":{"name":"Meter model","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":138,"deviceId":1,"type":"string","len":32,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.426 - debug: modbus.1 (2542) Add holdingRegisters.40155_C_Option: {"_id":"holdingRegisters.40155_C_Option","type":"state","common":{"name":"Export + Import, Production, consumption","role":"value","type":"string","read":true,"write":true,"def":"","unit":""},"native":{"regType":"holdingRegs","address":154,"deviceId":1,"type":"string","len":16,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40190_M_AC_Current: {"_id":"holdingRegisters.40190_M_AC_Current","type":"state","common":{"name":"AC Current (sum of active phases)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":189,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40194_M_AC_Current_S_F: {"_id":"holdingRegisters.40194_M_AC_Current_S_F","type":"state","common":{"name":"AC Current Scale Factor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":193,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40206_M_AC_Power: {"_id":"holdingRegisters.40206_M_AC_Power","type":"state","common":{"name":"Total Real Power (sum of active phases)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":205,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40210_M_AC_Power_SF: {"_id":"holdingRegisters.40210_M_AC_Power_SF","type":"state","common":{"name":"AC Real Power Scale Factor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":209,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40226_M_Exported: {"_id":"holdingRegisters.40226_M_Exported","type":"state","common":{"name":"Total Exported Real Energy","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":225,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40234_M_Imported: {"_id":"holdingRegisters.40234_M_Imported","type":"state","common":{"name":"Total Imported Real Energy","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":233,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.427 - debug: modbus.1 (2542) Add holdingRegisters.40242_M_Energy_W_SF: {"_id":"holdingRegisters.40242_M_Energy_W_SF","type":"state","common":{"name":"Real Energy Scale Factor","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"SF"},"native":{"regType":"holdingRegs","address":241,"deviceId":1,"type":"int16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57664_Battery_1 Device ID: {"_id":"holdingRegisters.57664_Battery_1 Device ID","type":"state","common":{"name":"Batterie Geräte ID","role":"value","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":17663,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57666_Battery_1 Rated Energy: {"_id":"holdingRegisters.57666_Battery_1 Rated Energy","type":"state","common":{"name":"Batterie Nennkapazität","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":17665,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57668_Battery_1 Max Charge Continues Power: {"_id":"holdingRegisters.57668_Battery_1 Max Charge Continues Power","type":"state","common":{"name":"Batterie maximale Ladeleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":17667,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57670_Battery_1 Max Discharge Continues Power: {"_id":"holdingRegisters.57670_Battery_1 Max Discharge Continues Power","type":"state","common":{"name":"Batterie maximale Entladeleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":17669,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57672_Battery_1 Max Charge Peak Power: {"_id":"holdingRegisters.57672_Battery_1 Max Charge Peak Power","type":"state","common":{"name":"Batterie maximale Ladespitzenleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":17671,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.428 - debug: modbus.1 (2542) Add holdingRegisters.57674_Battery_1 Max Discharge Peak Power: {"_id":"holdingRegisters.57674_Battery_1 Max Discharge Peak Power","type":"state","common":{"name":"Batterie maximale Entladespitzenleistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":17673,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57708_Battery_1 Average Temperature: {"_id":"holdingRegisters.57708_Battery_1 Average Temperature","type":"state","common":{"name":"Batterie Durchschnittstemperatur","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":17707,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57710_Battery_1 Max Temperature: {"_id":"holdingRegisters.57710_Battery_1 Max Temperature","type":"state","common":{"name":"Batterie maximale Temperatur","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"°C"},"native":{"regType":"holdingRegs","address":17709,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57712_Battery_1 Instantaneous Voltage: {"_id":"holdingRegisters.57712_Battery_1 Instantaneous Voltage","type":"state","common":{"name":"Batterie momentane Spannung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"V"},"native":{"regType":"holdingRegs","address":17711,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57714_Battery_1 Instantaneous Current: {"_id":"holdingRegisters.57714_Battery_1 Instantaneous Current","type":"state","common":{"name":"Batterie momentane Stromstärke","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"A"},"native":{"regType":"holdingRegs","address":17713,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57716_Battery_1 Instantaneous Power: {"_id":"holdingRegisters.57716_Battery_1 Instantaneous Power","type":"state","common":{"name":"Batterie momentane Leistung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"W"},"native":{"regType":"holdingRegs","address":17715,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.429 - debug: modbus.1 (2542) Add holdingRegisters.57718_Battery_1 Lifetime Export Energy Counter: {"_id":"holdingRegisters.57718_Battery_1 Lifetime Export Energy Counter","type":"state","common":{"name":"Batterie Gesamtenergie entladen","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":17717,"deviceId":1,"type":"uint64le","len":4,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57722_Battery_1 Lifetime Import Energy Counter: {"_id":"holdingRegisters.57722_Battery_1 Lifetime Import Energy Counter","type":"state","common":{"name":"Batterie Gesamtenergie geladen","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":17721,"deviceId":1,"type":"uint64le","len":4,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57726_Battery_1 Max Energy: {"_id":"holdingRegisters.57726_Battery_1 Max Energy","type":"state","common":{"name":"Batteriekapazität aktualisiert nach Alterung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":17725,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57728_Battery_1 Available Energy: {"_id":"holdingRegisters.57728_Battery_1 Available Energy","type":"state","common":{"name":"Batterie verfügbare Energie","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"Wh"},"native":{"regType":"holdingRegs","address":17727,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57730_Battery_1 State of Health (SOH): {"_id":"holdingRegisters.57730_Battery_1 State of Health (SOH)","type":"state","common":{"name":"Batterie Verhältnis von Nennkapazität zu Batteriekapazität nach Alterung","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":17729,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57732_Battery_1 State of Energy (SOE): {"_id":"holdingRegisters.57732_Battery_1 State of Energy (SOE)","type":"state","common":{"name":"Batterie Ladezustand (verfügbare Energie zu mögliche Kapazität)","role":"value","type":"number","read":true,"write":true,"def":0,"unit":"%"},"native":{"regType":"holdingRegs","address":17731,"deviceId":1,"type":"floatsw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.430 - debug: modbus.1 (2542) Add holdingRegisters.57734_Battery_1 Status: {"_id":"holdingRegisters.57734_Battery_1 Status","type":"state","common":{"name":"Batterie Zustand (0 = Aus, 1 = Standby, 2 = Initialisierung, 3 = Laden, 4 = Entladen, 5 = Fehler, 6 = Leerlauf)","role":"level","type":"number","read":true,"write":true,"def":0,"unit":""},"native":{"regType":"holdingRegs","address":17733,"deviceId":1,"type":"uint32sw","len":2,"offset":0,"factor":1,"poll":true}}
                                      2022-01-06 15:12:24.816 - info: modbus.1 (2542) Connected to slave 192.168.100.162
                                      2022-01-06 15:12:24.816 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:24.817 - debug: modbus.1 (2542) Initialization of scale factors done!
                                      2022-01-06 15:12:24.817 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:24.923 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:24.924 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:24.924 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:24.935 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:24.936 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:25.023 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:25.024 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:25.075 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:25.076 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:25.123 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:25.123 - warn: modbus.1 (2542) Poll error count: 1 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:26.175 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:26.175 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:26.184 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:26.184 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:26.185 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:26.287 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:26.287 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:26.296 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:26.296 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:26.392 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:26.393 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:26.474 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:26.474 - warn: modbus.1 (2542) Poll error count: 2 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:27.524 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:27.525 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:27.581 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:27.581 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:27.581 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:27.628 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:27.628 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:27.673 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:27.674 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:27.769 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:27.770 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:27.815 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:27.815 - warn: modbus.1 (2542) Poll error count: 3 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:28.867 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:28.867 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:28.917 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:28.917 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:28.917 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:28.926 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:28.926 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:28.970 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:28.971 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:29.027 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:29.027 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:29.087 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:29.087 - warn: modbus.1 (2542) Poll error count: 4 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:30.137 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:30.138 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:30.225 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:30.225 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:30.226 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:30.309 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:30.309 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:30.358 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:30.359 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:30.417 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:30.417 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:30.462 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:30.462 - warn: modbus.1 (2542) Poll error count: 5 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:31.512 - debug: modbus.1 (2542) [DevID_1] Poll start ---------------------
                                      2022-01-06 15:12:31.512 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN - NaN registers
                                      2022-01-06 15:12:31.544 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address NaN DONE
                                      2022-01-06 15:12:31.544 - warn: modbus.1 (2542) Null buffer length readHoldingRegisters for holdingRegs NaN
                                      2022-01-06 15:12:31.544 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 - 5 registers
                                      2022-01-06 15:12:31.593 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 189 DONE
                                      2022-01-06 15:12:31.593 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 - 5 registers
                                      2022-01-06 15:12:31.642 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 205 DONE
                                      2022-01-06 15:12:31.642 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 - 17 registers
                                      2022-01-06 15:12:31.679 - info: shelly.0 (1533) State value to set for "shelly.0.SHSW-PM#E8DB84D2FAB6#1.Relay0.longpush" has to be type "string" but received type "boolean"
                                      2022-01-06 15:12:31.743 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 225 DONE
                                      2022-01-06 15:12:31.744 - debug: modbus.1 (2542) [DevID_1/holdingRegs] Poll address 17663 - 12 registers
                                      2022-01-06 15:12:31.790 - debug: modbus.1 (2542) Received pdu describes an error.
                                      2022-01-06 15:12:31.790 - warn: modbus.1 (2542) Poll error count: 6 code: {"errorCode":131,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
                                      2022-01-06 15:12:31.842 - debug: modbus.1 (2542) Closing client on purpose.
                                      2022-01-06 15:12:31.842 - info: modbus.1 (2542) Disconnected from slave 192.168.100.162
                                      2022-01-06 15:12:31.903 - debug: modbus.1 (2542) Socket closed with error
                                      2022-01-06 15:12:31.903 - debug: modbus.1 (2542) Cleaning up request fifo.
                                      2022-01-06 15:12:32.903 - debug: modbus.1 (2542) Closing client on purpose.
                                      
                                      C 1 Reply Last reply Reply Quote 0
                                      • C
                                        ChrisL @ChrisL last edited by

                                        Update, habe nun alles ab 57 raus gelöscht - habe keine Batterie (noch nicht... :))

                                        Nun bleibt er Grün 🙂

                                        bei den Objekten bleibt aber weiterhin praktisch alles auf Orange und ohne Werte - einzig 40190 - 40242 zeigt etwas an

                                        L Glasfaser C 3 Replies Last reply Reply Quote 0
                                        • L
                                          lisalisa @ChrisL last edited by lisalisa

                                          @chrisl sagte in Solaredge Adapter (Photovoltaikanlage):

                                          Update, habe nun alles ab 57 raus gelöscht - habe keine Batterie (noch nicht... :))

                                          Nun bleibt er Grün 🙂

                                          bei den Objekten bleibt aber weiterhin praktisch alles auf Orange und ohne Werte - einzig 40190 - 40242 zeigt etwas an

                                          Dann verschieb mal die Adressen um 1

                                          1 Reply Last reply Reply Quote 0
                                          • Glasfaser
                                            Glasfaser @ChrisL last edited by

                                            @chrisl sagte in Solaredge Adapter (Photovoltaikanlage):

                                            einzig 40190 - 40242

                                            Zeige mal ein Screenshot davon

                                            C 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            425
                                            Online

                                            31.9k
                                            Users

                                            80.1k
                                            Topics

                                            1.3m
                                            Posts

                                            59
                                            431
                                            99515
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo