    Sigenstor Modbus

    This topic has been deleted. Only users with topic management privileges can see it.
    • Homoran
      Homoran Global Moderator Administrators @Matzebhv last edited by

      @matzebhv sagte in Sigenstor Modbus:

      bekomme aber nur

      bitte debug log!

      @matzebhv sagte in Sigenstor Modbus:

      Meine Settings ->

      Master wäre mMn falsch.
      ich hab da gar nicht stehen 🤔

      Geräte ID ist wirklich 1?

      keine ALIASES benutzen, wenn du schon 30003 nutzst!

      Matzebhv 1 Reply Last reply Reply Quote 0
      • Matzebhv
        Matzebhv @Homoran last edited by

        @homoran

        2
        62
        Log-Größe: 3.3 MB
        
        1
        Zeit
        debug
        Nachricht
        
        alexa2.0
        2025-05-20 18:23:51.731	info	Alexa-Push-Connection (macDms = true) established. Disable Polling
        
        alexa2.0
        2025-05-20 18:23:50.440	info	Alexa-Push-Connection disconnected - retry: Retry Connection in 1s
        
        modbus.0
        2025-05-20 18:23:42.875	debug	Closing client on purpose.
        
        modbus.0
        2025-05-20 18:23:41.874	debug	Cleaning up request fifo.
        
        modbus.0
        2025-05-20 18:23:41.874	debug	Socket closed with error
        
        modbus.0
        2025-05-20 18:23:41.855	info	Disconnected from slave 192.168.178.39
        
        modbus.0
        2025-05-20 18:23:41.855	debug	Closing client on purpose.
        
        modbus.0
        2025-05-20 18:23:41.804	warn	[DevID_1] Poll error count: 6 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:41.804	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:41.668	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:41.668	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:40.617	warn	[DevID_1] Poll error count: 5 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:40.617	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:40.508	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:40.507	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:39.456	warn	[DevID_1] Poll error count: 4 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:39.456	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:39.372	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:39.372	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:38.320	warn	[DevID_1] Poll error count: 3 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:38.320	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:38.199	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:38.198	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:37.148	warn	[DevID_1] Poll error count: 2 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:37.148	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:37.125	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:37.125	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:36.074	warn	[DevID_1] Poll error count: 1 code: {"errorCode":132,"exceptionCode":2,"message":"ILLEGAL DATA ADDRESS"}
        
        modbus.0
        2025-05-20 18:23:36.073	debug	Received pdu describes an error.
        
        modbus.0
        2025-05-20 18:23:36.057	debug	[DevID_1/inputRegs] Poll address 30003 - 1 registers
        
        modbus.0
        2025-05-20 18:23:36.057	debug	Initialization of scale factors done!
        
        modbus.0
        2025-05-20 18:23:36.056	debug	[DevID_1] Poll start ---------------------
        
        modbus.0
        2025-05-20 18:23:36.055	info	Connected to slave 192.168.178.39
        
        modbus.0
        2025-05-20 18:23:35.721	debug	Initialize Objects for holdingRegs: []
        
        modbus.0
        2025-05-20 18:23:35.720	debug	Add inputRegisters.30003_EMS_work_mode: {"_id":"inputRegisters.30003_EMS_work_mode","type":"state","common":{"name":"","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":30003,"deviceId":1,"type":"uint16le","len":1,"offset":0,"factor":1}}
        
        modbus.0
        2025-05-20 18:23:35.720	debug	Initialize Objects for inputRegs: [{"_address":"30003","deviceId":1,"name":"EMS work mode","description":"","unit":"","type":"uint16le","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":"","isScale":"","address":30003,"id":"inputRegisters.30003_EMS_work_mode"}]
        
        modbus.0
        2025-05-20 18:23:35.720	debug	Initialize Objects for coils: []
        
        modbus.0
        2025-05-20 18:23:35.719	debug	Initialize Objects for disInputs: []
        
        modbus.0
        2025-05-20 18:23:35.535	debug	Schedule restart: 0 9 * * *
        
        modbus.0
        2025-05-20 18:23:35.505	info	starting. Version 6.4.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.19.2, js-controller: 7.0.7
        
        modbus.0
        2025-05-20 18:23:34.391	debug	Plugin sentry Initialize Plugin (enabled=true)
        
        host.iOBroker
        2025-05-20 18:23:33.286	info	instance system.adapter.modbus.0 in version "6.4.0" started with pid 16220
        

        Der Inverter ist Slave, iobroker Master. Das sollte schon so passen.
        ID ist 1 laut den Einstellungen im Inverter.
        Alias aus hat leider keinen Unterschied gemacht.

        Homoran 1 Reply Last reply Reply Quote 0
        • Homoran
          Homoran Global Moderator Administrators @Matzebhv last edited by Homoran

          @matzebhv sagte in Sigenstor Modbus:

          type":"uint16le

          hat das e7nen Grund warum du little Endian nimmst?

          hab ich auf dem Microfilm
          Screenshot_20250520-182951_Firefox.jpg
          leider vorher nicht erkannt

          Matzebhv 1 Reply Last reply Reply Quote 0
          • Matzebhv
            Matzebhv @Homoran last edited by Matzebhv

            @homoran
            Oh man, jetzt gehts.

            1fffe627-8dc2-4edc-9090-d902d4122a06-image.png

            Außerdem muss für die Adressen im niedrigen Bereich die Slave-ID 247 eingestellt werden.

            Für alle Sigenstor-User:

            _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
            30554	1	Daily export energy		kWh	uint32be	2	0.01	0		level			
            30556	1	Accumulated export energy	Total Energy produced	kWh	uint64be	4	0.01	0		level			
            30560	1	Daily import energy		kWh	uint32be	2	0.01	0		level			
            30566	1	Battery daily charge energy		kWh	uint32be	2	0.01	0		level			
            30568	1	Battery accumulated charge energy		kWh	uint64be	4	0.01	0		level			
            30572	1	Battery daily discharge energy		kWh	uint32be	2	0.01	0		level			
            30574	1	Battery accumulated discharge energy		kWh	uint64be	4	0.01	0		level			
            30587	1	Active power		W	int32be	2	0	0		level			
            30602	1	Battery State of Health	Battery SOH	%	uint16be	1	0.1	0		level			
            31027	1	PV1 voltage	String Nord Voltage	V	int16be	1	0.1	0		level			
            31028	1	PV1 current	String Nord Current	A	int16be	1	0.01	0		level			
            31029	1	PV2 voltage	String Sued Voltage	V	int16be	1	0.1	0		level			
            31030	1	PV2 current	String Sued Current	A	int16be	1	0.01	0		level			
            31035	1	PV Power		W	int32be	2	0	0		level			
            30003	247	EMS work mode	0: max self consumption; 1:Sigen AI; 2:TOU, 7: Remote EMS		uint16be	1	0	0		level			
            30005	247	Grid Active Power	>0 buy from grid; <0 sell to grid	W	int32be	2	0.1	0		level			
            30009	247	On/Off Grid status	0: on grid; 1: off grid (auto); 2: off grid (manual)		uint16be	1	0.1	0		level			
            30014	247	SOC	Soc of system	%	uint16be	1	0.1	0		level			
            30015	247	L1 power	Phase 1 power	W	int32be	2	0.1	0		level			
            30017	247	L2 power	Phase 2 power	W	int32be	2	0.1	0		level			
            30019	247	L3 power	Phase 3 power	W	int32be	2	0.1	0		level			
            30027	247	Alarm (General)	If hybrid inverter has alaarm, this will be set		int32be	2	0	0		level			
            30031	247	Plant active power		W	int32be	2	0	0		level			
            30033	247	Plant reactive power		W	int32be	2	0	0		level			
            30035	247	PV power	PV Power from Roof	kW	int32be	2	0.001	0		level			
            30037	247	Battery Power	<0: discharging; >0: charging	W	int32be	2	0	0		level			
            30052	247	Grid sensor L1 active power		W	int32be	2	0	0		level			
            30054	247	Grid sensor L2 active power		W	int32be	2	0	0		level			
            30056	247	Grid sensor L3 active power		W	int32be	2	0	0		level			
            30064	247	Max charging capacity		kWh	int32be	2	0.01	0		level			
            30066	247	Max discharging capacity		kWh	int32be	2	0.01	0		level			
            30068	247	ESS charging power		kW	int32be	2	0.001	0		level			
            30070	247	ESS discharging power		kW	int32be	2	0.001	0		level		
            
            Homoran 1 Reply Last reply Reply Quote 0
            • Homoran
              Homoran Global Moderator Administrators @Matzebhv last edited by

              @matzebhv sagte in Sigenstor Modbus:

              Oh man, jetzt gehts.

              hast du nur den Haken gesetzt, oder uf das üblicherweise verwendete bigEndian umgestellt?

              Matzebhv 1 Reply Last reply Reply Quote 0
              • Matzebhv
                Matzebhv @Homoran last edited by Matzebhv

                @homoran Erst auf Big Endian, das alleine hat nicht geholfen. Die Checkbox hat es dann zum fliegen gebracht.

                L 1 Reply Last reply Reply Quote 0
                • L
                  looxer01 @Matzebhv last edited by

                  @matzebhv

                  Hi,

                  ich bin auch gerade auf Sigenergy gestoßen.
                  Die Technologie ist sehr beeindruckend und die können alles was ich gerne hätte und viel mehr. (Ich habe einige Anforderungen und bisher war Huawei am nächsten dran - Allerdings gibt es extrem schlechte Bewertungen zum Support von Huawei)

                  Der einzige Wermuttropfen ist, dass die Firma erst seit 2022 am Markt ist und es daher nicht soviel Erfahrungswerte gibt.

                  Kannst du ein paar Erfahrungen teilen ?
                  Bist du zufrieden mit der Anlage was zuverlässigkeit, effizient etc angeht ?
                  Hast du schon Erfahrungen mit dem Support gemacht ? (soll ja wesentlich besser als bei Huawei sein)
                  reichen die Modbus Daten für eine Vernünftige Visualisierung ?

                  vG Looxer

                  Matzebhv 1 Reply Last reply Reply Quote 0
                  • Matzebhv
                    Matzebhv @looxer01 last edited by Matzebhv

                    @looxer01
                    Moin,
                    sorry, jetzt erst gesehen.
                    Ich bin mit dem System mehr als zufrieden.
                    Wir haben 10,1kWp auf dem Dach, den 10 kW Inverter mit 8 kWh Batterie + Homemax TP Gateway.
                    Der Hersteller ist zwar noch recht jung und in DE noch nicht ganz so verbreitet, das sieht aber in anderen Ländern ( z.B. Australien und UK ) ganz anders aus. Da räumen die grade den Markt ab aus Gründen.
                    Im Nachgang werden wir wohl noch eine Batterie nachrüsten, da wir auch im Sommer nicht immer durch die Nacht kommen. Das hat aber natürlich immer was mit dem Stromverbrauch zu tun. Rechnen tut sich das vermutlich am Ende nicht, mich nervt das aber trotzdem 😀
                    Wichtig! Such dir einen guten Solateur, du kommst als Endkunde nicht an alle Einstellungen dran. Daher hilft ein kurzer Draht hier ungemein.
                    Über Modbus kommst du an alle benötigten Daten dran.

                    Das war der letzte ( durchwachsene ) Monat:

                    409b4e0e-36ec-40bf-95f3-3478ce0a3a21-image.png

                    L 1 Reply Last reply Reply Quote 0
                    • L
                      looxer01 @Matzebhv last edited by

                      @matzebhv
                      Hi,

                      vielen Dank für das Feedback.
                      Ein wenig nervös war ich schon aufgrund des jungen herstellers und der geringen Verbreitung.
                      Allerdings hat mich die Technik am Ende überzeugt. Es freut mich, dass du da Positives zu berichten hast.
                      Es gibt keinen Hersteller, der nur annähernd für meine Konstellation die perfekte Lösung hat, dieser schon.
                      Freut mich auch, dass es mit Modbus eine gute Integration zum ioBroker gibt.

                      Die Anlage wird Anfang September angeschlossen 🙂

                      vielen Dank fürs Feedback.

                      Looxer

                      Meine Konstellation
                      20 KW Wechselrichter (wegen der 4 MPP tracker aber auch die Ladung und Entladungskapazitäten)
                      11 kw Wallbox
                      16kwh Speicher
                      Gateway
                      15kwp pannels auf Süd-Ost ausgerichtet

                      1 Reply Last reply Reply Quote 0
                      • N P
                        N P last edited by

                        Sigenergy hat Register Total Energy produced in der Modbus Dokumentation V2.5 rausgenommen, in der V2.4 war es noch drin, ich schau mir die daten gerade näher an und versuche das Energieflussmonitoring in meiner Loxone abzubilden. Der Sigenmeter stimmt was den Momentanverbrauch angeht auch sehr gut mit dem Hauszähler überein. Problem ist das Register 30556 nachts den Batterieverbrauch als Produktion angibt zusätzlich zählt es den selben Wert auf dem Batterieverbrauchszähler. Jetzt stellt sich mir die Frage ist das absicht von Sigenergy oder ein Fehler. Falls der Solarstrom, welcher in die Batterie eingespeichert wurde hier erst gezählt würde, wenn er wieder abgegeben wird, würde es noch irgendwie sinn machen, ansonsten würde er ja doppelt gezählt. Habt ihr euch mal mit dem Register auseinandergesetzt?

                        L 1 Reply Last reply Reply Quote 0
                        • L
                          looxer01 @N P last edited by looxer01

                          @n-p
                          Hi,
                          stimmt, das Register ist nicht mehr dokumentiert.
                          Ich führe es dennoch in meinem Modbus Protokoll, nutze es aber nicht.
                          Den Wert des Registers kann ich im Moment nicht nachvollziehen, da es keine permanenten updates erhält.
                          Bekommst du die updates denn permanent ? sonst macht es im Energiefluß ja eh keinen Sinn.

                          vG Looxer

                          edit:
                          sorry, doch tatsächlich wird das register noch upgedated. Der Wert stimmt in etwa überein mit dem was die App zeigt

                          1 Reply Last reply Reply Quote 0
                          • First post
                            Last post

                          Support us

                          ioBroker
                          Community Adapters
                          Donate
                          FAQ Cloud / IOT
                          HowTo: Node.js-Update
                          HowTo: Backup/Restore
                          Downloads
                          BLOG

                          857
                          Online

                          32.3k
                          Users

                          81.0k
                          Topics

                          1.3m
                          Posts

                          4
                          12
                          679
                          Loading More Posts
                          • Oldest to Newest
                          • Newest to Oldest
                          • Most Votes
                          Reply
                          • Reply as topic
                          Log in to reply
                          Community
                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                          The ioBroker Community 2014-2023
                          logo