  4. Frage zur richtigen Konfiguration Modbus-Adapter

NEWS

  • Jahresrückblick 2025 – unser neuer Blogbeitrag ist online! ✨
    BluefoxB
    Bluefox
    16
    1
    1.0k

  • Neuer Blogbeitrag: Monatsrückblick - Dezember 2025 🎄
    BluefoxB
    Bluefox
    13
    1
    698

  • Weihnachtsangebot 2025! 🎄
    BluefoxB
    Bluefox
    25
    1
    2.0k

Frage zur richtigen Konfiguration Modbus-Adapter

Geplant Angeheftet Gesperrt Verschoben Einsteigerfragen
13 Beiträge 3 Kommentatoren 1.2k Aufrufe 2 Watching
  • Älteste zuerst
  • Neuste zuerst
  • Meiste Stimmen
Antworten
  • In einem neuen Thema antworten
Anmelden zum Antworten
Dieses Thema wurde gelöscht. Nur Nutzer mit entsprechenden Rechten können es sehen.
  • hruH hru

    Hallo zusammen,

    ich lese mit dem Modbus-Adapter den Wechselrichter Sungrow SH10RT aus.
    Im Log stehen die folgenden Einträge:

    2024-04-23 21:20:42.266 - info: host.pinas "system.adapter.modbus.0" enabled
    2024-04-23 21:20:42.347 - info: host.pinas instance system.adapter.modbus.0 started with pid 259892
    2024-04-23 21:20:44.121 - info: modbus.0 (259892) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
    2024-04-23 21:20:44.836 - info: modbus.0 (259892) Connected to slave 192.168.178.45
    2024-04-23 22:00:13.131 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
    2024-04-23 22:08:19.733 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
    2024-04-23 22:13:58.823 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
    2024-04-23 22:18:01.201 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
    2024-04-23 22:30:26.330 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
    2024-04-23 22:36:18.258 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
    

    Ist das in Ordnung so, dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

    Danke und Gruß

    Hartmut

    HomoranH Nicht stören
    HomoranH Nicht stören
    Homoran
    Global Moderator Administrators
    schrieb am zuletzt editiert von Homoran
    #2

    @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

    dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

    passiert bei mir auch ab und zu, bei dir jedoch gar nicht!

    Deine Meldungen zum Anmelden bezieht dich nicht auf Modbus sondern auf den Admin

    wer ist denn .40?

    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

    hruH 1 Antwort Letzte Antwort
    0
    • HomoranH Homoran

      @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

      dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

      passiert bei mir auch ab und zu, bei dir jedoch gar nicht!

      Deine Meldungen zum Anmelden bezieht dich nicht auf Modbus sondern auf den Admin

      wer ist denn .40?

      hruH Offline
      hruH Offline
      hru
      schrieb am zuletzt editiert von
      #3

      @homoran said in Frage zur richtigen Konfiguration Modbus-Adapter:

      @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

      dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

      passiert bei mir auch ab und zu, bei dir jedoch gar nicht!

      Deine Meldungen zum Anmelden bezieht dich nicht auf Modbus sondern auf den Admin

      wer ist denn .40?

      das ist die IP-Adresse von meinem Notebook mit dem ich mich auf den Raspi draufschalte um den iobroker zu bedienen.
      D.h. die Verbindung zwischen Raspi/iobroker und dem Notebook wird immer wieder unterbrochen? Warum?

      PV-Anlage:
      13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
      Sonstige Geräte:
      ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
      IR-Leseköpfe für Stromzähler

      HomoranH 1 Antwort Letzte Antwort
      0
      • hruH hru

        @homoran said in Frage zur richtigen Konfiguration Modbus-Adapter:

        @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

        dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

        passiert bei mir auch ab und zu, bei dir jedoch gar nicht!

        Deine Meldungen zum Anmelden bezieht dich nicht auf Modbus sondern auf den Admin

        wer ist denn .40?

        das ist die IP-Adresse von meinem Notebook mit dem ich mich auf den Raspi draufschalte um den iobroker zu bedienen.
        D.h. die Verbindung zwischen Raspi/iobroker und dem Notebook wird immer wieder unterbrochen? Warum?

        HomoranH Nicht stören
        HomoranH Nicht stören
        Homoran
        Global Moderator Administrators
        schrieb am zuletzt editiert von
        #4

        @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

        wird immer wieder unterbrochen? Warum?

        weil du den Admin wieder verlässt!??

        kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

        hruH 1 Antwort Letzte Antwort
        0
        • hruH hru

          Hallo zusammen,

          ich lese mit dem Modbus-Adapter den Wechselrichter Sungrow SH10RT aus.
          Im Log stehen die folgenden Einträge:

          2024-04-23 21:20:42.266 - info: host.pinas "system.adapter.modbus.0" enabled
          2024-04-23 21:20:42.347 - info: host.pinas instance system.adapter.modbus.0 started with pid 259892
          2024-04-23 21:20:44.121 - info: modbus.0 (259892) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
          2024-04-23 21:20:44.836 - info: modbus.0 (259892) Connected to slave 192.168.178.45
          2024-04-23 22:00:13.131 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
          2024-04-23 22:08:19.733 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
          2024-04-23 22:13:58.823 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
          2024-04-23 22:18:01.201 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
          2024-04-23 22:30:26.330 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
          2024-04-23 22:36:18.258 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
          

          Ist das in Ordnung so, dass die Verbindung immer wieder beendet und dann wieder neu aufgebaut wird?

          Danke und Gruß

          Hartmut

          ubeckerU Offline
          ubeckerU Offline
          ubecker
          schrieb am zuletzt editiert von
          #5

          @hru
          Hallo,
          arbeite dich hier mal durch. https://www.photovoltaikforum.com/thread/166134-daten-lesen-vom-sungrow-wechselrichtern-modbus/?pageNo=1
          Da findest du so ziemlich alles bezüglich der Kommunikation.

          Gruß Udo

          hruH 1 Antwort Letzte Antwort
          0
          • ubeckerU ubecker

            @hru
            Hallo,
            arbeite dich hier mal durch. https://www.photovoltaikforum.com/thread/166134-daten-lesen-vom-sungrow-wechselrichtern-modbus/?pageNo=1
            Da findest du so ziemlich alles bezüglich der Kommunikation.

            hruH Offline
            hruH Offline
            hru
            schrieb am zuletzt editiert von
            #6

            @ubecker said in Frage zur richtigen Konfiguration Modbus-Adapter:

            @hru
            Hallo,
            arbeite dich hier mal durch. https://www.photovoltaikforum.com/thread/166134-daten-lesen-vom-sungrow-wechselrichtern-modbus/?pageNo=1
            Da findest du so ziemlich alles bezüglich der Kommunikation.

            Hallo ubecker,

            ja diesen Thread kenne ich schon. Wenn ich auch nicht alles verstehe.
            Danke trotzdem für die Info.

            Gruß Hartmut

            PV-Anlage:
            13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
            Sonstige Geräte:
            ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
            IR-Leseköpfe für Stromzähler

            1 Antwort Letzte Antwort
            0
            • HomoranH Homoran

              @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

              wird immer wieder unterbrochen? Warum?

              weil du den Admin wieder verlässt!??

              hruH Offline
              hruH Offline
              hru
              schrieb am zuletzt editiert von
              #7

              @homoran said in Frage zur richtigen Konfiguration Modbus-Adapter:

              @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

              wird immer wieder unterbrochen? Warum?

              weil du den Admin wieder verlässt!??

              ich lasse das Browser-Fenster offen,
              aber vielleicht findet eine automatische Abmeldung statt, wenn man eine Zeit nichts eingegeben hat?

              PV-Anlage:
              13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
              Sonstige Geräte:
              ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
              IR-Leseköpfe für Stromzähler

              1 Antwort Letzte Antwort
              0
              • hruH Offline
                hruH Offline
                hru
                schrieb am zuletzt editiert von
                #8

                ich habe jetzt versucht auf die AC ELWA 2 per Modbus zuzugreifen.
                50ebc37a-6848-469f-8fbc-c4c5ebcbc460-image.png
                Im Log sieht man die folgenden Meldungen:

                2024-04-27 00:01:26.202 - info: host.pinas "system.adapter.modbus.1" enabled
                2024-04-27 00:01:26.249 - info: host.pinas instance system.adapter.modbus.1 started with pid 424006
                2024-04-27 00:01:28.022 - info: modbus.1 (424006) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                2024-04-27 00:01:28.357 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                2024-04-27 00:01:28.361 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                2024-04-27 00:01:38.369 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                2024-04-27 00:01:38.371 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                2024-04-27 00:01:48.377 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                2024-04-27 00:01:48.379 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                2024-04-27 00:01:58.136 - info: host.pinas "system.adapter.modbus.1" disabled
                2024-04-27 00:01:58.137 - info: host.pinas stopInstance system.adapter.modbus.1 (force=false, process=true)
                2024-04-27 00:01:58.141 - info: modbus.1 (424006) Got terminate signal TERMINATE_YOURSELF
                2024-04-27 00:01:58.145 - info: modbus.1 (424006) terminating
                2024-04-27 00:01:58.146 - info: modbus.1 (424006) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                2024-04-27 00:01:58.181 - info: host.pinas stopInstance system.adapter.modbus.1 send kill signal
                2024-04-27 00:01:58.649 - info: modbus.1 (424006) terminating
                2024-04-27 00:01:58.688 - info: host.pinas instance system.adapter.modbus.1 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                

                Ich habe noch keine Register eingetragen.
                Liegt es evtl. daran?

                Gibt es irgendwo eine Liste der Register der AC ELWA 2 als csv-Datei?

                PV-Anlage:
                13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
                Sonstige Geräte:
                ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
                IR-Leseköpfe für Stromzähler

                HomoranH 1 Antwort Letzte Antwort
                0
                • hruH Offline
                  hruH Offline
                  hru
                  schrieb am zuletzt editiert von hru
                  #9

                  Hallo zusammen,

                  ok ich habe mir eine Register-csv-Datei der AC ELWA-E besorgt und etwas angepasst.
                  (Ist noch nicht vollständig, soll aber für einen ersten Versuch reichen.)

                  _address	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
                  1000	Power	Power  (R/W)	W	uint16be	1	1	0		value		false	false
                  1001	Temp1	Temp1 (R)	°C	uint16be	1	0.1	0		value		false	false
                  1002	WW1_Temp_max	WW1 Temp max  (R/W)	°C	uint16be	1	0.1	0		value		false	false
                  1003	Status	Status (R)		uint16be	1	1	0		value		false	false
                  1004	Power_timout	Power timout  (R/W)	sec	uint16be	1	1	0		value		false	false
                  1005	Boost_mode	Boost mode  (R/W)		uint16be	1	1	0		value		false	false
                  1006	WW1_min	WW1 min  (R/W)	°C	uint16be	1	0.1	0		value		false	false
                  1007	Boost_time_1_start	Boost time 1 start  (R/W)		uint16be	1	1	0		value		false	false
                  1008	Boost_time_1_stop	Boost time 1 stop  (R/W)		uint16be	1	1	0		value		false	false
                  1009	Hour	Hour  (R/W)		uint16be	1	1	0		value		false	false
                  1010	Minute	Minute  (R/W)		uint16be	1	1	0		value		false	false
                  1011	Second	Second  (R/W)		uint16be	1	1	0		value		false	false
                  1012	Boost_activate	Boost_activate  (R/W)		uint16be	1	1	0		value		false	false
                  1013	AC ELWA2_Number	AC ELWA2_Number  (R/W)		uint16be	1	1	0		value		false	false
                  1014	max_Power	max_Power  (R/W)		uint16be	1	1	0		value		false	false
                  1015	tempchip	tempchip (R)	°C	uint16be	1	0.1	0		value		false	false
                  1016	Control_Firmware_Version	Control_Firmware_Version (R)		uint16be	1	1	0		value		false	false
                  1017	PS_firmware_version	PS_firmware_version (R)		uint16be	1	1	0		value		false	false
                  1018	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1019	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1020	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1021	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1022	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1023	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1024	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1025	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                  1026	Boost_time_2_start	Boost time 2 start  (R/W)		uint16be	1	1	0		value		false	false
                  1027	Boost_time_2_stop	Boost time 2 stop  (R/W)		uint16be	1	1	0		value		false	false
                  1028	Control_Firmware_sub_Version	Control_Firmware_sub_Version (R)		uint16be	1	1	0		value		false	false
                  1029	Control_Firmware_Update_Available	Control_Firmware_Update_Available (R)		uint16be	1	1	0		value		false	false
                  1030	Temp_2	Temp 2 (R)	°C	uint16be	1	0.1	0		value		false	false
                  1069	Meter_Power	Meter Power (R)		uint16be	1	1	0		value		false	false
                  1070	Control_type	Control type  (R/W)		uint16be	1	1	0		value		false	false
                  

                  Jetzt kommen folgende Meldungen im Log.

                  2024-04-27 01:02:31.563 - info: host.pinas "system.adapter.modbus.1" enabled
                  2024-04-27 01:02:31.614 - info: host.pinas instance system.adapter.modbus.1 started with pid 426953
                  2024-04-27 01:02:33.390 - info: modbus.1 (426953) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                  2024-04-27 01:02:34.090 - info: modbus.1 (426953) Connected to slave 192.168.178.43
                  2024-04-27 01:02:39.102 - warn: modbus.1 (426953) Error: undefined
                  2024-04-27 01:02:39.104 - error: modbus.1 (426953) Request timed out.
                  2024-04-27 01:02:39.106 - error: modbus.1 (426953) Client in error state.
                  2024-04-27 01:02:39.109 - warn: modbus.1 (426953) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                  2024-04-27 01:02:40.105 - info: modbus.1 (426953) Disconnected from slave 192.168.178.43
                  2024-04-27 01:02:50.110 - info: modbus.1 (426953) Connected to slave 192.168.178.43
                  2024-04-27 01:02:55.116 - warn: modbus.1 (426953) Error: undefined
                  2024-04-27 01:02:55.119 - error: modbus.1 (426953) Request timed out.
                  2024-04-27 01:02:55.120 - error: modbus.1 (426953) Client in error state.
                  2024-04-27 01:02:55.123 - warn: modbus.1 (426953) Poll error count: 2 code: {"err":"timeout","timeout":5000}
                  2024-04-27 01:02:56.119 - info: modbus.1 (426953) Disconnected from slave 192.168.178.43
                  2024-04-27 01:03:02.174 - info: host.pinas "system.adapter.modbus.1" disabled
                  2024-04-27 01:03:02.174 - info: host.pinas stopInstance system.adapter.modbus.1 (force=false, process=true)
                  2024-04-27 01:03:02.180 - info: modbus.1 (426953) Got terminate signal TERMINATE_YOURSELF
                  2024-04-27 01:03:02.184 - info: modbus.1 (426953) terminating
                  2024-04-27 01:03:02.186 - info: modbus.1 (426953) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                  2024-04-27 01:03:02.220 - info: host.pinas stopInstance system.adapter.modbus.1 send kill signal
                  2024-04-27 01:03:02.689 - info: modbus.1 (426953) terminating
                  2024-04-27 01:03:02.728 - info: host.pinas instance system.adapter.modbus.1 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                  2024-04-27 01:03:11.853 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
                  2024-04-27 01:04:51.364 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
                  

                  Die Verbindung kommt zustande, wird aber sofort wieder beendet.
                  Woran kann das liegen?

                  Anbei die von MyPV bereitgestellte Doku zur AC ELWA 2.

                  Könnte bitte mal jemand der das besser versteht als ich einen Blick auf die Doku und meine Register-CSV-Datei werfen, um zuerkennen, was ich ändern muss?

                  Vielen Dank vorab für jeden Tipp.

                  Gruß Hartmut

                  PV-Anlage:
                  13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
                  Sonstige Geräte:
                  ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
                  IR-Leseköpfe für Stromzähler

                  HomoranH 1 Antwort Letzte Antwort
                  0
                  • hruH hru

                    ich habe jetzt versucht auf die AC ELWA 2 per Modbus zuzugreifen.
                    50ebc37a-6848-469f-8fbc-c4c5ebcbc460-image.png
                    Im Log sieht man die folgenden Meldungen:

                    2024-04-27 00:01:26.202 - info: host.pinas "system.adapter.modbus.1" enabled
                    2024-04-27 00:01:26.249 - info: host.pinas instance system.adapter.modbus.1 started with pid 424006
                    2024-04-27 00:01:28.022 - info: modbus.1 (424006) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                    2024-04-27 00:01:28.357 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                    2024-04-27 00:01:28.361 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                    2024-04-27 00:01:38.369 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                    2024-04-27 00:01:38.371 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                    2024-04-27 00:01:48.377 - info: modbus.1 (424006) Connected to slave 192.168.178.43
                    2024-04-27 00:01:48.379 - info: modbus.1 (424006) Disconnected from slave 192.168.178.43
                    2024-04-27 00:01:58.136 - info: host.pinas "system.adapter.modbus.1" disabled
                    2024-04-27 00:01:58.137 - info: host.pinas stopInstance system.adapter.modbus.1 (force=false, process=true)
                    2024-04-27 00:01:58.141 - info: modbus.1 (424006) Got terminate signal TERMINATE_YOURSELF
                    2024-04-27 00:01:58.145 - info: modbus.1 (424006) terminating
                    2024-04-27 00:01:58.146 - info: modbus.1 (424006) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                    2024-04-27 00:01:58.181 - info: host.pinas stopInstance system.adapter.modbus.1 send kill signal
                    2024-04-27 00:01:58.649 - info: modbus.1 (424006) terminating
                    2024-04-27 00:01:58.688 - info: host.pinas instance system.adapter.modbus.1 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                    

                    Ich habe noch keine Register eingetragen.
                    Liegt es evtl. daran?

                    Gibt es irgendwo eine Liste der Register der AC ELWA 2 als csv-Datei?

                    HomoranH Nicht stören
                    HomoranH Nicht stören
                    Homoran
                    Global Moderator Administrators
                    schrieb am zuletzt editiert von
                    #10

                    @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

                    ich habe jetzt versucht auf die AC ELWA 2 per Modbus zuzugreifen.

                    ja, so sieht es bei mir auch paar mal am Tag aus.

                    @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

                    Woran kann das liegen?

                    stell mal die Instanz auf Logstufe debug. Vielleicht ist er dann gesprächiger

                    @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

                    Client in error state

                    heisst eigentlich das mit dem Gerät etwas nicht stimmt

                    kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                    1 Antwort Letzte Antwort
                    0
                    • hruH hru

                      Hallo zusammen,

                      ok ich habe mir eine Register-csv-Datei der AC ELWA-E besorgt und etwas angepasst.
                      (Ist noch nicht vollständig, soll aber für einen ersten Versuch reichen.)

                      _address	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
                      1000	Power	Power  (R/W)	W	uint16be	1	1	0		value		false	false
                      1001	Temp1	Temp1 (R)	°C	uint16be	1	0.1	0		value		false	false
                      1002	WW1_Temp_max	WW1 Temp max  (R/W)	°C	uint16be	1	0.1	0		value		false	false
                      1003	Status	Status (R)		uint16be	1	1	0		value		false	false
                      1004	Power_timout	Power timout  (R/W)	sec	uint16be	1	1	0		value		false	false
                      1005	Boost_mode	Boost mode  (R/W)		uint16be	1	1	0		value		false	false
                      1006	WW1_min	WW1 min  (R/W)	°C	uint16be	1	0.1	0		value		false	false
                      1007	Boost_time_1_start	Boost time 1 start  (R/W)		uint16be	1	1	0		value		false	false
                      1008	Boost_time_1_stop	Boost time 1 stop  (R/W)		uint16be	1	1	0		value		false	false
                      1009	Hour	Hour  (R/W)		uint16be	1	1	0		value		false	false
                      1010	Minute	Minute  (R/W)		uint16be	1	1	0		value		false	false
                      1011	Second	Second  (R/W)		uint16be	1	1	0		value		false	false
                      1012	Boost_activate	Boost_activate  (R/W)		uint16be	1	1	0		value		false	false
                      1013	AC ELWA2_Number	AC ELWA2_Number  (R/W)		uint16be	1	1	0		value		false	false
                      1014	max_Power	max_Power  (R/W)		uint16be	1	1	0		value		false	false
                      1015	tempchip	tempchip (R)	°C	uint16be	1	0.1	0		value		false	false
                      1016	Control_Firmware_Version	Control_Firmware_Version (R)		uint16be	1	1	0		value		false	false
                      1017	PS_firmware_version	PS_firmware_version (R)		uint16be	1	1	0		value		false	false
                      1018	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1019	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1020	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1021	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1022	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1023	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1024	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1025	AC ELWA2_serial_number	AC ELWA2 serial number (R)		string	2	1	0		value		false	false
                      1026	Boost_time_2_start	Boost time 2 start  (R/W)		uint16be	1	1	0		value		false	false
                      1027	Boost_time_2_stop	Boost time 2 stop  (R/W)		uint16be	1	1	0		value		false	false
                      1028	Control_Firmware_sub_Version	Control_Firmware_sub_Version (R)		uint16be	1	1	0		value		false	false
                      1029	Control_Firmware_Update_Available	Control_Firmware_Update_Available (R)		uint16be	1	1	0		value		false	false
                      1030	Temp_2	Temp 2 (R)	°C	uint16be	1	0.1	0		value		false	false
                      1069	Meter_Power	Meter Power (R)		uint16be	1	1	0		value		false	false
                      1070	Control_type	Control type  (R/W)		uint16be	1	1	0		value		false	false
                      

                      Jetzt kommen folgende Meldungen im Log.

                      2024-04-27 01:02:31.563 - info: host.pinas "system.adapter.modbus.1" enabled
                      2024-04-27 01:02:31.614 - info: host.pinas instance system.adapter.modbus.1 started with pid 426953
                      2024-04-27 01:02:33.390 - info: modbus.1 (426953) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                      2024-04-27 01:02:34.090 - info: modbus.1 (426953) Connected to slave 192.168.178.43
                      2024-04-27 01:02:39.102 - warn: modbus.1 (426953) Error: undefined
                      2024-04-27 01:02:39.104 - error: modbus.1 (426953) Request timed out.
                      2024-04-27 01:02:39.106 - error: modbus.1 (426953) Client in error state.
                      2024-04-27 01:02:39.109 - warn: modbus.1 (426953) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                      2024-04-27 01:02:40.105 - info: modbus.1 (426953) Disconnected from slave 192.168.178.43
                      2024-04-27 01:02:50.110 - info: modbus.1 (426953) Connected to slave 192.168.178.43
                      2024-04-27 01:02:55.116 - warn: modbus.1 (426953) Error: undefined
                      2024-04-27 01:02:55.119 - error: modbus.1 (426953) Request timed out.
                      2024-04-27 01:02:55.120 - error: modbus.1 (426953) Client in error state.
                      2024-04-27 01:02:55.123 - warn: modbus.1 (426953) Poll error count: 2 code: {"err":"timeout","timeout":5000}
                      2024-04-27 01:02:56.119 - info: modbus.1 (426953) Disconnected from slave 192.168.178.43
                      2024-04-27 01:03:02.174 - info: host.pinas "system.adapter.modbus.1" disabled
                      2024-04-27 01:03:02.174 - info: host.pinas stopInstance system.adapter.modbus.1 (force=false, process=true)
                      2024-04-27 01:03:02.180 - info: modbus.1 (426953) Got terminate signal TERMINATE_YOURSELF
                      2024-04-27 01:03:02.184 - info: modbus.1 (426953) terminating
                      2024-04-27 01:03:02.186 - info: modbus.1 (426953) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                      2024-04-27 01:03:02.220 - info: host.pinas stopInstance system.adapter.modbus.1 send kill signal
                      2024-04-27 01:03:02.689 - info: modbus.1 (426953) terminating
                      2024-04-27 01:03:02.728 - info: host.pinas instance system.adapter.modbus.1 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                      2024-04-27 01:03:11.853 - info: admin.0 (4139) ==> Connected system.user.admin from ::ffff:192.168.178.40
                      2024-04-27 01:04:51.364 - info: admin.0 (4139) <== Disconnect system.user.admin from ::ffff:192.168.178.40 modbus
                      

                      Die Verbindung kommt zustande, wird aber sofort wieder beendet.
                      Woran kann das liegen?

                      Anbei die von MyPV bereitgestellte Doku zur AC ELWA 2.

                      Könnte bitte mal jemand der das besser versteht als ich einen Blick auf die Doku und meine Register-CSV-Datei werfen, um zuerkennen, was ich ändern muss?

                      Vielen Dank vorab für jeden Tipp.

                      Gruß Hartmut

                      HomoranH Nicht stören
                      HomoranH Nicht stören
                      Homoran
                      Global Moderator Administrators
                      schrieb am zuletzt editiert von
                      #11

                      @hru sagte in Frage zur richtigen Konfiguration Modbus-Adapter:

                      Ist noch nicht vollständig, soll aber für einen ersten Versuch reichen.)

                      einen ersten Versuch macht man immer nur mit einem Register

                      kein Support per PN! - Fragen im Forum stellen - es gibt fast nichts, was nicht auch für andere interessant ist.

                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                      der Installationsfixer: curl -fsL https://iobroker.net/fix.sh | bash -

                      1 Antwort Letzte Antwort
                      0
                      • hruH Offline
                        hruH Offline
                        hru
                        schrieb am zuletzt editiert von
                        #12

                        Hallo,
                        ok ich habe jetzt nur noch ein Register in der Liste und den Debug-Level gesetzt.
                        Jetzt kommen folgende Meldungen im Log:

                        2024-04-27 22:17:57.601 - info: host.pinas "system.adapter.modbus.1" enabled
                        2024-04-27 22:17:57.636 - info: host.pinas instance system.adapter.modbus.1 started with pid 471073
                        2024-04-27 22:17:58.941 - debug: modbus.1 (471073) Redis Objects: Use Redis connection: 127.0.0.1:9001
                        2024-04-27 22:17:58.972 - debug: modbus.1 (471073) Objects client ready ... initialize now
                        2024-04-27 22:17:58.974 - debug: modbus.1 (471073) Objects create System PubSub Client
                        2024-04-27 22:17:58.976 - debug: modbus.1 (471073) Objects create User PubSub Client
                        2024-04-27 22:17:58.997 - debug: modbus.1 (471073) Objects client initialize lua scripts
                        2024-04-27 22:17:59.006 - debug: modbus.1 (471073) Objects connected to redis: 127.0.0.1:9001
                        2024-04-27 22:17:59.022 - debug: modbus.1 (471073) Redis States: Use Redis connection: 127.0.0.1:9000
                        2024-04-27 22:17:59.030 - debug: modbus.1 (471073) States create System PubSub Client
                        2024-04-27 22:17:59.031 - debug: modbus.1 (471073) States create User PubSub Client
                        2024-04-27 22:17:59.043 - debug: modbus.1 (471073) States connected to redis: 127.0.0.1:9000
                        2024-04-27 22:17:59.072 - debug: modbus.1 (471073) Plugin sentry Initialize Plugin (enabled=true)
                        2024-04-27 22:17:59.487 - info: modbus.1 (471073) starting. Version 6.1.0 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.20.2, js-controller: 5.0.19
                        2024-04-27 22:17:59.618 - debug: modbus.1 (471073) Initialize Objects for disInputs: []
                        2024-04-27 22:17:59.619 - debug: modbus.1 (471073) Initialize Objects for coils: []
                        2024-04-27 22:17:59.620 - debug: modbus.1 (471073) Initialize Objects for inputRegs: [{"_address":"1000","name":"Power","description":"Power (R/W)","unit":"W","type":"uint16be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"deviceId":1,"address":1000,"id":"inputRegisters.1000_Power"}]
                        2024-04-27 22:17:59.621 - debug: modbus.1 (471073) Add inputRegisters.1000_Power: {"_id":"inputRegisters.1000_Power","type":"state","common":{"name":"Power (R/W)","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"W"},"native":{"regType":"inputRegs","address":1000,"deviceId":1,"type":"uint16be","len":1,"offset":0,"factor":1}}
                        2024-04-27 22:17:59.621 - debug: modbus.1 (471073) Initialize Objects for holdingRegs: []
                        2024-04-27 22:17:59.864 - info: modbus.1 (471073) Connected to slave 192.168.178.43
                        2024-04-27 22:17:59.865 - debug: modbus.1 (471073) [DevID_1] Poll start ---------------------
                        2024-04-27 22:17:59.868 - debug: modbus.1 (471073) Initialization of scale factors done!
                        2024-04-27 22:17:59.869 - debug: modbus.1 (471073) [DevID_1/inputRegs] Poll address 1000 - 1 registers
                        2024-04-27 22:18:04.878 - warn: modbus.1 (471073) Error: undefined
                        2024-04-27 22:18:04.879 - error: modbus.1 (471073) Request timed out.
                        2024-04-27 22:18:04.879 - error: modbus.1 (471073) Client in error state.
                        2024-04-27 22:18:04.880 - warn: modbus.1 (471073) Poll error count: 1 code: {"err":"timeout","timeout":5000}
                        2024-04-27 22:18:04.883 - debug: modbus.1 (471073) Socket closed with error
                        2024-04-27 22:18:04.884 - debug: modbus.1 (471073) Clearing timeout of the current request.
                        2024-04-27 22:18:04.884 - debug: modbus.1 (471073) Cleaning up request fifo.
                        2024-04-27 22:18:05.879 - debug: modbus.1 (471073) Closing client on purpose.
                        2024-04-27 22:18:05.879 - info: modbus.1 (471073) Disconnected from slave 192.168.178.43
                        2024-04-27 22:18:15.885 - info: modbus.1 (471073) Connected to slave 192.168.178.43
                        2024-04-27 22:18:15.886 - debug: modbus.1 (471073) [DevID_1] Poll start ---------------------
                        2024-04-27 22:18:15.887 - debug: modbus.1 (471073) [DevID_1/inputRegs] Poll address 1000 - 1 registers
                        2024-04-27 22:18:20.889 - warn: modbus.1 (471073) Error: undefined
                        2024-04-27 22:18:20.891 - error: modbus.1 (471073) Request timed out.
                        2024-04-27 22:18:20.893 - error: modbus.1 (471073) Client in error state.
                        2024-04-27 22:18:20.894 - warn: modbus.1 (471073) Poll error count: 2 code: {"err":"timeout","timeout":5000}
                        2024-04-27 22:18:20.899 - debug: modbus.1 (471073) Socket closed with error
                        2024-04-27 22:18:20.900 - debug: modbus.1 (471073) Clearing timeout of the current request.
                        2024-04-27 22:18:20.901 - debug: modbus.1 (471073) Cleaning up request fifo.
                        2024-04-27 22:18:21.890 - debug: modbus.1 (471073) Closing client on purpose.
                        2024-04-27 22:18:21.892 - info: modbus.1 (471073) Disconnected from slave 192.168.178.43
                        2024-04-27 22:18:31.897 - info: modbus.1 (471073) Connected to slave 192.168.178.43
                        2024-04-27 22:18:31.900 - debug: modbus.1 (471073) [DevID_1] Poll start ---------------------
                        2024-04-27 22:18:31.901 - debug: modbus.1 (471073) [DevID_1/inputRegs] Poll address 1000 - 1 registers
                        2024-04-27 22:18:36.597 - info: host.pinas "system.adapter.modbus.1" disabled
                        2024-04-27 22:18:36.598 - info: host.pinas stopInstance system.adapter.modbus.1 (force=false, process=true)
                        2024-04-27 22:18:36.608 - info: modbus.1 (471073) Got terminate signal TERMINATE_YOURSELF
                        2024-04-27 22:18:36.611 - debug: modbus.1 (471073) Closing client on purpose.
                        2024-04-27 22:18:36.613 - info: modbus.1 (471073) terminating
                        2024-04-27 22:18:36.616 - debug: modbus.1 (471073) Plugin sentry destroyed
                        2024-04-27 22:18:36.618 - info: modbus.1 (471073) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        2024-04-27 22:18:36.628 - debug: modbus.1 (471073) Socket closed with error
                        2024-04-27 22:18:36.629 - debug: modbus.1 (471073) Clearing timeout of the current request.
                        2024-04-27 22:18:36.630 - debug: modbus.1 (471073) Cleaning up request fifo.
                        2024-04-27 22:18:36.653 - info: host.pinas stopInstance system.adapter.modbus.1 send kill signal
                        2024-04-27 22:18:37.120 - info: modbus.1 (471073) terminating
                        2024-04-27 22:18:37.159 - info: host.pinas instance system.adapter.modbus.1 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                        

                        Danke und Gruß
                        Hartmut

                        PV-Anlage:
                        13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
                        Sonstige Geräte:
                        ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
                        IR-Leseköpfe für Stromzähler

                        1 Antwort Letzte Antwort
                        0
                        • hruH Offline
                          hruH Offline
                          hru
                          schrieb am zuletzt editiert von hru
                          #13

                          Hier noch die Beschreibung meiner Infrastruktur:
                          Der AC ELWA 2 hat eine eigene IP Adresse.
                          Der AC ELWA 2 hat als Control IP Adresse die LAN-IP-Adresse des SH10RT eingetragen.
                          D.h. die Steuerdaten holt sich die AC ELWA 2 vom Wechselrichter.
                          Das funktioniert auch prima. (Überschuss wird verwendet um Wasser zu erwärmen)
                          Ich wollte jetzt die Infos per Modbus von der AC ELWA 2 auslesen.
                          In der MyPV-Cloud sind diese Infos ja auch zu sehen.
                          D.h. die AC ELWA 2 funkt diese Daten zur MyPV-Cloud.
                          c68b1e7d-ee9d-4697-912d-8c2406441dc7-image.png
                          9899d22e-9f4b-4e43-bf68-efe637a4010f-image.png
                          Nur bekomme ich mit iobroker und dem Modbus -Adapter keine Verbindung zur AC ELWA 2 hin.

                          PV-Anlage:
                          13,5 kWp, WR: Sungrow SH10RT, Speicher: Sungrow SBR128, Heizstab: MyPV AC ELWA2
                          Sonstige Geräte:
                          ShellyPlusSmoke Rauchwarnmelder, Shelly Gas Warnmelder, Shelly Flood,
                          IR-Leseköpfe für Stromzähler

                          1 Antwort Letzte Antwort
                          0
                          Antworten
                          • In einem neuen Thema antworten
                          Anmelden zum Antworten
                          • Älteste zuerst
                          • Neuste zuerst
                          • Meiste Stimmen


                          Support us

                          ioBroker
                          Community Adapters
                          Donate

                          665

                          Online

                          32.6k

                          Benutzer

                          82.0k

                          Themen

                          1.3m

                          Beiträge
                          Community
                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                          ioBroker Community 2014-2025
                          logo
                          • Anmelden

                          • Du hast noch kein Konto? Registrieren

                          • Anmelden oder registrieren, um zu suchen
                          • Erster Beitrag
                            Letzter Beitrag
                          0
                          • Home
                          • Aktuell
                          • Tags
                          • Ungelesen 0
                          • Kategorien
                          • Unreplied
                          • Beliebt
                          • GitHub
                          • Docu
                          • Hilfe