NEWS

  • UPDATE 31.10.: Amazon Alexa - ioBroker Skill läuft aus ?
    apollon77A
    apollon77
    48
    3
    8.8k

  • Monatsrückblick – September 2025
    BluefoxB
    Bluefox
    13
    1
    2.2k

  • Neues Video "KI im Smart Home" - ioBroker plus n8n
    BluefoxB
    Bluefox
    16
    1
    3.2k

Deye Wechselrichter Modbus Register beschreiben

Scheduled Pinned Locked Moved Einbindung von Geräten
230 Posts 27 Posters 59.3k Views 26 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • M Meintre 0

    @wendy2702
    Weil alle hier es geschrieben hatten. Ist der Bus auch 1,2,3 und 6,7,8 ?

    wendy2702W Offline
    wendy2702W Offline
    wendy2702
    wrote on last edited by
    #209

    @meintre-0 ok.

    Ich nutze beide Buchsen. Für das BMS das mitgelieferte Kabel, nicht drauf geachtet welche PINs belegt sind.

    Für Modbus Buchse kann ich es gerade nicht genau sagen und leider wegen Urlaub auch nicht nachschauen

    Bitte keine Fragen per PN, die gehören ins Forum!

    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

    M 1 Reply Last reply
    0
    • wendy2702W wendy2702

      @meintre-0 ok.

      Ich nutze beide Buchsen. Für das BMS das mitgelieferte Kabel, nicht drauf geachtet welche PINs belegt sind.

      Für Modbus Buchse kann ich es gerade nicht genau sagen und leider wegen Urlaub auch nicht nachschauen

      M Offline
      M Offline
      Meintre 0
      wrote on last edited by
      #210

      @wendy2702
      Danke für die Antwort, werde es mal ausprobieren.
      Schönen Urlaub wünsche ich noch.

      oberfraggerO 1 Reply Last reply
      0
      • wendy2702W Offline
        wendy2702W Offline
        wendy2702
        wrote on last edited by
        #211

        @meintre-0 Dankeschön

        Bitte keine Fragen per PN, die gehören ins Forum!

        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

        M 2 Replies Last reply
        0
        • M Meintre 0

          @wendy2702
          Danke für die Antwort, werde es mal ausprobieren.
          Schönen Urlaub wünsche ich noch.

          oberfraggerO Offline
          oberfraggerO Offline
          oberfragger
          wrote on last edited by
          #212

          @meintre-0 Wie gesagt, och habe das via Modbus-Anschluss gemacht. Und Kabel zum Akku splitten - da hast du ja die Fehler.
          Also nochmal via Modbus probieren.

          1 Reply Last reply
          0
          • wendy2702W wendy2702

            @meintre-0 Dankeschön

            M Offline
            M Offline
            Meintre 0
            wrote on last edited by
            #213

            @wendy2702
            Habe alles umgebaut und funktioniert super!

            Nochmals Danke und einen schönen Resturlaub:+1: :flushed:

            1 Reply Last reply
            0
            • wendy2702W wendy2702

              @meintre-0 Dankeschön

              M Offline
              M Offline
              Meintre 0
              wrote on last edited by Meintre 0
              #214

              @wendy2702
              Hallo Zusammen,
              habe jetzt herausgefunden, wie man "SamrtLoad-Einrichtung" umschalten kann.
              Also von
              Generator Input -> 000000000
              SmartLoad Output -> 000000001
              Miclnv Input. -> 000000002

              umschalten kann. Eventuell hilft es jemanden.

              Alias.png

              Register.png

              wendy2702W 1 Reply Last reply
              0
              • M Meintre 0

                @wendy2702
                Hallo Zusammen,
                habe jetzt herausgefunden, wie man "SamrtLoad-Einrichtung" umschalten kann.
                Also von
                Generator Input -> 000000000
                SmartLoad Output -> 000000001
                Miclnv Input. -> 000000002

                umschalten kann. Eventuell hilft es jemanden.

                Alias.png

                Register.png

                wendy2702W Offline
                wendy2702W Offline
                wendy2702
                wrote on last edited by
                #215

                @meintre-0 Danke.

                Meiner hängt nur Netz parallel ohne PV zum Akku laden/entladen.

                Ich stelle da aktuell nichts um sondern lasse einfach machen.

                Bitte keine Fragen per PN, die gehören ins Forum!

                Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                M 1 Reply Last reply
                0
                • wendy2702W wendy2702

                  @meintre-0 Danke.

                  Meiner hängt nur Netz parallel ohne PV zum Akku laden/entladen.

                  Ich stelle da aktuell nichts um sondern lasse einfach machen.

                  M Offline
                  M Offline
                  Meintre 0
                  wrote on last edited by
                  #216

                  @wendy2702
                  Ich habe:

                  1 x Senec mit 7,5 kWh Batterie und 9,5 kWp Solar
                  1 x Deye mit 12,5 kWh Batterie und 3 kWp Solar
                  1 x Zendure AIO 2400 als Balkonanlage mit 2,4 kWh Batterie.

                  Die Senec kann ich nicht Steuern. Dadurch lädt sie teilweise die Deye Batterie über Nacht.
                  Jetzt nicht mehr, durch das Umschalten!

                  1 Reply Last reply
                  0
                  • miaelM miael

                    Inzwischen habe ich meinen Anschluss noch aufgeräumt.
                    Vom BMS Port mit einem Adapter auf Schraubpins. Daran sind dann nur die Leitungen zum BMS und zum Modbus Adapter angeschlossen. 12Volt kommt direkt vom Inverter:
                    IMG_20230809_091040.jpg

                    Die Stromversorgung werde ich noch auf extern ändern, damit ich den WR auch per Modbus an und ausschalten kann.

                    Hier meine Iobroker Einstellunge:
                    Unbenannt1.JPG

                    Unbenannt2.JPG

                    Hier die vom Elfin:
                    Unbenannt3.JPG

                    Und hier noch Bsp für die Register:
                    60713d9f-52be-4c2c-a246-3fbfbaac1456-grafik.png

                    wendy2702W Offline
                    wendy2702W Offline
                    wendy2702
                    wrote on last edited by
                    #217

                    @miael sagte in Deye Wechselrichter Modbus Register beschreiben:

                    Die Stromversorgung werde ich noch auf extern ändern, damit ich den WR auch per Modbus an und ausschalten kann.

                    Hi, wie genau schaltest du den WR aus?

                    @uweklatt sagte in Deye Wechselrichter Modbus Register beschreiben:

                    Hallo Deye-Experten,

                    wie sind die Fehlermeldungen in Register 40555 - 40558 zu interpretieren?
                    Es gibt eine Fehlerliste mit 64 verschiedenen Meldungen, aber wie stellen sich diese in den 4 Registern dar?

                    Uwe

                    EDIT:
                    ​Anscheinend werden die 64 Meldungen einfach als jeweils 1 Bit in den 4 Registern dargestellt.
                    ​Problem gelöst ;-)

                    Bekommst du über die Register die Detailierten Fehler/Alarme?

                    Bitte keine Fragen per PN, die gehören ins Forum!

                    Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                    uweklattU 1 Reply Last reply
                    0
                    • wendy2702W wendy2702

                      @miael sagte in Deye Wechselrichter Modbus Register beschreiben:

                      Die Stromversorgung werde ich noch auf extern ändern, damit ich den WR auch per Modbus an und ausschalten kann.

                      Hi, wie genau schaltest du den WR aus?

                      @uweklatt sagte in Deye Wechselrichter Modbus Register beschreiben:

                      Hallo Deye-Experten,

                      wie sind die Fehlermeldungen in Register 40555 - 40558 zu interpretieren?
                      Es gibt eine Fehlerliste mit 64 verschiedenen Meldungen, aber wie stellen sich diese in den 4 Registern dar?

                      Uwe

                      EDIT:
                      ​Anscheinend werden die 64 Meldungen einfach als jeweils 1 Bit in den 4 Registern dargestellt.
                      ​Problem gelöst ;-)

                      Bekommst du über die Register die Detailierten Fehler/Alarme?

                      uweklattU Offline
                      uweklattU Offline
                      uweklatt
                      wrote on last edited by
                      #218

                      @wendy2702
                      Man bekommt über Modbus nur die Bits.
                      Die Zuordnung zu den Fehlern bekommt man dann aus der Dokumentation.

                      Tschau
                      Uwe

                      Proxmox/LXC/Docker

                      wendy2702W 1 Reply Last reply
                      0
                      • uweklattU uweklatt

                        @wendy2702
                        Man bekommt über Modbus nur die Bits.
                        Die Zuordnung zu den Fehlern bekommt man dann aus der Dokumentation.

                        Tschau
                        Uwe

                        wendy2702W Offline
                        wendy2702W Offline
                        wendy2702
                        wrote on last edited by
                        #219

                        @uweklatt danke.

                        Hast du die Doku oder gibt es die hier irgendwo?

                        Bitte keine Fragen per PN, die gehören ins Forum!

                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                        TheBamT 1 Reply Last reply
                        0
                        • wendy2702W wendy2702

                          @uweklatt danke.

                          Hast du die Doku oder gibt es die hier irgendwo?

                          TheBamT Offline
                          TheBamT Offline
                          TheBam
                          wrote on last edited by
                          #220

                          @wendy2702 in den neuen Anleitungen sind die Fehler hinten aufgeführt

                          1 Reply Last reply
                          0
                          • wendy2702W Offline
                            wendy2702W Offline
                            wendy2702
                            wrote on last edited by
                            #221

                            In meiner Anleitung ist mein Fehler/Alarm leider nicht aufgeführt.

                            Da scheint Software und Papier nicht zusammen zu passen

                            Bitte keine Fragen per PN, die gehören ins Forum!

                            Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                            TheBamT 1 Reply Last reply
                            0
                            • wendy2702W wendy2702

                              In meiner Anleitung ist mein Fehler/Alarm leider nicht aufgeführt.

                              Da scheint Software und Papier nicht zusammen zu passen

                              TheBamT Offline
                              TheBamT Offline
                              TheBam
                              wrote on last edited by
                              #222

                              @wendy2702 Kommt drauf an von wann deine Daten sind.

                              1 Reply Last reply
                              0
                              • I Offline
                                I Offline
                                iose
                                wrote on last edited by
                                #223

                                Bei 2 WR im Master/Slave Betrieb. Benötige ich dann 2 Modubs Ausleser oder kann alles über einen am Master ausgelesen werden?

                                TheBamT W 2 Replies Last reply
                                0
                                • I iose

                                  Bei 2 WR im Master/Slave Betrieb. Benötige ich dann 2 Modubs Ausleser oder kann alles über einen am Master ausgelesen werden?

                                  TheBamT Offline
                                  TheBamT Offline
                                  TheBam
                                  wrote on last edited by
                                  #224

                                  @iose
                                  Geht beides. Reicht auch ein Modbus ausleser

                                  1 Reply Last reply
                                  0
                                  • I iose

                                    Bei 2 WR im Master/Slave Betrieb. Benötige ich dann 2 Modubs Ausleser oder kann alles über einen am Master ausgelesen werden?

                                    W Offline
                                    W Offline
                                    warp735
                                    wrote on last edited by
                                    #225

                                    @iose
                                    Kein Problem an der BMS Buchse. An der Modebus Buchse geht nur der Master

                                    1 Reply Last reply
                                    0
                                    • wendy2702W Offline
                                      wendy2702W Offline
                                      wendy2702
                                      wrote on last edited by
                                      #226

                                      Muss nochmal Fragen ob hier jemand die Akku Daten (Details) irgendwie direkt aus dem Deye ausliest und wenn ja an welchem Anschluß.

                                      Mit Solarassistant funktioniert das derzeit bei mir mit folgendem Setup:

                                      Felicity Akku per CAN Bus Kabel mit dem Deye verbunden und das Kommunikations Protokoll auf "0" --> Pylon eingestellt.
                                      Dann per RS485 an den letzten Akku Block und dort an den freien BMS Port der zum nächsten Akku Block geht.

                                      Sieht dann so aus:

                                      290662b1-a6c8-4f01-88df-bbb2b594f390-grafik.png

                                      Ich habe aber eigentlich keine Lust mir mit Sa ein weiteres System ins Haus zu holen um die Akkus zu überwachen, deshalb bin ich an einer möglichen Lösung per IOB interessiert.

                                      Bitte keine Fragen per PN, die gehören ins Forum!

                                      Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                      1 Reply Last reply
                                      0
                                      • wendy2702W Offline
                                        wendy2702W Offline
                                        wendy2702
                                        wrote on last edited by
                                        #227

                                        @uweklatt @TheBam

                                        Habt ihr eine Anleitung in der auch die Bits für die Alarme erklärt sind?

                                        @uweklatt sagte in Deye Wechselrichter Modbus Register beschreiben:

                                        @wendy2702
                                        Man bekommt über Modbus nur die Bits.
                                        Die Zuordnung zu den Fehlern bekommt man dann aus der Dokumentation.

                                        Tschau
                                        Uwe

                                        Bitte keine Fragen per PN, die gehören ins Forum!

                                        Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                        1 Reply Last reply
                                        0
                                        • W Waly_de

                                          @thebam Ich hab mal ein wenig weiter gemacht und getestet. Klappt ganz gut, auch ohne Formeln.
                                          Ich hab auch die Register zum Schreiben eingefügt. Was mir großen Spaß macht: Mit "Fernsperre" und "SchalterModus" kann man den WR ein und aus schalten. (Nur vorher den Beeper abstellen denn er geht dann in Störung, so lange er abgeschaltet ist. ;-)

                                          Auch die Netzspeisung lässt sich nun schön fernsteuern. Das könnte vor allem für Leute mit dynamischen Stromtarifen (Timber & Co) eine Freude sein.

                                          Ich hab angefangen in Vis eine Oberfläche zum steuern zu bauen... klappt schon mal prima ;-) Bildschirmfoto 2023-07-28 um 14.22.12.jpg

                                          hier meine überarbeiteten Definitionen:

                                          _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                                          40001	1	Device type	Gerätetyp		uint16be	1	0	0		level		true	false	false	false
                                          40004	1	Seriennummer	Seriennummer		string	5	0	0		state		true	false	false	false
                                          40061	1	Fernsperre	Fernsperre		uint16be	1	0	0		level		true	false	false	false
                                          40081	1	SchalterModus	SchalterModus		uint16be	1	0	0		level		true	false	false	false
                                          40105	1	ZeroExport power	ZeroExport-Leistung	W	int16be	1	0	0		level		true	false	false	false
                                          40109	1	Max A Charge	Maximaler Ladestrom der Batterie	A	int16be	1	0	0		level		true	false	false	false
                                          40110	1	Max A discharge	Max A Entladung	A	int16be	1	0	0		level		true	false	false	false
                                          40122	1	Max-Gen-Time	Max-Gen-Time	h	int16be	1	0,1	0		level		true	false	false	false
                                          40123	1	Gen-Cool-Time	Gen-Cool-Time	h	int16be	1	0,1	0		level		true	false	false	false
                                          40124	1	Gen-Start-Volt	Gen-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
                                          40125	1	Gen-Start-Proz	Gen-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
                                          40126	1	Gen-Charge-Current	Gen-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
                                          40127	1	Grid-Start-Volt	Grid-Start-Volt	V	int16be	1	0,01	0		level		true	false	false	false
                                          40128	1	Grid-Start-Proz	Grid-Start-Proz	%	int16be	1	0	0		level		true	false	false	false
                                          40129	1	Grid-Charge-Current	Grid-Charge-Current	A	int16be	1	0	0		level		true	false	false	false
                                          40130	1	Gen-Charge-Enable	Gen-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
                                          40131	1	Grid-Charge-Enable	Grid-Charge-Enable		uint16be	1	0	0		level		true	false	false	false
                                          40144	1	Max Limit Power Output Grid Connection	Begrenzen Sie die maximale Ausgangsleistung des Netzes	W	int16be	1	0	0		level		true	false	false	false
                                          40145	1	External current sensor clamp phase	Klemmphase des externen Stromsensors	W	int16be	1	0	0		level		true	false	false	false
                                          40146	1	Solar sell	Verkauf von Solar		uint8be	1	0	0		value		true	false	false	false
                                          40147	1	TOUBits	TOUBits	Bits	uint8be	1	0	0		value		true	false	false	false
                                          40149	1	Sell mode time point 1	Sell mode time point 1		int16be	1	0	0		level		true	false	false	false
                                          40150	1	Sell mode time point 2	Sell mode time point 2		int16be	1	0	0		level		true	false	false	false
                                          40151	1	Sell mode time point 3	Sell mode time point 3		int16be	1	0	0		level		true	false	false	false
                                          40152	1	Sell mode time point 4	Sell mode time point 4		int16be	1	0	0		level		true	false	false	false
                                          40153	1	Sell mode time point 5	Sell mode time point 5		int16be	1	0	0		level		true	false	false	false
                                          40154	1	Sell mode time point 6	Sell mode time point 6		int16be	1	0	0		level		true	false	false	false
                                          40155	1	BatMaxPower1	BatMaxPower1	W	int16be	1	0	0		level		true	false	false	false
                                          40156	1	BatMaxPower2	BatMaxPower2	W	int16be	1	0	0		level		true	false	false	false
                                          40157	1	BatMaxPower3	BatMaxPower3	W	int16be	1	0	0		level		true	false	false	false
                                          40158	1	BatMaxPower4	BatMaxPower4	W	int16be	1	0	0		level		true	false	false	false
                                          40159	1	BatMaxPower5	BatMaxPower5	W	int16be	1	0	0		level		true	false	false	false
                                          40160	1	BatMaxPower6	BatMaxPower6	W	int16be	1	0	0		level		true	false	false	false
                                          40167	1	BatProz1	BatProz1	%	int16be	1	0	0		level		true	false	false	false
                                          40168	1	BatProz2	BatProz2	%	int16be	1	0	0		level		true	false	false	false
                                          40169	1	BatProz3	BatProz3	%	int16be	1	0	0		level		true	false	false	false
                                          40170	1	BatProz4	BatProz4	%	int16be	1	0	0		level		true	false	false	false
                                          40171	1	BatProz5	BatProz5	%	int16be	1	0	0		level		true	false	false	false
                                          40172	1	BatProz6	BatProz6	%	int16be	1	0	0		level		true	false	false	false
                                          40173	1	GridGenEn1	GridGenEn1	Bits	int16be	1	0	0		level		true	false	false	false
                                          40174	1	GridGenEn2	GridGenEn2	Bits	int16be	1	0	0		level		true	false	false	false
                                          40175	1	GridGenEn3	GridGenEn3	Bits	int16be	1	0	0		level		true	false	false	false
                                          40176	1	GridGenEn4	GridGenEn4	Bits	int16be	1	0	0		level		true	false	false	false
                                          40177	1	GridGenEn5	GridGenEn5	Bits	int16be	1	0	0		level		true	false	false	false
                                          40178	1	GridGenEn6	GridGenEn6	Bits	int16be	1	0	0		level		true	false	false	false
                                          40341	1	Max Solar Sell Power at Zero grid	Maximale Solarverkaufsleistung bei null einspeisung	W	int16be	1	0	0		level		true	false	false	false
                                          40341	1	Max Solar Sell Power by full in	Maximale Solarverkaufsleistung bei einspeisung	W	int16be	1	0	0		level		true	false	false	false
                                          40501	1	Status	Status (Standby, check, norm, altert, fault)		int16be	1	0	0		level		true	false	false	false
                                          40502	1	active power generation of today	active power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
                                          40503	1	reactive power generation of today	reactive power generation of today	kwh	int16be	1	0,1	0		level		true	false	false	false
                                          40504	1	Grid connection time of today	Grid connection time of today	s	uint16be	1	1	0		level		true	false	false	false
                                          40515	1	Today charge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40516	1	Today discharge of the battery 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40517	1	Total charge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40518	1	Total charge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40519	1	Total discharge of the battery low byte 	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40520	1	Total discharge of the battery high byte	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40521	1	Day Grid Buy Power kWh	Tag Netzabnahme Strom Wh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40522	1	Day_GridSell_Power kWh	Tages Verkaufs leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40523	1	Total_GridBuy_Power kWh_low word	Total_GridBuy_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40524	1	Total_GridBuy_Power kWh_high word	Total_GridBuy_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40525	1	Total_GridSell_Power kWh_low word	Total_GridSell_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40526	1	Total_GridSell_Power kWh_high word	Total_GridSell_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40527	1	Day_Load_Power kWH	Day_Load_Power kWH	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40528	1	Total_Load_Power kWh_low word	Total_Load_Power kWh_low word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40529	1	Total_Load_Power kWh_high word	Total_Load_Power kWh_high word	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40530	1	Day_PV_Power kWh	Tagesproduzierte leistung	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40531	1	Day_PV-1_Power kWh	Day_PV-1_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40532	1	Day_PV-2_Power kWh	Day_PV-2_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40533	1	Day_PV-3_Power kWh	Day_PV-3_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40534	1	Day_PV-4_Power kWh	Day_PV-4_Power kWh	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40535	1	Total PV power Wh low word	Gesamt-PV-Leistung Wh niedriges Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40536	1	Total PV power Wh high word	Gesamt-PV-Leistung Wh hohes Wort	kwh	uint16be	1	0,1	0		level		true	false	false	false
                                          40587	1	battery temperature	Batterietemperatur	°C	int16be	1	0,01	10		level		true	false	false	false
                                          40588	1	battery voltage	Batteriespannung	V	int16be	1	0,01	0		level		true	false	false	false
                                          40589	1	battery capacity	Batteriekapazität	%	int16be	1	1	0		level		true	false	false	false
                                          40591	1	Battery output power	Ausgangsleistung der Batterie	W	int16be	1	1	0		level		true	false	false	false
                                          40592	1	Battery output current	Ausgangsstrom der Batterie	A	int16be	1	0,01	0		level		true	false	false	false
                                          40593	1	Corrected AH	AH korrigiert	AH	int16be	1	1	0		level		true	false	false	false
                                          40599	1	Grid phase voltage A	Netzphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40600	1	Grid phase voltage B	Netzphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40601	1	Grid phase voltage C	Netzphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40602	1	Grid line voltage AB	Netzphasenspannung L1-L2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40603	1	Grid line voltage BC	Netzphasenspannung L2-L3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40604	1	Grid line voltage CA	Netzphasenspannung L3-L1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40605	1	L1 phase power on the inner side of the grid	L1 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                          40606	1	L2 phase power on the inner side of the grid	L2 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                          40607	1	L3 phase power on the inner side of the grid	L3 Phasenleistung auf der Innenseite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                          40608	1	active power from side to side of the grid	Wirkleistung von Seite zu Seite des Netzes	W	int16be	1	1	0		level		true	false	false	false
                                          40609	1	Grid side - inside total apparent power	Netzseite – innere Gesamtscheinleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40610	1	Grid-side frequency	Grid Seite Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                          40611	1	grid side inner current L1	netzseitiger Innenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
                                          40612	1	grid side inner current L2	netzseitiger Innenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
                                          40613	1	grid side inner current L3	netzseitiger Innenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
                                          40614	1	Out-of-grid - current L1	Außerhalb des Netzes – aktuelles L1	A	int16be	1	0,01	0		level		true	false	false	false
                                          40615	1	Out-of-grid - current L2	Außerhalb des Netzes – aktuelles L2	A	int16be	1	0,01	0		level		true	false	false	false
                                          40616	1	Out-of-grid - current L3	Außerhalb des Netzes – aktuelles L3	A	int16be	1	0,01	0		level		true	false	false	false
                                          40617	1	A Out-of-grid -power L1	A Außerhalb des Netzes - Strom L1	W	int16be	1	1	0		level		true	false	false	false
                                          40618	1	A Out-of-grid -power L2	A Außerhalb des Netzes - Strom L2	W	int16be	1	1	0		level		true	false	false	false
                                          40619	1	A Out-of-grid -power L3	A Außerhalb des Netzes - Strom L3	W	int16be	1	1	0		level		true	false	false	false
                                          40620	1	Out-of-grid-total-power	Außerhalb des Netzes - Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40621	1	Out-of-grid-total-apparent-power	Außerhalb des Netzes - Gesamtscheinleistung	VA	uint16le	1	1	0		level		true	false	false	false
                                          40622	1	Grid-connected power factor PF	Netzgekoppelter Leistungsfaktor PF		int16be	1	1	0		level		true	false	false	false
                                          40623	1	Grid side A-phase power	Netzseitiger L1-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                          40624	1	Grid side B-phase power	Netzseitiger L2-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                          40625	1	Grid side C-phase power	Netzseitiger L3-Phasen-Strom	W	int16be	1	1	0		level		true	false	false	false
                                          40626	1	Grid side total power	Netzseitige Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40628	1	Inverter output phase voltage A	Wechselrichter-Ausgangsphasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40629	1	Inverter output phase voltage B	Wechselrichter-Ausgangsphasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40630	1	Inverter output phase voltage C	Wechselrichter-Ausgangsphasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40631	1	Inverter output phase current A	Ausgangsphasenstrom des Wechselrichters L1	A	int16be	1	0,01	0		level		true	false	false	false
                                          40632	1	Inverter output phase current B	Ausgangsphasenstrom des Wechselrichters L2	A	int16be	1	0,01	0		level		true	false	false	false
                                          40633	1	Inverter output phase current C	Ausgangsphasenstrom des Wechselrichters L3	A	int16be	1	0,01	0		level		true	false	false	false
                                          40634	1	Inverter output phase power A	Ausgangsphase des Wechselrichters Macht L1	W	int16be	1	1	0		level		true	false	false	false
                                          40635	1	Inverter output phase power B	Ausgangsphase des Wechselrichters Macht L2	W	int16be	1	1	0		level		true	false	false	false
                                          40636	1	Inverter output phase power C	Ausgangsphase des Wechselrichters Leistung L3	W	int16be	1	1	0		level		true	false	false	false
                                          40637	1	Inverter output total power	Gesamtleistung des Wechselrichters Leistung	W	int16be	1	1	0		level		true	false	false	false
                                          40638	1	Inverter output total apparent power	Gesamtleistung des Wechselrichters Scheinleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40639	1	Inverter frequency	Wechselrichter frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                          40641	1	UPS load-side phase power A	USV-lastseitige Phasenleistung L1	W	int16be	1	1	0		level		true	false	false	false
                                          40642	1	UPS load-side phase power B	USV-lastseitige Phasenleistung L2	W	int16be	1	1	0		level		true	false	false	false
                                          40643	1	UPS load-side phase power C	USV-lastseitige Phasenleistung L3	W	int16be	1	1	0		level		true	false	false	false
                                          40644	1	UPS load-sidetotal power	Lastseitige Gesamtleistung der USV	W	int16be	1	1	0		level		true	false	false	false
                                          40645	1	Load phase voltage A	Load phasenspannung L1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40646	1	Load phase voltage B	Load phasenspannung L2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40647	1	Load phase voltage C	Load phasenspannung L3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40648	1	Load phase current A	Load phasenstrom L1	A	int16be	1	0,01	0		level		true	false	false	false
                                          40649	1	Load phase current B	Load phasenstrom L2	A	int16be	1	0,01	0		level		true	false	false	false
                                          40650	1	Load phase current C	Load phasenstrom L3	A	int16be	1	0,01	0		level		true	false	false	false
                                          40651	1	Load phase power A	Load phase Leistung L1	W	int16be	1	1	0		level		true	false	false	false
                                          40652	1	Load phase power B	Load phase Leistung L2	W	int16be	1	1	0		level		true	false	false	false
                                          40653	1	Load phase power C	Load phase Leistung L3	W	int16be	1	1	0		level		true	false	false	false
                                          40654	1	Load totalpower	Load Gesamtleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40655	1	Load phase apparent power	Scheinleistung der Lastphase	VA	int16be	1	1	0		level		true	false	false	false
                                          40656	1	Load frequency	Load Frequenz	Hz	int16be	1	0,01	0		level		true	false	false	false
                                          40662	1	Phase voltage of Gen port A	Phasenspannung von Gen-Port L1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40663	1	Phase voltage of Gen port B	Phasenspannung von Gen-Port L2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40664	1	Phase voltage of Gen port C	Phasenspannung von Gen-Port L3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40665	1	Phase power of Gen port A	Phasenleistung von Gen-Port L1	W	int16be	1	1	0		level		true	false	false	false
                                          40666	1	Phase power of Gen port B	Phasenleistung von Gen-Port L2	W	int16be	1	1	0		level		true	false	false	false
                                          40667	1	Phase power of Gen port C	Phasenleistung von Gen-Port L3	W	int16be	1	1	0		level		true	false	false	false
                                          40668	1	total power of Gen port	Gesamtleistung des Gen-Ports	W	int16be	1	1	0		level		true	false	false	false
                                          40673	1	PV1 input power	PV1 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40674	1	PV2 input power	PV2 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40675	1	PV3 input power	PV3 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40676	1	PV4 input power	PV4 Eingangsleistung	W	int16be	1	1	0		level		true	false	false	false
                                          40677	1	Dc voltage 1	Gleichspannung 1	V	int16be	1	0,1	0		level		true	false	false	false
                                          40678	1	Dc current 1	Gleichstrom 1	A	int16be	1	0,1	0		level		true	false	false	false
                                          40679	1	Dc voltage 2	Gleichspannung 2	V	int16be	1	0,1	0		level		true	false	false	false
                                          40680	1	Dc current 2	Gleichstrom 2	A	int16be	1	0,1	0		level		false	false	false	false
                                          40681	1	Dc voltage 3	Gleichspannung 3	V	int16be	1	0,1	0		level		true	false	false	false
                                          40682	1	Dc current 3	Gleichstrom 3	A	int16be	1	0,1	0		level		false	false	false	false
                                          40683	1	Dc voltage 4	Gleichspannung 4	V	int16be	1	0,1	0		level		true	false	false	false
                                          40684	1	Dc current 4	Gleichstrom 4	A	int16be	1	0,1	0		level		false	false	false	false
                                          

                                          Viel spaß Damit ;-)
                                          VG Markus

                                          wendy2702W Offline
                                          wendy2702W Offline
                                          wendy2702
                                          wrote on last edited by
                                          #228

                                          @waly_de sagte in Deye Wechselrichter Modbus Register beschreiben:

                                          Ich hab angefangen in Vis eine Oberfläche zum steuern zu bauen... klappt schon mal prima ;-) Bildschirmfoto 2023-07-28 um 14.22.12.jpg

                                          Magst du davon mal einen Export bereitstellen?

                                          Bitte keine Fragen per PN, die gehören ins Forum!

                                          Benutzt das Voting rechts unten im Beitrag wenn er euch geholfen hat.

                                          1 Reply Last reply
                                          0
                                          Reply
                                          • Reply as topic
                                          Log in to reply
                                          • Oldest to Newest
                                          • Newest to Oldest
                                          • Most Votes


                                          Support us

                                          ioBroker
                                          Community Adapters
                                          Donate

                                          855

                                          Online

                                          32.4k

                                          Users

                                          81.5k

                                          Topics

                                          1.3m

                                          Posts
                                          Community
                                          Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen | Einwilligungseinstellungen
                                          ioBroker Community 2014-2025
                                          logo
                                          • Login

                                          • Don't have an account? Register

                                          • Login or register to search.
                                          • First post
                                            Last post
                                          0
                                          • Home
                                          • Recent
                                          • Tags
                                          • Unread 0
                                          • Categories
                                          • Unreplied
                                          • Popular
                                          • GitHub
                                          • Docu
                                          • Hilfe